Post by fmon on Modbus : dis- / re-connect cable: modbus does not re-start
CODESYS Forge
talk
(Post)
Problem solved The client modbus cycle time was linked to a task at 500ms. Whereas the channel modbus was at 200ms. Certainly problem of packages synchronisation. I let the client modbus cycle time to be handled by itself (See attachement) --> "Use the bus cyle time parameters" (traduce from french) See attachement
Last updated: 2025-03-18
Modbus : dis- / re-connect cable: modbus does not re-start
CODESYS Forge
talk
(Thread)
Modbus : dis- / re-connect cable: modbus does not re-start
Last updated: 2025-03-18
Post by atone on Change IO-Link Device Interface connected to a Profinet-Slave at Runtime
CODESYS Forge
talk
(Post)
I need to be able to update (change) the interface of an IO-Link device at runtime. The reason is the connected sensor can be selected at runtime, and some sensors we use have a 2 byte IN interface, others have a 4 byte IN interface, others 16 byte IN, others 16 byte IN/OUT (see attached screenshot). Is it possible at all? When yes, which function should I use? Thank you!
Last updated: 2025-03-18
Post by peterkcontrols on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
Sorry to clarify the issues say as per the attached image. I copied and pasted the unresolved issues from someone else who had a similar problem.
Last updated: 2025-03-18
Post by eschwellinger on codesyscontrol.log exzessive Größe
CODESYS Forge
talk
(Post)
/var/opt/codesys/codesyscontrol.log auf dem PI.
Last updated: 2025-03-18
Post by peterkcontrols on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
Hello I am trying to download my project onto my Codesys Control RTE x64 soft PLC. and I have had an issue when downloading. [FATAL ERROR] Unresolved reference: 'SYSETHERNETADAPTEROPEN' [FATAL ERROR] Unresolved reference: 'SYSETHERNETADAPTERCLOSE' [FATAL ERROR] Unresolved reference: 'GETNUMBEROFADAPTERS' [FATAL ERROR] Unresolved reference: 'GETADAPTERINFO' [FATAL ERROR] Unresolved reference: 'SYSETHERNETIPFRAMERECEIVE' [FATAL ERROR] Unresolved reference: 'SYSETHERNETETHFRAMESEND' [FATAL ERROR] Unresolved reference: 'SYSETHERNETETHFRAMERECEIVE' [FATAL ERROR] Unresolved reference: 'SYSETHERNETIPFRAMESEND' [FATAL ERROR] Unresolved reference: 'SYSETHERNETFRAMERELEASE' Looking on the forum I have found other people had to install the network driver, which I have done following this youtube video by codesysGroup: https://youtu.be/10oj4wABaKc?si=664l83JXUGQSDlAe I have added the network driver, please see attached image. I have checked my BIOS to make sure my secure boot status is disabled, see attached image. when I go to component manager, the drop down menu doesnt have the new network adapter, see attached image. I have not yet purchased or installed any licenses is that what I am missing? What other reason is there that I can't download to the runtime. Thanks
Last updated: 2025-03-18
Post by peterkcontrols on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
Sorry to clarify the issues say as per the attached image. I copied and pasted the unresolved issues from someone else who had a similar problem.
Last updated: 2025-03-18
Post by peterkcontrols on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
I am using Codesys Control RTE V3 Version 3.5.21.0 I am not sure what you are asking. Which hardware ID has the network interface card? I have ran ipconfig /all and attached an image. Let me know what other information I can provide to you to help troubleshoot this problem. Thank
Last updated: 2025-03-18
Post by eschwellinger on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
is this latest Control RTE Version? Strange is that the component does not occure in the list of component to add.
Last updated: 2025-03-18
Post by eschwellinger on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
which Hw id has your nic in the windows device manager?
Last updated: 2025-03-18
Post by nz-dave on Ethernet/IP Scanner Exception
CODESYS Forge
talk
(Post)
Hi Trusty-Squire, just seen you post , thanks for the reply. I was out on site the other day as it had done it again and changed a few things like cycle time etc. plc load is only 7% at its highest. I took a few screenshots while i was there to add to this post. its been up for about a week now but seems to happen at random every couple of weeks. fingers crossed!
Last updated: 2025-03-19
Post by tk096 on Sm3_math
CODESYS Forge
talk
(Post)
Hi, SM3_Math is actually an internal library of SoftMotion. You can use it. The only restriction is that there is no compatibility guarantee - meaning that POUs in the library may change their interface, get moved/renamed/removed... in future versions of SoftMotion.
Last updated: 2025-03-19
windows runtime crashes.
CODESYS Forge
talk
(Thread)
windows runtime crashes.
Last updated: 2025-03-19
Ethernet/IP Scanner Exception
CODESYS Forge
talk
(Thread)
Ethernet/IP Scanner Exception
Last updated: 2025-03-19
Post by patrik on windows runtime crashes.
CODESYS Forge
talk
(Post)
Faulting application name: CODESYSControlService.exe, version: 3.5.20.30, time stamp: 0x66ebc91d Faulting module name: unknown, version: 0.0.0.0, time stamp: 0x00000000 Exception code: 0xc0000005 Fault offset: 0x0000028010670e31 Faulting process id: 0x0x1F50 Faulting application start time: 0x0x1DB1BA284347B9C Faulting application path: C:\Program Files\CODESYS 3.5.20.30\GatewayPLC\CODESYSControlService.exe Faulting module path: unknown Report Id: d3ac6a03-667a-4d61-ab36-d2ae703fc252 Faulting package full name: Faulting package-relative application ID: My runtime crashes from time to time. I'm not getting anything in the PLC logs. This is from the windows logs. Can anyone help me understand why this is happening?
Last updated: 2025-03-19
Change IO-Link Device Interface connected to a Profinet-Slave at Runtime
CODESYS Forge
talk
(Thread)
Change IO-Link Device Interface connected to a Profinet-Slave at Runtime
Last updated: 2025-03-19
Post by atone on Set DeviceID of an IO-Link Sensor at Runtime
CODESYS Forge
talk
(Post)
I need to be able to change (set) the DeviceID of an IO-Link sensor (see DeviceID.png) at runtime. I tried with both ProfinetCommon.PN_PortConfiguration and ProfinetCommon.IOL_PortConfiguration, but I get an error for both when I try to read the port configuration (see PN_PortConfiguration.png). Does one of those FBs is the right one for my purpose? Do I possibly make a mistake when assigning the parameter IOLD_ID/IOLM_ID?
Last updated: 2025-03-19
Post by otbeka on CAA File Handling: "Read only" error
CODESYS Forge
talk
(Post)
Hi, On CODESYS V3.5.19.50 I am using the latest 3S File Access library (CAA File & CAA Types) to save and retrieve configuration data from the User Data section of an SD card, via file called config.txt. The application reads the file to memory once upon initialisation, and then the only other operation is overwriting the file with the updated configuration whenever the user changes the settings. An issue is ocurring, seemingly randomly, where the config.txt file, and all surrounding directories, cannot be written to by the unit, returning a READ_ONLY_CAA error upon file open. This sometimes does not clear even after power-cycling the PLC several times, yet checking the file permissions with ls -l shows normal read, write, and execute access. I am wondering if this is caused by the PLC itself or by an issue in my application. I have included my CAA File handler function block (SD_Card_Bin(FB).txt) and any associated types/calls below: TYPE ConfigData : STRUCT Config : ARRAY[0..256] OF STRING(64); NumberOfStrings : UDINT; END_STRUCT END_TYPE TYPE Buffer : STRUCT Data : ARRAY[0..SIZEOF(ConfigData)] OF BYTE; DataLength : UDINT; END_STRUCT END_TYPE A case within my MAIN PRG: mode.WriteConfigDataToFile: VisuElems.CURRENTVISU := 'Screen_Write'; IF xModeHasChanged THEN iErrorCount := 0; iRoute := 0; END_IF CASE iRoute OF 0: inBuffer := ConfigData_To_Buffer(GVL.UnitData); xConfigError := FALSE; xDataConfigured := FALSE; iRoute := 1; 1 : //Read Data from Card SD_Card_Bin.strFileName :=FileName; SD_Card_Bin.iFileOperation := 2; SD_Card_Bin(xExecute :=TRUE, WriteBuffer := inBuffer, xDone =>xDataConfigured, xError=>xConfigError, strErrorCodes=>strError); IF xDataConfigured THEN SD_Card_Bin(xExecute :=FALSE); IF xConfigError THEN iRoute := 32767; ELSE iRoute :=100; END_IF END_IF 100: // The end bCurMode := mode.DisplayProcessVariables; 32767: // Config error iErrorCount := iErrorCount + 1; IF iErrorCount > 2 THEN // Repeats 3 times, if no progress abandons and returns error bCurMode := mode.WriteError; ELSE iRoute := 0; // Try again END_IF END_CASE I'd like to rule out my application as the cause of this bug - help via comments or criticism would be greatly appreciated.
Last updated: 2025-03-19
Post by peterkcontrols on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
Resolved this. There is a config file called CodesysControl_User that I had to edit to set the driver to component 5. I deleted the semi colon next to Component.5=CmpEt1000Drv
Last updated: 2025-03-19
Professional Developer Edition (git): Invalid URI
CODESYS Forge
talk
(Thread)
Professional Developer Edition (git): Invalid URI
Last updated: 2025-03-19
Post by r-c-r on SM3RaspiStepper 0.0.0.6 issue
CODESYS Forge
talk
(Post)
Hello, I noticed that version 0.0.0.6 is now available, so I tested it using CODESYS V3.5 SP19 Patch 7 and SoftMotion 4.17.0.0. While the project compiles and downloads without issues, I encountered a problem with the 'Enable: GPIO pin number that is set when the axis is enabled (with MC_Power) (0: not used)' functionality — it no longer works (HIGH level not present at the output pin). I observed the same behavior with version 0.0.0.5, whereas version 0.0.0.4 functions correctly. Could you help me identify what might be causing this issue or suggest how to resolve it? Thanks.
Last updated: 2025-03-19
Engineering Dissertation Help & Assignment Assistance.
CODESYS Forge
talk
(Thread)
Engineering Dissertation Help & Assignment Assistance.
Last updated: 2025-03-19
Post by lacypaige on Engineering Dissertation Help & Assignment Assistance.
CODESYS Forge
talk
(Post)
This thread is for discussing engineering dissertation help, including research methods, choosing a topic, writing, and data analysis. Whether you need advice on structuring your dissertation, understanding industry trends, or solving research challenges, this is the place to ask questions and share ideas. Feel free to exchange tips, discuss best practices, and get support with engineering assignments and dissertations.
Last updated: 2025-03-19
Codesys Symbolic Access
CODESYS Forge
talk
(Thread)
Codesys Symbolic Access
Last updated: 2025-03-20
Post by respl on Codesys Symbolic Access
CODESYS Forge
talk
(Post)
We need to exchange data between two controller IFM and EXOR. Our one controller support codesys symbolic access while other support COdesys V3 application. can anybody tell me how to do communication between these two. Sample program will be highly appreciable. Regards, Rahul Sayre
Last updated: 2025-03-20