Post by egau on Enable and Disable Project IO programmatically
CODESYS Forge
talk
(Post)
Hi @eschwellinger, I tried this with Modbus COM slaves. I was able to disable them (slave becomes greyed out in the device tree), but the DED.Reconfigure "eError" output shows "NOT_SUPPORTED". After this, when I tried to re-enable the slave, it did not work (device stayed greyed out in the device tree), and the DED.Reconfigure "eError" output also showed "NOT_SUPPORTED". Is there something to do about this, or the device just doesn't support reconfiguration? P.S: I tried this running locally on my computer (not in simulation mode). So of course I was not physically connected to the devices. I have two similar projects, but one of them doesn't have the Modbus_COM devices. I know I can "Exclude from build" the devices for that project, but I would really prefer not to do this if possible. I would prefer to dynamically toggle a configuration variable that would enable or disable the slaves.
Last updated: 2025-03-14
Post by peterkcontrols on Codesys Network driver install for Codesys Control RTE x64
CODESYS Forge
talk
(Post)
Hello I am trying to download my project onto my Codesys Control RTE x64 soft PLC. and I have had an issue when downloading. [FATAL ERROR] Unresolved reference: 'SYSETHERNETADAPTEROPEN' [FATAL ERROR] Unresolved reference: 'SYSETHERNETADAPTERCLOSE' [FATAL ERROR] Unresolved reference: 'GETNUMBEROFADAPTERS' [FATAL ERROR] Unresolved reference: 'GETADAPTERINFO' [FATAL ERROR] Unresolved reference: 'SYSETHERNETIPFRAMERECEIVE' [FATAL ERROR] Unresolved reference: 'SYSETHERNETETHFRAMESEND' [FATAL ERROR] Unresolved reference: 'SYSETHERNETETHFRAMERECEIVE' [FATAL ERROR] Unresolved reference: 'SYSETHERNETIPFRAMESEND' [FATAL ERROR] Unresolved reference: 'SYSETHERNETFRAMERELEASE' Looking on the forum I have found other people had to install the network driver, which I have done following this youtube video by codesysGroup: https://youtu.be/10oj4wABaKc?si=664l83JXUGQSDlAe I have added the network driver, please see attached image. I have checked my BIOS to make sure my secure boot status is disabled, see attached image. when I go to component manager, the drop down menu doesnt have the new network adapter, see attached image. I have not yet purchased or installed any licenses is that what I am missing? What other reason is there that I can't download to the runtime. Thanks
Last updated: 2025-03-18
Post by macman on Codesys 3.5 OPC UA Client to Kepware OPC UA Server
CODESYS Forge
talk
(Post)
Hi, I have problem with connecting Wago PLC WAGO 750-8212/0025-0002 configured as OPC UA client to Kepware OPC UA Server. I am using Codesys 3.5.19.70. What I did so far. To the Codesys project I added object Data Source Manager and configured connection OPC UA like below: pic 1 Then I can browse the OPC server tags in “Variables” tab after prior trust on the server side of the client certificate created in the “Communication” tab: pic 2 Additionally second certificate has been created in Codesys for runtime process in “Security screen” as well as the server certificate was approved here: pic 3 But when I compiled project, downloaded it to PLC and go to RUN I can’t read selected in “Variables” tab, OPC Server tags. I am getting such error (ID: 7001): pic 4 All two PLC certificates has been trusted in OPC server (Kepware) side: pic 5 and Kepware server configuration look like this: pic 6 I can easily connect using third party OPC UA client UaExpert to Kepware server without problem. In attachment I added also log from Kepware OPC UA server. pic # - this specifies the number of a concrete graphic from one of the collective in attachment
Last updated: 2025-04-02
Post by gmau on RS232 Communication in CODESYS Control RTE V3
CODESYS Forge
talk
(Post)
Hello, I would like to implement RS232 communication into CODESYS Control RTE V3. I was writing the program testing it on CODESYS Control Win V3, where it worked fine. When I changed it to RTE, the communication was on, but I cannot send the data between PLC and scale - there is no or little response from scale - mostly one time receive and that is it. On Win V3 it was working fine. I read that I am supposed to configure CODESYSControl file for a proper communication using RTE, but even after that I can not get a stable and working communication. I am attaching my CODESYSControl and CODESYSControlUser data below, as well as I am sending the code from communication function. The communication should be through COM1 port of PC. CODESYS Version: CODESYS V3.5 SP21 + (64-bit) Runtime + Version: CODESYS Control RTE V3 Version 3.5.21.0 / CODESYS Gateway V3 - x64 Version 2.5.21.0 I would be much gratefull for any help. Sincerely,
Last updated: 2025-07-16
Post by spiessli on Softmotion axis to CANopen Maxon IDX drive
CODESYS Forge
talk
(Post)
Thanks for the advise, indeed, this was somewhat, what my intention was. I tried around again with EDSes and DCFs, anyway. It appears that the DCFs end up in a subfolder in the attach device dialog. Astonishingly, when attaching the DCF version I get a device in the device tree, where I can add a SoftMotion axis, whereas when I attach the device not in the subfolder, then I cannot. Further astonishingly, when looking in the CANopen parameters in supported profiles, "402" is listed in the case of the DCF variant, whereas in the EDS variant "0" is shown. Comparing EDS and DCF files I cannot guess, where the difference is coming from. I cannot tell either why I have always attached the EDS variant and apparantly never the DCF variant. As I am not in the lab right now, I cannot test if the connection actually is working. Thanks again, spiessli
Last updated: 2024-01-07
Post by edepalos on Text list from sd card
CODESYS Forge
talk
(Post)
Hi guys, I have a textlist in my project which is working just as expected in a drop down list. I would like to move this text list to a sd card and access it from there, because I want to ease the editing of the contents of this textlist. I'm imagining a solution like the operator shuts down the plant, takes the sd card out, edits the textlist on the card with a windows machines notepad, then reinserts the card in the PLC and restarts the plant, having the new content of the textlist populating the dropdown list. I'm sorry that I'm asking you to spoonfeed me, but I did not find anything straightforward to do this... I saw in the Project>Project settings>Visualisation a relative path thingy, but I have the plant in operation and I would not like to make 100 trial and errors right now... I'm also not interested in SysLib file read commands and stuff, I would just like to access the file from the cards part, I don't want to replace its contents dynamically or such... nor I have language files or recipes... Thank You in advance! Br, Ede
Last updated: 2024-01-16
Post by sigurdrb on send appliaction files to wago plc (codesys 3.5) via ssh
CODESYS Forge
talk
(Post)
Hi, I was hoping I could send the two files "application.app" and "application.crc" directly to the directory "/home/codesys/PlcLogic/Application" instead of logging into the device with codesys, downloading the program to the controller and then do the "create boot application", so it will reboot with the correct program running. I think i also need to edit the file "eRUNTIME.cfg" located in the "/home/codesys/ folder, because when I create the boot application from the codesys IDE, these lines are added to the file: [CmpApp] Application.1 = Application [SysFileMap] /home/codesys/PlcLogic/Application/Application.app=0x212520, 0x2DBC747E, 2DBC747E.app I think the "eRUNTIME.cfg" file is the same as CODESYSControl.cfg I also dont know the purpose of the hexadecimal numbers etc. that is generated. When I tried to replicate what codesys was doing, I placed the same files in the same folder as when codesys generated the boot file. And also added the lines in the eRUNTIME.cfg file: [CmpApp] Application.1 = Application [SysFileMap] /home/codesys/PlcLogic/Application/Application.app The controller did not boot up with any program, so my method did not work at all. I guess these lines tells the controller to run an application and where to find it? Could any of you help me with the best way to get the compiled program to the controller without using codesys or wago-software?
Last updated: 2024-05-28
Post by aris on Modbus write via FB failure
CODESYS Forge
talk
(Post)
Hi all, I am using CoDeSys V3.5 and a soft controller Win V3x64. I am trying to read a modbus slave via Function Blocks and not via the channels of the hardware tree for the Slave. I created some requests of type ModbusRequest and I notice that I can read Input Registers and Coils but I can not write Holding Registers and Coils. I am using the library IoDrvModbusTCP 4.1.0.0. When i just use a single modbus request with FC06 (or FC16), there is no request sent to the slave and although the xExecute takes its true value from a pulse of 2 seconds duration, I take almost every 3 minutes an error "TCP_COMMUNICATION_ERROR - 16#A5 - TCP Port. error. Request was not sent". My code is ok because if i change the function code for reading registers, everything works fine. Did anyone have this issue in the past? Thank you in advance.
Last updated: 2025-11-06
Post by jonasz on Deploy LicenseServer for Linux SL
CODESYS Forge
talk
(Post)
Good morning, I'm digging into this topic because I'm curious about resolving my problem in a test environment. In my previous message, I asked about the CODESYS Safe Timeprovider SL package (4.18.0.0), which I saw in the illustration. I noticed that it runs as a service. I am asking about this because from the perspective of an "ordinary" user, this service provides easier access to the settings of the time provider's operating parameters. The basic time provider configuration is outlined at https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_virtual_safe_time_provider.html. Why my questions? They stem from my specific case, which is experiencing timeout issues. I know that my environment is currently only a test environment. I'm assuming a real-world scenario in which I won't be able to achieve a better result with my configuration, and I will ultimately need to increase the time provider's cycle time. By running the time provider service, I can easily influence the time provider's operation and thus eliminate the problem. I know, I know, safety systems are not life-enhancing extras.
Last updated: 2025-11-19
Post by suyash on Device User Logon
CODESYS Forge
talk
(Post)
Hello. Basic Info : I am using Codesys Control For Raspberry Pi SL. Version 4.4.0.0 Engineering version : CODESYS V3.5 SP19 Patch 1 (Its a old application) I am facing a difficulty with the "Device User Logon". The window (screenshot attached) pops up during login. When i enter the credentials (which i feel are correct), the windows pops up again no matter how many times I enter. To ascertain, I tried entering the incorrect credentials during which its clearly specifying that i have entered them incorrectly (which is why I am quite certain about the credentials being correct). I even tried going into Communication Settings > Device(drop down) > Change Runtime secuirity policy . However it again asks me for credentials which keep popping up again and again. I am thinking of upgrading the runtime to the latest version of 4.20 Will it cause any issues with the paid license? Please suggest me a solution. BR, Suyash
Last updated: 2026-05-13
Post by shamcke on Array with generic constant as persistent variable
CODESYS Forge
talk
(Post)
Hello, I have written a function block that uses a generic constant for the upper bound of an array. I wanted to have this array in the persistent memory area, thus I constructed my FB as follows: FUNCTION_BLOCK FbWithGenericArrayLength VAR_GENERIC CONSTANT uiArrayLength : UINT := 10; END_VAR VAR PERSISTENT arr : ARRAY[1..uiArrayLength] OF INT; END_VAR In my PLC_PRG I declare an instance of said FB PROGRAM PLC_PRG VAR myFb : FbWithGenericArrayLength<10>; END_VAR This compiles just fine. When I let CODESYS fill my persistent list, it adds duplicate entries {attribute 'qualified_only'} VAR_GLOBAL PERSISTENT RETAIN // Generated instance path of persistent variable PLC_PRG.myFb.arr: ARRAY [1..uiArrayLength] OF INT; // Generated instance path of persistent variable PLC_PRG.myFb.arr: ARRAY [1..uiArrayLength] OF INT; END_VAR so I manually delete the duplicate. When i now compile, I get errors ------ Build started: Application: Device.Sim.Device.Application ------- Typify code... [ERROR] Sandbox_FW31: PersistentVars [Device: PLC Logic: Application](Line 4): C0161: Border 'uiArrayLength' of array is no constant value [ERROR] Sandbox_FW31: PersistentVars [Device: PLC Logic: Application](Line 4): Type of mapped variable is not equal to original type Compile complete -- 2 errors, 0 warnings Build complete -- 2 errors, 0 warnings : No download possible Is is simply not possible to use a generic constant for the persistent array? Thanks in advance. Edit: It seems I can manually replace the uiArrayLength in the persisten list by the value 10 I used as the generic constant for this particular instance.
Last updated: 2026-05-29
Post by jami on Reading multiple lines from csv file
CODESYS Forge
talk
(Post)
Hello, i am trying to read multiple lines from csv file with caa file library and oscat. I have wrote 7 lines in the csv with separation '$R$L'. In my "extracting values" part I check line feeds and chars. After that I convert my buffer to string with oscat but I'm only able to read the first line from the csv. No matter if I even change start position where I start converting the buffer, I only get the first line. Here's my code for the reading and extracting value parts: 4: (*Reading the file*) fileread.hFile := filehandle; fileread.pBuffer := ADR(buffer); filesize1:=SIZEOF (buffer); fileread.szbuffer:=filesize1; fileread.udiTimeOut := 100000; fileread(xExecute := TRUE); IF fileRead.xDone THEN iFilesize:=TO_INT(fileread.szSize); writestate:=3; fileRead.xExecute := FALSE; END_IF 5: (*Extracting values*) //here i check the number of line feeds and chars. It works WHILE i < ifilesize DO c:=buffer[i]; IF c= 10 THEN IF lineindex<=99 THEN lineIndex := lineIndex + 1; END_IF ELSIF c <> 13 THEN IF charIndex <= 1000 THEN charIndex := charIndex + 1; END_IF END_IF i := i + 1; END_WHILE // Here i convert the buffer to string and transfer it to filelines:ARRAY[0..99] of string[254]. trig(CLK:=BUTTON); IF trig.Q THEN fileLines[i2]:=oscat_basic.BUFFER_TO_STRING(PT:=ADR(buffer), Size:=TO_UINT(fileread.szBuffer), start:=TO_UINT(bufferStart), stop:=TO_UINT(filesize1)); i2:=i2+1; bufferstart:=bufferstart+80; END_IF If anyone has idea how to read multiple lines, it would be nice. Even if you have example codes that work, that would help a lot.
Last updated: 2025-07-18
Post by cer-wa on Not able to connect multiple profinet encoder in codesys Linux ARM64
CODESYS Forge
talk
(Post)
Hello, currently im working with a RevPi connect 5 on a codesys project. Up until now I was having a blast because things were going really smooth but for like almost a day im kind of stuck on the integration of multiple profinet sensors into my project. This is kind of a bummer because that should be an easy thing to do. What I tried so far was to create and additional ethernet adapter where I then tried to connect my devices. in the beginning I tried to connect the devices directly which was not working because I could assign the IP-adress only to the ethernet adapter and not to the devices but the device was found in the device repository (this gets important in the second part) So what I tried next was to setup a PN-Controller and connect my devices subsequently to the Controller. Sadly now the devices wont show up in the device repository anymore. To me its not clear why this is happening. And the worst thing is: I went ahead and setup a device completely like I would want to have it in the project and when I then click on scan devices I can even find the device. But it can not be added to project for whatever reason eventhough im 100% certain that the gsdml file is the correct one. Can anyone help me with this. Like I said this seems like an easy thing to do and its taking me way longer than expected already. The only thing that came to my mind why this might not work is because I have codesys license which only allows one profinet instance. Could that be the case? The error message seems then pretty unfit but ok. I will be grateful for every advice. Thanks in advance! Best regards!
Last updated: 2025-09-25
Post by timvh on STRING conversions to DWORD
CODESYS Forge
talk
(Post)
I guess that the printer expects to receive an array of byte values. So where it is described that it expects to receive: Hercules String : 1B4F513030311B7532626C61636B04 it actually expects to receive an array of bytes with the values 1B,4F,51,30,30, etc. So what you can do is create an array of bytes and assign the byte value to each item in the array: VAR abyToSend : ARRAY[0..99] OF BYTE; END_VAR abyToSend[0] := 16#1B; // ASCII Escape character, hexadecimal representation uses 16# as prefix abyToSend[1] := 16#4F; // ASCII 'O' abyToSend[2] := 16#51; // ASCII 'Q' abyToSend[3] := 16#30; // ASCII '0' // you can do the rest yourself // maybe could be created a lot smarter, but gives you an indication how to handle this. Then with the serial communication (or TCP/IP?) you can send a message with the reference to the array (abyToSend) and the number of bytes to send (15 bytes for the string you gave as example).
Last updated: 2025-02-02
Post by edson-bueno on SysProcess Execute Command unable to run commands with special characters
CODESYS Forge
talk
(Post)
Hi, I found the same issue, and I fixed with this steps: 1st go to codesys .cfg file. sudo nano CODESYSControl.cfg Then insert this: [SysProcess] BasePriority=Realtime Command=AllowAll Now we need to grant codesys root rights on Linux. Step 1: Create or edit the systemd override configuration: sudo systemctl edit codesyscontrol In the editor that opens, insert: [Service] User=root Save and exit: Press Ctrl+O to save Press Ctrl+X to exit Step 2: Reload systemd and reboot To apply the override: sudo systemctl daemon-reexec sudo systemctl daemon-reload sudo reboot Step 3: Confirm CODESYS is running as root After reboot, open the terminal and run: ps aux | grep codesyscontrol You should see something like: root 1234 ... /opt/codesys/bin/codesyscontrol.bin ... If instead it shows admin or another user, the override was not applied correctly. Step 4: (Optional) Confirm from within CODESYS In your CODESYS project, insert this test code to run the Linux command whoami: Make sure the lib SysProcessImplementation, SysTypes, and CmpErrors is on the project. VAR sCommand : STRING := '/usr/bin/whoami'; sOutput : STRING(255); refCommand : REFERENCE TO STRING; refOutput : REFERENCE TO STRING; resultCmd : UDINT; END_VAR refCommand REF= sCommand; refOutput REF= sOutput; SysProcessExecuteCommand2( pszCommand := refCommand, pszStdOut := refOutput, udiStdOutLen := SIZEOF(sOutput), pResult := ADR(resultCmd) ); Notes & Warnings This method gives full system access to the CODESYS runtime — do not expose this system to the public network without protection. Do not use sudo in commands inside CODESYS when the runtime is already running as root. @tomas111, in case you want to read the temperatur, use this command: sCommand:STRING:='/usr/bin/vcgencmd measure_temp';
Last updated: 2025-05-20
Post by jackbrady on Function Blocks and arrays of function blocks
CODESYS Forge
talk
(Post)
Hello, I am new to Codesys and PLC programming in general (please go easy ha!) I'm not looking for code to be written for me just some help and pointing in the right direction. I am writing some code to send commands to a relay based on input values (to put it simply). Quite basic stuff. I have wrote a function block that takes a global variable (Open_command:BOOL) and outputs to another global variable (Opened : BOOL). The function block is simulating a device so I'll eventually get the globals from that. I now need to create multiple versions of this function block/ device (lets say 100) but I need each iteration of that function block to reference it's own relevant global variable. I think that the best way of doing this would be to use arrays, although I could be wrong. I am aware that for up to 100 instances I could very well manually assign everything but that seems rather time consuming and I want a fancier way of doing it. Here is a very basic example of what I am looking to do, please note I have not written this in proper code it's just to show what I mean. Global Variables V[0-100] int Open_command [0-100] Bool Opened [0-100] Bool Function Block var input x : BOOL Var output y : BOOL if x then y = TRUE ELSE y = FALSE The input to my function block will be Open_command, output will be Opened Example code. If V[x] > 10 then Open_command [x] = TRUE ELSE Open_command [x] = FALSE (So when V1 goes above 10 I need Open_command1 = TRUE therefore initiating FB1 output. V2 > 10, open_command2 = True > FB2 output V3 > 10, open_command3 = True > FB3 output ... ... ) What I can't seem to figure out is how to tie all this together, I have read through the codesys documentation and if anything it has confused me more! ha. Apologies for the poorly written post but hopefully you understand what I am trying to get at. Thanks, Jack
Last updated: 2024-02-14
Post by matthew on Persistence Manager Backup
CODESYS Forge
talk
(Post)
Hi, Is there a process to restore Persistence Manager files? I have backups of persistence variables used in a machine that is currently operating and tuned and all set points adjusted. There are about 500 persistence variables, they are building another identical machine. I would like to use Persistence Manager files from the first machine in the second also. I have tried copying the files and replacing them on the new RPI but then the Persistence Manager gets errors and then they are all reset to 0 etc I have tried adjusting the times to match. Instead of replacing whole file, I tried just changing the contents inside the file, but still does not work. I may be missing something here, but surely there must be a way to load a backup. Thanks!
Last updated: 2023-10-18
Post by felipemsgarcia on Edge Gateway online, but PLC is not online
CODESYS Forge
talk
(Post)
Hello, Up until yesterday (2023/11/20) I was able to connect to the PLC remotely with no issues through Edge Gateway. However, today I can see the Edge Gateway online but I can find the PLC even if I do a network scan. Following the same path as janber0206 @ https://forge.codesys.com/forge/talk/automation_server/thread/e78b11d7e9/, I looked into certificates and found that one of the Trusted publisher certificates has expired earlier today (2023/11/21). Please see image. Questions are: Does it affect the connection to the PLC through Edge Gateway? How do I fix it? Thank you very much in advance!
Last updated: 2023-11-21
Post by tomgr on Codesys 3.5.19 Control Win x64 - network adapter for EtherCAT master not working
CODESYS Forge
talk
(Post)
Hi guys I am trying to run on my laptop Codesys 3.5.19 Control Win x64 where I created a EtherCAT master. I have defined the controler, specified network adapter (my docking station) and everything worked as expected. Later I needed to test it on site (without docking station) so I changed the network adapter by EC master to my laptop network card. After that it shows "Network adapter opened" but no device can be found by scanning and in LOG is saying "SysEthernet: packet could not be sent, error code: -1". Same error with USB network card, but if I switch back to docking station, all is working again... Any idea what I'm doing wrong?
Last updated: 2023-11-22
Post by seppi on Establishing communication between a Raspberry Pi 4 and an Arduino UNO R3 using I²C.
CODESYS Forge
talk
(Post)
Hello everyone, I want to establish communication between my Arduino and my Raspberry Pi via I²C, but I have no idea how to make it work. However, it should work because there are many examples available, although none of them were programmed using Codesys, but rather using Python. My Raspberry Pi will be the master and is supposed to exchange measurement data such as speed and battery capacity with the slave (Arduino). I would be very grateful if someone could help me with my problem. Here is another link that could be helpful. However, I can't find the mentioned libraries
Last updated: 2023-12-03
Post by hazarath on How extract JSONElement containing Array data
CODESYS Forge
talk
(Post)
I want to extract each element of an Array. Can someone help me with this. When I use JSONElementToString (part of JSON Utilities SL), I am seeing output as "ARRAY" instead of actual data. Here is the JSON content that I want to read : { "value1Unit": { "units": "M" }, "data": { "stepSize": 300.23, "points": [6,8] } } I would like to read each item of the element "points" i.e. 6 and 8. Here is the code I used, // Reading the content as JSON reader ( xExecute := execute , pwData := ADR ( converted_value ), jsonData := jsonDataStorage ); // Get the JSON Element jsonDataStorage.FindFirstValueByKey( wsKey := fidKeyVar, diStartIndex := searchElem, jsonElement => jsonElement ); JSON.JSONElementToString ( element := jsonElement , wsResult := valueWstring ); The content of the output of valueWstring is shown as "ARRAY" instead of the array items i.e. 6 and 8 Please can someone help me.
Last updated: 2024-07-30
Post by micik on Ethercat project loaded to Win V3 x64 bit SoftPLC
CODESYS Forge
talk
(Post)
Hello, I have almost exactly problem already discussed here in this old thread: https://forge.codesys.com/forge/talk/Engineering/thread/03af9426eb/ However, this is quite old and I assume not completely relevant. In my case, I use v3.5.20 on windows 11, so Winpcap is no longer supported on newer OS. Also, this hint about adding entry to the .cfg file under ProgramFiles(x86) is also not relevant anymore. I guess, I need to add entry SysEthernet to this .cfg file: C:\ProgramData\CODESYS\CODESYSControlWinV3x64...\CODESYSControl.cfg like this one: [ComponentManager] Component.1=CmpTargetVisuStub Component.2=CmpWebServer Component.3=CmpWebServerHandlerV3 Component.4=SysCpuMultiCore Component.5=SysReadWriteLock Component.6=SysCpuBreakpoints Component.7=SysPipeWindows Component.8=SysEthernet But I'm not sure about Npcap vs WinpCap. Please, if applicable, update these instructions. I hope it is still possible to
Last updated: 2024-08-22
Post by micik on Reverse bytes in an array
CODESYS Forge
talk
(Post)
Hello, I'm getting the data in Codesys that is an array of 8 bytes. From this array, I need to foram LREAL number, however, because of different endiannes I need to reverse bytes in this array and then copy to a LREAL variable. For this I'm using a loop and it works OK. I wonder if there is a built in function to do this. I have found CAA Memory library but it has functions like reverse bytes in DWORD. But it seems it doesn't have what I need. https://content.helpme-codesys.com/en/libs/CAA%20Memory/Current/CAA_Memory/Reverse-Bit-Swap-ByteWord-order/ReverseBYTEsInDWORD.html What I need is a function to reverse bytes in an 8 byte array, or something similar.
Last updated: 2024-08-22
Post by micik on Reverse bytes in an array
CODESYS Forge
talk
(Post)
Hello, I'm getting the data in Codesys that is an array of 8 bytes. From this array, I need to foram LREAL number, however, because of different endiannes I need to reverse bytes in this array and then copy to a LREAL variable. For this I'm using a loop and it works OK. I wonder if there is a built in function to do this. I have found CAA Memory library but it has functions like reverse bytes in DWORD. But it seems it doesn't have what I need. https://content.helpme-codesys.com/en/libs/CAA%20Memory/Current/CAA_Memory/Reverse-Bit-Swap-ByteWord-order/ReverseBYTEsInDWORD.html What I need is a function to reverse bytes in an 8 byte array, or something similar.
Last updated: 2024-08-22
Post by gilbertamine on Comparing Arrays of structure
CODESYS Forge
talk
(Post)
Hi Everybody, I'm looking for a simple way of comparing two array of a structure. My structure is define like this : TYPE Positions_T : STRUCT PosX: DINT; PosY: DINT; PosZ: DINT; END_STRUCT END_TYPE I have multiples Var : ARRAY [0..220] OF Positions_T, that I need to compare quickly. I don't really want to do a Loop that goes by every 220 points and compare each one of them so I was wondering if there is another way. I came accross the MEM.Compare function, but it require to know the size in Bytes of the memory, and I don't know how to do that... Has anybody an idea on how to do the comparing easily ? Thanks in advance
Last updated: 2024-08-22