Post by dengsberg on Disable Communications to 'Modbus_Server_COM_Port' from the logic
CODESYS Forge
talk
(Post)
I have a serial Modbus RTU communicating to the Slave device. But when the control system is not in Run there is no power applied to one of the Modbus Devices. Can I enable / disable the communications to that Modbus Slave in the code based on my running mode, so I don't get all the errors?
Last updated: 2024-08-29
Post by wbj0t on tool 'update raspberry pi' unavailable
CODESYS Forge
talk
(Post)
Hi all. Codesys 3.5.19, patch 3. After installing raspberry 4.10 package I can see raspberry device, but can't see update raspberry pi tool. In custimsation->tools I found: Unknown command (8ec1a...) [plugin unavailable] Unknown command (7216f...) [plugin unavailable] Codesys installed in default directory. I reinstalled Codesys, thats not help.
Last updated: 2024-09-26
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
Hi, thanks for the fast response :) Yes I Have a .err file. Sorry I forgot to upload it. It is a binary file though... "Runtime goes in exception before the shutdown ?" I think it goes into exception at the same time as the power is lost...
Last updated: 2024-10-03
Post by csu-chris on No file found
CODESYS Forge
talk
(Post)
I'm having trouble getting started with the SysFile library. I tried copying and running the code found here: https://forge.codesys.com/forge/talk/Engineering/thread/f17c3d0e64/ Every time I try to run the file handle pointer returns: 16#FFFFFFFFFFFFFFFF <dereference of="" invalid="" pointer=""></dereference> I can see the file when I look in the Device -> Files window Any idea what I'm doing wrong?
Last updated: 2024-10-15
Post by winki on Scan Network on gateway created with Control Sl
CODESYS Forge
talk
(Post)
Hello, I am new on CODESYS environement. I am used to BECKHOFF env. I would like to use codesys on debian distribution. I followed this tutorial : https://www.youtube.com/watch?v=TVF0LV279_4 But I am stuck on selected the device. I do not understand, everything is running correctly Someone have an idea ? Loic
Last updated: 2024-10-16
Post by eschwellinger on RS485 CAN HAT to Cosesys
CODESYS Forge
talk
(Post)
Hi if you add in (ttyAMA0 should fit to your HAT's device [SysCom] Linux.Devicefile.1=/dev/ttyAMA0 to /etc/CODESYSControl_Usr.cfg since 4.12.0.0 version /etc/codesyscontrol/CODESYSControl_Usr.cfg then access in CODESYS with Com1 should do it. Keep in mind that only adapters work (for RS485) which do determine the send/receive direction in hardware
Last updated: 2024-10-28
Post by jeroenaero on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
yes i took the library from another forum: https://forge.codesys.com/forge/talk/Runtime/thread/f1400b71b6/, it is made for the ads1115 but the ads1015 is almost the same device with same adresses i only changed the divide value of the analog value, because thats the only difference between the ads1115 and ads1015.
Last updated: 2024-11-07
Post by jeroenaero on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
Okay i will try. I tried already the different settings. The CodeSys version i use, is CodeSys 3.5 SP20 Patch 3. The device which i use is CodeSys Control For Raspberry PI 64 SL version 4.13.0.0. The wiring should be okay because i'm using the Edatec ED-CM4IND-1432-4C(EU).
Last updated: 2024-11-07
Post by jeroenaero on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
I don't have a multiplexer so it very weird that it connects with that multiplexer. If i do a I2C scan on the PI terminal, i only get the device addresses 0x48 and 0x51. One for the ADC and one for RTC. I will try again with your libraries
Last updated: 2024-11-12
Post by giackanto on Eoe issues with Windows and Linux
CODESYS Forge
talk
(Post)
Hello, I've been trying to use EoE for communication between a Windows PC and an M753 drive from Control Technique. Despite following some online guides (https://content.helpme-codesys.com/en/libs/EtherCATStack/4.3.0.0/Ethernet_over_EtherCAT/fld-Ethernet_over_EtherCAT.html) I havenβt had any success. Both are connected to a Debian device where RTE is running: The PC is connected via the Ethernet port. The drive is connected via the EtherCAT port. I'm unable to ping the drive from my Windows PC. Here is my configuration: On Debian: (See attachments 1, 2, 3) enp1s0 = Ethernet port enp2s0 = EtherCAT port tap2 = TAP device IP forwarding and routes are both configured. On Windows: (See attachments 4, 5) On Codesys: (See attachments 6, 7) Version: Windows 11 Debian GNU/Linux 11 Codesys 3.5.17 Control for Linux SL 4.7.0 EtherCAT 4.4.0 With this configuration, I can ping the TAP device, but not the drive (See attachment 8). Could someone explain how to properly configure all these settings? Thank you, GA
Last updated: 2023-12-19
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by mikek10 on Ethernet/IP 4.6.0 causing exceptions?
CODESYS Forge
talk
(Post)
Hi, I have a project currently in development, it has a number of Ethernet/IP devices (18 adapter devices with Codesys as scanner, another scanner device with codesys as adapter). This has been stable whilst on factory floor for several months (though prior to that I did have some Ethernet/IP issues which were resolved by adjusting RPI rates). Today I tried updating to Ethernet /IP 4.6.0 from 4.5.1, subsequent to this I had 2 exceptions in a 2 hour period, I reverted to 4.5.1 and have had no further exceptions. Note I do have a device (Zebra printer) that frequently times out and reconnects, this does not seem to cause any issues in operation and does not cause any exceptions with 4.5.1. I believe the root cause of this is on the Zebra side, however there does not seem to be any adjustment I can make to prevent the time outs. Information from device log is in screenshot attached.
Last updated: 2024-06-27
Post by mondinmr on First IO address of a CAADiagDeviceDefault.
CODESYS Forge
talk
(Post)
I have a device CAADiagDeviceDefault: IoConfig_Globals.Axis_A In our library, we perform introspection of the Etc_SlaveDiag. In that case, we have connectors, and by searching for them by address, I can find them in the IO mapping using the offset and size provided by EtherCAT. However, a Lenze i700 drive, instead of placing the IO mapping in the Etc_SlaveDiag device, places it in a sub-device CAADiagDeviceDefault. So, when I perform introspection, I cannot find the IO correspondences. Yet, in the CAADiagDeviceDefault, I do not find the connectors and cannot do the matching. Is there a way with a pointer or reference to a CAADiagDeviceDefault to obtain the address of the first input and the address of the first output? This is because we have our own motion library with many EtherCAT devices that automatically configure the mappings, but I can't manage to do so with the Lenze i700.
Last updated: 2024-08-22
Post by lbartik on J1939 TX/RX PDU1
CODESYS Forge
talk
(Post)
Is it possible to transmit a PDU1 PGN using the J1939 manager and local device? What if I need to transmit a PGN RQST via 0xEA00 (PGN 59904)? How would I do this P2P (Destination < 0xFF) or broadcast (Destination 0xFF)? I don't think this is possible for any destination type. I don't think it's possible to receive broadcast PDU1 messages either. For example, an address claim PGN 60928 (0x18EEFF80) is addressed to all nodes (0xFF) and not any specific local device so it will be filtered out. These are major oversights in the IoDrvJ1939 library to not support every PDU1 RX/TX scenario. IoDrvJ1939 supported scenario: 1. Receive (RX) PDU1 (P2P) destination-specific (PDU-specific < 255) to local device with matching address IoDrvJ1939 unsupported scenarios: 1. Receive (RX) PDU1 (P2P) global (PDU-specific = 255) 2. Transmit (TX) PDU1 (P2P) global (PDU-specific = 255) 3. Transmit (TX) PDU1 (P2P) destination-specific (PDU-specific < 255)
Last updated: 2024-09-23
Post by edvard-munch on How I can get "Done flag" for "Modbus Slave Channel"?
CODESYS Forge
talk
(Post)
This is from 10 years ago, I know. But I have been using (SLAVE_DEVICE.iChannelIndex = CHANNEL_NUMBER) AND (SLAVE_DEVICE.xDone) I suppose that it shows xDone for the channel that shows up in the iChannelIndex at the same cycle? It seems to be working properly for two devices that I have been using it before But now I have another device and using two write channels, for one register each. One channel works properly and returns DONE flag When another channel is triggered, I see that it shows up in iChannelIndex, but flag DONE not received, but no Error for the channel. Also, when i check the register in the device it's evident that data has been transferred. Is this could happen sometimes with CODESYS, so DONE flag not received? Or this is a problem with a given device? With this certain register
Last updated: 2024-12-19
Post by ragarcia on Error while using UpdateConfiguredIPSettings to change IP address
CODESYS Forge
talk
(Post)
Hello everyone, I am trying to change dynamically by code the IP address of a Weidmuller controller. So I am basically using IoDrvEthernet library to use UpdateConfiguredIPSettings function but I am getting constantly the 'INVALID_STATE' error. Even though I am following a procedure it should work: * First I added on the config file of codesys the following: [SysSocket] Adapter.0.Name="eth0" Adapter.0.EnableSetIpAndMask=1 Adapter.1.Name="eth1" Adapter.1.EnableSetIpAndMask=1 * Secondly I am first disabling the ethernet interface by using Ethernet_0.Enable = FALSE and then executing DED.Reconfigure. After that, I run the Ethernet_1.updateConfiguredIPSettings Code: Ethernet_1.Enable:= EnableDisable; Reconfigure(xExecute:= TRUE, itfNode:= Ethernet_1, xError=> ErrorReconfigure, eError=> ErrorCodeReconfigure); IF Reconfigure.xDone THEN ErrorCodeIP:= Ethernet_1.UpdateConfiguredIPSettings(IPAddress:= newIP, SubnetMask:= newMask, Gateway:= newGW); END_IF IF Reconfigure.xDone OR Reconfigure.xError THEN Reconfigure(xExecute:= FALSE); END_IF Ethernet_1.Enable:= TRUE; Reconfigure(xExecute:= TRUE, itfNode:= Ethernet_1); IF Reconfigure.xDone OR Reconfigure.xError THEN Reconfigure(xExecute:= FALSE); END_IF Can someone help me? Thank you. All I am trying is to find a way to change dynamically with code, the IP addresses of my controller (2 ethernet ports).
Last updated: 2023-12-11
Post by dekelec on Codesys 2.3 & Peak PCAN
CODESYS Forge
talk
(Post)
I use Peak USB adapter daily to download from CoDeSys 2.3 and 3.5 to IFM, EPEC and other controllers. The process: - First you need to install the appropriate driver. Link: https://www.peak-system.com/Drivers.523.0.html?&L=1 - Restart the computer - Start the CoDeSys application - Change the name of the adapter in Communication parameters, as mentioned in previous comment. Write the name exactly as written "Peak_USB", as it could also be case sensitive (defines which .dll file to use). If this doesn't work I would contact the vendor of the controller to find out the procedure. In the attachment I've added a FAQ document from IFM regarding using PCAN USB. P.S. I've noticed in your picture of communication parameters a channel via TCP/IP is mentioned. In this case a USB to CAN connection is not being used. First you should change the channel/gateway to connect via CANbus or connect using an Ethernet cable.
Last updated: 2024-07-09
Post by martinlithlith on Device User Logon and No device is responding.. Pi4b codesys 3.5 SP19 2 + (64-bit)
CODESYS Forge
talk
(Post)
Hi! Im slowly starting to loose it and i need som help! After a few night of reading up and testing iΒ΄m still stuck as a rock and you guys and girls are my last resort for this project. Basic facts; Win 11 Codesys 3.5 SP19 2 + (64-bit) Raspberry pi 4 model b 2 gb Raspian release 11 aarch64 What keeps me up late at night; Username and Password when trying to connect to device and device only beeing connectable for a few seconds. Some of the things I have tried; Username and passord; Credientials from the raspberry Administrator Administrator admin admin Admin Admin administrator administrator Usernames and passwords that I sometimes use (this was a longshot i know, but i was running out of ideas and energy). :) Epand filesystem, activating i2c, spi, 1-wire I can start the gateway and start the runtime. I cant install the edgearm64, arm64 runtime package eventhough I guess i should, i get code [ERROR] Error output: dpkg: error processing archive /tmp/codesysedge_edgearm64_4.8.0.0_arm64.deb (--install): [ERROR] Error output: package architecture (arm64) does not match system (armhf) [ERROR] Error output: Errors were encountered while processing: [ERROR] Error output: /tmp/codesysedge_edgearm64_4.8.0.0_arm64.deb code as a respons. I have tried to Reset Origin Device - no change. I have tried to remove the /etc/CODESYSControl_User.cfg [CmpUserMgr] but i could not find it and i was not sure if i should add it instead but i did not want to mess somthing up. I have tried to create a second gateway with the specific ip if the pi, that did not help. Could it be that iΒ΄m currently connected to the pi through WIFI? I can ping the pi and I can connect and control it through VNC. When i scan to select gateway target (scan edge gateway) i find 17-21 devices but can find the pi throug the mac adress. I started of trying to use the "CODESYS Control for Raspberry Pi SL" (I have a license sience earlier) as i read somewhere that this could be used on a Pi4 as well but now iΒ΄m trying with the MC SL, no changes, same problem. Right now - gateway version 4.8.0.0 (edgearmHF, armhf), Runtime Package 4.5.0.0 (raspberry, armhf). Any sugestions are very welcome! As mentioned above, theese are some of the things that i have tried/done - but i have been going at this for a while. Best, Martin
Last updated: 2023-09-10
Post by george32 on Readable IO names
CODESYS Forge
talk
(Post)
Hello Folks, I have a quite basic understanding of how PLC programming works. However I keep getting stuck on 1 problem I could not get my head around. The problem is as follow: I have a PLC with 60 IO (20 inputs, 40 outputs). Each IO is defined as a function block. Furthermore I have an external IO card connected trough a CanBus connection. This IO card has 4 analog input channels (USINT), 4 digital inputs (Bool) and 4, digital outputs (Bool) Because I have 2 different components which both has data have I made 4 arrays to store the data off every component in one variable. PLC_Input: Array [1..20] of BOOL; PLC_Output: Array [1..40] of BOOL IOCard_Input: Array [1..8] of BOOL IOCard_Output: Array [1..4] of BOOL Because the control and reading of the different in and outputs is done by a TCP connection I want to use some kind of enumeration or struct to give each index a name so that my main would be a little bit more readable instead of all the magic numbers. Also this would make my program more dynamic for the furter in case I need to changes some in the IO nummers. For example: pump is placed on the fysical terminal strip number place 54, which is the 3th output of the IO card in the program: if I am sending a message with value 54 I would like to control IOCard_Output[3]. If there is a solution or methode to get this done, I can eventually do the following in my main program: IOCard_Output[Pump]. I have tried the following: IOCard_Output[Pump - 51] with an enumration but this keeps raising an error I hope some of you could help me further with this problem. In gross lines: I want to couple all the different IO to a more readable name and this readable name should control the right Array index Thanks in advance, George
Last updated: 2024-09-26
Post by imdatatas on MC_CamIn did not work properly with SMC_FreeEncoder on SoftMotion 4.17.0.0
CODESYS Forge
talk
(Post)
Hello, I am facing a problem with the new Softmotion 4.17.0.0 version. Has anyone encountered a similar problem, what is the solution? I would be happy if you could share it. Problem description: -- "SMC_FreeEncoder" encoder axis is the master, -- The motor of the servo driver on the EtherCAT bus is the slave axis. -- When the MC_CamIn block executed, the InSync output is activated. However, although the master encoder axis position value changes, there is no movement in the slave servo axis! Test steps: 1-) EtherCAT servo axis installed, configured and motion test was performed with MC_Jog. No problem. 2-) Softmotion general axis pool > SMC_FreeEncoder was added and pulse amount configuration was performed. No problem. 3-) Incremental encoder actual count value was transferred to the "SMC_FreeEncoder.diEncoderPosition" variable as DINT under the ethercat task in every cycle and the encoder axis position value was observed. No problem. 4-) A simple CAM table with a 1:1 ratio was created under the project tree. (For example: Simply, when the encoder rotates 1 turn, the motor will rotate 1 turn.) 5-) The SMC_FreeEncoder axis enabled with MC_Power and brought to the StandStill state. 6-) The MC_CamTableSelect block was run with default input values ββ(all absolute) and only the Cam table name was specified. The Done output was seen successfully. No problem. 7-) The MC_CamIn block was activated with default input values ββ(absolute) and only the master encoder axis name, slave servo axis name, CamTableID input pins was specified and then "Execute" input set to TRUE. 8-) The InSync output information of the MC_CamIn block observed as TRUE. However, although the encoder axis value changed, the position value of the slave axis did not change at all, it did not move. It always remained at 0.0mm. 9-) When I repeated the same steps above, only changing the master axis to SM_Drive_Virtual instead of FreeEncoder and gave movement to the virtual axis, this time the slave axis moved successfully. However, when the same steps and operations are performed with the same IDE just downgrade SoftMotion version from 4.17.0.0 to 4.10.0.0, everything works normally and without problems as expected in MC_CamIn block with FreeEncoder master. (By the way, The used IDE version is Codesys V3.5 SP20patch3.) Best Regards Imdat
Last updated: 2024-11-11
Post by rringo on Function block not autofilling
CODESYS Forge
talk
(Post)
I am attempting to place a block and make it an Analog sensor. When I go to change the name like in the instructional video on youtube it does not give me an option to autofill the block with a known configuration. This is a problem I have in Codesys 2.5 and 3.5. Did I mess up the install of the program or need to install a library? Any help would be appreciated. https://www.youtube.com/watch?v=PkJYQeIUmIM&t=136s at time mark 2:15ish The first image is what I can do and the second is what the videos function autofills to.
Last updated: 2023-08-24
Post by rossanoparis on How to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server
CODESYS Forge
talk
(Post)
Hello at all I'd like to know how to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server. In the past, I tried to ask in "Forge" about this topic, but I could find neither help nor document informations about it. Reading the file "codesyscontrol.log" I see these logs OPC UA Server Started: Hostname: NTLRPICTRL01, Port: 4840 URL: opc.tcp://NTLRPICTRL01:4840 Loopbackadapter activated. **All available networkadapters are used.** Multithreading activated. 3 workers used. My controller, which is a Linux PC, has got two network cards eth0 and eth1 I whant to use the card with name "eth0" as a server for OPCUA and keep the "eth1" free for other stuffs. Is it possible ? Best regards Rossano
Last updated: 2023-08-25