Post by timvh on VisuElems.CurrentUserGroupId is not stable CODESYS Forge talk (Post)
I'm not sure what you are trying to do, but getting the CurrentUserGroupID like this will not work, because there could be multiple Visualization Clients and each can have a different user that is logged in. Also when you go online with CODESYS and open an Visualization, this is counted as a client. Probably this is the reason you see it changing. What you can to is "iterate" over all clients and then see which user is logged in on which visualization Client. For this you need to add the Visu Utils library to the project and call the FbIterateClients. See https://content.helpme-codesys.com/en/libs/Visu%20Utils/4.4.0.0/VisuUtils/VisuActionUtilities/Function-Blocks/FbIterateClients.html fbClientIteration( xExecute := x_Execute, itfClientFilter := VU.Globals.AllClients, itfIterationCallback := fbIterator, xDone => x_Done, xBusy => x_Busy, xError => x_Error, eError => e_Error); The fbIterator, in the example above, should be an instance of an FB which you have created yourself and this must implement VU.IVisualizationClientIteration. For example: FUNCTION_BLOCK FB_ITERATOR IMPLEMENTS VU.IVisualizationClientIteration Then automatically the corresponding methods will be called. In the HandleClient Method, you will get an interface to the client(s) and then you can get the current user through this interface: itfClient.UserGroupId You can also get the UserName: itfClient.UserName
Last updated: 2023-11-14

Post by timvh on Device diagnosis ( EtherCAT IO card ) CODESYS Forge talk (Post)
You can get the state by just using the name of your node (same name as in device tree): VAR etcState: IoDrvEthercatDriverLib.ETC_SLAVE_STATE; END_VAR etcState := EJ1100.wState; Alternatively, you can iterate through the device tree to get the status of all (Ethercat) nodes. See here an example (no guarantee it works, just give as suggestion): PROGRAM P_IO_State VAR CONSTANT uiMAX_NR_OF_TERMINALS : UINT := 100; END_VAR VAR // general device diagnosis // can only be used when the Device - PLC Settings - Advanced settings - enable diagnosis for devices is enabled // this will add the DED library coupler: DED.INode; terminal: DED.INode; aDeviceState: ARRAY[0..uiMAX_NR_OF_TERMINALS - 1] OF DED.DEVICE_STATE; uiTerminalCount : UINT; uiIndex : UINT; // for each terminal check if it implements device diagnostics xQueryResult: BOOL; itfDevice : DED.IDevice2; xDiagAvailable: BOOL; eError: DED.ERROR; xEverythingOK: BOOL; END_VAR uiTerminalCount := 0; // start at the top of the device tree with the first EtherCAT coupler coupler := EtherCAT_Master.FirstChildNode; WHILE coupler <> 0 DO // for each coupler that is found start at the first terminal terminal := coupler.FirstChildNode; WHILE terminal <> 0 AND uiTerminalCount < uiMAX_NR_OF_TERMINALS - 1 DO // for each terminal that is found get the status through the device diagnosis interface xQueryResult := __QUERYINTERFACE(terminal, itfDevice); IF xQueryResult THEN aDeviceState[uiTerminalCount] := itfDevice.GetDeviceState(xDiagnosisInfoAvailable => xDiagAvailable, eError => eError); uiTerminalCount := uiTerminalCount + 1; END_IF terminal := terminal.NextSiblingNode; END_WHILE coupler := coupler.NextSiblingNode; END_WHILE uiIndex := 0; xEverythingOK := TRUE; WHILE uiIndex < uiTerminalCount DO IF aDeviceState[uiIndex] <> DED.DEVICE_STATE.RUNNING THEN xEverythingOK := FALSE; EXIT; END_IF uiIndex := uiIndex + 1; END_WHILE
Last updated: 2025-02-06

Post by pistola on C0357: "GetNextClient" is obsolete, use VisuUtils instead CODESYS Forge talk (Post)
I'm having some troubles with this same issue and I'm wondering if someone can help me out. On a settings visual I allow the operator to enter some values however if they activate the page change button it will change the change with the Numpad dialog open. Since I'm using Visuelems.CURRENTVISU to change the pages I came across this code noted below for determining if the Numpad dialog was active. This code worked great however now in 3.5.19 it's now obsolete. I've tried following the directions in the attached program above however I can't see to get it to work in my program. Can anyone provide some help to determine if a dialog is open? FUNCTION Check_Dialog_Open : Bool VAR_INPUT sDialogName : STRING; // Input variable for the name of the dialog END_VAR VAR pstClientData : POINTER TO VisuElems.VisuStructClientData; // Pointer to the client data structure itfDialogManager : VisuElems.IDialogManager; // Interface for the dialog manager itfMyDialog : VisuElems.IVisualisationDialog; // Interface for the specific visualisation dialog END_VAR // Begin the iteration over the client manager VisuElems.g_ClientManager.BeginIteration(); // Loop through each client until no more clients are found WHILE (pstClientData := VisuElems.VisuElemBase.g_ClientManager.GetNextClient()) <> 0 DO // Get the dialog manager interface itfDialogManager := VisuElems.g_VisuManager.GetDialogManager(); // Get the specific dialog interface using the dialog name itfMyDialog := itfDialogManager.GetDialog(sDialogName); // Check if the dialog is open for the current client Check_Dialog_Open := VisuDialogs.VisuDlgUtil_IsDialogOpen(itfMyDialog, pstClientData, itfDialogManager); // If the dialog is open, exit the loop IF Check_Dialog_Open THEN EXIT; END_IF END_WHILE
Last updated: 2025-03-27

Post by westcountryewe on Displaying a Target Web Page on WebVisu CODESYS Forge talk (Post)
I have a main PLC with my CODESYS project on, including Web Visu. I also have a second device used for pump monitoring, all of this is displayed on a seperate HMI. I am looking at displaying the pump monitoring HMI on WebVisu so that I can solely use 1 HMI rather than having two. I can project the pump monitoring HMI into Chrome, and log in and it works fine. When I'm using the Web Browser element in Web Visu, enter my URL (device IP) it shows me the web page, but doesn't show me all of it. It uses parts of JavaScript for the login authenticiation and various other widgets. Similarly, I cannot get Youtube or Google to display on WebVisu either (possibily because of the same reason). Does anybody have any tips on how I can display the likes of Youtube or Google onto WebVisu so I can view it on my 7inch HMI (I suspect that if I can get Youtube or Google to work, then I will also be able to get my pump montitoring web page to work too).
Last updated: 2025-07-09

Post by gvdb on Raspberry Pi 4 mod B icm codesys linking USB serial device (arduino) to com port CODESYS Forge talk (Post)
Raspberry Pi 4 Codesys 3.5.20 sp3 Codesyscontrol 4.15.0.0 based on sdk 3.5.21.0 Hi all, I have found a lot of topics but none of them get me on the right path, therfore i started a new post. Usually i work with plc based systems and codesys but now im trying to create an project where i read out a serial data stream from an arduino connected by an USB port. in the future this need to be more arduino's but first trying to make it work with one I had my program working but i needed to update my raspberry pu to the letest version to get the mimo screen working. Now i tried several rules in the CODESYSControl.cfg and/or CODESYSControl_User.cfg files but i never get the com port opened. At this moment i have an file CODESYSControl_User.cfg with entry: [SysCom] Linux.Devicefile.1=/dev/ttyUSB0 I tested the connection with minicom and the data runs fluently. Can somebody help me with what could be wrong? the com port states ERROR_UNKNOWN 5004 when i tried to open.
Last updated: 2025-07-17

Post by mtho on JSON Utilities - JSON file written with invalid structure CODESYS Forge talk (Post)
I'm using the JSON Utilities SL library to write configurations in my program to a file. I'm generating the JSON data using the builder function block and all appears to work correctly. When I write the jsondata to file, I'm finding that some of the JSON elements are not being written in the right location in the file. Rather than writing they keys under the parent object, they get written outside the root JSON object at the end of the file. If I then try to read the file back into the program, I get an invalid_structure error. I don't get any errors when populating the JSON data or when writing the file. I attached an example of the JSON writer output. The problems begin with key P200. Each P200 should go under MBR1 through MBR3. Among the rest of the keys, they are supposed to be under different parent objects. I am using default values for wsLineBreak and encoding.
Last updated: 2024-03-06

Post by leafy on Use third party actuator with IO-Link Master (IFM) CODESYS Forge talk (Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16

Post by leafy on Use third party actuator with IO-Link Master (IFM) CODESYS Forge talk (Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16

Post by tjacks on Opc UA Data Source Client Browse Error in Codesys HMI CODESYS Forge talk (Post)
Codesys V3.5 SP21 Patch 3 Codesys HMI 3.5.21.30 I'm trying to connect to an OPC UA server on a Kuka robot controller using Codesys HMI's data source manager. I get through the login phase and the client browses most of the data structure on the server but errors out toward the end with a generic: Error while browsing the client, Failed with service result: BadUnexpectedError. If I complete the data source setup and try to update variables, I get the attached stack trace for the error. I've tried several different endpoint and security options. Most get me through the login but all error out while browsing. UA Expert happily connects and browses with the same configuration. I've connected this same version of Codesys to TwinCAT OPC UA servers and Siemens PLC OPC UA servers. Any ideas on what may be causing the generic BadUnexpectedError during OPC UA server browse?
Last updated: 2025-11-17

Post by tk096 on Some 'pathetic' errors in SoftMotion program CODESYS Forge talk (Post)
Meanwhile, I would like to understand why the motion FB instances must still be called even after the Execute is set to FALSE, especially in view of the fact that the next instruction is programmed to abort the previous one, with BufferMode set to 'Aborting'. All these unnecessary FB calls are an unnecessary overhead on the CPU anyway. Is there any precise rule about when to cease calling the various instances? (It should precisely be the 'done' status that says this one has finished its work). In general: - Motion function blocks have to be called until they report 'Done', 'Error', 'CommandAborted' or a subsequent motion FB with BufferMode=Aborting is started in the current cycle. - Setting the Execute input to FALSE will not abort any ongoing motion of the motion function block. For example, one case that is often problematic is the execution of the Axis Halt instruction. When, after a MoveAbosulte instruction this returns the event as 'done' and indeed the axis is in standstill, the state machine first sets the move instruction to FALSE, and the next cycle sets the Halt request to TRUE. Some of the time everything works out fine. Occasionally, however, in this exchange, the axis goes into fault, also losing the OPERATIONAL state. I think the error SMC_FB_WASNT_CALLED_DURING_MOTION is only a follow-up (and misleading) error that results from the axis not being in operational state anymore (bus problems). Is there an error 'regulator or start not set' in the device log before the error 'motion generating FB wasn't called for at least one cycle'? Which error does the respective function block (Halt.ErrorId) report?
Last updated: 2024-07-22

Post by yannickasselin on MQTT QoS 1 & 2 CODESYS Forge talk (Post)
Hello, I am using Codesys sp20p3 and IIoT library 1.11. I am trying to test QoS 1 & 2 and I have some issues. I am using mosquitto as the broker. I am also using some other MQTT clients like Node-Red and TwinCAT. They all work as expected for every QoS levels. I only have issues with Codesys MQTT client. In the Codesys client, if I subscribe to a topic as QoS 1 or 2, and a client publishes to this topic, I receive the message. But if I disconnect the Codesys client from the network and a client publishes to the subscribed topic, when I reconnect Codesys client to the network, I don't receive the messages as expected. Also there does not seem to be an auto-reconnect feature. So I have to manually set the mqttClient.xEnable bit to FALSE then back to TRUE in order to reconnect to the broker, then I also have to set the subscribe.xEnable to FALSE and back to TRUE in order to re-subscribe to the topic, but even then, I don't receive the messages that were published while I was disconnected. What am I doing wrong? I set the cleanSession bit to FALSE and I give my client a clientID. With the TwinCAT MQTT Client, I do the same thing and everything works as expected. It even auto-reconnects to the broker. I would expect Codesys MQTT Client to be as reliable as TwinCAT. Maybe I am doing something wrong? I also noticed that when trying to publish a QoS 1 or 2 message while disconnected from the broker, it does not work. In TwinCAT, I am still able to publish. The messages are stored in the client and published once reconnected to the broker. I would expect to be able to do the same thing in Codesys. Is this all possible? Am I doing something wrong? Thank you
Last updated: 2024-10-26

Post by timvh on CANbus issue CODESYS Forge talk (Post)
On a PC with the Control Win, this is probably related to the fact that the CAN drivers are not loaded. Go to the folder where your Control Win Configuration file is: - E.g. C:\ProgramData\CODESYS\CODESYSControlWinV3x64\E1FA7ABE - Open the CODESYSControl.cfg - Remove the semi-colon in front of the CAN driver you want to use (section ComponentManager). - Set the component ID to the next number in the list (e.g. Component.8) - Save this file and restart the Control Win.
Last updated: 2023-09-14

Post by timvh on When Keyboard Key is in Hold, then Webvisu is extreme slow and latent CODESYS Forge talk (Post)
I'm not really sure what you are trying to do, but maybe you are referring to using the CmpCharDevice library? When you "open" the connection to a device, you can pass flags. What helped me is to set the non-blocking flag. I'm not sure if this is what you are referring to, but maybe it helps: dFlags: DINT := CmpCharDevice.ACCESS_MODE.O_RDONLY + DINT#4000; // see details for flags: http://linux.die.net/man/2/open, + DINT#4000 is for non-blocking hDevice := CmpCharDevice.CDOpen(szFilename, dFlags, Result);
Last updated: 2023-09-20

Post by ofey on Device parameter - ‘ModbusTCP Configuration’ CODESYS Forge talk (Post)
Hi! Do anybody know how I can add and enable the parameter 'Default Modbus TCP slave' on a device? I am currently writing a program where the PLC shall be set up as a Modbus TCP client, but I dont know how to add parameters to devices in codesys. I'm pretty new to the codesys environment. The picture in the attachment is on a similar PLC project where I have not written the code. my goal is to add this parameter in another project.
Last updated: 2023-10-04

Post by damian177 on Codesys MQTT subscribe CODESYS Forge talk (Post)
Hi, In my project I have MQTT Client like below: //mqtt client mqttClient( xEnable:=connect_to_broker, sHostname :=sHostname, uiPort:= uiPort, xUseTLS:=FALSE, wsUsername:="", wsPassword:="", xCleanSession:=TRUE, sClientId:='694d45587761676f4b6f6e74656e6572', pbWillMessage := ADR(sWillMessage), uiWillMessageSize:=DINT_TO_UINT(Stu.StrLenA(ADR(sWillMessage))), xWillRetain:=FALSE, udiTimeOut:= 10000000); And ten subscriber's , one of those is below: //subscribe a topic1 mqttSubscriber_S1(xEnable:=subscribe, eSubscribeQoS := 0, pbPayload:=ADR(sSubscribeMessage_S1), udiMaxPayloadSize :=SIZEOF(sSubscribeMessage_S1), mqttClient:=mqttClient, wsTopicFilter:=wsSubcribeTopic_S1); TerminateString(ADR(sSubscribeMessage_S1), mqttSubscriber_S1.udiPayloadSize); After connected to broker I set subscribe to TRUE in alls subscribers and my mqttclient recive error : ACKNOWLEDGE_TIMEOUT what can be wrong ?
Last updated: 2023-10-11

Post by tehthoams on Find Function: Object reference not set to an instance of an object. CODESYS Forge talk (Post)
Hey, Sorry this isn't super helpful, but i had this problem once and was able to resolve it. I can't recall how I solved it and whether it was a problem with my codesys installation or the project itself. If it is the codesys installation, make sure all your required libraries and plugins are installed and available. compare with a colleagues installation if possible. I vaguely recall saving a copy of my project and deleting things one by one until the error went away...
Last updated: 2023-10-30

Post by tehthoams on Find Function: Object reference not set to an instance of an object. CODESYS Forge talk (Post)
Hey, Sorry this isn't super helpful, but i had this problem once and was able to resolve it. I can't recall how I solved it and whether it was a problem with my codesys installation or the project itself. If it is the codesys installation, make sure all your required libraries and plugins are installed and available. compare with a colleagues installation if possible. I vaguely recall saving a copy of my project and deleting things one by one until the error went away...
Last updated: 2023-10-30

Post by snhatton on Running webvisu with Codesys Control Win V3 in Simulation Mode CODESYS Forge talk (Post)
Yes, you can use the CODESYS ControlWin V3 Soft PLC. However, if simulation is enabled on the device this will disable all communication, so you need to turn off simulation to view the visualization in a web browser. In simulation mode, all IO and communication is disabled for standalone testing. In addition, make sure to set the start visualization in the WebVisu object in the application tree. I hope this helps!
Last updated: 2023-12-04

Post by taqamert on Codesys 2.3 & Peak PCAN CODESYS Forge talk (Post)
Despite working on it for days, I haven't achieved any results. I followed the necessary steps one by one as mentioned in the file you sent, but there hasn't been the slightest change. I couldn't find the step you mentioned "Set the 'Can Board Type' to PCAN USB" in the Word document. There is no such setting anywhere I looked. Is there a more detailed explanation available, or can you explain it in more detail? What am I missing?
Last updated: 2024-07-16

Post by mubeta on Some 'pathetic' errors in SoftMotion program CODESYS Forge talk (Post)
Yes, this point is part of my misunderstanding. Why, after the execution ot the motion FBs is set to FALSE and exsecuted at lest one time, it must be continuosly called, even if the motion control it's take from another subsequent instruction. This is what I really don't undertand, but what in fact it's happening. For example, in case of stopping a MoveVelocity FB, then Halting the motion by the related FB, the axis at spot goes into error. If there was bad trigger management, the various instructions would NEVER work.
Last updated: 2024-07-18

Post by mikek10 on Error IoDrvEthernetIP: Connection Failure. (16#1) How to solve CODESYS Forge talk (Post)
Your connection configuration should look something like the attachment. Consuming assembly O->T will be the hex of the assembly you want to reference for output data - I want 102 (DO Data Only) shown in the Wago web page 102 = 16#66. Producing assembly (T->O) is the assembly you require for input data - again shown in the Wago web page - I want 108 (DI Data Only) or 16#6C Then set the number of bytes as per the data in the Wago web page too (both 2 in my case)
Last updated: 2024-07-22

Post by stuartjr on POU Private variables CODESYS Forge talk (Post)
Pretty sure I know the answer, but thought I would ask just in case. Is there a way to set variables declared in a POU to private so that they can not be accessed from other POUs. I tried using the library pragma, but that just stops the variables being displayed in the selection tree. My compiler version is 2.3.9.62 if that's relevant, and I'm using an ABB AC500 V2 PLC. Cheers
Last updated: 2024-07-31

Post by alex-at-xana on EThercat Dynamic configuration CODESYS Forge talk (Post)
Ah - forgot another question as it may be related to the PLL problem: I am executing a 4ms cycle. I do not call (from what I know) the Ethercat_MAster periodically in my program. The bus cycle task is set to the Ethercat task. I would assume that the master should send 250 frames per second. Yet, the status of the master says it transmits 500 frames per second which would indicate that the master is called twice. Any ideas there?
Last updated: 2024-09-10

Post by dkugler on TargetVisu Freezing CODESYS Forge talk (Post)
The only weird situation i remeber with particular or complete frozen target visu was after the rtc clock was fallen or set back to the past. It looked like after running a while the alarm history database crashed during writing entries at a date lot of years in the past. After setting the rtc clock to actual date/time and deleting the alarm db every thing worked fine. I don't know, if this is/was a problem of our PLC hardware/firmware? Maybe check date/time at your system?
Last updated: 2024-09-13

Post by winki on Modbus TCP & RTU with Control for Linux SL CODESYS Forge talk (Post)
For small project, I would like to use my industrial computer as a PLC + Industrial Computer. Like that I can save the cost of one PLC. That why I am using Codesys on Linux. With the nic it is not working. I already set the IP adress with /etc/network/interfaces. Can it comes from there ? looking to "Control Linux SL" docuemntation it should work with rtu.
Last updated: 2024-10-23