Post by tk096 on Sm3_math CODESYS Forge talk (Post)
Hi, SM3_Math is actually an internal library of SoftMotion. You can use it. The only restriction is that there is no compatibility guarantee - meaning that POUs in the library may change their interface, get moved/renamed/removed... in future versions of SoftMotion.
Last updated: 2025-03-19

Post by pistola on C0357: "GetNextClient" is obsolete, use VisuUtils instead CODESYS Forge talk (Post)
I'm having some troubles with this same issue and I'm wondering if someone can help me out. On a settings visual I allow the operator to enter some values however if they activate the page change button it will change the change with the Numpad dialog open. Since I'm using Visuelems.CURRENTVISU to change the pages I came across this code noted below for determining if the Numpad dialog was active. This code worked great however now in 3.5.19 it's now obsolete. I've tried following the directions in the attached program above however I can't see to get it to work in my program. Can anyone provide some help to determine if a dialog is open? FUNCTION Check_Dialog_Open : Bool VAR_INPUT sDialogName : STRING; // Input variable for the name of the dialog END_VAR VAR pstClientData : POINTER TO VisuElems.VisuStructClientData; // Pointer to the client data structure itfDialogManager : VisuElems.IDialogManager; // Interface for the dialog manager itfMyDialog : VisuElems.IVisualisationDialog; // Interface for the specific visualisation dialog END_VAR // Begin the iteration over the client manager VisuElems.g_ClientManager.BeginIteration(); // Loop through each client until no more clients are found WHILE (pstClientData := VisuElems.VisuElemBase.g_ClientManager.GetNextClient()) <> 0 DO // Get the dialog manager interface itfDialogManager := VisuElems.g_VisuManager.GetDialogManager(); // Get the specific dialog interface using the dialog name itfMyDialog := itfDialogManager.GetDialog(sDialogName); // Check if the dialog is open for the current client Check_Dialog_Open := VisuDialogs.VisuDlgUtil_IsDialogOpen(itfMyDialog, pstClientData, itfDialogManager); // If the dialog is open, exit the loop IF Check_Dialog_Open THEN EXIT; END_IF END_WHILE
Last updated: 2025-03-27

Post by eschwellinger on Accessing parameters from a structure or function block with the web interface CODESYS Forge talk (Post)
yes, but you could use a demo project in the analyzer to check other types: https://analyzer-eu.automation-server.com/help/en/tags this should work.
Last updated: 2025-12-02

Post by alexgooi on Codesys KNX implementation CODESYS Forge talk (Post)
Dear Forum, For anyone interested we have solved this problem. Before we were using a KNX TP/IP interface, now we are using a KNX TP/IP router, and it works like a charm now.
Last updated: 2026-03-04

Post by alexgooi on Modbus writing on value change CODESYS Forge talk (Post)
Hi Duvan, You could make this in 1 single object (FB), Indeed don't use a function for this beacuse you need some memory to keep the old value. For i := 0 TO 200 BY 1 DO //Check if the value has been changed IF Old_Value[i] <> Value[i] THEN //Set the trigger to TRUE Trigger[i] := TRUE; Old_Value[i] := Value[i]; END_IF END_FOR If you define the Value array as an In_Out and the Trigger as an In_Out you arn't claiming any aditional memory to your system. You ofcourse then need to add some code arround it that does something with the trigger and writes it back to FALSE again. If you want more flexability you also could use pointers instead of using the IN_OUT FOR i := 0 TO 200 BY 1 DO address := address_Input + i * SIZEOF(*Put type here); IF Address^ <> Old_Value[i] THEN Trigger[i] := TRUE; Old_Value[i] := Address^; END_IF END_FOR
Last updated: 2024-04-02

Post by risele on Modbus connection via Qronox PCD3 M6893 CODESYS Forge talk (Post)
First, if you don't need to change conversion rules in runtime, take a look at "Unit conversion" module (Application -> add object -> UnitConversion). You can specify there biderectional conversion with different units, limits and so on. Second, since MODBUS don't have "real" types but only general 16-bit registers and Real is 32-bit, generally you need a byte-was conversion Real <> two Words. Note, that depending on the devices on both sides, there are two options: Real-> Word1, Word2 or Real-> Word2, Word1, where Word1 is minor register in Modbus register pair and Word2 is major. You can use simple union: TYPE u_Real : UNION rVal:REAL; wVal:ARRAY[0..1] OF WORD; dwVAL:DWORD; //same as previous, may be easier to specify the MB register END_UNION END_TYPE and convert it as following: VAR myUnion:u_Real; rValue_TO_SEND:REAL; rValue_TO_GET:REAL; END_VAR myUnion.rVal:=rValue_TO_SEND; rValue_TO_GET:=myUnion.rVal; Note, that WORD-order should be properly set in MODBUS registers, otherwise you will get strange values. This tool is helpful: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/ Alternative, you can use functions as REAL_TO_DW and DW_TO_REAL from OSCAT_BASIC, for example.
Last updated: 2026-02-19

Post by fefefede on Get the numer of day CODESYS Forge talk (Post)
Hello i tro to create a program to turn on or off the air condition in relationship temperature and numer of day. I can't get the number of day. I try this after installing SysTime library but this not work and have this error on debug ------ Build started: Application: Device.Sim.Device.Application ------- Typify code... Generate code... [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0032: Cannot convert type 'Unknown type: 'SysTimeCore(TRUE)'' to type 'TIME' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0035: Program name, function or function block instance expected instead of 'SysTimeCore' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0032: Cannot convert type 'Unknown type: 'DayOfWeek(CurrentTime)'' to type 'INT' [ERROR] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0035: Program name, function or function block instance expected instead of 'DayOfWeek' [INFORMATION] giorno_accensione_aria: PLC_PRG Device: PLC Logic: Application: C0181: Related position Build complete -- 4 errors, 0 warnings : No download possible PROGRAM PLC_PRG VAR Temperatura: UDINT; AriaCondizionata: BOOL := FALSE; CurrentDayOfWeek: INT; //Variabile Giorno CurrentTime: TIME; GiornoDellaSettimana: INT; DayOfWeek: INT; END_VAR CurrentTime := SysTimeCore(TRUE); // Ottieni l'ora corrente CurrentDayOfWeek := DayOfWeek(CurrentTime); CASE GiornoDellaSettimana OF 1: // Azioni per Lunedì 2: // Martedì se più 10° accend altrimenti spegni IF Temperatura >= 10 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 3: // Mercoledì se più di 50° accendi altrimenti spegni IF Temperatura >=50 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 4: // Giovedì se più di 40° accendi altrimenti spegni IF Temperatura >=40 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 5: // Venerdì se più di 50° accendi altrimenti spegni IF Temperatura >=50 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 6: // Sabato se più di 25° accendi altrimenti spegni IF Temperatura >=25 THEN AriaCondizionata := TRUE; ELSE AriaCondizionata := FALSE; END_IF 7: // Domenica sempre spenta AriaCondizionata := FALSE; END_CASE
Last updated: 2023-09-14

Post by athuum on Error 'Library not found' and 'Unkown type' CODESYS Forge talk (Post)
Hello, I am getting the following error and warning when trying to download a project into a PLC: - Library CmpTargetVisu has not been added to the Library manager, or no valid license could be found - Unkown type: 'CmpEventMgr.EventParam' As far as I can see, both are included, and licensed, in the library manager (see image). What could the problem be, and how would I resolve this?
Last updated: 2024-10-08

Post by apurv on Cannot pass array of constant size to a function as a reference CODESYS Forge talk (Post)
I have a Array of constant size defined like this Var Constant MAX_SIZE :UINT := 10; End_var VAR array : ARRAY[0..MAX_SIZE] OF INT; END_VAR Now I want to pass this array to a function by reference, Function fun : INT VAR_IN_OUT CONSTANT MAX_SIZE : UINT; END_VAR VAR_INPUT array : REFERENCE TO ARRAY[0..MAX_SIZE] OF INT; END_VAR but when I run this it gives strange Errors Error : Cannot Convert type 'ARRAY [0..MAX_SIZE] OF INT' to type 'ARRAY[0..MAX_SIZE] OF INT'
Last updated: 2024-01-07

Post by marlutec on [ERROR] The PLCopenXML import is not possible because Device not found. Type: 89, Id: 0000 0005, Version: 3.5.10.0 CODESYS Forge talk (Post)
Hello every one. Now i'm instaling a Weintek cMT2108x2(v2) with IR-ETN40R. When I start to import the archive content the code of I/O remote IR-ETN40R, ocurred this error. [ERROR] The PLCopenXML import is not possible because Device not found. Type: 89, Id: 0000 0005, Version: 3.5.10.0 Can someone help me? Marcos Gentil, from Brazil.
Last updated: 2024-02-15

Post by adam on Get/Set I/O Address Mapping of DeviceObjects in python Script CODESYS Forge talk (Post)
I want to cancel the automatic address allocation for all IO mappings. If I directly set the automatic_iec_address in class ScriptIoMapping to False, the address becomes None. So I reset manual_iec_address with itselfs value. It only work with the Input IOMapping . For output, it reports an error: "Invalid address: The channel type 'Output' requires address type '%Q'." I checked the description file ,both accessRight are total same. Does anyone know what causes this?
Last updated: 2025-11-14

Post by alimans on OPC-UA Server, Symbol Set: Raise an error: Object reference not set to an instance of an object. CODESYS Forge talk (Post)
Hi everyone, I just created a very simple library without any code and, added it to my very simple project. after adding this library, I get an error when I try to open "Symbol Set" in "OPC UA Server" in "Communication Manager". Here is the code of my POU in the library: FUNCTION_BLOCK POU VAR eCommand : (CMD_NONE:=0, CMD_RESET:=-1) INT := CMD_NONE; END_VAR Attached is the error that I get. I also noticed that by removing the enumeration variable above (eCommand), I can open the "Symbol Set" again. Anybody has any idea why this error is raised and how could I use enumeration variables without error in "OPC UA Symbol Set"?
Last updated: 2024-08-08

Post by sigurdrb on OPC server in "Communication manager" CODESYS Forge talk (Post)
Hi! I was thinking of switching the OPC server config from "Symbol Configuration" to the "Communication manager" in the device tree. I Have a lot of arrays of structs that I have previously declared in the "Persistent Variable" object in the device tree. It seems as it is not supported to directly expose persistant variables to the OPC server like the "older" way of doing it in the symbol config. Is this correct? Do you recommend to just do it the old fashioned way, or should I edit the structure of the global variable list / persistant data / OPC server and set up the OPC server from the "Communication manager" object?
Last updated: 2025-01-20

Post by alberto on ExportPLCopenXML is failing CODESYS Forge talk (Post)
I'm trying to export my whole project through the option ExportPLCopenXML. It seems working, but when I'm trying to import the xml I have the following error during the importation process: Object reference not set to an instance of an object. It seems a usual issue with this process that affects to the pointer to user classes inside a procedure. I receive this error for two general functions that have this pointer declarations in the VAR_INPUT section. It seems a bug into the export/import process of CodeSYS and I couldn't skip it so far. Anyone could help me? Thanks in advance.
Last updated: 2025-03-15

Post by spiessli on Objects in OPC UA Information Model CODESYS Forge talk (Post)
Hi, I have an OPC UA information model with objects defined in it. I can import the model and use the data types defined in it and create instances of these types. These instances are accessible at Root > Objects > DeviceSet > CODE[...] > Resources > Application > GlobalVars > OPC_UA_Symbols for created instances and at [...] > Programs > PLC_PRG for mapped instances. The object defined in the information model is accessible in UA Expert by the name I have defined in the information model (Manipulator) at Root > Objects > Manipulator. How can I assign values to the Variables defined in the object "Manipulator"? Cheers, spiessli
Last updated: 2025-03-27

Post by sawicpx on CANbus Remapping PDOs During Runtime CODESYS Forge talk (Post)
Hello, I am working on an application where I need to remap PDOs to a different CANopen object during runtime depending on what value is at a specific register. I have gotten to the point where I put the device into Preoperational State using the CIA405.NMT function. I then reconfigure the PDO 180x and 1a0x obejcts usings SDOs to point to a new canopen object on the device however when I go to restart the Device from PREOP to OP using the CIA405.NMT function the device is reset back to the original configuration as per the initial setup. I am wondering is there any way to change the PDOs at runtime is there some more functionaility I can access to do this. Any direction is appreciated!
Last updated: 2023-12-22

Post by rau00 on Touch Probe 0x60B8 writting CODESYS Forge talk (Post)
Hi erveyone, Rau here, first time asking on CODESYS Forge: When working with my servodrives, a special behaviour is required on dsp402 0x60B8 object, a control that is not supported by MC_TouchProbe. For this reason, I'd like to ask: Anyone knows if there is any way to bypass or change the softmotion axis writting into 0x60B8 object? My main problem is that MC_TouchProbe.TriggerInput.iTriggerNumber only allows to choose between TP 1 and TP 2 (not both at the same time). iTriggerNumber only allows values [0, 1, 2, 3], other values triggers an error in the FB, wether SMC_TP_COMM_ERROR for values [4, 5, 6, 7] and SMC_TRIGGER_OUT_OF_RANGE with any other value. Best regards, Guillem
Last updated: 6 days ago

Post by snhatton on Retain memory change to ZERO CODESYS Forge talk (Post)
I think more information is needed to help solve the issue. Can you list the exact steps to reproduce the issue? What version of Codesys are you using? Did you add a persistentVars object to your project? I would recommend browsing all instances of the retain variable to see all possible writes to the variable in question.
Last updated: 2023-09-18

Post by turndapage on Can't Add Symbol Configuration CODESYS Forge talk (Post)
I've got a Weintek HMI with CodeSYS built-in. I've got it connecting to CodeSYS and downloaded. The connection guide says I need to add a symbol configuration by right-clicking on the application and adding it, but it does not show up in the available objects. Is there something else I have to do to create a symbol configuration object?
Last updated: 2023-10-04

Post by charleskentyfz on (no subject) CODESYS Forge talk (Post)
I have created an EtherCAT slave code and fixed two slaves (IDs written in the 0xF050 object dictionary). The module IDs are 0x1 and 0x101, respectively. It can be scanned normally in TwinCAT, but when scanning in CODESYS, it reports an error. Why is this happening?text in the second pic means 'device cannot be found in repository'
Last updated: 2024-07-07

Post by mmpl on Array to String CODESYS Forge talk (Post)
I would like to create one large JSON string from an array of objects, where each object contains a value. My current approach involves using a for loop and string concatenation, but with 20,000 elements in the array, this method takes almost 7 seconds and negatively affects the PLC scan time. Is there a more efficient way to accomplish this?
Last updated: 2024-07-18

Post by mmpl on Array to String CODESYS Forge talk (Post)
I would like to create one large JSON string from an array of objects, where each object contains a value. My current approach involves using a for loop and string concatenation, but with 20,000 elements in the array, this method takes almost 7 seconds and negatively affects the PLC scan time. Is there a more efficient way to accomplish this?
Last updated: 2024-07-18

Post by bjarne-pagaard on Unable to add alarm configuration object to project CODESYS Forge talk (Post)
I believe it should be available. It may be the case, that your device does not support the alarm configuration. Some smaller PLCs sometimes do not support it. You can try changing to a different device, like a Codesys Control Win, in your project, and see if then allows you to add the alarm configuration.
Last updated: 2024-09-27

Post by timvh on Library ENUM text representation in visualization CODESYS Forge talk (Post)
Probably the enum from the library doesn't have text support. In that case you need to add your own TextList to the application. In the rectangle you should use the property "dynamic text" to link this object to the textlist which you have created yourself and then link the text index to your enum variable.
Last updated: 2025-01-09

Post by alexgooi on How to protect library project? CODESYS Forge talk (Post)
Hi aniket-b, If you save the library as a compiled library you are not able to see the source code. When the end user tries to view inside the object, CODESYS will give a notification that the source code is missing, see attachment. In short if you don't send the source code, it will not show.
Last updated: 2024-01-25