Post by madskaizer on ModbusTCP Slave Device, maximum uiClientConnections? CODESYS Forge talk (Post)
I got a Wago PFC200V2, running Codesys 3.5.16.40, 100ms scan cycle, consumes about 20ms. It will randomly crash the runtime every 10 minutes to a few hours. We suspect an overloaded ModbusTCP Slave Device, as this is work done by a 3rd party contractor, but we can not find anything in the help files or documentation, that mentions a hard limit on maximum number of clients connections. This PLC currently has 44 client connections to the Slave Device and 29 slaves configured for its own Master Device. This topic metnions a hard limit of maximum 16 connections, but where is this written? https://forge.codesys.com/forge/talk/Engineering/thread/bd95b9d6d2/
Last updated: 2025-03-26

Post by kporter on High-resolution drive with SoftMotion CODESYS Forge talk (Post)
I'm beta-testing a new EtherCAT drive for a rotary (modulo) axis in a system where the encoder resolution is 81920000 counts per rotation. If I enter this in the SoftMotion Scaling/Mapping tab for "increments <=> motor turns", I get the error below on the Commissioning tab. Is SM unable to handle a high-resolution encoder? The bus cycle is currently set to the default of 4 msec (Control Win V3 x64), although I plan to reduce that to reduce latency, possibly by switching to the realtime (RT) master. Is SoftMotion incompatible with high-resolution encoders? SMC_CGR_INVALID_POSPERIOD Invalid modulo period (<= 0 or greater than half the bus bandwidth)
Last updated: 2025-08-25

Post by pernockham on AC Persistence - values are not read from file during start? CODESYS Forge talk (Post)
I swear I tested this like 20 times yesterday without success. Repeated it today and it works. Maybe the system needed a "real" power reboot? To note. To make a manual edit of a variable I tried some different approaches this is what worked for me. "system/online edited" gvl_var.example_variable REAL:F16#2FFB334H-4 767.7 "manually edited" (with runtime stopped followed by a "cold start" to read from file) gvl_var.example_variable REAL:790.1 (the system will use the manual value but will not set an equivalent "hex" value until next online edit/write cycle)
Last updated: 2025-09-03

Post by niloufar on Execution Order of Function Blocks CODESYS Forge talk (Post)
Hi, Our program incorporates various function blocks and programs written in different languages such as St and SFC. They implement numerous actions and methods using different languages from their function blocks. My question is whether the execution order of function blocks is associated with the programming languages used. I understand that cycle time can be configured in the task configuration, but I'm curious if there is a specific sequence order of execution for function blocks written in different languages. For example, all function blocks in (ST) are executed first, followed by the execution of (SFC). Specifically, when the function is written in (ST) and the action is implemented in (SFC). I modified all function blocks in the main PLC program and configured a task configuration for the main program.
Last updated: 2023-12-13

Post by cedriclee on RaspberryPI reconnection error CODESYS Forge talk (Post)
"Hello, I'm Cedric Lee, a PLC engineer based in Korea. I'm reaching out about an ongoing issue with the connection when attempting to control Beckhoff modules using Raspberry Pi with CODESYS for the first time. I use CODESYS to target the Raspberry Pi's IP, install version 4.10.0.0 of the CODESYS Runtime Package, and upon pressing Start in the Runtime, the target connects to the Raspberry Pi. However, within about a minute, an error window appears, stating 'no connection to the device. please rescan your network,' leading to the disconnection of the target. This cycle repeats. I've attached some pictures for your reference. I'm using CODESYS Development System V3, Raspberry Pi 4 Model B (installed as 64-bit), and Beckhoff EK1100 modules. If anyone has a solution to this issue, please help. Your assistance is greatly appreciated."
Last updated: 2024-01-11

Post by timvh on Is it possible to use debug functions such as Step Execution while the PLC ladder is in Running? CODESYS Forge talk (Post)
Yes, it is possible to set breakpoints and use step into / step over (also in Ladder diagram). Yes, the PLC will actually stop, so be carefull with this. How a PLC works is that at the start of the execution of the Task, the Inputs are read, then the code is being executed and then the outputs are written. So if you set a breakpoint, you will not see your analog inputs changing, because the task cycle is interrupted and the inputs and outputs are not refreshed. For detailed information, see: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_using_breakpoints.html
Last updated: 2024-01-16

Post by alexgooi on Update boot project default unchecked CODESYS Forge talk (Post)
Dear Forum, I'm currently switching to Codesys V3.5 SP19. When I want to do an online change, I get the option to update the boot project, in other (codesys based) packages this is checked on by default. In Codesys V3.5 SP19 (and maybe older versions) this is unchecked by default. We are doing a lot of remote updates with systems that almost never power cycle. In other words when this box is forgotten the system will run fine until a blackout. Is it possible to get it checked on by default? This question was asked before, but no answers where given. https://forge.codesys.com/forge/talk/Engineering/thread/ffb4ffa298/ Thank you in advance.
Last updated: 2024-02-09

Post by alessandro on SysMemCmp SysMemCpy CODESYS Forge talk (Post)
VAR Data1:ARRAY[1..10] OF SINT ; Data2:ARRAY[1..10] OF SINT ; Data3:ARRAY[1..10] OF SINT ; Data4:ARRAY[1..10] OF SINT ; ex_1 : BOOL ; ex_2 : BOOL ; enable : BOOL :=0 ; END_VAR // PROGRAM // The scope of this example is compare and copy the values of two ARRAY only if some value is different using SysMemCmp and SysMemCpy. // In this 2 example we don't use a FOR cicle for do this, and pBuffer1 and pBuffer2 is just a pointer to ARRAY. See details in Library util.SysMem of Codesys // The compare funcion util.SysMem.SysMemCmp is bidirectional if Data1 chanege respect Data2 ex_1 go to 1 and if Data2 change respect Data1 also // but the copy function util.SysMem.SysMemCpy work only from source ARRAY pSrc:=ADR(Data1) to destination ARRAY pDest:=ADR(Data2) // Example 1 Full ARRAY compare and copy // This compare 2 different equal ARRAY and if there is some difference ex_1 go to 1 and if you give enable he copy Data1 in Data2 ex_1 := TO_BOOL(util.SysMem.SysMemCmp(pBuffer1:=ADR(Data1), pBuffer2:=ADR(Data2), udiCount:=SIZEOF(Data1))); IF ex_1 AND enable THEN util.SysMem.SysMemCpy(pDest:=ADR(Data2), pSrc:=ADR(Data1), udiCount:=SIZEOF(Data1)); END_IF // Example 2 Only selected area of the ARRAY compare and copy // This compare 2 different equal ARRAY starting from position number [3] for 4 byte in this case start at position [3] and finish at position number [6] // and if there is some difference only in area [3..6] of the ARRAY ex_2 go to 1 if you give enalbe he copy Data3[3..6] in Data4[3..6] // if something change in other array position[0..2] or [7..10] are ingnored ex_2 := TO_BOOL(util.SysMem.SysMemCmp(pBuffer1:=ADR(Data3[3]), pBuffer2:=ADR(Data4[3]), udiCount:=4)); IF ex_2 AND enable THEN util.SysMem.SysMemCpy(pDest:=ADR(Data4[3]), pSrc:=ADR(Data3[3]), udiCount:=4); END_IF // Attention udiCount input is intended in <byte> in the example 1 I pass to udiCount:=SIZEOF(Data1) for compare and copy the intere ARRAY and // SIZEOF pass the size of intere ARRAY in byte to the function input, in this 2 examples I used variable type SINT each one occupie 1 byte and one position in the ARRAY // and in the example 2 I pass udiCount:=4 for compare and copy only 4 position of Data3/4[3..6] if you want to extend this example and use it for an ARRAY OF WORD // remember that each WORD will occupe 2 byte (16 bit) and you will have to pass udiCount:=SIZEOF(Data1) if you need to compare intere ARRAY example 1 // but need udiCount:=(42) for the example 2 because need to compare and copy 4 word each occupie 2 byte (16 bit). // For REAL (32 bit) need udiCount:=SIZEOF(44) for LREAL or (64 bit) need udiCount:=SIZEOF(416) // a good rule is calculate the dimension of the ARRAY in byte without empty space at the end, multiple of data type number for variable bigger then 8 bit // Example : If you want to create an ARRAY for 5 REAL (32 bit) each occupie 4 byte the correct size is ARRAY[0..19] OF REAL 54=20 position. // NOTE : In the example the position of compare function util.SysMem.SysMemCmp is first and the copy function util.SysMem.SysMemCpy inside the IF is after // in one cycle of the program the two array is compared and if there is some difference and enable are copied. // If you move util.SysMem.SysMemCmp after the IF cycle he will copare the ARRAY in the current cycle but the copy of the value will do in the next cycle.</byte>
Last updated: 2025-10-24

Post by mubeta on Some 'pathetic' errors in SoftMotion program CODESYS Forge talk (Post)
Thank you for your interest. Your answers are in line with what I knew, so at least it comforts me that I did not misinterpret the situation. However, I don't have an exact match as, for this project over the past few days I have: 1) I have gone back to leaving the various FBs of the motion always called, all of them, and in the state machine I use a boolean to activate the various useful Execute. (But in the future I want to go back and try the programming technique with which I wanted to develop this project); 2) For the occasional error: SMC_FB_WASNT_CALLED_DURING_MOTION perhaps it was due to the fact that I had set the Ethercat bus synchronism only at the CAN master level, but not at the level of individual drives. I have now also activated it for the individual drives and it does indeed seem to have been resolved, but having also adopted the programming technique mentioned in point 1), I cannot say whether this was the solution to the problem, or instead the previous point. Is there an error ‘regulator or start not set’ in the device log before the error ‘motion generating FB wasn't called for at least one cycle’? I can't answer that right now. By now the machine is running and I am no longer there, at this one. Also, I seem to remember that the 'fbeFBerror' drive structure (5-element array), does not cycle, BUT ONCE THE 5 EVENTS AFTER SWITCHING ON, IT DOES NOT UPDATE ANYMORE (but that's another issue), so diagnostics were not easy.
Last updated: 2024-07-24

Post by dnordenberg on BOOL variable in OPC UA and modbus simultaneously CODESYS Forge talk (Post)
How can I have an BOOL variable that is read/write in both modbus TCP server and from OPC UA at the same time? Variables with %MX.n %QX.n addressing which is used for BOOL/coils in modbus server is not allowed in OPC UA symbol list on Schneider M251 controllers. I have already asked on Schneiders forum but there are not a lot of codesys experts over there :( So OPC symbols can't have a address and the modbus TCP server needs a address. So how should I do it then? It seems like an impossible combination. Since I want read/write access from both ways I can't just simply make a second variable and assign it the value of another since it would be a one way assignment. I also tried using VAR_CONFIG which then makes the address syntax %Q or %M in my main variable list and that fools OPC UA Symbol Configuration to allow it and then I add the complete %MX.n address of it in the VAR_CONFIG list. This semi works, I can toggle the BOOL from modbus but the OPC UA symbol seems to be read only. It displays symbol status but nothing happens when I toogle it. I think I need another way to have the variables and symbols pointing to the same bits in memory... My plan B is to write a BOOL array compare FB that saves a history bit from previous cycle and if that does not match current status at next cycle for either the OPC symbol or the modbus variable then it copies the new status over to the other. Maybe ugly but it's like my last alternative. Kind regards David
Last updated: 2025-07-14

Post by duvanmoreno24 on Modbus writing on value change CODESYS Forge talk (Post)
Hi all, I want to know if someone has an idea of how I can write on value change in Modbus Codesys. I have a Wago PLC and I was used to work with E-cockpit which it was quite easy to do that without the necessity to trigger any value when there was a change in the variable ( I will put how easy is ). how you can see just changing the trigger in "On value Change" will do that channel writing automatically when It detects a change in those arrays. On the other hand, in Codesys if I enable the rising edge in Codesys It ask me to put a bool variable and if triggers is going to write that value. That is making me that I have to create a function or a logic to detect the change, the problem I have is that doing that is very tedious. I first approach I got it was to create a Function who returns a bool when the value change, but I tried to keep the old value but what is happening is that in Functions all the data is erased every cycle so I can not keep any Old value. so in the Main program the trigger is going to be TRUE all the time due, the old value is cero every cycle. The second approach I got it was using a function Block (POU_1) and it works but I dont want to instance that function for every Channel or value that I want to check if the value change, Basically if I have 200 values to write trhough modbus I have to create 200 instances of that function which I think it is not practicall at all. It should be a better way to implement this as e-Cockpit from Wago Does. However, I haven't been able to know how.
Last updated: 2024-03-26

Post by manuknecht on Maximum dynamic limits of MC_MoveLinearAbsolute and MC_MoveLinearRelative CODESYS Forge talk (Post)
Hello all I use an axis group with two linear axes in a kinematic system. Using MC_MoveLinearAbsolute and MC_MoveLinearRelative, I am trying to realise dynamic movements (set velocity: 1 m/s, set acceleration: 30 m/s^2) with the highest possible jerk, as I want to compare this with a movement with a trapezoidal velocity profile. However, my measurements show that the axes accelerate with a maximum jerk of approx. 800 m/s^3, even if the value in the function block was set to 10,000 m/s^3. I have already increased the dynamic limits of the two axes accordingly (Velocity: 5000 u/s, Acc-/Deceleration: 250'000 u/s^2, Jerk: 100'000'000 u/s^3, where 1 u = 1 mm), but this had no effect. I have checked the input parameters of the function blocks and the VelFactor, AccFactor and JerkFactor factors are all set to the maximum (value 1). Reducing the cycle time has resulted in a higher jerk, but as we are already working with a cycle time of 1 ms, there is nothing more that can be done here. The axes themselves are still a long way from drawing the maximum current, which is why I assume that this should not be a problem either. Are there other factors or parameters that influence the dynamic limits and therefore allow faster movements? The PLC I am using is a Raspberry Pi 4 and Codesys V3.5 SP20 with all libraries up to date. Thanks in advance Manuel
Last updated: 2024-05-08

Post by mubeta on Some 'pathetic' errors in SoftMotion program CODESYS Forge talk (Post)
Hello everyone, I have a very simple program for the process, but it's driving me crazy and I can't see the problems I'm left with: Short topological description: Dual Core Berghof controller with softmotion runtime version 3.5.19.30; Two axes with servodrive on canopen bus, clocked distributed from master; Ethercat I/O node; 2 ms ethercat task, 2 ms canopen bus cycle time; I/O objects of the canopen master and canopen drives connected to the ethercat task cycle; Problem 1: Two separate programs each manage their own axis and drive, with separate state machines. A first axis moves primarily in velocity, except having to position itself absolutely at a predetermined point at the end of the job; the second axis, on the other hand, is a paper unwinder that changes, for each job cycle, from actions in absolute, relative, and cam displacement with the master axis. Well, the state machine of both axes was written in such a way as to call running the useful FB and change it on state change in this way: CASE i_stateMachine OF 0: o_Power(Enable := TRUE, bRegulatorOn := FALSE, bDriveStart := FALSE, Axis := o_PaperUnwinderAxis); o_MoveAbs(Execute := FALSE, Axis := o_PaperUnwinderAxis); o_MoveRel(Execute := FALSE, Axis := o_PaperUnwinderAxis); o_CamSelect(Execute := FALSE, Master := o_MachineAxis, Slave := o_PaperUnwinderAxis, CamTable := cam_PaperUnwinder); o_CamIn(Execute := FALSE, Master := MachineEncoder, Slave := o_PaperUnwinderAxis); o_CamOut(Execute := FALSE, Slave := o_PaperUnwinderAxis); o_SetPosition(Execute := FALSE, Axis := o_PaperUnwinderAxis); IF ... THEN i_StateMachine := 10; END_IF; 10: o_Power( Enable := TRUE, bRegulatorOn := TRUE, bDriveStart := TRUE, Axis := o_PaperUnwinderAxis ); IF o_Power.Status THEN i_StateMachine := 20; END_IF; 20: (* Avanzamento carta *) o_MoveAbs( Execute := TRUE, Position := o_Somewhere, Velocity := 25.0, Acceleration := 3666.7, Deceleration := 3666.7, Jerk := 48000.0, Direction := MC_DIRECTION.positive, Axis := o_PaperUnwinderAxis ); IF o_MoveAbs.Done THEN o_MoveAbs(Execute := FALSE, Axis := o_PaperUnwinderAxis); i_StateMachine := 30; END_IF 30: d_HomingPosition := ...; o_SetPosition( Execute := TRUE, Position := d_HomingPosition, Mode := FALSE, Axis := o_PaperUnwinderAxis ); (* ... *) IF o_SetPosition.Done = TRUE THEN o_SetPosition(Execute := FALSE, Axis := o_PaperUnwinderAxis ); o_LogServer.Append(sMessage := '...', lscClass := LOGSERVER_CLASS.ALWAYS, sdt := o_CommonsMgrData.systime.sdtLocal); i_StateMachine := 40; END_IF; 50: ... The code above is a sketchy example of what I wanted to write. But it gives me a spot problem: in some, the state change results in a drive error, which is unrecoverable except with a reinitialization via SM3_ReinitDrive(). Things are improved a little if in the program I always run the call of all softmotion blocks in this way: o_Power(Axis := o_PaperUnwinderAxis); o_Jog(Axis := o_PaperUnwinderAxis); o_Halt(Axis := o_PaperUnwinderAxis); o_MoveAbs(Axis := o_PaperUnwinderAxis); o_MoveRel(Axis := o_PaperUnwinderAxis); o_CamIn(Master := MachineEncoder, Slave := o_PaperUnwinderAxis); o_CamOut(Slave := o_PaperUnwinderAxis); If I don't execute all the calls of all the motion FBs used, when exchanging machine state often (but not always), the axis goes into error with event id THE_FB_WASNT_CALL... Done a little diagnostics it seems that the FBs return the bDone, before they are completely terminated. I tried doing the machine state exchange not with the bDone bit of the FBs, but with the 'standstill' state of the axis. It didn't seem to change anything. Problem 2: During the use SM3_ReinitDrive() I get the erro in the log: "NetID 0: SDO read error for object 16#607C..." Assuming that the device involved it's one of the two servodrive, (no others device are present in the network), I don't found any object 0x607C in the 'possible object list in/out' of the two drive, and I don't understand where this object can be listed. So any ideas and suggestions regarding these two issues will be very, very welcome. If you need the source project, I am willing to send it.
Last updated: 2024-07-17

Post by ryandmg on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS) CODESYS Forge talk (Post)
Thanks So Much for the reply! Were using the Weidmuller UV66-ADV-10-CAP-W The HMI is pointed to the URL which is assigned through u-OS. Basically when you log into the controller's webserver via browser you can view the installed apps. One of which is the Codesys runtime. When you click on that it takes you to the visualization. That corresponding url is what the HMI is looking for. I apologize I don't have that on hand as I'm in the office right now. I don't think I tried connecting using the port you mentioned and https in lieu of the u_OS URL. I can certainly try. Out of the box the u-OS is set for HTTP. Since we're isolated I havent changed that yet. When this has happened while logged on via chrome on my laptop, simply refreshing brings the visualization right back. In the case of the HMI in kiosk mode, we power cycle the HMI to force a reconnect, log back in u-OS and the visualization is back.
Last updated: 2023-09-06

Post by danwoodlock on RPI Zero w - Edge gateway cant install CODESYS Forge talk (Post)
Hello all, First post. I recently acquired an RPI zero W from amazon, and have been using it with Codesys v3.5 SP19 patch 2. I first got it working yesterday, and after installing the runtime on the Pi, I was prompted to install the edge gateway. Installation of the edge gateway failed because of unsupported architecture, undeterred I was able to connect to the pi and program as I wanted. The issue I've noticed is that if I do not load anything to the pi overnight, I can then no longer connect to the pi and download, although I can still ping it from my pc. I found that if I power cycle the PI, I am then able to connect again, and it works as normal. I did some googling and found instances where people recommended downloading the newest edge gateway, which brings me here. Wondering if there are any suggestions, or if this is a known issue. I actually tried installing all 3 versions of edge gateway for science, but all fail with the same message. Thanks -Dan
Last updated: 2023-09-13

Post by sturmghost on Initialization of visualization variables and cyclic code execution CODESYS Forge talk (Post)
I'm looking for a smart and short way to implement initialization of visualization variables depending on the visualization input. For an easy example consider a rectangle which rests at XPos := 0 when the input state is false and at XPos := 50 when the input state is true. My visualization variables look like this: VAR_IN_OUT State : BOOL; END_VAR VAR XPos : INT; END_VAR I put this rectangle via a visualization frame element into another visualization and link a frame reference variable with the state to it. If the variable is true, the rectangle should rest at XPos := 50 and false at XPos := 0 at visualization init but how should I assign the 50 or 0 to the internal visualization variable XPos? I would need some init-methode for the visualization but I dont want a global init-method for such tasks. I want to do it inside of the visualization element but I can't see any solution for this? It would be good to be able to define ST-code within the visualization element which runs cyclic at each VISU_TASK task-cycle then I could just check the input state and change the XPos accordingly. Does someone have a solution?
Last updated: 2023-10-01

Post by martinlithlith on Mux I2C CODESYS Forge talk (Post)
Hi! I´ll try to get this thread going again as i´m having simliar problems. Right now i get a red triangle on my connected devices (i´m testing with a BME280 sensor and a PCA9685 resvo driver). The TCA9548 have the green symbol beside it. On the "red" devices i get that the bus is not running. I have tried to either run it using the parent bus cycle setting or creating a new freewheeling task prio 1 but nothing helps. I have compared my settings to the settings from the example from the MUX package and i have read (i think) every thread in forge that could be of interest. EDIT: The ic2detect only shows the mux (70-70) and the servo drive (70-76) so i´ll look in to if i managed to burn the 280-sensor while soldering). Another question regarding the 280 sensor. I have a sensor GY-BM E/P 280 that should record humidity and temperatur. Could this be a problem with the library? Does anyone have an idea of what i might be doing wrong? I have some experience from Codesys but not much so this could be an easy one. All suggestions are welcome. I tried to upload the project archive but it did not work. Should i upload the export or how could i show you my horrible project? Best, Martin
Last updated: 2023-10-22

Post by riccardo on VisuElems.CurrentUserGroupId is not stable CODESYS Forge talk (Post)
GoodMorning everyone. I have a system that, in case of alarm, have to block. When the operator logs in must have to acknoledge the alarm and should operate in the system freely. To perform this I detect the logged User by (VisuElems.CurrentUserGroupID <> 0) with a similar code to the the following: PROGRAM AlarmMngt VAR alarm : BOOL:= FALSE; Ack : BOOL:= TRUE; PushBottonOpening : BOOL:= FALSE; Valve : BOOL := FALSE; Flag: BOOL := FALSE; END_VAR IF alarm AND Ack AND (NOT Flag) THEN valve := FALSE; PushBottonOpening := FALSE; Ack := FALSE flag := TRUE; ELSIF (NOT alarm) AND Ack THEN flag := FALSE; END_IF (* if the system is in alarm but there is a logged operator that acknowledge the alarm the system allows the valve opening.*) IF (VisuElems.CurrentUserGroupID <> 0) AND Ack AND Alarm AND PushBottonOpening THEN Valve := TRUE; ELSIF (VisuElems.CurrentUserGroupID = 0) AND Alarm THEN valve := FALSE; END_IF The problem I have is in the last 5 lines of the code: Even if there is a logged in user, the GroupID variable is subjected to a refresh that cyclically set for an instant it to 0 and this close the valve making difficult to the user to work Now I solved it creating a time hysteresys cycle but it is not a good solution. Someone is able to explane me why the GroupID variable is sobjected to this refresh and how to stabilize to avoiding it? Thank you in advance, Riccardo
Last updated: 2023-11-10

Post by open on How to create a stopwatch? CODESYS Forge talk (Post)
Hi @ph0010421, I tried the program the TimeTaken is calculated when stop is triggered. I want the TimeTaken to be continuously calculated and counting when a BOOL variable is true. I tried to program this way: Declaration: PROGRAM PLC_PRG VAR bStartStop: BOOL := FALSE; // Start/Stop button bReset: BOOL := FALSE; // Reset button bRunning: BOOL := FALSE; // Flag indicating whether the stopwatch is running tStartTime: TIME; // Variable to store the start time tElapsedTime: TIME; // Variable to store the elapsed time END_VAR Implementation: // Main program logic IF bReset THEN // Reset button pressed, reset the stopwatch bRunning := FALSE; tElapsedTime := T#0s; ELSIF bStartStop THEN // Start/Stop button pressed, toggle the running state IF bRunning THEN // Stop the stopwatch bRunning := FALSE; ELSE // Start the stopwatch bRunning := TRUE; tStartTime := tElapsedTime; END_IF; END_IF // Update the elapsed time when the stopwatch is running IF bRunning THEN tElapsedTime := tElapsedTime + T#1s; // Adjust the time increment as needed END_IF However counting of the seconds is not accurate. I tried changing the main task cycle time interval to 1000ms. The counting of seconds become slower. (see attached) Please help
Last updated: 2023-12-08

Post by trusty-squire on Confused by dwIpoTime input for SMC_Interpolator CODESYS Forge talk (Post)
Hi, Learning Codesys CNC, and I am confused by the dwIpoTime parameter. I have a basic demo application, using SMC_Interpolator feeding into SMC_TRAFO_Gantry2Tool2, which then sets the position of the x/y SM_Drive_Virtual axis. I also have a C axis which revolves the tool, which is controlled using a simple tangential angle calculation SMC_CalcDirectionFromVector. The GCode I'm using has feed/accel set at 500. The axis configuration limits are well above that (2000). What's strange is that, when I run the simulation, the feed speed changes drastically when I update the variable dwIpoTime. The larger the number, the faster it moves. What's going on here? The documentation only says "This variable has to be set for each call. It represents the cycle time in μsec." Why does it change the feed speed I'm seeing the in simulation? What is a good number to use? The example I was looking at set it at 5000. Screenshot attached.
Last updated: 2024-07-18

Post by edvard-munch on How I can get "Done flag" for "Modbus Slave Channel"? CODESYS Forge talk (Post)
This is from 10 years ago, I know. But I have been using (SLAVE_DEVICE.iChannelIndex = CHANNEL_NUMBER) AND (SLAVE_DEVICE.xDone) I suppose that it shows xDone for the channel that shows up in the iChannelIndex at the same cycle? It seems to be working properly for two devices that I have been using it before But now I have another device and using two write channels, for one register each. One channel works properly and returns DONE flag When another channel is triggered, I see that it shows up in iChannelIndex, but flag DONE not received, but no Error for the channel. Also, when i check the register in the device it's evident that data has been transferred. Is this could happen sometimes with CODESYS, so DONE flag not received? Or this is a problem with a given device? With this certain register
Last updated: 2024-12-19

Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia CODESYS Forge talk (Post)
Using SDO, I can read the EtherCAT mappings and offsets from various registers like 0x1c12, 0x1c13, etc. When I obtain registers mapped in the PDOs and various offsets, I could technically access directly to the statusword, controlword, etc., if they are mapped. I have noticed that on IoDrvEthercatLib.ETCSlave_Diag I can find pointers to the input and output buffers. However, although the input buffer can be easily read by referring to what has been obtained from the SDOs, it is not possible to write to the output buffer, as it is overwritten in each cycle by the data from the IOMapping task. Is there a way, knowing an instance of IoDrvEthercatLib.ETCSlave_Diag, to obtain the pointer to the first data in the IOMapping? The offsets are identical to those of the PDOs, but obviously the data is a copy. For me, the cleanest thing would be to access the pointers on IOMapping, for DS402a devices to retrieve the key data and point them to internal references. I need to know this as, having developed our own motion library, I would like to simplify the initial setup by eliminating unnecessary and nonsensical mappings that can lead users to unnecessary errors. In the current version that we have been using for years, we have to map everything manually. I would like to pass only the slave reference to the FB_init constructors and eliminate the mapping.
Last updated: 2024-02-12

Post by rmaas on Fieldbus has lost synchronicity CODESYS Forge talk (Post)
Hi, On a gantry system with 2 axis i am getting the following error: SMC_DI_FIELDBUS_LOST_SYNCRONICITY This happens random, sometimes it happens every 5 minutes and sometimes no error for 2 hours... The Setup: - Using codesys 3.5 SP20 with all latest libs... - Kontron AL Pi-Tron CM4 with Preempt realtime patch (Raspberry Pi 4) - Codesys runtime 4.11.0.0 (single core) - CODESYS Control for Raspberry Pi SL licensed - Softmotion + CNC + Robotics licensed - 2x Leadshine EL8-EC400 servo drives - Axis group for a 2-axis T-Gantry Ethercat network wiring: Ethercat master softmotion -> Beckhoff EK1100 -> Servo drive #1 -> Servo drive #2 Ethercat Cycle time = 4ms Max Jitter = 140~150 What i have tried so far: - changed the sync offset from 20% to 30% - changed ethercat task priority from 1 to 0 Running tasks: - Ethercat tast: Prio = 0, Interval = 4ms - Main task: Prio = 1, Interval = 8ms - Visu task: Prio = 31, Interval = 100ms - Softmotion planning task: Prio = 15, Freewheeling - 3 other default tasks that were created by AC_Persist Motion fb's are called in the ethercat task... Does anyone have an idea how to fix this? Any help is greatly appreciated!
Last updated: 2024-04-11

Post by mp9876 on Problem using MeasureFrequence FB CODESYS Forge talk (Post)
Hi everyone, new at Codesys and PLC programming in general. I am using Codesys Win V3.5 SP20 I would like to measure an encoder's frequency output (obtaining that pulse train from Factory IO) and intended to use the MeasureFrequence FB (Intern/CAA/Utilities/CAA Mathematics/3.5.19.0). As mentioned in the title what I need to measure is low frequency, such as lower than 40hz (a cycle every 25mS) or so; I could even go lower frequency if required as this is for test purposes) therefore I am not expecting problem measuring a low frequency with that FB The library in question appears to be installed as I can retrieve it from the Library Repository. I can also see it from the Device's Library Manager. Problem arises when I am trying to instantiate this particular FB. I go like this: VAR MeasF:MeasureFrequence; END_VAR Please note that as soon as I start typing the "MeasureFrequence", the MeasureFrequence comes out as a viable option in auto-typing; seems to indicate that the FB is recognized somehow. But there is no way I can compile this as it comes back with the following: C0046: Identifier 'MeasureFrequence' not defined. Tried to rename that to ABC instead of MeasF; same issue. Possibly that the library is not properly installed ? Placeholder ? I would greatly appreciate a bit of guidance if possible. Thank you and regards, Mike
Last updated: 2024-06-24

Post by jonasz on Deploy LicenseServer for Linux SL CODESYS Forge talk (Post)
Good morning, I'm digging into this topic because I'm curious about resolving my problem in a test environment. In my previous message, I asked about the CODESYS Safe Timeprovider SL package (4.18.0.0), which I saw in the illustration. I noticed that it runs as a service. I am asking about this because from the perspective of an "ordinary" user, this service provides easier access to the settings of the time provider's operating parameters. The basic time provider configuration is outlined at https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_virtual_safe_time_provider.html. Why my questions? They stem from my specific case, which is experiencing timeout issues. I know that my environment is currently only a test environment. I'm assuming a real-world scenario in which I won't be able to achieve a better result with my configuration, and I will ultimately need to increase the time provider's cycle time. By running the time provider service, I can easily influence the time provider's operation and thus eliminate the problem. I know, I know, safety systems are not life-enhancing extras.
Last updated: 2025-11-19