I got this working using OPC UA. In the logic application I just added a Symbol Configuration. In the HMI application I added a Data Sources Manager and OPC UA Data Source. The one thing I don't like is the way the tags end up being named in the HMI application. In the logic application I have a program named PLC_PRG. It has a variable named testDINT. In the HMI application the name I get for this variable is DeviceSet.CODESYS_Control_Win_V3_x64.Resources.Logic.Programs.PLC_PRG.testDINT. This is very long and looks like it could change if I used this on a different device type. Any ideas how I could get this name shortened down to just PLC_PRG.testDINT like it is on the Logic application?
Last updated: 2025-03-06
Post by timvh on Problem Reading Registers via Modbus from non Codesys device
CODESYS Forge
talk
(Post)
According to the documentation: https://wiki.teltonika-networks.com/view/RUT956_Modbus You need to create a Channel to read 2 registers from address 143 to get the lattitude. It doesn't specify if you need to read it as a Holding Register or as an Input Register. You could try both. So in the Teltonika router, you need to enable it as being a Modbus Server. Then in CODESYS add an Ethernet Adapter, then a Modbus Client (Master) and to the Client (Master) add the Modbus Server (Slave). Set the IP address and add the Channel. The please consider that CODESYS doesn't update any variables when they are not used in the application. In the I/O mapping tab of your I/O configuration, you can set the "Always update" to enabled.
Last updated: 2025-03-08
Post by spiessli on Objects in OPC UA Information Model
CODESYS Forge
talk
(Post)
Hi, I have an OPC UA information model with objects defined in it. I can import the model and use the data types defined in it and create instances of these types. These instances are accessible at Root > Objects > DeviceSet > CODE[...] > Resources > Application > GlobalVars > OPC_UA_Symbols for created instances and at [...] > Programs > PLC_PRG for mapped instances. The object defined in the information model is accessible in UA Expert by the name I have defined in the information model (Manipulator) at Root > Objects > Manipulator. How can I assign values to the Variables defined in the object "Manipulator"? Cheers, spiessli
Last updated: 2025-03-27
Post by eaglealex on Length of string and Array of bytes
CODESYS Forge
talk
(Post)
Hello! I have tried read a file to the string variable. But I faced a problem - there is about 2800 bytes of information in file, but string have a limit 2393 bytes. I made two variables with same address (for automatic convertion) - string[3000] and array of bytes[1..3000]. And I noticed that array of bytes contains all information from file, but string shows only first 2393 bytes. So I have lost information. Is there really such a limitation? Or I have an error in my program and Codesys 2.3 have no limit for such kind of conversation between string and array of bytes? Thank you very much!
Last updated: 2025-04-01
Post by imdatatas on Programmatically change Tappet on a cam
CODESYS Forge
talk
(Post)
Yes, There is. As explained "Manual creation of CAM structure" on below section. Likewise tappet structure also can be create manual and value of the switching point can be change during IEC program running. https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_basic_cam_programmatic_creation.html Just create a cam table and define some tapped points as sample for your project. Then on project compile, the created cam tapped data is converted internally into a global variable list. By clicking "Display generated code" in the "cam editor", you can display the automatically created global variables for both cam & tappets. Regards, Imdat
Last updated: 2025-04-02
Post by benemenn on OPC UA Method - How to wait for result?
CODESYS Forge
talk
(Post)
so from what i've learned. Codesys OPCUA Server can only provide OPC UA Methods, when they are created in an XML Model beforehand. So you have to create the XML Model with OPC UA Methods. Then load that model into codesys and create the IEC Blocks. This is automated Code and will create all the variables and Methods from your XML Model. Then they will be displayed on discovery with an OPC UA Client. As far as I understood. There is no way for Methods to be shown in OPC UA when not using an external XML Informationmodel. Codesys can not yet create the informationmodel on itself. Regards
Last updated: 2025-04-02
Post by benemenn on OPC UA Method - How to wait for result?
CODESYS Forge
talk
(Post)
so from what i've learned. Codesys OPCUA Server can only provide OPC UA Methods, when they are created in an XML Model beforehand. So you have to create the XML Model with OPC UA Methods. Then load that model into codesys and create the IEC Blocks. This is automated Code and will create all the variables and Methods from your XML Model. Then they will be displayed on discovery with an OPC UA Client. As far as I understood. There is no way for Methods to be shown in OPC UA when not using an external XML Informationmodel. Codesys can not yet create the informationmodel on itself. Regards
Last updated: 2025-04-02
Post by bjarne-pagaard on Global Variables
CODESYS Forge
talk
(Post)
Old thread, I know - but it still has good answers. I would like to add a bit of info to it, as I was having a problem that lead me to this thread, but didn't give an exact answer. I am porting a project to a different PLC architecture. (Wago PFC300) A GVL named 'GVL' in the POUs section of my project was shadowed by a PLC-specific library in the Application->Library Manager. So all the existing references in the device specific code to 'GVL.something' would not resolve. Right-clicking the GVL in the code and 'Go to definition' would point me to the library in the Application Library Manager. All I had to do from there, was right-click the library, and set the property 'Only allow qualified access to all identifiers' in the library.
Last updated: 2025-04-11
Post by kut69 on Retain / Persistent Variables in Codesys for Raspberry Pi
CODESYS Forge
talk
(Post)
Hi, I am interested in details about the .ret file in the filesystem. I have already a project where the file is used (write on demand, read by start) and I want to share it as 'default input' for test devices using the identical application. Opening the .ret file content in a hex editor (I only use a single string retain var) I asked myself what the meaning of the first 24 bytes is. It neither contains a handle to the application nor a reference to the variable. Is this maybe a timestamp? Or a CRC/checksum? Regards, Thomas
Last updated: 2025-05-19
Post by rer-code on Codesys 3.5.18.60 – Application Loss and Persistent Data Corruption
CODESYS Forge
talk
(Post)
Hi, I’m currently managing over 50 PLCs running Codesys version 3.5.18.60. At seemingly random intervals, some of these devices experience a failure where: All persistent variables are lost. Attempting to log in results in the message: “The application does not exist on device. Do you want to create it and proceed with download?” The log shows: “Loading retain-data/bootproject failed.” From what I’ve gathered, this may be due to a corrupted persistent data file, but I’m not entirely sure how to confirm or resolve this issue. If anyone has encountered something similar or has suggestions for troubleshooting or preventing this, I would greatly appreciate your input. Best regards
Last updated: 2025-08-19
Post by sumit on Remote Ethernet/ip Adapter communication with scanner running on codesys
CODESYS Forge
talk
(Post)
Hello there, I have my ethernet/ip adapter (from Texas Instrument) running on Texas Instrument Board and I have configured the scanner on codesys. I have mapped the I/Os and I can see (on wireshark) the frames coming from adapter but I don't see my input variables in scanner get updated, they just stay at 0. I wanted to see the real data that has been sent from adapter to scanner on codesys. I am not sure if the problem is in I/O mapping or there is a step/s that I have missed. I have attached the screenshot of my project for your ref. Thank you, Sumit
Last updated: 2023-12-15
Post by sumit on Remote Ethernet/ip Adapter communication with scanner running on codesys
CODESYS Forge
talk
(Post)
Hello there, I have my ethernet/ip adapter (from Texas Instrument) running on Texas Instrument Board and I have configured the scanner on codesys. I have mapped the I/Os and I can see (on wireshark) the frames coming from adapter but I don't see my input variables in scanner get updated, they just stay at 0. I wanted to see the real data that has been sent from adapter to scanner on codesys. I am not sure if the problem is in I/O mapping or there is a step/s that I have missed. I have attached the screenshot of my project for your ref. Thank you, Sumit
Last updated: 2023-12-15
Post by fajean on Issues with "Add all instance path"
CODESYS Forge
talk
(Post)
In the past, we have routinely used the "add all instance paths" function to automatically add variables to VAR_CONFIG lists. My recollection is that compiling a project did not require VAR_CONFIG to be fully populated, and, once successfully compiled, instance paths could be added. Errors related to missing declarations, if I recall correctly, were thrown when downloading to the PLC, they did not prevent a successful compile. At some point, it stopped working. Missing declarations in a VAR_CONFIG now cause a compile error, so the application is never "current", the only reason I can see being the missing VAR_CONFIG declarations themselves (no other error). We observe the same behavior across all our projects. This is really aggravating, and I must be missing something simple. We use 3.5 SP17p3, 64 bits. Can anyone help?
Last updated: 2023-12-29
Post by macros8 on Translation - How to get text as reference in Frames translated?
CODESYS Forge
talk
(Post)
Hi, thanks for the link. Maybe I create elements in incorrect way. I always use Interface Editor to create variables which are used inside element (see pics). After that I place element in my visu and use Reference property to link variable or set the value. In that case the value of string is not transferred to general text list for translation as I mentioned before. Do I have to all properties which influence behavior of my element create in Frame configuration instead? What´s the difference to the Interface editor? Thanks a lot. M.
Last updated: 2024-01-02
Post by riccardo on Error while processing the visualization: Client id not present or no longer valid
CODESYS Forge
talk
(Post)
Hallo goodmorning, I am using codesys 3.5 sp19 with Weidmueller PLC. I created a page with several checkbox to manage an array of bool. When I build the project the system doesn't signal any error, when I go in simulation mode everything works until I click on checkbox to toggle the variables. Other visu elements works proprerly (e.g. bottons, lights, ect, ect) but the check boxes cause a crash giving the following error: Error while processing the visualization: Client id not present or no longer valid I serched to figure the problem out and to search a solution on the web but nothing. Can someone help? Thanks and Regards, Scanu
Last updated: 2024-01-23
Post by alexgooi on Function Blocks and arrays of function blocks
CODESYS Forge
talk
(Post)
Hi Jack, I think you have to look at a FB in a different way. A Function block (Class) can contain its own data. In other words don't define loose data in your GVL, but define a instance of a FB (Object) in your GVL: Example: Function_Block Basic_Class VAR_INPUT Open_Command: BOOL; END_VAR VAR_OUTPUT Opened: BOOL; END_VAR if Open_Command then Opened := TRUE; ELSE Opened := FALSE; END_IF Global Variables Objects: ARRAY[1..100] OF Basic_Class; //Here you ar defining you objects END_VAR In your code you can directly acces the data and couple it to the IO: GVL.Objects[1].Open_Command := %IX0.0; %QX0.0 := GVL.Objects[1].Opened; //To call the code itself use: GVL.Objects[1](); If you want to take this a step further you are also able to add methods and properties to the FB/Class end thereby creating a OOIP program
Last updated: 2024-02-15
Post by dhumphries on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
Does the device have a green icon next to it when the PLC is running? If not you have some kind of communication problem, wireshark may be picking up some data but the scanner may not be configured correctly to receive the data. Check the T>O and O>T bytes and make sure they match on both the scanner and adapter. I've had very little success loading a .eds file and having the configuration work without some manual configuration. If you have a green icon, have you enabled the device to always update variables?
Last updated: 2024-03-02
Post by khaledkhalil on Import OPC UA model to Codesys
CODESYS Forge
talk
(Post)
I have added a models in SiOME which a software to design nodes and add instances. and created a resultant xml file. I tried to import the xml file to Codesys through OPC UA information model Repository the problem i don't know how to view my objects which i have designed. and map it to my PLC to make viewable on my server UaExpert. I watched the tutorial video https://youtu.be/aJhzN3Uk-Do?feature=shared. But it only give you how to add the Information model, and my resultant model doesn't have information type. So how in Codesys i can view a model which i have designed in SiOME and mapped my instances (Objects, Variable or methods) with my Variables in PLC I saw people do it in Tia Portal or other Software, but i have no clue how to do it on CODESYS
Last updated: 2024-03-12
Post by esave on Stepper Drive with Ethercat
CODESYS Forge
talk
(Post)
Hello everybody I am new into Codesys. I have a stepper driver (EM3E-556E) from Leadshine. I want to controll the stepper driver via EtherCat to a ST programm but I dont have any function block or anything that i can use. I only have the XML-File wich I loaded. With it I implemented the drive as a Ethercat slave and now I see these variables. (See picture) I dont know how to controll the stepper drive. And the manufacturer doesnt provide support for me. Can anybody help me or atleast tell me how they would do it?
Last updated: 2024-03-14
Post by david24 on Map in Codesys
CODESYS Forge
talk
(Post)
Hello everyone, I have the task of programming a map. With the help of the visualization element "Table", I have managed to accomplish this. In the Input Configuration, I activated the option: "Write Variables", so that the user can change the values in the map. To test the program, I select the Online Mode (Simulation).There I change the values in the map. When restarting the program in CODESYS, the changes in the map are no longer there. Does anyone know an approach how to save the changes in the map? Thank you for your support Best regards David
Last updated: 2024-04-02
Post by esave on OPC UA Server with on Codesys + OPC UA Client on Labview
CODESYS Forge
talk
(Post)
Hello everyone I want a communication between my PLC as an OPC UA Server and Labview on my PC as the OPC UA Client. I have an Festo CPX-E-CEC-C1-PN PLC and I have the OPC UA Toolkit from Labview. I created some Variables for testing (see picture 1) on Codesys. I tried to use this Labview block diagram (see picture 2) but I cant connect the PLC to it. What do I have to type in the Server Endpoint URL and what in the Node ID? Is this a good way for communication with a PLC to a PC? If not is there another way?
Last updated: 2024-04-12
Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20
CODESYS Forge
talk
(Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20
Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20
CODESYS Forge
talk
(Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20
Post by gseidel on CNC / G01 Speed is very slow (or go-stop motion) in Continuous short segment .
CODESYS Forge
talk
(Post)
Hi k2saki, I would recommend to have a look at SMC_SmoothMerge, followed by SMC_SmoothPath. SmoothMerge will combine the small G1 elements to longer splines, SmoothPath will avoid stops between the splines. https://content.helpme-codesys.com/en/libs/SM3_CNC/Current/SM_CNC_POUs/SoftMotion-CNC/SoftMotion-Function-Blocks/SMC_SmoothMerge.html For SmoothMerge to work, you have to configure a tolerance, i.e. by how much it may deviate from the lines. To graph the output of the interpolator, you can use the trace. (Add a trace object below the application, and add the variables you are interested in to the trace.) Best regards, Georg
Last updated: 2024-04-30
Post by robpqs on Program from one PLC to other WAGO 750-8204
CODESYS Forge
talk
(Post)
Hello, You use the WAGOUpload tool. You can download it on the download center of WAGO. Make a backup and restore it on the new device. (if can check the remanent data to copy the persistent variables if necessary) You can also use a SD card, go to the WBM copy it the image to the SD card and restart the other controller on the SD card. In the WBM, copy it back to the internal flash. If you contact your local Wago office, they will more than probably help you. There is also a WAGO forum. RP,