Post by pazderai on CanOpen write issue
CODESYS Forge
talk
(Post)
Thank you for an answer. Unfortunatelly, it doesn't work. The slave needs command byte as follows 0x22. It means expedited transfer where s-bit is not set, therefore data length is not specified. If I use segmented mode by CiA405.SDO_WRITE_DATA it produce command byte as follows 0x21 which is unfortunately supported by the slave and it returns with error 0x05040001 - SDO Abort Code -Client/server command specifier not valid or unknown. I can use CAN API low level to overcome this problem where it is possible to set 0x22 as a command byte, but than I can use user interface to set the communication probably, because I thing that machine expert uses library CiA405.SDO_WRITE for setting the slave. Or am I wrong?
Last updated: 2024-07-16
Post by ucconversions on displaying all incoming CAN bus messages
CODESYS Forge
talk
(Post)
Hello Im using CAN API Im receiving CAN messages with no problem. below is my code. METHOD ProcessMessage VAR_IN_OUT ( Incoming message ) Message : CAN.RxMESSAGE; END_VAR VAR i: USINT; END_VAR recvCANid := Message.udiCanID; IF recvCANid = 16#18FF8247 THEN UserVarGlobal.g_countMsg_RPMset := UserVarGlobal.g_countMsg_RPMset + 1; FOR i := 0 TO 7 DO myDataFF82[i] := Message.abyData[i]; END_FOR END_IF but in this way I can only display CAN messages which I know its ID. I want to display all incoming CAN messages for example first incoming CAN message - I assign it into a variable Message1. second incoming CAN message - I assign it into a variable Message2. third incoming CAN message - I assign it into a variable Message3. Can you give me guidance? Thank you BR
Last updated: 2024-07-18
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
I let this project rest for a while and picked it up last week. I have been in contact with the support from beckhoff and got the information that the terminals were identical (communication wise). As the Log of the Axis (not the drive's log) shows the error when trying to write into the register 0x8012 and set the value for an encoder to a value that is the default - at least according to the manual - I was wondering if it is possible to "not write that value" to skip that part? Or am I misunderstanding the way the library communicates with the drive?
Last updated: 2024-07-24
Post by mubeta on Reset problem with CMZ SD/SVM drive
CODESYS Forge
talk
(Post)
In a recent project with SoftMotion 4.15.0.0, where I integrated two SD drives from CMZ (from catalogue EDS and not imported), on CANopen bus, I found that the SoftMotion MC_Reset function does not reset the drive faults. Even if the drive is in fault, either on the device or on the drive at the CoDeSys level, the function does not reset, instead reporting the error code: no error to reset. Finally, I had to connect the reset bit of the ControlWord directly to a tag in my program. Something I never had to do on other drives: Lexium, etc. all reset simply with MC_Reset.
Last updated: 2024-07-24
Post by askic on Generate FBs from source
CODESYS Forge
talk
(Post)
Hello, I'm coming from Siemens (TIA) world and currently learning Codesys. I'd like to know if there is an option to add external txt file with ST code for creation of a function block and then use this file as a source file from which FB will be generated? For example, in TIA, there is an option add external source file to the project structure and then use option "Generate blocks from source". This would create a FB. Does Codesys have something similar? This external source file would look like this: FUNCTION_BLOCK Scaling VAR_INPUT x, k, n : REAL; END_VAR VAR_OUTPUT y : REAL; END_VAR VAR END_VAR y := k*x+n; END_FUNCTION_BLOCK
Last updated: 2024-07-31
Post by abrarsk on SysCom Library Usage
CODESYS Forge
talk
(Post)
Hello all, I am facing issues with using SysCom library. With SysCom23 library things were simple but since we are migrating to 64bit systems, I am writing a Porting program. With SysCom23, opening the comport was as simple as providing the ComPort no. which returns the Handle as a DWORD. dwHandle:=SysComOpen(Port); But the new library is a bit different. It is asking for 2 input parameters to open the Com Port - Port Number and POINTER to RTS_IEC_RESULT IF hCom = 0 THEN hCom := SysComOpen(ComSettings.sPort, ADR(pResult)); How should I use the RTS_IEC_Result? I can find RTS_IEC-REUSLT under SysType2Interfaces of SysCom library. Also, can someone give me a general understanding of this RTS_IEC_REULT and RTS_IEC_HANDLE, etc.?
Last updated: 2024-08-05
Post by sangeetnenwani on Test Driver Availability in CODESYS 64-bit and Test Manager 5.1.0.0
CODESYS Forge
talk
(Post)
I’m operating with CODESYS in a 64-bit configuration and the Test Manager at version 5.1.0.0, where I’m attempting to use project scripts from an earlier version. These scripts call for certain test drivers that are not present in my installation. It’s unclear whether the absence is due to the 64-bit system, an update in the test drivers, or if I need to enable or install additional elements. For instance, the loadproject(Codesys.Base) command is missing, but loadproject(testmanager.project) is available. The FileIO command for CODESYS isn’t accessible, yet the testmanager’s driver for it exists, as does the execuptscript command.
Last updated: 2024-08-06
Post by sangeetnenwani on Test Driver Availability in CODESYS 64-bit and Test Manager 5.1.0.0
CODESYS Forge
talk
(Post)
I’m operating with CODESYS in a 64-bit configuration and the Test Manager at version 5.1.0.0, where I’m attempting to use project scripts from an earlier version. These scripts call for certain test drivers that are not present in my installation. It’s unclear whether the absence is due to the 64-bit system, an update in the test drivers, or if I need to enable or install additional elements. For instance, the loadproject(Codesys.Base) command is missing, but loadproject(testmanager.project) is available. The FileIO command for CODESYS isn’t accessible, yet the testmanager’s driver for it exists, as does the execuptscript command.
Last updated: 2024-08-06
Post by micik on Download EtherCAT project on SoftPLC (ControlWin-V3 x64)
CODESYS Forge
talk
(Post)
Hello, I have almost exactly problem already discussed here in this old thread: https://forge.codesys.com/forge/talk/Engineering/thread/03af9426eb/ However, this is quite old and I assume not completely relevant. In my case, I use v3.5.20 on windows 11, so Winpcap is no longer supported on newer OS. Also, this hint about adding entry to the .cfg file under ProgramFiles(x86) is also not relevant anymore. I guess, I need to add entry SysEthernet to this .cfg file: C:\ProgramData\CODESYS\CODESYSControlWinV3x64...\CODESYSControl.cfg like this one: [ComponentManager] Component.1=CmpTargetVisuStub Component.2=CmpWebServer Component.3=CmpWebServerHandlerV3 Component.4=SysCpuMultiCore Component.5=SysReadWriteLock Component.6=SysCpuBreakpoints Component.7=SysPipeWindows Component.8=SysEthernet But I'm not sure about Npcap vs WinpCap. Please, if applicable, update these instructions.
Last updated: 2024-08-08
Post by cfam on Codesys Control for PLCnext SL, Bus not running
CODESYS Forge
talk
(Post)
Good day I would appreciate it if you can give me some advice on how to fix my "Bus Not Running Error". I am Using Codesys 3.5 SP20 and Codesys Control PLCnext SL V4.12.0.0. Codesys control was installed on the device and I can log into it but it seems that it does not pick up the PLC or the IO attached (Please see attached Image). The Bus Cycle Task of the AXL F 2152 is set to Main Task and the "Always update Variable" is Enabled on each IO Module. My Main Task interval is set to 100ms and Priority is set to 0. I have tried other options and none seem to work. Your response to this issue will be highly appreciated.
Last updated: 2024-08-12
Post by micik on Python scripting - print whole project tree
CODESYS Forge
talk
(Post)
Hello, I have found a script for printing device tree in Codesys project. This script is available as code snippet as an exmaple for using Python in Codesys. However I feel main documentation is lacking. For example, where can I find that object has "is_device" attribute? Code examples are given here: https://content.helpme-codesys.com/en/CODESYS%20Scripting/_cds_access_cds_func_in_python_scripts.html However, I have a question how to print the whole Project tree and not just devices? Of course I need to remove check: if treeobj.is_device: But simply removing this test condition will not produce what I want. I need to print PLC Logic, Application, ad other nodes in the Project tree. Where to find this documentation?
Last updated: 2024-08-12
Post by cfam on Codesys Control for PLCnext SL, Bus not running
CODESYS Forge
talk
(Post)
Good day I would appreciate it if you can give me some advice on how to fix my "Bus Not Running Error". I am Using Codesys 3.5 SP20 and Codesys Control PLCnext SL V4.12.0.0. Codesys control was installed on the device and I can log into it but it seems that it does not pick up the PLC or the IO attached (Please see attached Image). The Bus Cycle Task of the AXL F 2152 is set to Main Task and the "Always update Variable" is Enabled on each IO Module. My Main Task interval is set to 100ms and Priority is set to 0. I have tried other options and none seem to work. Your response to this issue will be highly appreciated.
Last updated: 2024-08-12
Post by c3po on SNMP Communication with WAGO 750-8212 PFC
CODESYS Forge
talk
(Post)
Hello folks, my problem is a bit bigger for just one question. So let's start with the easiest. But first, my system setup: It's a WAGO 750-8212 PFC with some I/O-modules. I try to communicate with the controlsystem over SNMP using the IIoT library from codesys. https://content.helpme-codesys.com/de/CODESYS%20Examples/_ex_iot_snmp_service.html Is there some expirience with this kind of communication? It's just about transfering some data from PFC to network and setting some analogsettings from network to the PFC. So my easiest question: Do I ever need the SNMP_Agent or can I use the SET / GET function as standalone, without the agent? (maybe some more questions will follow, if someone will answer to my request) thanks so far
Last updated: 2024-08-21
Post by micik on Ethercat project loaded to Win V3 x64 bit SoftPLC
CODESYS Forge
talk
(Post)
Hello, I have almost exactly problem already discussed here in this old thread: https://forge.codesys.com/forge/talk/Engineering/thread/03af9426eb/ However, this is quite old and I assume not completely relevant. In my case, I use v3.5.20 on windows 11, so Winpcap is no longer supported on newer OS. Also, this hint about adding entry to the .cfg file under ProgramFiles(x86) is also not relevant anymore. I guess, I need to add entry SysEthernet to this .cfg file: C:\ProgramData\CODESYS\CODESYSControlWinV3x64...\CODESYSControl.cfg like this one: [ComponentManager] Component.1=CmpTargetVisuStub Component.2=CmpWebServer Component.3=CmpWebServerHandlerV3 Component.4=SysCpuMultiCore Component.5=SysReadWriteLock Component.6=SysCpuBreakpoints Component.7=SysPipeWindows Component.8=SysEthernet But I'm not sure about Npcap vs WinpCap. Please, if applicable, update these instructions. I hope it is still possible to
Last updated: 2024-08-22
Post by micik on Reverse bytes in an array
CODESYS Forge
talk
(Post)
Hello, I'm getting the data in Codesys that is an array of 8 bytes. From this array, I need to foram LREAL number, however, because of different endiannes I need to reverse bytes in this array and then copy to a LREAL variable. For this I'm using a loop and it works OK. I wonder if there is a built in function to do this. I have found CAA Memory library but it has functions like reverse bytes in DWORD. But it seems it doesn't have what I need. https://content.helpme-codesys.com/en/libs/CAA%20Memory/Current/CAA_Memory/Reverse-Bit-Swap-ByteWord-order/ReverseBYTEsInDWORD.html What I need is a function to reverse bytes in an 8 byte array, or something similar.
Last updated: 2024-08-22
Post by micik on Reverse bytes in an array
CODESYS Forge
talk
(Post)
Hello, I'm getting the data in Codesys that is an array of 8 bytes. From this array, I need to foram LREAL number, however, because of different endiannes I need to reverse bytes in this array and then copy to a LREAL variable. For this I'm using a loop and it works OK. I wonder if there is a built in function to do this. I have found CAA Memory library but it has functions like reverse bytes in DWORD. But it seems it doesn't have what I need. https://content.helpme-codesys.com/en/libs/CAA%20Memory/Current/CAA_Memory/Reverse-Bit-Swap-ByteWord-order/ReverseBYTEsInDWORD.html What I need is a function to reverse bytes in an 8 byte array, or something similar.
Last updated: 2024-08-22
Post by gilbertamine on Comparing Arrays of structure
CODESYS Forge
talk
(Post)
Hi Everybody, I'm looking for a simple way of comparing two array of a structure. My structure is define like this : TYPE Positions_T : STRUCT PosX: DINT; PosY: DINT; PosZ: DINT; END_STRUCT END_TYPE I have multiples Var : ARRAY [0..220] OF Positions_T, that I need to compare quickly. I don't really want to do a Loop that goes by every 220 points and compare each one of them so I was wondering if there is another way. I came accross the MEM.Compare function, but it require to know the size in Bytes of the memory, and I don't know how to do that... Has anybody an idea on how to do the comparing easily ? Thanks in advance
Last updated: 2024-08-22
Post by yannickasselin on codesys VLAN tagging
CODESYS Forge
talk
(Post)
Hi, I am looking for exactly the same thing. I would think that using a layer 2/3 managed switch should work but I am not convinced. I would like to test it in order to see if it would be possible to run many Codesys Docker instances on a server and run only 1 ethernet cable from the server to a managed switch closer to the machines beeing controlled instead of having to run multiple long ethernet cables. I was going to buy a managed switch in order to test it but I want to first make sure it is possible and I want to figure out exactly what kind of switch I would need. Is this even possible? I think this is a feature that would be very useful paired with "Codesys Virtual Control SL". Thank you
Last updated: 2024-09-07
Post by shabroz-gill on Exception when OPCUA datasource disconnects from Server
CODESYS Forge
talk
(Post)
If i loose the network and the opcua data source suddenly looses connection with the server, i get an exception and my application stops working. I am using the latest version of the communication add v4.5.2.0 Is this a known issue? This makes the datasource unusable because it is inevitable that we will loose connectivity at some point, and the datasource crashing everything due to that seems to be a deal breaker. I can provide more details is someone from codesys is reading this. You can recreate is by just shutting off the Opc server after the codesys data source is connected and reading data from it. The codesys app does not crash everytime and sometimes it is able to reconnect without crashing, so you may have to try this a few times to see the exception. Best regards
Last updated: 2024-09-16
Post by wbj0t on Raspberry Pi CM4. CoDeSyS files corrupted after hard reset.
CODESYS Forge
talk
(Post)
Hello everyone. Raspberry Pi CM4 after some 1 week of work was hard reset mannualy several times and after these hard resets User Management file was missed (when click login button, enter login/password, error: User Management File missed). Also programm can not open file via SysFile library, but this file exists and size of him is 0 bytes, but must be more any way (I keep some kind of archive via this lib). What happens, how files corrupted? Where do I need try to find this error of the codesys or system whole? In the log files of codesys nothing interesting about this happens. Thanks for reading Is this enough hold PlcLogic and SysFileMap.cfg as reserve copy in another place for restoring the programm? And how automate restoring actions if programm files corrupted?
Last updated: 2024-09-16
Post by jari-koivuluoma on Newly created texlists wont appear in the selection dropdown
CODESYS Forge
talk
(Post)
When I create a new textlist in Codesys 3.5 SP19 Patch 5, it wont appear in the dropdown menu at Rectangle element > Dynamic texts > Text list. If I just type the name of the textlist to the field (in quotes), I get an error saying that some file is missing. Any good ideas what to do and what is going on. I recently updated to that version and I only now noticed this when I needed to add a new textlist so Im quite screwed with this not being able to add text lists. While im typing this, I tried copying an existing list and modifying it and it seems to show. Any ideas?
Last updated: 2024-09-19
Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time
CODESYS Forge
talk
(Post)
I have noticed that a rm file1.txt command on a shell has an impact on the cycle time for a TASK writing to file2.txt. Seen in the Monitor fane of the Task configuration Furthermore if a TASK makes a system call like rm, its cycle time increases of course but it seems to have an invisible impact on other TASKs too. I have a TASK for handling communication over the CANbus (SPI) where it stops sending "Heartbeats" for many seconds when another TASK does a system rm. Why is that not seen on the Monitor fane? Is even codesyscontrol paused when system calls are made? The CPU load is about 30-40%
Last updated: 2024-09-23
Post by timvh on Clarifications regarding the appropriate runtime system to use
CODESYS Forge
talk
(Post)
If you are not using any specific Raspberry Pi functionality, then probably the "universal" Control Linux ARM SL is the approriate runtime to run on the Pi. For the license it doesn't matter which runtime version you choose, because this is not hardware based anymore, but application based. Best is to use the latest version of CODESYS. To determine which license you need, double click on your device, go to the tab License metrics.... Generate the code for your application and see which license you need based on the metrics of your application.
Last updated: 2024-09-24
Post by timvh on Visuutils FbOpenDialog(Extended) not open Dialog from POUs
CODESYS Forge
talk
(Post)
I had a similar situation recently where this didn't work, but read to the end to see the solution. The reason is that CODESYS only downloads visualisations (dialogs) if they are part of the project or linked to the project. In your case the dialog is not loaded onto the controller. But the solution is pretty simple: Double click on the Visualization Manager in your application. Select the Tab "Visualizations". Here you can see that your dialog is not "checked". Do this manually and load your project on the controller. Then your code should be able to open the dialog, because now it exists on the controller.
Last updated: 2024-09-28
Post by pernockham on Linking to IO during runtime with hot swap?
CODESYS Forge
talk
(Post)
I have a project where a single PLC shall control multiple nodes (up to 10 units?) with IO connected through profinet. Ideally each node should be identical however with time I see situations were different setups/configurations will be used. Codesys PLC (GVLs) |Profinet | |--PNIO-node-1--| | | AIO, | | DIO, | | CNT etc. | |--PNIO-node-2--| | | AIO, | | DIO, | | CNT etc. Ideally I think of a configuration through yaml/xml-files (the assignment/linking of the profinet nodes towards GVL-variables in the PLC as well as scaling, channel configration etc.). Would be grateful if someone could suggest library/-ies that can handle the following: - Verify what IO is connected to a device/node. - Hot-swap/assign link for IO towards GVLs, either automatically or through a HMI.
Last updated: 2024-10-11