Post by dsa28 on OPC UA subscriber not operational
CODESYS Forge
talk
(Post)
Hi, Thanks for the reply. Please note that the information and links provided are related to OPC UA Client/Server. My problem was related to OPC UA Pub/Sub. In the end I have managed to establish OPC UA Pub/Sub communication between Codesys and TwinCAT systems. Keep in mind that OPC UA Pub/Sub example is not provided in the latest library version 1.1.0.0. The user needs to download the previous version to get the example. During the configuration I ended up with some doubts regarding the usage of IEC_ARRAY type in the dataset definition (see attachment). Can you please give more information on how to use this type? Many thanks.
Last updated: 2024-11-29
Post by ben1 on Help understanding analog in-/outputs
CODESYS Forge
talk
(Post)
Hi there mate Most PLC's have a very similar concept with AI/AO - have you used any other software before? I have not used a Wago before myself, but I assume the concept would very much be: 1. Add the analog in & out cards to your hardware config. 2. Setup the raw input scaling on the hardware (eg. 4 - 20mA = 4000 - 20000) 3. Use a built in or homemade scaling block to scale your input as needed (eg. 4000 - 20000 = -100 - 2000kPa. 4. Write code as required 5. Scale output as needed (eg. 0 - 100% = 0-10000 = 0 - 10V) Is this the information you require?
Last updated: 2024-12-15
Post by trusty-squire on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
Hi, Is there a way to read the homed status from the EtherCAT drive directly? I am currently flagging the homed status on the succesful completion of the MC_Home function block, but I have had false triggers where the drive didn't actually execute the homing procedure but the MC_Home FB is marked as complete without error. I looked at other MC/SMC function blocks but the closest I can find is the "Homing" bit from MC_ReadStatus FB, but this doesn't show if the drive is succesfully homed, only that it's homing. Any guidance is welcome. Thanks!
Last updated: 2025-01-07
Post by teichhei on The selected container ... does not fit your ticket
CODESYS Forge
talk
(Post)
Hi, When trying to activate a control Basic L license on a Wago PFC200 750-8203 the error The selected container ... does not fit your ticket comes up and won't allow licensing. I have deleted the /var/opt/codesys/cmact_license/ content 3 times and the container number changed each time after a reboot, but the problem persists. Not a happy first time experience with those weird application based licenses. IDE is 19.20. This was a e!Cockpit FW22 PLC and I used Deploy Control SL to make the green web interface red. WBM shows Codesys 2 and e!Runtime active which is a bit weird. What do I do now? Regards Heinz
Last updated: 2025-01-08
Post by sigurdrb on Read codesys version in the codesys application
CODESYS Forge
talk
(Post)
Hi! I want to read the codesys version into the project, so I can highlight it in the SCADA system. VAR dwVersion : DWORD; END_VAR SysTarget.SysTargetGetVersion(pulVersion := ADR(dwVersion)); This gives me the value 100859909. I tried to search ths up and found som older post (https://forge.codesys.com/forge/talk/Runtime/thread/a55981ff4d/) that said each 4 bytes reads a number in the version. Example is 50662666 = 16#03050D0A which reads to V3.5.13.10 When I run this code I get the value 100859909, which I cant translate to anything meaningful. I am running it on Codesys V3.5.19.70. Help appreciated!
Last updated: 2025-01-17
Post by pedegani on "Do you really want to perform" dialog boxes
CODESYS Forge
talk
(Post)
I have the same annoying problem. The confirmation prompt for every single action appeared recently after an update from CODESYS 3.5 SP20 Patch 3 to Patch4, but I don't think it's due to this. Having to confirm every operation while debugging an application is a considerable waste of time and does not help at all to concentrate on development, not to mention that many times you miss the long-awaited event because you are busy looking for the 'yes' button to resume debugging or force a variable. Does anyone know how to disable the confirmation messages?
Last updated: 2025-02-14
Post by askic on Library Documentation Export Error
CODESYS Forge
talk
(Post)
Hello, I have encountered a very strange and non descriptive error when creating libraries. Basically, when user just create a new CODESYS library, and then just add Text List, save build with no errors and then try to save as compiled library, the following error would be generated: "The library documentation export error" and nothing more, just like shown in the attachment. Of course I have installed package CODESYS Library Documentation Support v 4.6.0.0 I'm Using Codesys 3.5.20 Patch 2 Does anybody have any suggestion about the cause of this error or any advice on how to troubleshoot further?
Last updated: 2025-02-15
Post by tmarmy1 on Redundancy for RTE x64 - stuck in standalone
CODESYS Forge
talk
(Post)
Sorry if this has been asked before, but I can't seem to locate a thread that leads me answers. I am running two RTE x64 softPLCs, one on the host machine and a second via a VM. I have managed to finally get both to a position that they see each other, but they are in standalone mode instead of an active/passive state for failover (image attached). Every attempt to sync via the button fails. There is probably some step or option that I have missed in my bumbling through this learning process, but for the life of me I can't seem to figure it out. Anyone got any suggestions what I need to look at to get this into an active/passive redundancy state?
Last updated: 2025-02-20
Post by rshabsh on Using Latch Variable in Alarm as input from text list
CODESYS Forge
talk
(Post)
I am currently utilizing Alarm Manager’s Latch Variable 1 to display additional information related to alarms. However, instead of mapping this latch variable to a fixed PLC variable, I would like to dynamically update its text content based on the selected language in the system. To achieve this, I am considering using a text list that corresponds to different languages rather than directly linking Latch Variable 1 to a PLC variable. This approach would allow the displayed alarm information to be automatically translated according to the active language setting. Could you please confirm if this method is feasible within the Alarm Manager configuration? Additionally, if there are specific steps or best practices to follow when implementing this functionality, I would appreciate any guidance you can provide. Looking forward to your insights.
Last updated: 2025-02-26
Post by mkintegration on Reading Absolute Encoder Position From Yasakawa Drive
CODESYS Forge
talk
(Post)
I am looking to read in the absolute position of a yaskawa servo drive Sigma 7 that is using absolute encoder. It looks like yaskawa outputs this across there CN1 I/O connecter and during operation just outputs encoder pulses. But at boot up transmits the Multiturn data position and the Position within one rotation (pulse train) on two different wires. Once the drives are enabled it just uses incremental pulses. Does any one have experience with what IEC blocks to use to read this information in. I attached the Yaskawa Manual section that talks about the format.
Last updated: 2025-02-26
Post by mkintegration on Reading Absolute Encoder Position From Yasakawa Drive
CODESYS Forge
talk
(Post)
I am looking to read in the absolute position of a yaskawa servo drive Sigma 7 that is using absolute encoder. It looks like yaskawa outputs this across there CN1 I/O connecter and during operation just outputs encoder pulses. But at boot up transmits the Multiturn data position and the Position within one rotation (pulse train) on two different wires. Once the drives are enabled it just uses incremental pulses. Does any one have experience with what IEC blocks to use to read this information in. I attached the Yaskawa Manual section that talks about the format.
Last updated: 2025-02-26
Post by peterkcontrols on Copying 2 byte word to output
CODESYS Forge
talk
(Post)
Hello. I am using codesys 3.5. I would like to know if it is possible to set a variable to an output without declaring in. I have defined a STRUCT and within this struct I have a Struct for inputs called I and a struct for outputs called O. I have declared a variable of the type of this Struct, I would like to set or alias the value in this variable to an input/output value of an IO block that has a module on the ethernet tree. Is it possible to copy the contents of %IW0 -> STRUCT.I ? The size of both of these is 2 bytes. I understand that I can declare a variable with the input like Input01 AT %IX0.0 : BOOL; However how can I make STRUCT.I.D00 AT %IX0.0? Is this possible? Thanks
Last updated: 2025-03-03
Post by felipemsgarcia on Axis EtherCAT address
CODESYS Forge
talk
(Post)
Hello, Thank you for your answer. I'm afraid I was not clear on what I was trying to achieve. I'm trying to change parameters and command axes from inside a function block and the first thing that came to my mind was pass both the EtherCAT slave and axis to the function block (as image attached). But, I believe it's worse than just pass directly the EtherCAT slave address to the function block (is it???). However I was wondering if there was a way to get the EtherCAT address directly from the axis, so I don't need to pass the EtherCAT slave nor the EtherCAT address to the function block. Thank you again!
Last updated: 2025-03-07
Post by struccc on Problem Reading Registers via Modbus from non Codesys device
CODESYS Forge
talk
(Post)
Hi, Might be a good idea first to try out the connection and the device with some handy software, like Modbus Poll. There you can see better, what's really going on... - Is it really connected? - What error code does it return? - Can it read from the register address? - Maybe try Input registers and Holding Registers - can make a difference - Sometimes register addresses are messed up: shifted +-1 (mixing of 2 standards) - Sometimes register addresses start with offset 30000, 40000 ... - Are you using the right protocol? - Is it RTU or TCP? Maybe ASCII? - Can even have a look at the data packets, etc... All this is easier to figure out first with some modbus utility... and then to set it up in CODESYS should not be an issue. P.
Last updated: 2025-03-09
Post by mehakfatima on Need Help Configuring Energy Analyzers via Modbus TCP & RTU (RS-485) in CODESYS 3.5
CODESYS Forge
talk
(Post)
Hello everyone, I am currently working on reading data from energy analyzers using Modbus TCP and RTU (RS-485). In my previous software, I used the following method to add slave devices (i have attached the image) and configure registers: Add the Modbus slave device. Configure the communication parameters (baud rate, parity, etc.). Define the registers and their addresses for data retrieval. Now, I am trying to achieve the same in CODESYS 3.5, but I am not sure how to configure the Modbus master, add slave devices, and set up the registers properly. If anyone has experience with Modbus TCP/RTU setup in CODESYS 3.5, I would really appreciate your guidance! A step-by-step explanation or any references/tutorials would be extremely helpful.
Last updated: 2025-03-13
Post by madskaizer on ModbusTCP Slave Device, maximum uiClientConnections?
CODESYS Forge
talk
(Post)
I got a Wago PFC200V2, running Codesys 3.5.16.40, 100ms scan cycle, consumes about 20ms. It will randomly crash the runtime every 10 minutes to a few hours. We suspect an overloaded ModbusTCP Slave Device, as this is work done by a 3rd party contractor, but we can not find anything in the help files or documentation, that mentions a hard limit on maximum number of clients connections. This PLC currently has 44 client connections to the Slave Device and 29 slaves configured for its own Master Device. This topic metnions a hard limit of maximum 16 connections, but where is this written? https://forge.codesys.com/forge/talk/Engineering/thread/bd95b9d6d2/
Last updated: 2025-03-26
Post by hemuv on Dialog Open
CODESYS Forge
talk
(Post)
I'm programming an HMI for a machine. I want to log all the parameter's changes (used text field for displaying and changing) for particular User levels. Created a Numpad and want to log oldvalue and Newvalue on 'ok' Button press. To retrieve the oldvalue, i check if the dialogue opened is my Numpad, Then I retrieve the dialogue interface via GetDialogInterface(ADR(myNumpad)) --> numpadData.stVariableValue which contain my oldvalue and save it locally. Problem is sometimes i retrieve the data and sometimes not. Also observed when Numpad Dialogue is Opened, VisuDlgUtil_IsDialogOpen returns False in some cycles.Attached you will find my Project. please let me know what went wrong or if there is a better approach to collect old and New Value of a textfield. Thank you.
Last updated: 2025-03-26
Post by anlebr on Alarm group template - Is it not possible with several instances?
CODESYS Forge
talk
(Post)
Hi In the POU section of my project I have created a Fan function block and defined an alarm group template for this FB with one alarm (Motor fault). In the PLC program I define two instances of the fan function block. When going to the alarm configuration and pressing "Create or update alarm instances", I get two alarms listed. So far so good. However, when I start my program and check the alarm table in the visualization I only see one alarm, even if both are active. Am I doing something wrong, or is it not possible to define alarms on a function block level and get one set of alarms per instance of the function block?
Last updated: 2025-04-01
Post by timvh on How to manage soft container licenses for (remote) multi units?
CODESYS Forge
talk
(Post)
You need to activate an individual license (ticket number) for each device. THe hardware of each device is unique, so you cannot copy a soft container from one device to another. This license can be installed in a local (wibu - codemeter) soft container, or you could optionally activate it on a hardware (USB) key. The benefit of the key is that you can easily move it to another device, nor does it get lost when you replace parts of the hardware of the device or completely overwrite the image. See: https://store.codesys.com/en/codesys-key.html
Last updated: 2025-04-08
Post by rossanoparis on Internal Error (ARM): Unsupported conversion! With new version v3.5 SP21
CODESYS Forge
talk
(Post)
I have updated CODESYS development tool to the version v3.5 SP21 (64bit) The previous version was v3.5.20.40 Compiling an existing application with the new evelopment tool I get the following error. kunbusiodrvrevpibridge, 1.4.1.0 (kunbus gmbh): IoDrvScanModules [IoDrvRevPiBridge](Line 51, Column 1 (Impl)): Internal Error (ARM): Unsupported conversion! This error was not reported in the previous compiler version and is now highlighted in a third-party library, which I cannot change or modify. The error is due to the following conversion: m_udiError := TO_UDINT(excCode); . The excCode variable is a system type, declared as shown below, and should be converted to a UDINT excCode : __SYSTEM.ExceptionCode; m_udiError: UDINT; . I would appreciate it if someone could provide feedback on this issue.
Last updated: 2025-04-15
Post by andrej on Creating, using an external Function.
CODESYS Forge
talk
(Post)
Hello all, I would like to create a simple which runs directly on Control WinV3 x64 3.5.21.0 For this purpose I created a simple dll myAdder.dll in Cpp // MyAdder.cpp // cl /LD /EHsc MyAdder.cpp /Fe:MyAdder.dll #include <windows.h> extern "C" __declspec(dllexport) int __cdecl CmpMyAdder_Add(int a, int b) { return a + b; } I added the dll in the respective folder. Furthermore I "registred" the dll in the CODESYSControl.cfg. However, when I want to use the library I get the error message: Uresolved reference: *'CMPMYADDERADD' * Can you give me a hint what step I missed or where I need to declare the dll, such that the dll resp. the reference can be resolved. Many thanks and kind regards
Last updated: 2025-04-18
Post by otbeka on CAA File Handling: "Read only" error
CODESYS Forge
talk
(Post)
Hi, sorry for the late reply. After some investigation, the read-only error was being triggered by a FAT-fs filesystem panic on the kernel end, probably caused by unfinished write/reads causing corruption. I found this thread https://forge.codesys.com/forge/talk/Engineering/thread/e637d252b7/ which seems to give a solution of using SysProcess to send the 'sync' command to the console immediately following a write to prevent issues if power is lost or, in my case, if the unit is harshly power cycled. Indeed this seems to resolve the issue bar the worst possible edge cases.
Last updated: 2025-05-02
Post by l-lll on The plug-in is required by the current version profile but has not been installed
CODESYS Forge
talk
(Post)
Hello everyone, I meet this problem after installing Codesys SP20 Patch 5 on Windows 11 while the dialog box shows that the installation process has been successfully completed. Every time I open Codesys I get an error that says (Attached image): 'One or more issues ocurred with the current version profile. Please contact the vendor to resolve these problems. The plug-in {....} (Exactly x.x.x.x) is required by the current version profile., but has not been installed. It is highly recommended that the tools is terminated. Do you wanto to terminate now?' Can someone help me please, thanks very much!
Last updated: 2025-05-14
Post by l-lll on The plug-in is required by the current version profile but has not been installed
CODESYS Forge
talk
(Post)
Hello everyone, I meet this problem after installing Codesys SP20 Patch 5 on Windows 11 while the dialog box shows that the installation process has been successfully completed. Every time I open Codesys I get an error that says (Attached image): 'One or more issues ocurred with the current version profile. Please contact the vendor to resolve these problems. The plug-in {....} (Exactly x.x.x.x) is required by the current version profile., but has not been installed. It is highly recommended that the tools is terminated. Do you wanto to terminate now?' Can someone help me please, thanks very much!
Last updated: 2025-05-14
Post by l-lll on The plug-in is required by the current version profile but has not been installed
CODESYS Forge
talk
(Post)
Hello everyone, I meet this problem after installing Codesys SP20 Patch 5 on Windows 11 while the dialog box shows that the installation process has been successfully completed. Every time I open Codesys I get an error that says (Attached image): 'One or more issues ocurred with the current version profile. Please contact the vendor to resolve these problems. The plug-in {....} (Exactly x.x.x.x) is required by the current version profile., but has not been installed. It is highly recommended that the tools is terminated. Do you wanto to terminate now?' Can someone help me please, thanks very much!
Last updated: 2025-05-14