Post by mqi2r on Newly created texlists wont appear in the selection dropdown
CODESYS Forge
talk
(Post)
For anyone with this issue, you may need to: Open the text list properties (right-click the text list once you create it). Select the Text List tab. Change the Download by option to Visualization. I was fighting this for so long. Once you do that, you should find your text list appears in the drop down when editing a visualisation.
Last updated: 2025-08-19
Post by wagokurt on TargetVisu option missing in IDE
CODESYS Forge
talk
(Post)
I have installed both the Codesys Control for Linux SL 4.16.0.0 and Target Visu for Linux 4.16.0.0 packages in Codesys 3.5 SP21 Patch2. When I try to add a target visu, it is missing. I have spent hours on this and tried different machines, all behave the same way. Is this a bug?
Last updated: 2025-08-21
Post by eksheep on Unit Tests and C007: Unknown Type
CODESYS Forge
talk
(Post)
Hello, I am attempting to implement unit tests for my POUs. When building and running the unit tests I receive error C007: Unknown Type for all types defined in the library, Standard, 3.5.18.0. Which is included in the POU Library Manager. Any input would be appreciated. TIA.
Last updated: 2025-08-27
Post by antonz on CoDeSys v3.5: creating libraries for both 32-bit and 64-bit controllers
CODESYS Forge
talk
(Post)
Thanks Tim. I would think it somehow is relevant when creating a compiled library, but that may very well not be the case. If I understand you correctly, then the same compiled library created from my source code would work for both 32 bit as well as 64 bit controllers.
Last updated: 2025-09-01
Post by onstage on Unable to add EL6751 to Control RTE V3 on W11 IoT LTSC using Eng. V3.5 SP21
CODESYS Forge
talk
(Post)
For reference, it was just me being unfamiliar with EtherCAT in CoDeSys. Anyone with knowledge who would have opened the ScanResult screenshot would have identified that the preceding EK1100 was the device missing in the library. Bottom line - Do something else for a while and then get back at it with fresh eyes!
Last updated: 2025-09-08
Post by smartcoco on Add visual background FB blocks.
CODESYS Forge
talk
(Post)
Can you add a background FB block to the visualization page, and loop through this FB block when the page is in display mode. This FB block requires two more functions, one for executing when the page is displayed and the other for executing when the page is closed.
Last updated: 2024-01-16
Post by nmcc on Toggling Visualizations using HMI Physical Buttons
CODESYS Forge
talk
(Post)
Hello, I am extremely new to using codesys. I have an IFM CR1102 HMI with physical buttons on the right side. I need to have these buttons toggle which visualization is active. I currently have ladder logic for when the button is pressed just need the action side for setting the active visualization. Any help is appreciated.
Last updated: 2024-02-12
Post by thewizard8 on Raspberry PI4 Serial Port
CODESYS Forge
talk
(Post)
Hi All, I finally figured out how to solve it. The only away that I got it to work was to define parity to None on modbus configuration, and now works like a charm. Just for the record I'm using the GPIO port pins (8,10) and a RS485 to ttl shield that you can find online. Thanks all for the support! Regards Ricardo
Last updated: 2024-03-19
Post by mani-i4point0 on Issue with WebVisu on Raspberry PI
CODESYS Forge
talk
(Post)
Hi, Any insights highly appreciated. Was wondering , Is this issue related to License ? The License I have is 'Codesys Control for Raspberry PI MC SL' Or is this issue related to any Memory ? kindly refer to the attached images for the License and memory. Any suggestions highly appreciated. Regards, Mani
Last updated: 2024-04-10
Post by nano on CODESYS Edge Gateway for Linux on embedded distribution
CODESYS Forge
talk
(Post)
yocto isn't the part. which architecture you are using? arm, x86, 32bit?, 64bit? normally u can use the deliveral from store and integrate it into yocto. for resolv the dependencies, its best way todo using an recipe and let yocto do prebuildchecks jefore the install-commands
Last updated: 2024-04-17
Post by k2saki on CNC / G01 Speed is very slow (or go-stop motion) in Continuous short segment .
CODESYS Forge
talk
(Post)
Hi, gseidel. Thank you so much for your advice. I have created a program to preprocess G-code as follows 1.SMC_ReadNCFile2 2.SMC_Interpreter 3.SMC_CheckVelocities Then I put SMC_OUT_QUEUE in SMC_Interpolator. Where should I insert SMC_SmoothMerge and SMC_SmoothPath? Or are there any example link for it ?
Last updated: 2024-04-30
Post by stiller on OPC-UA ApplicationUri / ProductUri
CODESYS Forge
talk
(Post)
Thank you for your answer! I'm not sure, but it seems this is not what I am looking for. I attached three pictures. The first one is from the Codesys IDE. I use an Information Model to generate an OPC-UA server. I connected via UA-Expert, and there I see the URIs I would like to change.
Last updated: 2024-05-10
Post by eschwellinger on RecipeManCommands.ReloadRecipes
CODESYS Forge
talk
(Post)
does this recipe example help you here? https://forge.codesys.com/prj/codesys-example/home/Home/ https://forge.codesys.com/prj/codesys-example/recipe-manageme/home/Home/ and additional keep in mind that all files which are generated / or read should be exist in the iecfilepath this means: for Windows (Control Win as example) c:\ProgramData\CODESYS\CODESYSControlWinV3x64\268E8ADF\PlcLogic for Linux /var/opt/codesys/PlcLogic
Last updated: 2024-05-24
Post by thisischris on "You are using inconsistent overlay settings, please check your compiler defines for the current application" error
CODESYS Forge
talk
(Post)
Hello. I am a new user. On generating the first test project I am receiving this error message. You are using inconsistent overlay settings, please check your compilerdefines for the current application (-> GENERATE_OVERLAY_VISU) and the setting within the visualization manager. Can anyone help?
Last updated: 2024-05-28
Post by mp9876 on Problems with simulation in Window 10
CODESYS Forge
talk
(Post)
Hi Eschwellinger, sorry for so late reply but I found a solution back then; uninstall completely Codesys V3x64 and re-installed Codesys V3x32 to properly note the password I created and everything went ok. thank you for your suggestion and have a good day/evening Mike
Last updated: 2024-05-30
Post by kalmeyer on Stepper motor control with (SM_Drive_RaspStepper_direct)
CODESYS Forge
talk
(Post)
Hi Helpers I'm trying to work with stepper motor on Rasp 5 for the first time. So I'm pretty new.π₯here. I've used: https://forge.codesys.com/drv/sm3raspistepper/home/Home/ but I get the following error when I insert. I also get 6 errors when I "rebuilder" after installering "SM_Drive_RaspStepper_direct" from the tree. Hope there is help for me. Thanks in advance /Klaus
Last updated: 2025-11-04
Post by eschwellinger on Deploy LicenseServer for Linux SL
CODESYS Forge
talk
(Post)
As I see from your logs I think the Timeprovider is not accurate enough in your case. Things to check - at the moment you run it on the same device? (for tesing purpose ok) I would set 127.0.0.0 as IP and set it not really to Core 0 ( many other stuff is there)
Last updated: 2025-11-20
Post by bruno-roth on Parker Compax3 controlled by Schneider LMC 201
CODESYS Forge
talk
(Post)
Hello, You could not run EtherCAT-Softmotion drives with LMC201 PLC. This Controller has an EtherCAT master but only to run simple I/O devices. You could not use this EtherCAT master on the LMC201 for Motion. Schneider PACdrive Controller use SERCOS and only own drives (LXM62 with Sercos) for motion.
Last updated: 2026-01-13
Post by eschwellinger on Deploy LicenseServer for Linux SL
CODESYS Forge
talk
(Post)
for the package you net to install 32bit support(to have the native timprovider availble to deploy) sudo apt-get install libc6:i386 Then native Safeplc and native Safetimeprovider should be available to install. Raspi yes - but there is no official package available till now and you need have a rt_preemt patched kernel on the Pi, then it works like charm
Last updated: 2025-11-18
Post by poliautomacao on Absolute movement controlled by an external encoder.
CODESYS Forge
talk
(Post)
Georg, the encoder's actual position was -208 because I moved it manually for testing, but I managed to get it working. Your information is correct; there was a parameter error, Kp was at 0. After I adjusted it, it responded as expected. Thank you very much for your help.
Last updated: 2026-04-02
Post by fabrp on CPU + EtherCAT redundancy
CODESYS Forge
talk
(Post)
Hi TimvH, thanks for feedback. I also test the redundancy with Wago PFC 8212 but when I did it (firmware 28) it was not so much stable..Did you have some issue on master/slave switchover? are you using with EtherCAT remote I/O? I was looking for a most powerful hardware (PC based, x64) BR
Last updated: 2026-02-01
Post by buczekj on ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks
CODESYS Forge
talk
(Post)
Many issues with the alarmmanager and alarmstorage can be solved by deleting the configuration, rebooting, and redownloading. I've found that the configurator doesn't always update when you make chanegs. For linux installations it is typically located in /var/opt/codesys/PlcLogic/alarms/ look for file Application.AlarmConfiguration.xml cd /var/opt/codesys/PlcLogic sudo rm -r alarms sudo reboot
Last updated: 2026-04-09
Post by gseidel on CODESYS SoftMotion Generic DSP402 on WAGO PFC200 + Festo CMMT-AS: MC_Power stays Busy, Controlword remains 0
CODESYS Forge
talk
(Post)
Hi gilad, the missing license does not prevent the axis from being enabled. As far as I know, Festo distributes a CODESYS SoftMotion driver for the CMMT drives together with their software. I would contact Festo and ask for the driver. Best regards, Georg
Last updated: 2026-06-25
Post by scoob on ModbusFB - Slow Response Time
CODESYS Forge
talk
(Post)
Hello, I have been trying to use the ModbusFB functions so I can put some code into libraries, but it seems to be very slow for me. I have a Modbus device with 100ms registers. I previously setup 10 channels in the 'traditional' Modbus Slave with channels and mappings - and set a cyclic trigger at 100ms - this worked fine. I then tried the ModbusFB example, and setup reading the same 10 blocks of modbus addresses, copying the example and putting all of the requests into an array and triggering the requests sequentially. I timed how long the requests are taking to get round to each one, and it is around 1s 450ms. How do I speed this up to match the cyclic time? IF NOT(init) THEN init := TRUE; // Set the required IP address: ipAddress[0] := 192; ipAddress[1] := 168; ipAddress[2] := 1; ipAddress[3] := 10; // Pass the required IP address to the clinet FB: client_NetworkSwitch.aIPaddr := ipAddress; client_NetworkSwitch.udiLogOptions := (ModbusFB.LoggingOptions.ClientConnectDisconnect OR ModbusFB.LoggingOptions.ClientReceivedValidReplies); // Try to connect the client client_NetworkSwitch(xConnect:=TRUE); // Configure all the channels to read connecting them to the client: portStatus_Request(rClient := client_NetworkSwitch, uiStartItem := 4096, uiQuantity := 32, pData := ADR(portStatus), udiReplyTimeout := udiReplyTimeout); portSpeed_Request(rClient := client_NetworkSwitch, uiStartItem := 4352, uiQuantity := 32, pData := ADR(portSpeed)); flowControl_Request(rClient := client_NetworkSwitch, uiStartItem := 4608, uiQuantity := 32, pData := ADR(flowControl)); linkUpCounter_Request(rClient := client_NetworkSwitch, uiStartItem := 5888, uiQuantity := 32, pData := ADR(linkUpCounter)); txPacketCounter1_Request(rClient := client_NetworkSwitch, uiStartItem := 8192, uiQuantity := 100, pData := ADR(txPacketCounter1)); txPacketCounter2_Request(rClient := client_NetworkSwitch, uiStartItem := 8292, uiQuantity := 28, pData := ADR(txPacketCounter2)); rxPacketCounter1_Request(rClient := client_NetworkSwitch, uiStartItem := 8448, uiQuantity := 100, pData := ADR(rxPacketCounter1)); rxPacketCounter2_Request(rClient := client_NetworkSwitch, uiStartItem := 8548, uiQuantity := 28, pData := ADR(rxPacketCounter2)); txErrors_Request(rClient := client_NetworkSwitch, uiStartItem := 8704, uiQuantity := 64, pData := ADR(txErrors)); rxErrors_Request(rClient := client_NetworkSwitch, uiStartItem := 8960, uiQuantity := 64, pData := ADR(rxErrors)); // Trigger all client requests initially FOR clientRequestsCnt := 0 TO (SIZEOF(clientRequests)/SIZEOF(clientRequests[0]))-1 DO pClientRequest := clientRequests[clientRequestsCnt]; pClientRequest^.xExecute := TRUE; END_FOR // Prepare sequential trigger / control of client requests. clientRequestsCnt := 0; pClientRequest := clientRequests[clientRequestsCnt]; END_IF // Call the client to do request processing: client_NetworkSwitch(); // Now we trigger client request sequentially ... IF NOT pClientRequest^.xExecute AND NOT pClientRequest^.xDone AND run AND client_NetworkSwitch.xConnected THEN pClientRequest^.xExecute := TRUE; END_IF // .. and check result/error IF pClientRequest^.xExecute AND run AND client_NetworkSwitch.xConnected THEN IF pClientRequest^.xDone THEN // Prepare next trigger of client request (a rising edge of xExecute) pClientRequest^.xExecute := FALSE; IF clientRequestsCnt < SIZEOF(clientRequests)/SIZEOF(clientRequests[0])-1 THEN // next client request clientRequestsCnt := clientRequestsCnt + 1; ELSE clientRequestsIterationCounter := clientRequestsIterationCounter + 1; clientRequestsCnt := 0; END_IF pClientRequest := clientRequests[clientRequestsCnt]; END_IF END_IF I did try a semi-coded way using the IoDrvModbusTCP library, and setting the slave com settings, then 10 commands and 10 requests, then using a TP on xDone as a pause, before triggering another request - this is time the delay is around 120ms - so the device is fine with the speed, just something I am doing wrong in the ModbusFB method I am sure.
Last updated: 2024-04-26
Post by mozed on Connection to device closed
CODESYS Forge
talk
(Post)
Hello I am using an OpusA3 with version 3.5 SP17 Patch 3 as part of a project. I had no real problem before I encountered a problem that blocked me. The detection of the OpusA3 from Codesys is done correctly. The gateway is well configured and if I ping the gateway or the OpusA3 I receive the response correctly. The problem is that when I try to connect, the Opus screen freezes and a few moments later Codesys displays an error message ("connection to device closed"). I tried to change PC, to update the runtime, to change OpusA3 but the problem remains the same. I'm a little lost knowing that before it worked without problem. I went back to a previous version of the project (where it worked correctly) but the message still appears. Do you have any clues to solve the problem? Sincerely,
Last updated: 2023-08-23