Post by pernockham on Control for linux SL, 4.14.0.0 -> 4.15.0.0 breaks web page access. URL requires authentication
CODESYS Forge
talk
(Post)
I have a problem which I have identified with a device-update from 4.14.0.0 to (4.15.0.0-4.17.0.0) where the newer versions will stop any local access to the internal web page with the browser responding "The requested URL requires authentication". Setting the device back to 4.14.0.0. the web page will respond. Access to web page through Automation server is possible also for the newer version, but not "local" access. Runtime (Codesys control for linux SL) is on 4.17.0.0. I have tried to manipulate settings for 'Access-Control-Allow-Origin' '*' always; through nginx (normally a proxy_pass to localhost:8080). Also tested bypassing nginx by accessing 8080 directly with the same result.
Last updated: 2025-09-08
Post by snhatton on OpC UA server on Raspberry Pi 64 SL runtime
CODESYS Forge
talk
(Post)
Good afternoon, After changing the security settings to: CommunicationPolicy: POLICY_BASICSHA256SHA256 CommunicationMode: ALL Activation: Activated UserAuthentication: ENABLED Then generate a new certificate on the device for the OPC-UA server from Security Agent->Device->OPC UA Server. Restart the runtime using tools->Update Raspberry Pi->Stop->Start for the changes to take effect. It may take a minute for the runtime to start. Initiate the connection from the UA server side. You should see a pop-up asking you to trust the certificate. Click on the button 'Trust Server Certificate'. Next, you should see a certificate in the quarantined folder of the security agent in CODESYS. Click and drag this from quarantined to trusted and then try connecting from UA expert to the device. These steps worked for me and my setup and I hope they can help you!
Last updated: 2023-12-11
Post by cedriclee on RaspberryPI reconnection error
CODESYS Forge
talk
(Post)
"Hello, I'm Cedric Lee, a PLC engineer based in Korea. I'm reaching out about an ongoing issue with the connection when attempting to control Beckhoff modules using Raspberry Pi with CODESYS for the first time. I use CODESYS to target the Raspberry Pi's IP, install version 4.10.0.0 of the CODESYS Runtime Package, and upon pressing Start in the Runtime, the target connects to the Raspberry Pi. However, within about a minute, an error window appears, stating 'no connection to the device. please rescan your network,' leading to the disconnection of the target. This cycle repeats. I've attached some pictures for your reference. I'm using CODESYS Development System V3, Raspberry Pi 4 Model B (installed as 64-bit), and Beckhoff EK1100 modules. If anyone has a solution to this issue, please help. Your assistance is greatly appreciated."
Last updated: 2024-01-11
Post by alexgooi on Function Blocks and arrays of function blocks
CODESYS Forge
talk
(Post)
Hi Jack, I think you have to look at a FB in a different way. A Function block (Class) can contain its own data. In other words don't define loose data in your GVL, but define a instance of a FB (Object) in your GVL: Example: Function_Block Basic_Class VAR_INPUT Open_Command: BOOL; END_VAR VAR_OUTPUT Opened: BOOL; END_VAR if Open_Command then Opened := TRUE; ELSE Opened := FALSE; END_IF Global Variables Objects: ARRAY[1..100] OF Basic_Class; //Here you ar defining you objects END_VAR In your code you can directly acces the data and couple it to the IO: GVL.Objects[1].Open_Command := %IX0.0; %QX0.0 := GVL.Objects[1].Opened; //To call the code itself use: GVL.Objects[1](); If you want to take this a step further you are also able to add methods and properties to the FB/Class end thereby creating a OOIP program
Last updated: 2024-02-15
Post by struccc on Release SP20 - Changes in behaviour?
CODESYS Forge
talk
(Post)
This... is not very practical for me - as I have a bunch of different classes - it's just doesn't seems to be very practical to define a NULL for each of them... Something like this I use in parameter definitions. For example: VAR_INPUT refVFD_Drive : REFERENCE TO FB_VFD_Drive := GVL_DUMMY.Dummy_VFD; END_VAR I use this to prepare objects for code I don't control: Typycally visualizations - had many troubles with references set on the fly, right before opening a corresponding visualization... And yes, the instance in GVL_Dummy reports itself as "Fake", so it does not influence the actual application at all. Actually this way I could invalidate a reference, just to set it to a "Dummy" instance.
Last updated: 2024-03-25
Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
The way I usally tackle this is by syncing only words (then you are able to use the FB above). If you then want to write a Boolean simply type it like this. Value[1].0 := Bool1; Value[1].1 := Bool2; Value[1].2 := Bool3; Uints have the same number of bits than a INT/WORD so these ones will work as well (they are only represented diffrently). A Real will work but you will loose some infomration in the conversion. If you want to keep the information you can convert 2 words to a float with a function (for example with the IEEE-754 standard) . In this way the syncing to the server is very simple and in the Codesys Program you decide what part of the word you want to use.
Last updated: 2024-04-03
Post by valenting on Can't use new licensing with Raspberry Pi
CODESYS Forge
talk
(Post)
Hi, I'm using Codesys control for Raspberry Pi in the latest version (4.11.0.0) When I try to install a license with the new application-based licensing, I have an error "returncode 403046401" (using codesys SP18) I updated to codesys SP20, and now I get the following error: "The selected conainer [0]: SN=..., Version=1.18, Chip=0, Rev=0 does not fit to your ticket. Please select a suitable one." The license I'm trying to install is a Codesys Control Basic L license, with a Codesys Visualization L option, according to the needs of my application. What can I do to activate my license ?
Last updated: 2024-04-22
Post by rafael on Wbm/runtime and visualization login
CODESYS Forge
talk
(Post)
Hello everyone, I’m trying to understand if it is this way or I can change it. I’m making a PLC code and visualization screens, the ideia is to operate via webvisu some controls. So i made a code, made some screens and when i try it in my web browser, first it asks me to insert te user and password of the wbm/runtime of the plc (user: admin, password: wago by default), then i can acess my screens but I have to login again with the user and password that i created in the visualization user managment. My question is: is there a way to disable this first login to the visualization screens (webvisu)? Or create another user/password for this first screen? I have a PFC200 and a Edge Controller, both are working the same way. Thanks in advance Thanks
Last updated: 2024-06-25
Post by msegon on OPC UA Client failed to connect
CODESYS Forge
talk
(Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I'm trying to read data from Tridium Niagara 4.15 OPC UA Server, but I get the error BadCertificateInvalid. As far as I understand, you need to add a CA certificate somewhere to establish a secure connection, but I don't know where. 2025-10-27T09:06:43.247Z, 0x0000008d, 4, 0, 0, * ERROR: OpcUa_Channel_BeginConnect: Cannot create secure channel without certificates! 2025-10-27T09:06:43.247Z, 0x00001090, 4, 0, 0, * ERROR: Datasource: Error Failed (268468242) in state Connecting I tried communicating without encryption, but it doesn't find the point. Has anyone managed to establish encrypted OPC UA communication?
Last updated: 2025-10-28
Post by pernockham on Trend legend naming and access/config to/of trend/legend-variables
CODESYS Forge
talk
(Post)
Trying the web-version of trend-data. This seems to be a impressive tool, but I lack/cant find a number of what I would think are important parts. There does not seem to be a way to get away from the dot.notated variable naming in the legend.. A developer might want the dot-notation but an end-customer will surely not. For instance I want to display 12 temperatures, instead of t1, t2 etc.. they will be named. gvl_io.unit[1].trend.temps.t1_a gvl_io.unit[1].trend.temps.t1_b gvl_io.unit[1].trend.temps.t1_c gvl_io.unit[1].trend.temps.t2_a .. gvl_io.unit[1].trend.temps.t4_b.. gvl_io.unit[1].trend.temps.t4_c.. Quite a lot of unnecessary text/data taking space from the actual trend => Is there a way to access/interface the legend-data programmatically so I can change the presentation/naming?
Last updated: 2025-12-16
Post by swol on HTML 5 - Controls -> Change Content-Security-Policy settings
CODESYS Forge
talk
(Post)
Sorry for being late to the party... so it is not possible to use the webbrowser tool to display external websites in a visu anymore? As it is not possible to simply "adjust the ContentSecurityPolicyIncludeTrustedOrigins setting in the automatically generated webvisu.cfg.json file" as stated in the docs? We need to display data read from a Raspberry Pi (part of our computer network) in our webvisu. We used to do it by entering the Pi's IP address as the URL variable in the webbrowser element but now (I don't know since when, I'm new on the job) "The page’s settings blocked the loading of a resource (frame-src) at 'IP address' because it violates the following directive: “default-src 'self' 'unsafe-inline'”. What are the options for displaying the data?
Last updated: 2025-11-11
Post by kporter on Codesys EtherCAT Driver (CmpEt1000MPD) can't set MAC address
CODESYS Forge
talk
(Post)
EtherCAT is a point-to-point protocol so it doesn't need a unique MAC address. It would be very useful to set the MAC address to 020000000000, the standard address for this kind of application. (The important bit is the 02 at the start of the address, which means locally-administered MAC.) The stock Windows driver can do this for my i210 card. But the CODESYS CmpEt1000MPD driver cannot. The image shows the setting with the Windows driver. If I set all my customers' cards to this address, then I don't need to deal with this when deploying my application. A simple PowerShell script can be used to set the MAC address once when the NIC is installed and the driver is changed.
Last updated: 2026-02-09
Post by dvmaris on Control for Linux ARM64-User Management issue
CODESYS Forge
talk
(Post)
I'm trying to work with Codesys Control for Linux ARM64 SL 4.18.0.0 on a Toradex Verdin NXP iMX8MP. I have the runtime installed and operational as well as Codemeter lite 8.40.7141.503 (arm64). I'm running 3.5.20.60 and when "Scan Network" I see the Verdin popup. When I try to connect to it, the "mandatory use of the user management" popup shows...which makes sense. I click YES and enter user information and click OK. It immediately displays a "No device is responding to the scan request" popup. The IDE can see the Verdin in the scan...so this popup does not make sense to me. I thought maybe it was a read only issue but I've made all partitions and paths RW. Has anyone experienced this? Can anyone tell me where it is trying to write user data?
Last updated: 2026-02-11
Post by pernockham on Unable to deploy "Control for Linux SL 4.18.0.0"
CODESYS Forge
talk
(Post)
And the strange thing for me is that if i connect with an older IDE version (where I only have 4.17.0.0 installed) I can see both "CODESYS Control for Linux SL" and "CODESYS Edge Gateway for linux". And that I loose (both presence and possibility to update) the first option (Control SL) if i let the updater install "Control for linux SL" vers. 4.18.0.0 or later. (Note that runtime 4.17.0.0 is installed and it is running and I can login to that system, but no apparent option available to update it to 4.19.0.0). Attached print screen where I connected the "deploy sl tool" to the same system, where the upper (IDE) one has 4.19.0.0 installed, while the lower one has 4.17.0.0 installed..
Last updated: 2026-02-17
Post by thim on Bibliothek mit C-Library erzeugt unerwarteten Fehler beim Aufsetzen des Projekts.
CODESYS Forge
talk
(Post)
Um eine C-Library als Codesys Bibliotheksfunktion zu erstellen, bin ich den fünf Videoanleitungen von https://de.codesys.com/news-events/gut-zu-wissen.html gefolgt. Das funktioniert auch am Anfang gut, ich kann unter x86-Linux und RasPi-Linux auch die C-Libraries kompilieren. Wenn ich dann die Library aber wie in Video 4 gezeigt in der Codesys-Bibliothek verknüpfen möchte, (siehe Screenshot) bekomme ich schon bei Auswahl der Datei und auch danach bei Klick auf "Geräte auswählen" den Fehler "Der Dateiname sollte mit dem Bibliotheksnamensraum enden." angezeigt. Meine *.so Datei endet aber meinem Verständnis nach mit dem richtigen Namen analog zum Beispiel und wie es auch in meinem Projekt heißt. Mir ist unklar, was mir diese Fehlermeldung anderes sagen will. Hat jemand eine Erklärung? (Codesys V3.5 SP 20 + (64-bit))
Last updated: 2024-08-22
Post by timvh on Codesys virtual control redundancy
CODESYS Forge
talk
(Post)
I think it depends on what you consider as redundant. Is it allowed to plug the network cable in another device (server), move the USB key with license to the other device (server) and then start it up? Or should it automatically switch over within msec and take over the communication with the I/O flawlessly without noticing the switchover? We helped several customers setting up the CODESYS Redundancy functionality and the nice thing is that when you have it up and running, you can easily switchover from active to passive and when you download a new applicaiton, CODESYS handles the update of boot project on the passive controller automatically. Sure this will require an additional license and the license for redundancy, but if your installation is that critical it should be worth it. Please contact us (Extend Smart Coding) if you need any further information. We could help you setup the configuration and possibly provide the licenses for it (I noticed you are situated in the Netherlands).
Last updated: 2025-09-04
Post by charleskirkland on Connect to Azure IoT Hub
CODESYS Forge
talk
(Post)
It sounds like your TLS setup is basically correct, since the handshake works via OpenSSL, so the issue is likely on the CODESYS side rather than the certificates themselves. From what I’ve seen with the Azure IoT Hub Client SL library, you should double-check that the SAS token is actually being generated and passed correctly to the function blocks (especially wsDeviceSaS) and that the MQTT/HTTPS FB is really triggered cyclically-otherwise the controller won’t initiate the connection at all. Also, make sure DNS, time (NTP), and full certificate chain trust are properly configured on the controller, since IoT Hub authentication depends on them even when using SAS tokens. Another thing worth checking is the library/runtime version-there are reports that certain versions changed behavior and caused connection issues. I’d recommend starting with the official demo project (AzureMQTTDemo) and comparing it step by step with your setup to see what’s missing or not triggered. Speed Stars
Last updated: 2026-04-27
Post by mondinmr on COL.IMap2 and HashTableFactory cause frequent Access Violation
CODESYS Forge
talk
(Post)
Good morning, I’ve been using the Collection library for a long time, mostly with Stack, LinkedList, and List. From your examples I was able to manage the different factories, even for custom elements. Now I need a hashtable, but with this object I’m running into a lot of random access violations. If I append something inside FB_Init after constructing the hashtable, it crashes, even though the list was already created. If I only create the hashtable in FB_Init and append afterwards, it usually works. I don’t understand the meaning of the dispose call in this code: pSlave := ADR(slave); uSlave := TO_ULINT(pSlave); iKey := fKey.Create(uSlave); IF hash.CountKeys() = 0 THEN Service.logger.appendLog('Filling hashtable', 'HashManager', AdvLogType.AdvDebugMsg); ok := FALSE; ELSE eError := hash.ContainsKey(iKey, xResult => ok); END_IF IF NOT ok THEN pI := __NEW(UINT); iVal := fKey.Create(TO_ULINT(pI)); Service.logger.appendLog(CONCAT('New slave', TO_STRING(uSlave)), 'HashManager', AdvLogType.AdvDebugMsg); hash.AddKeyValuePair(iKey, iVal); appendNewSlave := pI; ELSE eError := hash.GetElementByKey(iKey, itfValue => iElem); xResult := __QUERYINTERFACE(iKey, itfIInstance); IF xResult THEN itfIInstance.Dispose(); END_IF IF eError <> COL.COLLECTION_ERROR.NO_ERROR THEN Service.logger.appendLog(CONCAT('ERROR ', TO_STRING(eError)), 'HashManager', AdvLogType.AdvCriticalMsg); appendNewSlave := nullptr; RETURN; END_IF __QUERYINTERFACE(iElem, iVal); {warning disable C0033} pI := TO___UXINT(iVal.UlintValue); {warning restore C0033} appendNewSlave := pI; END_IF Without the dispose call, every second cold reset crashes immediately when I try to access iVal, even if eError doesn’t report any error. With the dispose call, the cold reset issue disappears, but I get other problems: a) If I start the runtime using systemctl start codesyscontrol, it crashes at IF hash.CountKeys() = 0 THEN b) If I delete the files in PlcLogic and download again, it works and survives multiple cold resets. But as soon as I run systemctl restart codesyscontrol, everything gets corrupted again and it starts crashing at that point. FUNCTION_BLOCK SlaveMapCounter VAR hash : COL.IMap2; eError : COL.COLLECTION_ERROR; END_VAR In its FB_Init I create it: METHOD FB_Init: BOOL VAR_INPUT bInitRetains: BOOL; // TRUE: retain variables are initialized (reset warm / reset cold) bInCopyCode: BOOL; // TRUE: the instance will be copied to the copy code afterward (online change) END_VAR VAR hF : COL.HashTableFactory; END_VAR hash := hF.Create(256); In another FB I instantiate it statically: FUNCTION_BLOCK ABSTRACT AbstractServoEthercatController EXTENDS AbstractServoController VAR_STAT hashSlaves : SlaveMapCounter; END_VAR VAR field : REFERENCE TO ADVAbstractFieldUnitEthercatCia402; initCnt : REFERENCE TO UINT; END_VAR The append method is the one shown above, and I call it after the runtime has started. The accesses are performed by a single task, and in any case I’m working on an isolated single core. I’ve tried everything, moving the create, the instances, and all the rest several times, but nothing seems to work. I’d like to point out that these FBs are part of our own library, which is used in many applications.
Last updated: 2025-09-11
Post by bbm1995 on Security Screen - Custom Certificates for OPC UA Server?
CODESYS Forge
talk
(Post)
Hi everyone, is it possible to use selfsigned/created certificates (eg. with X - Certificate and Key Management) as a OPC UA Server certificate in the Security Screen? As far as I know I can only upload client certificates to the PLC and move it to "Trusted", "Untrusted" and "Quarantined". Same question is on sps-forum.de
Last updated: 2023-08-23
Post by ryandmg on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
Ohhh OK. Yeah this seems to be timing like you said. Yeah I read through that document and came to the same conclusion. I haven't tried setting them both to 200ms. Maybe I'll give it a shot. Thanks so much for your input. Its greatly apreciated.
Last updated: 2023-09-06
Post by lucaver89 on Raspberry pi 3 and runtime 4.9.0.0
CODESYS Forge
talk
(Post)
Good morning, I'm using a raspberry pi3 as plc with the runtime 4.9.0.0. My program has many of retrain variables but when an update is performed the retrain variables comes back to default values. Is the a way to backups the retrain variables n a csv file? Is still the way to restore them from the csv? Thank you for helping Luca
Last updated: 2023-09-23
Post by callumo1 on Check For Open Dialogs On Client
CODESYS Forge
talk
(Post)
Is it possible to make a function that checks to see if there are any open dialogs on a given clients. I think VisuDialogs.VisuDlgUtil_IsDialogOpen does this for a given dialog name, but is it possible to do this for any dialog. Appretiate any help Cheers Callum
Last updated: 2023-09-25
Post by transmin01 on SafetyApp - "Invalid ERR Ack input"
CODESYS Forge
talk
(Post)
Hi, I am trying to get a basic safety application to download but I keep getting an "Invalid ERR Ack input" and "The Standard Inputs Size of zero is not allowed". I am simply using 2 safety inputs through an "AND" block to 2 safety outputs. Any help would be appreciated. Regards Trevor.
Last updated: 2023-09-27
Post by transmin01 on SafetyApp - "Invalid ERR Ack input"
CODESYS Forge
talk
(Post)
Hi, I am trying to get a basic safety application to download but I keep getting an "Invalid ERR Ack input" and "The Standard Inputs Size of zero is not allowed". I am simply using 2 safety inputs through an "AND" block to 2 safety outputs. Any help would be appreciated. Regards Trevor.
Last updated: 2023-09-27
Post by totorovic on CSVReaderInit returns error : INVALID_HANDLE
CODESYS Forge
talk
(Post)
We changed the path where the CSV file is. From intern memory of the IPC to a USB key. We still have this error 'INVALID_HANDLE'. We must restart the Codesys runtime to clear it. That is a big problem for us because machine is in production. @eschwellinger What do you mean by "this is a security issue not to read/write in the plc allowed path"
Last updated: 2023-10-27