Post by timvh on CODESYS: Combining Master Redundancy with EtherCAT Ring Topology – Is it Supported?
CODESYS Forge
talk
(Post)
Yes, this works (at least we have it running with Wago PLC and Beckhoff I/O), but the concept works. You need 2 PLC's with at leat 3 network interfaces. And 2 switches (can be unmanaged). See the attached simple diagram for the solution.
Last updated: 2026-02-05
Post by gatto on EXCEPTION [watchdog] how to find position cause
CODESYS Forge
talk
(Post)
hi. My plc is weidmuller UC20-WL200-AC, IDE CODESYS 3.5.20.40, see picture for task settings. sometime i've got the plc stop. Reading the log, I find: EXCEPTIONPOSITION : IP=0x(nil) (no IECcontext could be retrieved) component CmpIecTask EXCEPTION [Watchdog] occurred: App=[Application], Task=[TASK_O_MAIN] component CmpIecTask How to find the position of problem?
Last updated: 2026-02-06
Post by mait-tim on Unknown Type
CODESYS Forge
talk
(Post)
Hello, Im working with EPEC PLC's and working on the HMI and i'm running into the following errors: Unknown Type ISOImages.TargetContainer.TDS (and similars) I cannot locate the error and the source position is the visutalisation manager where i cannot find anything related to this type. Im working with: Codesys V3.5 SP18 patch 3 and i cannot update since the hardware does not allow for newer SP versions
Last updated: 2026-04-03
Post by gordonkeller360 on Equal Objects at Unstaged Changes - Git (Codesys Pro)
CODESYS Forge
talk
(Post)
Hi -- curious to know the same thing! Lots of "The objects are equal" randomly popping up... my solution (for now) is simply to commit the actual changes and then execute the rollback (git clean + checkout) on all that are giving me the issue in question. Does anyone know if this repairable?
Last updated: 2026-05-14
Post by gunstr on CODESYS control on RPi starts, shortly runs, then exits
CODESYS Forge
talk
(Post)
Thank you very much for the quick answer! The RPi hw were delivered last week so it's probably a resent version. I found an old scrapped board (2 years or so) with a broken GPIO that I tested with the same SD card image and with that board Codeys can run for the full 2h demo period without issues. Then I went back the the new board to test the 4.17.0.0 release but the installation fails... [INFORMATION] Standard output: create and install daemon [INFORMATION] Standard output: codesyscontrol started [WARNING] Unable to detect Raspberry Pi Architecture. Setting armv6l as default, you can change this through the settings panel. [INFORMATION] Standard output: codesyscontrol stopped [ERROR] Expected exit value of command failed: expected 0, received 1 [WARNING] Error setting the Raspberry Pi Architecture [ERROR] Error installing codesyscontrol Do you have any idea what could be the reason? I'm using an OS image including Python drivers for LCD and some I/O:s from last year to keep things stable, but also after upgrading with sudo apt update && sudo apt upgrade I still get the same error Reverting back to 4.15.00 works fine: [INFORMATION] Standard output: create and install daemon [INFORMATION] Standard output: codesysedge started [INFORMATION] Successfully installed codesyscontrol [INFORMATION] Successfully started CODESYS Edge Gateway for Linux [INFORMATION] Successfully started CODESYS Control for Raspberry Pi SL but as before the Codesys services stops after 30 seconds. And I noticed that the Codesys control stops and is not reachable also if I have no application loaded.
Last updated: 2025-09-02
Post by arnaud on eCockpit - unable to start simulation
CODESYS Forge
talk
(Post)
Hi there! I'm using eCockpit WAGO software to develop HMI's for multiple projects. As I recently starting this, my knowledge on the software is somewhat limited (so maybe my question is a simple one). For most of my projects I can simulate the application and start it to test the code and HMI. However for two projects, I can initiate the "simulation activation" but I cannot start it. Nothing happens when I press start and the visualization shows "The online visualization is waiting for connection. please start the application". - I don't see any errors in the messages - Initially the project are made by a colleague, which moved on. I guess I'm forgetting something, like missing a setting. I appreciate any help I can get. If you need more information to help me out, let me know. Thanks!
Last updated: 2023-08-25
Post by jonathan1321351 on IO-Link write parameters Ethernet/IP
CODESYS Forge
talk
(Post)
I want to read and write parameters of an IO-Link device using acyclic messages. I have a Cube67+ in Ethernet/IP, connected to an IO-Link master. In the datasheet, I can find the parameters required for the message (Service, Class, Instance, etc.). I see the function block "Set_attribute_single" in the "EthernetIP Services" library, but I'm not sure how to correctly send the index and sub-index for the IO-Link device. The class in the datasheet is 0x80 for the IO-Link Parameter Object, but it’s not present in the CPIClass enum. Is there another function block more suitable for configuring IO-Link devices? (similar to "iol_call" in PROFINET or what’s used in EtherCAT).
Last updated: 2024-09-02
Post by jonathan1321351 on IO-Link read/write parameters Ethernet/IP
CODESYS Forge
talk
(Post)
I want to read and write parameters of an IO-Link device using acyclic messages. I have a Cube67+ in Ethernet/IP, connected to an IO-Link master. In the datasheet, I can find the parameters required for the message (Service, Class, Instance, etc.). I see the function block "Set_attribute_single" in the "EthernetIP Services" library, but I'm not sure how to correctly send the index and sub-index for the IO-Link device. The class in the datasheet is 0x80 for the IO-Link Parameter Object, but it’s not present in the CPIClass enum. Is there another function block more suitable for configuring IO-Link devices? (similar to "iol_call" in PROFINET or what’s used in EtherCAT).
Last updated: 2024-09-04
Post by dkugler on Webvisu Combined Authentication
CODESYS Forge
talk
(Post)
you are able to do this all in one screen. It is possible to set the rights of every element to visible but not editable for the user "none". so everyone is able to see this elements, but can't do any changes. At the login button you set the rights to editable for the user "none" to be able to go to the login. Every element that should be hidden before logging in, set the rights visible and editable only for "higher" users. Hint: to change rights you are able to select more then one element and edit rights for all at the same time. Saves a lot of time! Good luck!
Last updated: 2025-09-03
Post by struccc on Release SP20 - Changes in behaviour?
CODESYS Forge
talk
(Post)
This... is not very practical for me - as I have a bunch of different classes - it's just doesn't seems to be very practical to define a NULL for each of them... Something like this I use in parameter definitions. For example: VAR_INPUT refVFD_Drive : REFERENCE TO FB_VFD_Drive := GVL_DUMMY.Dummy_VFD; END_VAR I use this to prepare objects for code I don't control: Typycally visualizations - had many troubles with references set on the fly, right before opening a corresponding visualization... And yes, the instance in GVL_Dummy reports itself as "Fake", so it does not influence the actual application at all. Actually this way I could invalidate a reference, just to set it to a "Dummy" instance.
Last updated: 2024-03-25
Post by pernockham on Unable to deploy "Control for Linux SL 4.18.0.0"
CODESYS Forge
talk
(Post)
The option to update "Control for Linux SL" is not shown in the "deploy control SL tool", I can see and update the gateway but not the control (3.5.21 SP4). Has the way to update control SL changed? In the process of fault finding I removed the control SL entirely from my target, then I had to revert to version 3.5.21.0 SP 1 to re-install "Control SL 4.17.0.0". So I thought it was just a matter of using SP1 to update also to 4.18.0.0, but after installing the files for 4.18.0.0 in the SP1-version, the behavior was identical to SP4, ie no Control for Linux SL shown in the deploy tool.. See screenshots.
Last updated: 2025-12-19
Post by baotthitawat on Cloud SCADA for Industrial Energy Monitoring
CODESYS Forge
talk
(Post)
Recently I’ve been exploring ATSCADA iEnergy Tools for SCADA-based energy monitoring systems. One thing I find interesting is how modern SCADA platforms are evolving beyond traditional machine monitoring. Many industrial systems are now using Cloud SCADA architectures for centralized energy management, remote dashboards, and operational analytics. ATSCADA iEnergy Tools supports: Real-time energy monitoring Historical data logging MySQL integration Reporting and Excel export Remote SCADA dashboards Cloud-based monitoring systems I think this type of solution is practical for factories, power monitoring applications, building management systems, and other industrial automation projects where energy optimization is becoming increasingly important. Industrial automation is clearly moving toward web-based and cloud-connected SCADA platforms, especially as more facilities focus on digital transformation and smarter energy management
Last updated: 2026-05-26
Post by baotthitawat on Cloud SCADA for Industrial Energy Monitoring
CODESYS Forge
talk
(Post)
Recently I’ve been exploring ATSCADA iEnergy Tools for SCADA-based energy monitoring systems. One thing I find interesting is how modern SCADA platforms are evolving beyond traditional machine monitoring. Many industrial systems are now using Cloud SCADA architectures for centralized energy management, remote dashboards, and operational analytics. ATSCADA iEnergy Tools supports: Real-time energy monitoring Historical data logging MySQL integration Reporting and Excel export Remote SCADA dashboards Cloud-based monitoring systems I think this type of solution is practical for factories, power monitoring applications, building management systems, and other industrial automation projects where energy optimization is becoming increasingly important. Industrial automation is clearly moving toward web-based and cloud-connected SCADA platforms, especially as more facilities focus on digital transformation and smarter energy management
Last updated: 2026-05-26
Post by climblinne on OPC UA Method - How to wait for result?
CODESYS Forge
talk
(Post)
Hello, I am already able to run an OPC UA method in Codesys. Now my question, how can I interact with other tasks (e.g. read an SDO from EtherCAT and return it by the function)? The OPC UA method seems to be called only once (I tried to return BOOL or UINT values). Up to now I only found to do a while loop to wait for the result of the other task. Is there a better way to do it? Is this the way OPC UA functions should be used (for "not too long" function calls) or should I use another mechanism (method: Start, event: Finish, method: getResult)? Regards
Last updated: 2025-01-13
Post by george32 on Learning ST in an object-oriented way.
CODESYS Forge
talk
(Post)
Dear all, I am currently creating a program in the ST language. Because the program is starting to grow nicely I would like to switch to a more object-oriented way of programming. (Like for example in Python). By surfing the internet I found out that Function Blocks is the best method for this. Now I would like to delve further into this, with all the possibilities that Function Blocks have only I cannot find a clear course, explanation of what everything is around the function block thing and how to approach everything. I find the standard documentation around Function Blocks rather abstract and the examples are minimal. Therefore I am looking for a page/course/document explaining object oriented programming in Codesys (or other PLC programming environment). Do you have any recommendations on this?
Last updated: 2025-06-10
Post by jeroenaero on Targetvisualisation full screen with CmpTargetVisu settings
CODESYS Forge
talk
(Post)
Hi, How can i display targetvisualization in full screen on the target device? I installed Targetvisu For Linux SL 4.16.0.0 on target device which contains Raspberry PI 64bit PIXEL desktop. When i connect my PLC program to the remote targetvisu, the targetvisu displays for 60% horizontally. We contacted CODESYS and they said it is a bug. they had a workaround, and with the settings below added to the file /etc/codesysvisualization/CODESYSVisualizationTV.cfg, the targetvisualization display for 100%, but with the taskbar at the top. VisuClient.BestFit=1 ;VisuClient.ScaleTypeIsotropic=0 VisuClient.FillWholeBackground=1 [CmpTargetVisu] WindowPositionX=0 WindowPositionY=0 WindowSizeWidth=1280 WindowSizeHeight=800 WindowType=2 How can we let it display fullscreen without taskbar?
Last updated: 2025-07-24
Post by dhumphries on How to determine code size
CODESYS Forge
talk
(Post)
I'm trying to determine which Codesys Control license I need, the Control Standard S has all the features I think I'll need, but the code size is limited to 3mb, I created a simple program with only 1 line of ladder logic and a simple visualization with a button and an indicator. When I generate code I get some messages, one indicates that the total allocated memory size for code and data is 2.1mb. Is this metric the correct size of the code? I question the size because it exceeds the allowable code size for the Basic S and Basic M licenses and consumes 2/3 of the available memory for the Basic L or Standard S license. What tool can I use to estimate the size of code as it relates to the runtime license limit?
Last updated: 2024-04-05
Post by matt-purcell on Which Lib to use, connect to a socket with URL instead of IP address
CODESYS Forge
talk
(Post)
Hello, I have a new project and I need to connect to a TCP socket using the URL instead of an explicit IP address, myendpoint@mydomain.com Which library is best suited for this? This is for a new enterprise project, the endpoint is a server in a datacenter running some real time application. We have big IP, it will automatically reassign the IP address to the backup server if a crash occurs so an explicit IP won't work for me. I've done this in RS logix, working now to migrate that code over to codesys. Thanks in advance!
Last updated: 2024-06-17
Post by rohan on Child Application Alarm
CODESYS Forge
talk
(Post)
Hi All, I'm trying to develop a multi-application project that allows me to switch between applications. I currently have a parent application and several child applications, as this is the only way for them to share CAN/Ethernet communication. I've noticed that I am only able to create an Alarm Configuration for the parent application. But the children application do not seem to be displaying alarms on the Alarm Table in the visualisation for when an alarm is raised. Does anyone know of a fix, solution or a way around this? I am utilising Codesys v3.5 SP16 Patch 5 64Bit
Last updated: 2024-06-21
Post by imdatatas on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
Dear @alimans, Additionally, As far as I know since starting from Softmotion V4.18.0.0 automatic restart behaviour for an axis has been changed for this issue. See below explanation from release notes. "With CODESYS SoftMotion 4.18.0.0, the behavior of SoftMotion axes after a loss of communication to the servo drive has changed. Now, an automatic reinitialization is performed as soon as the communication is established again. Before, an explicit call to SMC3_ReinitDrive had to be performed. An example for a loss of communication is that the cable to one of the drives is unplugged." Regards, imdatatas
Last updated: 2025-10-23
Post by egr99 on Modbus TCP Server connection is ESTABLISHED but all holding registers are value 0?
CODESYS Forge
talk
(Post)
You're absolutely right. Sorry for that. In the meantime I wrote a Function block to handle the reads and writes to the different attached RTU-devices. It processes the parameter like (str_Modbus:=(usiSlave:=1, uiFC:=5, uiLEN:=1, uiOFFSET:=0, uiInterval:=500)) and the corresponding output, waits for the response and processes next request in a 5-state procedure. It's working for 2 gateways (stable without errors, although error recovery is included). But nevertheless it should be possible with the Channel definitions of Codesys. Much easier to maintain :)
Last updated: 2026-04-08
Post by timvh on HTML5 visualization controls disabled on CODESYS Control for Linux SL - overlay not supported?
CODESYS Forge
talk
(Post)
I was able to reproduce this by doing something wrong. I guess what you did is first create an application for the Control Win, or some other device and then switched this to the Linux SL. But then the Visualization Manager still has the "TargetVisu" component, besides the WebVisu component. The Linux SL doesn't support this TargetVisu as part of the runtime. You should run a separate process for this. So remove the TargetVisu from the Visualization Manager and then you will be able to load the application.
Last updated: 2026-08-06
Post by ranadheer on Codesys Control for PLCnext (PLC - AXL F 2152)
CODESYS Forge
talk
(Post)
Hello Jaco Pretorius, I came across your post regarding CodeSys control for PLCnext. I’m currently working on a similar setup and had a quick question. Here am using the CODESYS V3.5 SP21 PATCH2 ,VERSION 3.5.21.20 , and Downloaded extension package 4.16.0.0 (old versions are not available in the extension CodeSys installer) Devices used here are: BUS COUPLER : 2403869 BK PN TPS Module carrier slot 1 : 1088127 AXL SE DI16/1 Module carrier slot 2 : 1088062 AXL SE AI4 | 4-20 Module carrier slot 3 : 1088129 AXL SE DO16/1 Module carrier slot 4 : 1088123 AXL SE AO4 | 4-20 -->Start a New Project Type: Standard Project Device: CODESYS Control Win V3 x64 Language: Structured Text -->Install GSDML File Navigate to: Tools > Device Repository > Install Select the GSDML file path (downloaded from Phoenix Contact for device coupler Part ID: BK PN TPS 2403869) Click Renew Device Repository Close the dialog -->Add Device to Project -->Right-click on Devices > Add Device Issue: Devices from the repository are not available to select or call into the project! I’d really appreciate any guidance or suggestions you can offer. Best Regards Ranadheer Reddy
Last updated: 2025-09-09
Post by ranadheer on Codesys Control for PLCnext (PLC - AXL F 2152)
CODESYS Forge
talk
(Post)
Hello Jaco Pretorius, I came across your post regarding CodeSys control for PLCnext. I’m currently working on a similar setup and had a quick question. Here am using the CODESYS V3.5 SP21 PATCH2 ,VERSION 3.5.21.20 , and Downloaded extension package 4.16.0.0 (old versions are not available in the extension CodeSys installer) Devices used here are: BUS COUPLER : 2403869 BK PN TPS Module carrier slot 1 : 1088127 AXL SE DI16/1 Module carrier slot 2 : 1088062 AXL SE AI4 | 4-20 Module carrier slot 3 : 1088129 AXL SE DO16/1 Module carrier slot 4 : 1088123 AXL SE AO4 | 4-20 -->Start a New Project Type: Standard Project Device: CODESYS Control Win V3 x64 Language: Structured Text -->Install GSDML File Navigate to: Tools > Device Repository > Install Select the GSDML file path (downloaded from Phoenix Contact for device coupler Part ID: BK PN TPS 2403869) Click Renew Device Repository Close the dialog -->Add Device to Project -->Right-click on Devices > Add Device Issue: Devices from the repository are not available to select or call into the project! I’d really appreciate any guidance or suggestions you can offer. Best Regards Ranadheer Reddy
Last updated: 2025-09-09
Introductory short video series on PLC programming (CODESYS)
CODESYS Forge
talk
(Thread)
Introductory short video series on PLC programming (CODESYS)
Last updated: 2023-08-28