Post by reinier-geers on License problem gateway
CODESYS Forge
talk
(Post)
16.4 Epis What has it to do with the manufacture? It just a licence more not. So basicly the idee of codesys sucks. 3s acts like its posible to add a license. And then it depence on the manufacturer. Why ?? Its a computer !! has nothing to do with the manufacturer. Most dont what a basic licence because they have to pay for that. 3s is the problem not the manufacture of the hardware. Its like the licence of the raspberry pi. HMI is not working. Sorry you get a refund. Why suggest that its possible wen its not !!. It cost me a lot of time. Who pays my time. Why do i have to pay for somting thats not working.
Last updated: 2024-04-26
Post by jonasz on Discontinuity of A/B/C axis movement.
CODESYS Forge
talk
(Post)
Hi, My problem was related to the behavior of the modulo axis, but maybe you will find something useful from what I write. The solution lies in path processing. Codesys offers a G-code analysis tool. Insert a CNC object into the project. The CNC settings object will be added automatically. By inserting appropriate processing modules into the CNC settings object and parameterizing them, you can test the behavior of the axis. When the effect is satisfactory, remember to add the module from CNC settings in the correct order in the processing path. Each CNC machine case is different. You need to spend some time to get your design tailored like an Armani suit. Good luck.
Last updated: 2024-05-09
Post by westcountryewe on Persistence Variables missing and DO NOT retain from Persistence Channel when using Boot Application
CODESYS Forge
talk
(Post)
We've been experiencing an issue through SP18, SP19 and now SP20 where the Persistence Variables do not retain if we upload our program via a Boot Application. If we use the exact same program, and perform a Direct Upload via the Laptop and Ethernet connection, the Persistence Variables work exactly as expected. I have submitted 2 bug support tickets but I haven't had a response back from Codesys. Has anybody experienced the same issues and discovered a workaround? We have a requirement to utilise the Boot Application method because of logistical restrictions of being able to get out to every site, so at the moment it's a bit restriction.
Last updated: 2024-05-15
Post by fugtwad on Automation Builder V2.5 EtherCAT CM579 Master Scan for devices - >No gateway selected
CODESYS Forge
talk
(Post)
ABB Automation Builder v2.5.0.22 Premium CodeSys 2.3.9.62 Running on Win 10 VM x64 Goal: I have an EtherCAT topology issue which normally a "Scan for devices.." on the EtherCAT master would shed some light on. Issue: Upon trying such I get a "No gateway selected" error. Question: How might I point the the "scanner" at a gateway? What is working: Gateway is running in system tray. I can go online to PLC. A scan from the "Diagnostics live" tab of the EtherCAT master gives slave status. What I have tried: Restarting gateway in system tray. Exiting system tray gateway and reloading it. Turning off firewall. Contacting ABB support multiple times. Any help appreciated.
Last updated: 2024-05-20
Post by stewnguth on New License not working.
CODESYS Forge
talk
(Post)
Hey there, I am pretty new to the codesys space, but I got a codesys control basic M license for my raspberry pi that isntalled with no problem yesterday. Today, I went to install the visualization M locense as well because I went over the variable limit and am getting a "servernotfound" error in codesys when attempting to activate. I also tried to follow the advice in some other threads and install using a license request file on the web interface but am getting a message saying "An internal error occured" when attempting to install the license. Can anyone help me get this up and running? Thanks for your time.
Last updated: 2024-05-23
Post by jaspergain on Non-existing identifiers
CODESYS Forge
talk
(Post)
Hello, I got a bit of a weird issue going on which is kind of annoying. So recently we switched a lot of Modbus IO to EtherCAT, as we were having issues with stability. All works fine, which is great. But sometimes when I change the program I get errors claiming that identifiers are not defined. Meaning I can't go online. See the picture below. I believe this is because some of these identifiers were used with Modbus, and they weren't properly removed/deleted? A clean all temporary fixes the issue, but it comes back again after a while of changing the code, and building. Any way to fix these non-existing required identifiers, or even find out where they are required? Thanks for the help in advance. Jasper.
Last updated: 2024-05-29
Post by kronlundo on Licensing info not available (WAGO PFC200 + Codesys V3)
CODESYS Forge
talk
(Post)
Hi! We're using a WAGO PFC200 for several projects towards the energy sector, and recently upgraded to CODESYS V3. We have the "IEC 60870-5-104 Server" package in a test program, and it works well with the package in DEMO mode. However, when we acquired a license for the "IEC 60870-5-104 Server" package and tried to add the license on the PFC200 through the license manager, we get an error (see attached file). It seems like there is no CmContainer on the device, does anyone have an idea on how to fix this? We've also contacted WAGO on this issue a while back with no feedback yet.
Last updated: 2024-06-10
Post by jens on Modbus tcp - channel
CODESYS Forge
talk
(Post)
Help wanted This is the first time i'm doing a Modbus Tcp project. I have some VLT with a extension module MCA-122. i'm currently unable to write to the VLT slave, but i can read from status word parameter=1603 and address := 16029 where the address is calculated from parameter is ((id x 10)-1). in the manual the functions that are supported are 3 hex, 6 hex, 10 hex, b hex and 11 hex. read holdin registers, write single register, write multiple registers, get comm. event counter, report slave id. i'm only using the Modbus Slave Channel is this wrong when trying to write to the vlt ?
Last updated: 2024-06-13
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by tayhim on WAGO HMI Device not found
CODESYS Forge
talk
(Post)
Hello, I'm trying to connect with a Wago TP600 HMI but without success. I'm using codysis 3.5 SP19 patch 7 (SP20 block all the time) and the official wago package is installed. However, when I scan and select my device, I get a message saying that the device doesn't match the project's device object with the possibility to update the device (as shown in the attached picture). however, after choosing to update i got a message that the device is not found. I've tried with a new empty project but the same results. do you have any ideas? Thanks.
Last updated: 2024-06-25
Post by mikek10 on HTTP Client TCP Init Error
CODESYS Forge
talk
(Post)
Hi, I tried posting in the discussion for the HTTP Client example but perhaps that is not monitored? I have been using http client successfully for approximately 12 months, however in recent weeks I have begun to get TCP_INIT_ERROR when attempting to communicate. The only resolution seems to be power cycling and then the connection begins to work again for a time. I am not aware of any changes to code or libraries between working ok and now. Cold reset does not resolve, only power cycle. It seems the error from NBS.TCP_Client is 6002 which I think is invalid_addr However the address is the same when working and not working?
Last updated: 2024-07-04
Post by amy123 on Alarm Manager Example Alarm Client doesn't Populate
CODESYS Forge
talk
(Post)
Hello, I tried to run the example project from https://forge.codesys.com/prj/codesys-example/alarm-manager/home/Home/ However, I can not get the interface for Alarm History 12 Alarm Manager client to populate with any alarms. 'udiResult := AlarmManager.g_AlarmHandler.RegisterClient(itfAlarmManagerClient12, ADR(arritfAlarmsFromHistory12), iMaxCountAlarmsFromHistory12);' when I look at itfAlarmManagerClient12 its always empty. What is confusing is that when I simulate 2 alarms, iCountActiveAlarms 12 has a vlaue of 2, associated with itfAlarmManagerClient12 - so that appears to work. And yet, its useless as the ProcessAlarms Function can't extract anything from the empty array. I dont understand how these arrays are supposed to be populated and why its not working. Any help would be greatly appreciated!
Last updated: 2024-07-15
Post by shrikantp007 on new to codesys help on modbus with ardunio modbus rtu
CODESYS Forge
talk
(Post)
Hello , I am new to codesys ,working with it for just 15-17 days so ,i think i am able to installed it and configure it ,not i want to use ardunio program (smart dustbin ,college project using motor and Ultrasonic Module HC-SR04 and servo motor). i use ardunio program to write code with chatgpt to work ardunio as a modbus rtu as i dont have ethernet or wifi shild ,i wrote program in ariduno but now don have idea what change i have to make in codesys to comunicate as modbus slave it give error with bus error ,where i can get all errors ? Thanks in advance :)
Last updated: 2024-07-21
Post by hazarath on How extract JSONElement containing Array data
CODESYS Forge
talk
(Post)
I want to extract each element of an Array. Can someone help me with this. When I use JSONElementToString (part of JSON Utilities SL), I am seeing output as "ARRAY" instead of actual data. Here is the JSON content that I want to read : { "value1Unit": { "units": "M" }, "data": { "stepSize": 300.23, "points": [6,8] } } I would like to read each item of the element "points" i.e. 6 and 8. Here is the code I used, // Reading the content as JSON reader ( xExecute := execute , pwData := ADR ( converted_value ), jsonData := jsonDataStorage ); // Get the JSON Element jsonDataStorage.FindFirstValueByKey( wsKey := fidKeyVar, diStartIndex := searchElem, jsonElement => jsonElement ); JSON.JSONElementToString ( element := jsonElement , wsResult := valueWstring ); The content of the output of valueWstring is shown as "ARRAY" instead of the array items i.e. 6 and 8 Please can someone help me.
Last updated: 2024-07-30
Post by dawidr on Best practices for querying multiple MODBUS devices
CODESYS Forge
talk
(Post)
Hi! What are the best practices for querying multiple Modbus devices? Single PRG or maybe multiple PRG (so basically multiple thread) per each Modbus device. In my current implementation I'm using single PRG and I'm utilizing FbMbMasterMultiQuerySerial and WagoAppPlcModbus.FbDigitalTwinMbSlaveDevice in eCockpit with PFC200. I've the timer with 2 seconds delay there and it was working fine for single device. But now I have three Modbus devices and for two of them I need to run 2/3 queries to get data from all registers. I noticed that the delays for getting the data from the Modbus devices is much bigger right now.
Last updated: 2024-07-31
Post by expertplas on No connection to opc server from codesys opc client
CODESYS Forge
talk
(Post)
Hello, we have aproblen to connect our CODESYS OPC Client to the OPC Server. We installed the client according the CODESYS manual. We can browse the server and variables can be linked to the PLC. I created a self signed certificate for the CmpOPCUAClent as described. The server has a cerificate also. I copied the certificates to the trusted zone of server and client. But when it comes to data exchange we get an error message. "Communication error in data source OPC UA Library. Error ID : 7001 German : "Kommunikatinsfehler inder Datenquelle OPC UA -Bibiothek. Es wurde kein genauer Fehler angegeben. Fehler ID : 7001" It semms that there is no cerificate exchange. We are working with CODESYS 3.5 SP19 Patch 5. Can anyone here say something about this error or has an idea for a solution? Thanks.
Last updated: 2024-08-19
Post by shabroz-gill on Exception when OPCUA datasource disconnects from Server
CODESYS Forge
talk
(Post)
If i loose the network and the opcua data source suddenly looses connection with the server, i get an exception and my application stops working. I am using the latest version of the communication add v4.5.2.0 Is this a known issue? This makes the datasource unusable because it is inevitable that we will loose connectivity at some point, and the datasource crashing everything due to that seems to be a deal breaker. I can provide more details is someone from codesys is reading this. You can recreate is by just shutting off the Opc server after the codesys data source is connected and reading data from it. The codesys app does not crash everytime and sometimes it is able to reconnect without crashing, so you may have to try this a few times to see the exception. Best regards
Last updated: 2024-09-16
Post by jari-koivuluoma on Newly created texlists wont appear in the selection dropdown
CODESYS Forge
talk
(Post)
When I create a new textlist in Codesys 3.5 SP19 Patch 5, it wont appear in the dropdown menu at Rectangle element > Dynamic texts > Text list. If I just type the name of the textlist to the field (in quotes), I get an error saying that some file is missing. Any good ideas what to do and what is going on. I recently updated to that version and I only now noticed this when I needed to add a new textlist so Im quite screwed with this not being able to add text lists. While im typing this, I tried copying an existing list and modifying it and it seems to show. Any ideas?
Last updated: 2024-09-19
Post by timvh on FB string and naming
CODESYS Forge
talk
(Post)
I see, you want to initialize the FB. To be able to initialise it like you described, you need to add the FB_Init method to your FB. (right click on the FB, select add object --> method). Then press the arrow down, to select the FB_Init (overwrite default implementation). In the VAR_INPUT section of this method, add the variable --> Tag : STRING; Then in the code section of this method add: THIS^.Tag := Tag; // copy initial value to local variable in FB Search Google if you want to know more about FB_Init. PS, reflection + instance path, is also an option if you want to get the full name of the instance (path) of the Function Block. See: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_pragma_attribute_instance_path.html
Last updated: 2024-09-30
Post by andrebrandt on FB string and naming
CODESYS Forge
talk
(Post)
Thank you so much. This worked. Waht im trying to do here is to automatically tag each sensors, valves and so on. There is a preatty nasty tag system i working on. "_320" is not alloved. I can have a tag "+4f=320.004-RT001V" In codesys I want to build the FB in folders. -4f | --320 | --001 This is the system structure. Inside here is all of the sensors and so on. But with Codesys, I cannot tag this like this. So what I'm trying to do now is to Make a folder for the building "4f" and one for the system "320", and a POU _001. Is there a way in init to get folder names?
Last updated: 2024-10-01