Post by alimans on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
For anyone still experiencing this issue, here’s how I managed to solve it: Symptoms: 1. Sometimes, on the first start of CODESYS Runtime, the modules fail to run. 2. After disconnecting and reconnecting the communication cable, the drive does not start again. 3. MC_Reset cannot clear the fault. Solution (what worked for me): 1. Check the axis communication using the SMC_CheckAxisCommunication function block (FB). 2. If CheckAxisCommunication.eComState of the axis is equal to or higher than SMC_CommunicationState.SMC_COMSTATE_BASE_COM_INITIALIZATION, then 3. Use the SMC3_ReinitDrive function block to reset the drive — and it works. For more information, refer to the official CODESYS documentation: 👉 https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/DriveInterface/AXIS_REF/SMC3_ReinitDrive.html
Last updated: 2025-10-23
Post by malte on OPC UA multiple Endpoints
CODESYS Forge
talk
(Post)
My CODESYS OPC UA server provides endpoints using both the hostname and the IP address. Connecting via the IP address works fine, but connecting via the hostname does not. The endpoint list shows both opc.tcp://<hostname>:4840 and opc.tcp://<ip>:4840. When using the hostname, the OPC UA client (UA Expert) fails to connect. Using the IP address connects without issues. Main goal is to conect via Python but opcua-asyncio seems to prefer the hostname. How can I configure CODESYS or my system so that the OPC UA connection via hostname also works properly or disable it completly? Running Codesys for PFC200 sl 4.18.0.0
Last updated: 2025-10-28
Post by bitor-leao on *EXCEPTION* [ProsessorLoadWatchdog] codesys 3.5.11.40
CODESYS Forge
talk
(Post)
Good night. I am having a problem with CODESYS 3.5.11.40, which gives the exception EXCEPTION [ProcessorLoadWatchdog]. I followed some forum posts and tried to modify the CODESYSControl.cfg file, but it shows: [SysFile] Windows.WorkingDirectory=C:\ProgramData\CODESYS\CODESYSControlWinV3\D5050FE1 Then I go to this directory and try to modify CODESYSControl.cfg according to the forums, but it doesn’t work: [CmpSchedule] ;EnableLogger=0 ProcessorLoad.Maximum=80 ;Timeslicing.Mode=Internal ;Timeslicing.PlcSlicePercent=80 ;Timeslicing.PlcSliceUs=4000 ;Timeslicing.StartOnProcessorLoad=1 ;SchedulerPriority=5 ;SchedulerInterval=1000 I tried to change ProcessorLoad.Maximum to 0 or 100, but it doesn’t compile when I try. I really don’t know what to do,
Last updated: 2025-11-16
Post by bitor-leao on *EXCEPTION* [ProsessorLoadWatchdog] codesys 3.5.11.40
CODESYS Forge
talk
(Post)
Good night. I am having a problem with CODESYS 3.5.11.40, which gives the exception EXCEPTION [ProcessorLoadWatchdog]. I followed some forum posts and tried to modify the CODESYSControl.cfg file, but it shows: [SysFile] Windows.WorkingDirectory=C:\ProgramData\CODESYS\CODESYSControlWinV3\D5050FE1 Then I go to this directory and try to modify CODESYSControl.cfg according to the forums, but it doesn’t work: [CmpSchedule] ;EnableLogger=0 ProcessorLoad.Maximum=80 ;Timeslicing.Mode=Internal ;Timeslicing.PlcSlicePercent=80 ;Timeslicing.PlcSliceUs=4000 ;Timeslicing.StartOnProcessorLoad=1 ;SchedulerPriority=5 ;SchedulerInterval=1000 I tried to change ProcessorLoad.Maximum to 0 or 100, but it doesn’t compile when I try. I really don’t know what to do,
Last updated: 2025-11-16
Post by davidbo on RETAIN PERSISTENT only stored at gracefully shutdown?
CODESYS Forge
talk
(Post)
I have {attribute 'checksumnoinit_override' := '2629838988'} {attribute 'init_related_code' := '5c6efcf8-e0f4-4166-a9fa-17eadd8908df'} VAR_GLOBAL RETAIN PERSISTENT {attribute 'order_in_persistent_editor' := '0'} segmentValue: ARRAY[0..49] OF REAL; {attribute 'order_in_persistent_editor' := '1'} segmentTime: ARRAY[0..49] OF REAL; // Generated instance path of persistent variable PRG.test: INT; // Generated instance path of persistent variable PRG.nw_storage: SysSocket_Implementation.SysSocket_Interfaces.SOCK_ADAPTER_INFORMATION2; END_VAR When I have changed PRG.nw_storage it will not be stored at a power off, but if I do a: sudo systemctl restart codesycontrol and then a power off it will be stored. Is there a way to store persistent variables without a restart of codesyscontrol? Can anyone explain how and when CODESYS store persistent variables?
Last updated: 2025-11-17
Post by mr-ege on Error: C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr
CODESYS Forge
talk
(Post)
Hi all! I'm trying to learn PLC Programing. Today I was making a simple PLC program, as you can see. When I compile the program without the visualization, there are no errors. However, when I add the visualization and then compile it, I get this error. I don’t know how to solve the problem. I have tried the following solutions: rebooting the PC and updating the software. Error Code: C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr Compile complete -- 1 errors, 0 warnings Build complete -- 1 errors, 0 warnings : No download possible Version: CODESYS V3.5 SP21 Patch 3
Last updated: 2025-11-25
Post by gseidel on Can't get SMC_SmoothPath to work
CODESYS Forge
talk
(Post)
Hi bertus, I cannot see any problem in the code you posted. Just some ideas: What is the value of D_ANGLE_TOL? - Do you need the assignment bAbort := NOT bDecoder? Does it help to leave it out? Any errors (e.g. SMC_SmoothPath.Error/ErrorID) or PLC log messages? What if you comment out SMC_SmoothMerge and SMC_LimtiDynamics, is corner smoothing still not working? Is bDecode written from a different task (e.g. visu)? Then I would recommend to assign to a local variable (bDecodeLocal := bDecode) and use that for all FBs. Otherwise, FBs might see different values of bDecode in a single cycle, which will cause problems. Regards, Georg
Last updated: 2025-12-17
Post by mait-tim on Drive communication errors
CODESYS Forge
talk
(Post)
With a machine I'm working with i get a communication error when I'm updating some softstop limits. As soon as I update the code the drives do not want to operate. Using the MC_readStatus I'm receiving errors as soon as i want to start a movement. Using MC_ReadAxisError i see that i receive error 131, no response. With a SMC3_ETC_ReadParameter_CoE i do not recieve any driver errors. Does anyone know how i can figure out what the error is and how to solve it. When i go back to the old software no errors occur. Im working with a legacy machine running a Beijer PLC with some Mitsubishi drives. running on Codesys 3.5 SP10. the runtime version is probably 3.5.3. The drives are all Ethercat Drives (CoE). All using the SM3_drive_ETC libary and the SM3_basic library.
Last updated: 2025-12-22
Post by jp0951269346 on How to reset forgotten User Management / Administrator password on CODESYS Control Win V3 (V3.5 SP22 Patch 2)?
CODESYS Forge
talk
(Post)
Hi everyone, I forgot the Administrator credentials for my local Soft PLC (CODESYS Control Win V3x64) running on CODESYS V3.5 SP22 Patch 2 (Windows 11). When I try to login/connect to the device, it asks for the Device User Management username and password. I checked the CODESYSControl.cfg file, which points the working directory to: Windows.WorkingDirectory=%APPDATA%\CODESYS\CODESYSControlWinV3x64\905D4E32 However, I cannot locate the actual database/credentials files in AppData or ProgramData to clear them, and resetting the runtime directory doesn't seem to clear the authentication prompt. Could anyone please advise the correct steps to completely reset or wipe the User Management credentials for the Control Win V3.5 SP22 runtime? Thank you in advance!
Last updated: 2026-08-25
Post by timvh on Codesys complains about matching versions
CODESYS Forge
talk
(Post)
Open the CODESYS Installer. Create an export file from your current PC from your current version. Then on the other PC Open the installer and install a new version based on the same essentials version, but additionally select the export file which you have created on the first PC. Or just install (import) it within the already existing version. For the installer, you can install it from: https://store.codesys.com/en/codesys-installer.html For help see: https://content.helpme-codesys.com/en/CODESYS%20Installer/_inst_install_setups_and_addons.html On PC 1, save the project as projectarchive (which will then include all the libraries and devices). Then extract this projectarchive on PC 2.
Last updated: 2025-12-15
Post by infinitetool on No connection could be made because the target machine actively refused it
CODESYS Forge
talk
(Post)
Hi! I'm having trouble connecting to a device in Deploy Control SL. I'm able to see the device is available during a scan, and I can ping the device as well, but when I try to connect I get the message "No connection could be made because the target machine actively refused it". I've worked on this for hours including turning off the firewall on the device PC but nothing seems to work. The device is running a fresh install of Windows 11 IoT Enterprise 2024 and the Development System is 3.5.21.50 running on Windows 11. Thank you in advance for any ideas!
Last updated: 2026-03-10
Post by cvrettacos-dse on Table Element Scroll Return
CODESYS Forge
talk
(Post)
Hello, I would like to use swipe/pan gestures to scroll a table visualization element (CODESYS 3.5.21.10) on a DSE M810 display. The swipe / pan gesture control works fine, however, I cannot figure out how to reset / navigate to the top of the table again with code. I have tried the Scrolling begin variable, and the visu manager is setting it to FALSE right away but the table doesn't actually scroll back to top. If I check the “Scroll elements with scrollbar” box, then the Scrolling begin variable works perfectly, but now the swipe/pan scrolling no longer works and you have to use the scrollbar. Is it possible to do what I've described? Any assitence you can provide is appreciated. Thanks.
Last updated: 2026-06-10
Post by afrazeh2026 on Curtis 1226BL Drive
CODESYS Forge
talk
(Post)
Subject: Curtis 1229-4105 CANopen (CiA 301 / CiA 402) Hello everyone, I am developing a battery-powered industry vehicle using a Curtis 1229-4105 motor controller together with a Siemens S7-1200 PLC and an HMS (Ixxat) CANopen Master. I am looking for someone who has practical experience with the Curtis 1229-4105 CANopen implementation. I would appreciate your help with the following questions: Does the Curtis 1229-4105 support only CANopen CiA 301, or does it also support CiA 402? Is an EDS file available for this controller? Is the CANopen Object Dictionary available? Has anyone successfully communicated with the Curtis 1229-4105 from a Siemens S7 PLC or another CANopen master? Are the CANopen PDOs and Object Dictionary based on the standard CiA profile, or are they Curtis-specific? Any documentation, examples, or practical experience would be greatly appreciated. Thank you very much.
Last updated: 2026-07-15
Post by jari-koivuluoma on Comparing between SP19 patch 5 and patch 7
CODESYS Forge
talk
(Post)
Hello. Has anyone here used project compare tool across different versions of Codesys? I tried the compare of the title but it does not seem to do much. It lets me choose the project files and then seems to be comparing but no results are ever shown. If the compare tool cannot be used how else would I keep 2 nearly identical projects in sync when the versions differ? On the other hand it might be possible to just have one project but then I would need to use the older codesys with older target device description to develop for devices that have newer device description. Codesys will let me do that but its not recommending it. Any advice?
Last updated: 2026-08-20
Post by winki on Error in licence activation
CODESYS Forge
talk
(Post)
Hello, I think I understand: On my debian gateway I have done: sudo cmu --list cmu - CodeMeter Universal Support Tool. Version 8.30a of 2025-May-06 (Build 6885) for Linux/ARMHF 64-Bit Copyright (C) 2007-2025 by WIBU-SYSTEMS AG. All rights reserved. List all locally connected CmContainers: - CmContainer with Serial Number 130-XXXXXXXX and version 3.00 (empty) - CmContainer with Serial Number 130-XXXXXXXX and version 3.00 (locked) Result: 2 CmContainer(s) listed. The licence has been activated with a computer Name, but the guy who did it make a mistake in the name, so he changed it after to have activate the licence. I think this has created a second container. The licence is actived on the other container.
Last updated: 2026-02-06
Post by konstantin on CAM Motion Recover after STO
CODESYS Forge
talk
(Post)
Hello, one of the projects I work on is about a racetrack collator with two independent belts on it - two different servo motors. Both motors share the same mechanical frame and there is a train on a belt that collects items from the input conveyor. The way the motion is performed is the following - there is a virutal master axis and both real axis are synchronised with different cam motion profiles. The problem is when an STO is triggered on any of the slave axis, the synchronization process starts from position 0 of the slaves. How can I force the slaves to retain their current position until the master passes their position? Then the slaves should catch up with the master according to the profile, the slaves should not start synchronization from 0 position. Best Regards Konstantin Kolev
Last updated: 2026-02-12
Post by gseidel on CAM Motion Recover after STO
CODESYS Forge
talk
(Post)
Dear Mr. Kolev, I'm not sure I understood correctly. But this is my take on your question: When the STO of the slave is triggered, store the current master position (e.g. 225 units) After the reset of the slave error, call MC_SetPosition on the virtual master and reset it to the stored position (225 units) Optionally, before MC_CamIn is restartet, move the slave back to the slave position corresponding to the stored master position. (If you do this, no ramping in will be necessary) Restart MC_CamIn, with absolute master position and absolute slave position. Choose the StartMode that is appropriate for your machine. Best regards, Georg Seidel
Last updated: 2026-02-16
Post by hannibal on Codesys Trend - setting Y axis minimum and maximum as variables - error
CODESYS Forge
talk
(Post)
I am experiencing an issue when trying to define the Y-axis limits in a Trend Graphic using variables. When I set the Minimum and Maximum values as variables, an error is triggered. My goal is to make the Y-axis limits dynamic so they can adjust according to the installation. Both variables are initialized as follows: gP_YMin = -100.0 gP_YMax = 100.0 However, I still get the following error: "The minimum axis value must be less than the maximum axis value" Does anyone have an idea why this is happening or how to resolve it?
Last updated: 2026-03-22
Post by hannibal on Codesys Trend - setting Y axis minimum and maximum as variables - error
CODESYS Forge
talk
(Post)
I am experiencing an issue when trying to define the Y-axis limits in a Trend Graphic using variables. When I set the Minimum and Maximum values as variables, an error is triggered. My goal is to make the Y-axis limits dynamic so they can adjust according to the installation. Both variables are initialized as follows: gP_YMin = -100.0 gP_YMax = 100.0 However, I still get the following error: "The minimum axis value must be less than the maximum axis value" Does anyone have an idea why this is happening or how to resolve it?
Last updated: 2026-03-22
Post by poliautomacao on Absolute movement controlled by an external encoder.
CODESYS Forge
talk
(Post)
Hello, I made this configuration, I'm moving the encoder value to SM_Driver_PosControl.in.wActPosition. When I make the absolute movement of my PosControl axis, my physical drive axis rotates perfectly, but I noticed that the movement is not followed by the encoder. That is, if I hold the encoder and keep it in position 0, the PosControl axis makes the absolute movement of 314 mm and stops, which is strange because the encoder is at 0. Theoretically, the PosControl axis should accelerate to try to compensate for the movement error. I haven't yet achieved perfect functionality.
Last updated: 2026-03-24
Post by husarz17 on How change Unity-ID in TCP Modbus Slave
CODESYS Forge
talk
(Post)
My codesys is 3.5.21.30. I am using function ModbusServer from library ModbusTCP_Slave. The reason is that I need share 9000 Holding registers. By standard configuration it is only 4096. fbMbTcpDevice: ModbusTCP_Slave.ModbusServer; fbMbTcpDevice( wPort := 502, pInputData := ADR(awInputReg), pOutputData := ADR(awHoldingReg), uiInputDataSize := 10, uiOutputDataSize := 9000, xEnable := TRUE, tTimeout := 10000, InterfaceName := "eth0", xBusy => xBusy, xError => xError, byClientConnections => byConnections ); Ethernet port is cofigured: Network interface: eth0 IP address: 10.10.22.55 Subnet maskL 255.255.255.0 Default gateway: 0.0.0.0 And it only works when I am reading registers with ID 255 by Modbus Poll. Any other IDs don't work. The actual TCP client device try to read registers with ID 1 and I can't change it... Thanks in advance for your help!
Last updated: 2026-04-01
Post by cvrettacos-dse on How to reset scroll of a table element
CODESYS Forge
talk
(Post)
Hello, I would like to use swipe/pan gestures to scroll a table visualization element (CODESYS 3.5.21.10) ona DSE M810 display. The swipe / pan gesture control works fine, however, I cannot figure out how to reset / navigate to the top of the table again with code. I have tried the Scrolling begin variable, and the visu manager is setting it to FALSE right away but the table doesn't actually scroll back to top. If I check the “Scroll elements with scrollbar” box, then the Scrolling begin variable works perfectly, but now the swipe/pan scrolling no longer works and you have to use the scrollbar. Any assitence you can provide is appreciated. Thanks.
Last updated: 2026-04-21
Post by timvh on Codesys v3.5.22.10 - Fail to create a project Archive
CODESYS Forge
talk
(Post)
There is an issue with adding the visu styles to the archive with Visu add-on 4.9.0.0 and 4.9.1.0. When you create the projectarchive disable the option to add the style(s) to the archive. CODESYS support informed me it will be fixed with visu add-on 4.10.0.0 (May 26th 2026). An alternative is to start CODESYS as Administrator. Then it will work with styles as well. You could start CODESYS as Administrator by first opening the CODESYS Installer. At the bottom you can select to start the Installer as Administrator. If you do this and then start the CODESYS version from this installer, it will work.
Last updated: 2026-04-25
Post by timvh on library inside library
CODESYS Forge
talk
(Post)
1) it should be possible to access the type SysTime in the project as A_Lib.SysTime. 2) you could add the SysTimeCore library to the library manager of your library (POU Pool). This might seem as a double library, but because of the placeholder resolution only one will be used. Then, in your library manager of your library, select the SysTimeCore library, right-click, select "Properties" and enable the option "Publish all IEC symbols ...." For more information about library development, you could follow our advanced training course in Ridderkerk. The next is scheduled for 24 and 25 June 2026 https://www.extendsmartcoding.nl/codesys-training/
Last updated: 2026-04-25
Post by brouwyka on JSON Utilities - JSON file written with invalid structure
CODESYS Forge
talk
(Post)
Hey there! I am currently running into the exact same issue (and have also posted to a similar post here: https://forge.codesys.com/forge/talk/Engineering/thread/c45929e2f1/#e27f). The JsonData object has all inexes & parent indexes in the way I expect, everything is correctly "linked". It purely seems that the writer is incorrectly parsing said JsonData, not based on parent & child index, but on something else that breaks it and puts things at the root, instead of the specified parent index. Did you ever manage to find a solution, or another way of achieving your JSON composing? I'm currently working on Codesys V3.5 SP19 Patch 7 with IIOT Libraries SL 1.13.0.0, specifically JSON Utilities SL 1.13.0.0 (to send requests to APIs with JSON bodies using Web Client SL 1.13.0.0).
Last updated: 2026-06-08