Post by aniket-b on Scara3 kinematic robot error CODESYS Forge talk (Post)
Here I have attached the task monitor data. What is very weird is that I am using MC__MoveDirectAbsolute FB, when I choose Vel/ACC/Jerk Factor to 1.0 it run fine. It ran 10 hours without the issue. But I get the error randomly when I use factor as 0.5
Last updated: 2025-12-29

Post by bruno-roth on Parker Compax3 controlled by Schneider LMC 201 CODESYS Forge talk (Post)
Hello, You could not run EtherCAT-Softmotion drives with LMC201 PLC. This Controller has an EtherCAT master but only to run simple I/O devices. You could not use this EtherCAT master on the LMC201 for Motion. Schneider PACdrive Controller use SERCOS and only own drives (LXM62 with Sercos) for motion.
Last updated: 2026-01-13

Post by timvh on Legacy IFM CANopen I/O modules with CR710S / CODESYS 3.5 CODESYS Forge talk (Post)
I don't work for IFM, nor for CODESYS and didn't create the .eds file or developed the CAN protocol. I have no knowledge of the exact contents and SDO's or PDO's which are exchanged. So no, I am not sure. But if the .eds file confirms to the CANopen specifications, why shouldn't it?
Last updated: 2026-10-02

Post by gatto on warning C0195 CODESYS Forge talk (Post)
Good morning dear codesys users. I'm using 3.5.20.40 and I get this warning C0195 when I assign an initial value to xyz. However, if I do it on a single byte (abc), it doesn't display any warning. Why? VAR_GLOBAL abc : BYTE := 100 ; xyz : ARRAY [1..10] OF BYTE := [10(100)] ; END_VAR
Last updated: 2025-11-20

Post by dat422 on OPC UA Enum Issue CODESYS Forge talk (Post)
Hi everyone, I’m using CODESYS V3.5 SP22 with the Communication Manager to run an OPC UA server. I have a problem with enums: when I view them in a client like UaExpert, only the last enum member is shown, and it has the wrong value. Has anyone seen this issue before or knows what might cause it? Thanks!
Last updated: 2026-03-27

Post by poliautomacao on Absolute movement controlled by an external encoder. CODESYS Forge talk (Post)
Georg, the encoder's actual position was -208 because I moved it manually for testing, but I managed to get it working. Your information is correct; there was a parameter error, Kp was at 0. After I adjusted it, it responded as expected. Thank you very much for your help.
Last updated: 2026-04-02

Post by nulltrace on Codesys Installation Always Freeze when the installing is almost done CODESYS Forge talk (Post)
in most of this cases the Installer ins't frozen, it's more likely that the Antimalware-Service-Executable slow's them down. Turning it off during installation of Codesys helped me all the time. Also keep attention on Taskmanager to get e feeling for the Installer Give it a try.
Last updated: 2026-04-05

Post by nulltrace on Modbus TCP Server connection is ESTABLISHED but all holding registers are value 0? CODESYS Forge talk (Post)
your case looks different, the first one was an codesys modbus tcp-slave, your's an Master-Application with gateway. I dont know this Unit, but i would say, from Point of Codesys it looks wrong configured. Just give us more detailed configuration and the please make a sketch of the topology you're trying to realise.
Last updated: 2026-04-08

Post by alexgooi on No Bootproject possible CODESYS Forge talk (Post)
Hello Simon, Thank you for your response. The problem occurs after about 10 online changes, after this a full download is required, but that means that the installation is going down. Is it possible to enlarge the space reserved for online changes, so that the problem occurs after 100 online changes for example? Kind regards Alex
Last updated: 2026-04-14

Post by alexgooi on Network variable stops sending CODESYS Forge talk (Post)
Are you making use of structs in the NVL? In the past I had similar behavior (NVL stops sending) when I added something in the struct. if you are making use of structs makes sure that the structs are identical in both projects. If this is not the case, have you tried changing the port number to something different than 1202?
Last updated: 2026-04-29

Post by petra on Gateway not configured properly when read_online_value CODESYS Forge talk (Post)
Here is what I use to read online the parameter value. proj = projects.primary app = proj.active_application plc = proj.find("Device", True)[0] onlineapp = online.create_online_application(app) onlineapp.login(OnlineChangeOption.Try, True) dev1 = proj.find("DEV1", True)[0] for conn in dev1.connectors: > parms = conn.host_parameters > if len(parms) > 0: > p = parms.by_id(1074855985) > p.read_online_value(2000) ---> error: Gateway not configured properly
Last updated: 2026-06-12

Post by petra on Gateway not configured properly when read_online_value CODESYS Forge talk (Post)
Here is what I use to read online the parameter value. proj = projects.primary app = proj.active_application plc = proj.find("Device", True)[0] onlineapp = online.create_online_application(app) onlineapp.login(OnlineChangeOption.Try, True) dev1 = proj.find("DEV1", True)[0] for conn in dev1.connectors: > parms = conn.host_parameters > if len(parms) > 0: > p = parms.by_id(1074855985) > p.read_online_value(2000) ---> error: Gateway not configured properly Does anyone know about this?
Last updated: 2026-06-12

Post by gilad on CODESYS SoftMotion Generic DSP402 on WAGO PFC200 + Festo CMMT-AS: MC_Power stays Busy, Controlword remains 0 CODESYS Forge talk (Post)
Hello, I am trying to connect a Festo CMMT-AS-C4-3A-MP-S1 servo drive to a WAGO PFC200 (750-8210) using EtherCAT and CODESYS SoftMotion. Hardware PLC: WAGO PFC200 750-8210 Drive: Festo CMMT-AS-C4-3A-MP-S1 Communication: EtherCAT CODESYS version: Device description version 6.3.1.1 Drive firmware: 36.10.3 Current Status EtherCAT communication is working correctly: EtherCAT master = Running Drive detected and operational PDO input and output mapping is active Statusword, position and velocity are updating correctly Current PDO mapping: Outputs: 6040 Controlword -> %QW0 6060 Modes of operation -> %QB2 607A Target position -> %QD1 60FF Target velocity -> %QD3 Inputs: 6041 Statusword -> %IW2 6061 Modes of operation display -> %IB6 6064 Position actual value -> %ID2 606C Velocity actual value -> %ID3 SoftMotion Axis I added a SoftMotion CiA402 axis under the EtherCAT slave: Axis type: SM_Drive_GenericDSP402 Axis communication state: operational (100) No SoftMotion mapping errors anymore Problem MC_Power is executed with: Enable = TRUE bRegulatorOn = TRUE bDriveStart = TRUE but: Status = FALSE Busy = TRUE Error = FALSE ErrorID = SMC_NO_ERROR The axis remains in: SMC_AXIS_STATE.power_off DSP402 state = SWITCH_ON_DISABLED The most important observation: Statusword = 32784 (0x8010) Controlword (%QW0) remains 0 all the time SoftMotion never writes 6, 7, or 15 to the Controlword. Additional Information The axis status page reports: "The license is missing or invalid. The PLC runs in demo mode." I am not sure whether: The missing SoftMotion license prevents Controlword generation completely. The axis is still not correctly connected to the EtherCAT slave despite operational communication. There is an additional CiA402 configuration step required for the Festo CMMT-AS drive. Has anyone successfully used a Festo CMMT-AS MP drive with CODESYS SoftMotion Generic DSP402 on a WAGO PFC200? Any suggestions on what should be checked next would be greatly appreciated.
Last updated: 2026-06-24

Post by timvh on PROFINET Controller SL: WRREC remains BUSY forever, no DCE/RPC packets transmitted (RevPi Connect 5 + NORD SK205E) CODESYS Forge talk (Post)
A customer of us had the same issue. They updated (at that time) to CODESYS 3.5.21.50 and Control for Linux SL versie 4.19.0.0. After that they couldn't reproduce the issue anymore. You might give this a try too.
Last updated: 2026-07-21

Post by timvh on From target start Win OnScreenKeyboard CODESYS Forge talk (Post)
Check the CODESYS log. Do you see something like this?: 2026-10-28T14:27:50.602Z: Cmp=SysFile, Class=2, Error=39, Info=4, pszInfo=!!!! Access denied to 'C:/Windows/System32/osk.exe' due to ForceIecFilePath 2026-10-28T14:27:50.602Z: Cmp=SysFile, Class=1, Error=0, Info=0, pszInfo= To grant access, this path may be configured as a PlaceholderFilePath PS, if you give an irritating, or annoying or blaming answer, I will never try to help you again. Some additional info... do you run the Control Win as user, or as service. Test it first by running it as a user, else check the info that Claude gave me as suggestion (not tested): Watch out: the keyboard may not appear CODESYS Control Win normally runs as a Windows service. Windows keeps services in a separate, invisible session (session 0). The command then succeeds, but nobody sees the keyboard. You can check this in Task Manager: if osk.exe runs under the user SYSTEM, this is the cause. A reliable workaround uses the Windows Task Scheduler: Create a task named ShowOSK that starts C:\Windows\System32\osk.exe with “Run only when user is logged on” checked. That option makes it open on the user’s desktop. Have the PLC start that task instead of osk.exe: iecst sApp := 'C:\Windows\System32\schtasks.exe'; sArgs := 'schtasks /run /tn "ShowOSK"'; The command line usually repeats the program name as the first argument. 3. Whitelist it in the config: Command.1=C:\Windows\System32\schtasks.exe
Last updated: 2026-10-28

Post by gseidel on Absolute movement controlled by an external encoder. CODESYS Forge talk (Post)
Hi polyautomacao, hmm, did you tune the PD parameters as shown in the link I posted above? One thing that could cause the behavior are bad parameters. I also don't understand the screen shot: when you hold the encoder to 0, why is the actual position of the DrivePosControl -208? Best regards, Georg
Last updated: 2026-03-27

Post by jasonhogan on Login problem with FileTransfer on Raspberry Pi 5 CODESYS Forge talk (Post)
That’s a classic CODESYS quirk. As soon as you enable AllowFileTransferServices=1, the web server locks down and demands authentication for everything, including WebVisu sessions. Since you're on a Raspberry Pi / Linux, trying to make the built-in CODESYS web server do both secure file handling and unauthenticated kiosk visu is usually a losing battle. A couple of ways to get around this: The cleaner route (separate the jobs): Turn AllowFileTransferServices back off in the config so your kiosk WebVisu opens freely without any login prompts. Then, handle the file download outside of CODESYS — just run a dead-simple Nginx/lighttpd file server or a tiny Python script on the Pi pointed at your export folder (/var/opt/codesys/...). That way your PLC security stays intact, and the kiosk screen just works. If you really want it through CODESYS: Check your Device -> Users and Groups in the IDE. Make sure the Everyone / Anonymous user group actually has explicit view permissions checked for the Visualization. Sometimes when file services are toggled, anonymous users lose the default visu-read rights and get booted straight to the login dialog. URL / Browser trick for kiosk: If the Pi is just opening a local browser on startup, you can sometimes pass the basic credentials in the browser launch script or use a small reverse proxy on localhost to inject the headers automatically so you don't see the popup. Honestly, running a lightweight HTTP/FTP endpoint on Linux (option 1) is by far the least headache.
Last updated: 2026-08-15

Post by egret on Issue with J1939, PGN 65267 (Vehicle Position) CODESYS Forge talk (Post)
I have a J1939 network (ISOBUS) connected to my PLC. I can receive various PGNs such as 65256 (Vehicle Direction/Speed) and 65254 (Time/Date). However, I cannot receive 65267 (Vehicle Position). PGN 65267 (VP) contains SPN 584 (Latitude) and SPN 585 (Longitude). On the network both SPNs return a value of -210 (meaning the CAN message payload is zero in both cases). The conversion settings are the default values and appear to be correct (see attached screenshot). Using a CAN analyser I can see that PGN 65267 (Vehicle Position) is being transmitted over the network with valid (non-zero) data that matches the latitude and longitude coordinates I would expect. I've created a program to read the raw J1939 data and this also returns valid data. It seems that the Codesys J1939 database has a problem with reading PGN 65267 messages. Can anybody else confirm this? I'm using Codesys Version 3.5 SP16 Patch 5.
Last updated: 2023-09-13

Post by user3000 on Can't find an Extended Pulse Timer (TP and LTP) CODESYS Forge talk (Post)
Hello, For my program I need an extended pulse timer, which can be referred to as a retriggerable pulse timer. Where every rising edge of the input resets the elapsed time zero, extending the lenght of the output pulse. The Codesys pulse timer (TP) is a one-shot timer and only resets the elapsed time with the falling edge of the input. There is also a pulse timer (LTP) in codesys, but in my simulation it was also functioning as a one-shot even though the description sounds like LTP should be retriggerable. I have uploaded some timing plots from another PLC program for reference. I am looking for a timer equivalent to the "TEP" diagram. Is there an Extended Pulse Timer in Codesys? Maybe there is a way to manipulate the input so it resets the elapsed time outside the function block?
Last updated: 2023-12-06

Post by xgongx on What is the insights of IoDrvEtherCAT.DCInSyncWindow? CODESYS Forge talk (Post)
It is well known that you need to increase the value of IoDrvEtherCAT.DCInSyncWindow to solve the "Fieldbus lost synchronicity" issue. In the official document, IoDrvEtherCAT.DCInSyncWindow is explained as the toleration of a certain jitter. But the official document doesn't explain what kind of the jitter is. Is it the jitter of DC sync deviation, master timer or something else? It is very important to know the insights of IoDrvEtherCAT.DCInSyncWindow. For example, if it is the toleration of DC sync deviation, and the official recommending value is 200us for CODESYS SoftMotion. It means maximum of DC sync deviation is 200us. It is unacceptable for some high precision motion control tasks, for example high speed gear task, etc. Increasing the value of IoDrvEtherCAT.DCInSyncWindow will increase the deviation of motor rotation sync if it is the toleration of DC sync deviation. So, would anyone tell me what the insights of IoDrvEtherCAT.DCInSyncWindow is? Thanks.
Last updated: 2024-07-09

Post by kleeswi on Visualization scaling problem with B&R T30 panel CODESYS Forge talk (Post)
The probelm arises for the B&R T30 panel after updating Codesys from 3.5.17 to 3.5.19 patch 5. We have to use 3.5.19 for other reasons so we cannot downgrade the version. The scaling problem only exists for the B&R 6PPT30.0702.20F025 panel, the B&R T50 panel and a esa lumia panel work. When we choose a fixed resolution it looks also good, however we also want to support the esa lumia panel with a different resolution. The images show the anisotropic and isotropic option. In the anisotropic option it scales the hight correctly but not the width and in the isotropic option is scales both hight and width false, it also does not start in the top left corner. Does someone have any suggestion why it does not work anymore with the new codesys version and are there workarounds? I added all versions with visualization packages as an image, visuElems is 4.4.0.0.
Last updated: 2024-07-29

Post by mondinmr on First IO address of a CAADiagDeviceDefault. CODESYS Forge talk (Post)
I have a device CAADiagDeviceDefault: IoConfig_Globals.Axis_A In our library, we perform introspection of the Etc_SlaveDiag. In that case, we have connectors, and by searching for them by address, I can find them in the IO mapping using the offset and size provided by EtherCAT. However, a Lenze i700 drive, instead of placing the IO mapping in the Etc_SlaveDiag device, places it in a sub-device CAADiagDeviceDefault. So, when I perform introspection, I cannot find the IO correspondences. Yet, in the CAADiagDeviceDefault, I do not find the connectors and cannot do the matching. Is there a way with a pointer or reference to a CAADiagDeviceDefault to obtain the address of the first input and the address of the first output? This is because we have our own motion library with many EtherCAT devices that automatically configure the mappings, but I can't manage to do so with the Lenze i700.
Last updated: 2024-08-22

Post by bruceae on Ethernet/IP Scan CODESYS Forge talk (Post)
Hello, I have a robot configured as a Generic Ethernet Module under Ethernet/IP Scanner. I can not see the change of state of the outputs coming from the robot on the codesys side in real-time. (The robot has it's own internal program that would changes the values of remote outputs 0-3 off and on). Also when I send data down to the inputs of the robot it doesn't transfer over as expected. As an example I'll send to the robot's input bit 0 a value of 1. It doesn't see that value change. However, when I write that input bit 0 back to a value of 0, the robot changes state and shows a value of 1. And if I change the state of a different bit, the other bits update properly, except for the bit that I changed. Any advice would be greatly appreciated, and if anything else is needed let me know.
Last updated: 2024-09-10

Post by imdatatas on Read "Homed" status from EtherCAT drive CODESYS Forge talk (Post)
Hello, I have experienced such situations with some servo drive devices in the past. The home completion information is reported to the upper controller by the slave drive with the states of the relevant bits in the StatusWord (for example; 6041h Bit10, Bit12 in Home mode). If the states of these bits are correct in terms of number and state but the motor does not actually perform the action; You can contact the slave drive manufacturer. There may be a problem with the device firmware. Another area you can play around with is looking at the settings in the "Advanced configuration" for Softmotion axis on the page the link to below, and trying it out and using the one that works for you. https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_cmd_add_softmotion_cia402_axis.html A method I recommended worked for a user as in below message. https://forge.codesys.com/forge/talk/Engineering/thread/40bc82454d/ I hope your problem will be solved as soon as possible and by sharing the result here, you will help others to know and overcome it. Good luck. Best regards, Imdat
Last updated: 2025-01-08

Post by ojz0r on Assignment Efficiency - Repetitive Assignment vs IF statement CODESYS Forge talk (Post)
Its important that you know the difference between the two. Example 1: Coils[0] := Coils[0] OR (Buttons[0] AND Sensors[0] > 6); In this case the statements will be evaluated every scan and result in either true or false for Coils[0]. Example 2: IF NOT Coils[0] AND Buttons[0] AND (Sensors[0] > 6) THEN Coils[0] := TRUE; END_IF In this example Coils[0] will latch the result in a true evaluation, if you want it to behave the same way as example 1 then you need to do it like example 3 below: IF NOT Coils[0] AND Buttons[0] AND (Sensors[0] > 6) THEN Coils[0] := TRUE; ELSE Coils[0] := FALSE; END_IF However back to the real question. There is no problem using either example 1 or example 3, if im not requiring a latch i usually go with example 1 as it is more compact.
Last updated: 2025-03-07