Post by alexgooi on Disable OPC-UA server
CODESYS Forge
talk
(Post)
Dear Forum, I recently updated to the newest Codesys IDE (3.5 SP19 patch 5) The program wouldn't download cause of the amount of OPC-UA server tags (see picture) I'm not planning on using the OPC-UA server and therefore I unchecked the "Support OPC-UA features" checkbox in the symbol configuration. But this didn’t solve the issue of the OPC-UA server exceeding its license. How can I disable the OPC-UA server while still maintaining the symbol configuration. Thank you in advance Alex
Last updated: 2024-03-01
Post by ph0010421 on TCP/IP client
CODESYS Forge
talk
(Post)
Hello Use 'Import PLCOpenXML' to bring this into your project.
Last updated: 2023-12-20
Post by macman on Codesys 3.5 OPC UA Client to Kepware OPC UA Server
CODESYS Forge
talk
(Post)
Hi, I have problem with connecting Wago PLC WAGO 750-8212/0025-0002 configured as OPC UA client to Kepware OPC UA Server. I am using Codesys 3.5.19.70. What I did so far. To the Codesys project I added object Data Source Manager and configured connection OPC UA like below: pic 1 Then I can browse the OPC server tags in “Variables” tab after prior trust on the server side of the client certificate created in the “Communication” tab: pic 2 Additionally second certificate has been created in Codesys for runtime process in “Security screen” as well as the server certificate was approved here: pic 3 But when I compiled project, downloaded it to PLC and go to RUN I can’t read selected in “Variables” tab, OPC Server tags. I am getting such error (ID: 7001): pic 4 All two PLC certificates has been trusted in OPC server (Kepware) side: pic 5 and Kepware server configuration look like this: pic 6 I can easily connect using third party OPC UA client UaExpert to Kepware server without problem. In attachment I added also log from Kepware OPC UA server. pic # - this specifies the number of a concrete graphic from one of the collective in attachment
Last updated: 2025-04-02
Post by winki on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
For small project, I would like to use my industrial computer as a PLC + Industrial Computer. Like that I can save the cost of one PLC. That why I am using Codesys on Linux. With the nic it is not working. I already set the IP adress with /etc/network/interfaces. Can it comes from there ? looking to "Control Linux SL" docuemntation it should work with rtu.
Last updated: 2024-10-23
Post by stefhanyestuda on codesys 2.3
CODESYS Forge
talk
(Post)
estou com um PLC festo CECX-X-C1, gostaria de comunicá-lo com a ihm weintek, o clp possui o módulo ethernet e no maual fala que por conta disso deve comunicar em tcp ip, modbus e etc, mas já tentei seguir o manual e nada. Na configuração do hardware ele não me aparece o módulo de ethernet pra configurar e não consigo encontrar o pacote para codesys 2.3 contendo esse módulo, alguém poderia me ajudar?
Last updated: 2025-07-04
Post by goki on WAGO RS485 (753-652) on a 750-362
CODESYS Forge
talk
(Post)
hi guys Maybe someone can help me in this case. Im working with codesys 3.5 with an PFC200 (750-8212) with a Modbus TCP conection to the 750-362. On the 750-362 i have a 4DO, 8DI and a RS485 interface card. the 4DO and 8DI cards a working fine but im strugling with the rs485 card. Does someone have a example for this?
Last updated: 2024-02-08
Post by rh-pk on v3.5 SP19 - Modbus TCP Devices - Channel Limit?
CODESYS Forge
talk
(Post)
Hello Vincent, I don't have 75 channels but it works for me as described above without any problems. There is also a parameter MAX_MODBUS_CHANNELS in the library parameters for the IoDrvModbusTCP module. The default value there is 100. Perhaps you are reaching the limit there? The value can be adjusted accordingly. I assume that this value is not accepted in the input dialogue and therefore the 'fixed' limit value 10 is used.
Last updated: 2024-04-10
Post by garrian on How to write multiple coils (Modbus FC15)
CODESYS Forge
talk
(Post)
Hi there! I'm testing out modbus TCP/IP for my home brewery, using Wago PFC200 as both slave and master. I'm using Wago library WagoAppPlcModbus. Holding registers, input registers' and discrete inputs works fine, but when trying to write multiple coils, it doesn't work. Any idea what I'm doing wrong here? Attached is a screenshot of my code. I tried both using bit mapping and without. If I change to FC05, and write only 1 coil at the time, it works fine. But I want to write all at the same time.. Any help is very appreciated :)
Last updated: 2024-11-16
Post by veneto on OPC UA Client
CODESYS Forge
talk
(Post)
Ciao damian177, provo a chiederti un'informazione. Sul mio progetto Codesys(ver.3.5 SP17) non è visibile l'oggetto "Data Source Manager". Il PC con il progetto Codesys(client) è collegato via rete TCP ad un PLC Siemens1200(server). Sul PC con Codesys ho installato UAexpert(client) e riesco a vedere le variabili del PLC1200. Riesci ad aiutarmi a capire come mai non è visibile l'oggetto "Data Source Manager"? Molte grazie
Last updated: 2024-09-06
Post by ph0010421 on Task time too fast?
CODESYS Forge
talk
(Post)
Hello I've made an FB which is a TCP server. It uses the excellent CAA NetServices library. If I have the FB in a task <4ms, then the RT crashes immediately at boot up. If the task >=4ms, it starts and runs perfectly. This is even if the block is not doing anything; just instantiated. Am I missing something silly? Why would a low task time cause this? 4ms is perfectly adequate, but I'm just interested why... thanks PH
Last updated: 2024-11-27
Post by rmaas on TCP Server
CODESYS Forge
talk
(Post)
Hi George, I do not know what the problem is with the syssocket implementation, but when i read the forums it seems the Net Base Services library is the recommended way to go. There is another more extensive example here: https://forge.codesys.com/prj/codesys-example/plc-chat-nbs/home/Home/ I have just tested this example and it works very well, also with closing and opening the connection from hercules... good luck!
Last updated: 2025-02-20
Post by matt-purcell on Which Lib to use, connect to a socket with URL instead of IP address
CODESYS Forge
talk
(Post)
Hello, I have a new project and I need to connect to a TCP socket using the URL instead of an explicit IP address, myendpoint@mydomain.com Which library is best suited for this? This is for a new enterprise project, the endpoint is a server in a datacenter running some real time application. We have big IP, it will automatically reassign the IP address to the backup server if a crash occurs so an explicit IP won't work for me. I've done this in RS logix, working now to migrate that code over to codesys. Thanks in advance!
Last updated: 2024-06-17
Post by atcprojectteam on Modbus Function Code 15, writing multiple coils
CODESYS Forge
talk
(Post)
Hi all, I am using an RSTI-EP I/O card along with the EPXMBE101 Modbus/TCP network adapter. I have a Control Standard L license. I successfully connected to the I/O card via Modbus and can read inputs without any issues. However, when I try to write to the digital output modules using function code 15, I am unable to make any changes. Here’s what I have done so far: I created a small project using Structured Text. I set up Modbus channels (as shown in the attached image) and mapped the pins. When I use cyclic mode, the connection results in an error. However, when I use the rising edge, the connection works, but I don’t see any changes on the I/O card. For the output module, I assigned one bit to high. After that, I ran CODESYS Control Win V3. (Should I be running the PLC as well?) I built the program, but I am not receiving any response from the I/O card. Could you please advise on what might be causing this issue?
Last updated: 2025-02-26
Post by atcprojectteam on Modbus Function Code 15, writing multiple coils
CODESYS Forge
talk
(Post)
Hi all, I am using an RSTI-EP I/O card along with the EPXMBE101 Modbus/TCP network adapter. I have a Control Standard L license. I successfully connected to the I/O card via Modbus and can read inputs without any issues. However, when I try to write to the digital output modules using function code 15, I am unable to make any changes. Here’s what I have done so far: I created a small project using Structured Text. I set up Modbus channels (as shown in the attached image) and mapped the pins. When I use cyclic mode, the connection results in an error. However, when I use the rising edge, the connection works, but I don’t see any changes on the I/O card. For the output module, I assigned one bit to high. After that, I ran CODESYS Control Win V3. (Should I be running the PLC as well?) I built the program, but I am not receiving any response from the I/O card. Could you please advise on what might be causing this issue?
Last updated: 2025-02-26
Post by forest on SM Drive license error
CODESYS Forge
talk
(Post)
Hi, when it comes about license, I used INVTmatic Studio, which uses Codesys, for programming INVT plc. I bought Codesys Modbus license, it was not expensive, and then realised that INVT didn't have License Manager option (greyed out in program) which is needed for using of Codesys License. I contacted support from INVT, but developers told me that option is still not available. So depending on environment for programming Codesys, you can or not use Modbus license. Good thing about this version of Modbus TCP it works both direction. I could send commands and receive feedbacks from drive. But communication stops after 30 mins. So I used simple version of ethernet modbus which is somewhere in INVT or Condesys library (I can check tomorrow) which works only one way. I could send cmd to drive, and control it, but didn't have any feedback, like some readings back in PLC. which is bad, but at least I could start it and it didn't fail after 30 mins.
Last updated: 2024-01-10
Post by bjarne-pagaard on OPC UA Server Status on Win RTE
CODESYS Forge
talk
(Post)
Hi there, An "OPC Expert" client software is connecting to a Codesys Control RTE (x64) OPC UA Server. It reads only about 25 variables every 5 minutes. The OPC UA Server seems to shut down on the Codesys runtime. Is there any way to get information about the Codesys OPC UA Server status? Restart it? There is nothing in the PLC Logs after the OPC UA Server has started. It works for a while, then it doesn't. Any ideas? Any way of getting more info out of the Codesys OPC UA Server? -Bjarne
Last updated: 2024-10-21
Post by schorge on Modbus RTU Slave
CODESYS Forge
talk
(Post)
Ich wĂĽrde gerne bestimmt Modbus RTU Slave Adressen auslesen, leider bekomme ich keine Werte vom Bus. Verbindung erfolgt ĂĽber einen Raspberry mit Modbus RS485 Adapter, welcher erfolgreich verbunden ist. Mit einem IOBroker kann ich die Daten erfolgreich auslesen. In der Modbus_COM_Port => Modbus_Serial_Device habe ich Input Register 4000 %QW und Startadressen auf Input Register 3000, als Variable ein Array[0..2999] of Word, kann aber keine Werte auslesen.
Last updated: 2023-12-06
Post by dengsberg on Disable Communications to 'Modbus_Server_COM_Port' from the logic
CODESYS Forge
talk
(Post)
I have a serial Modbus RTU communicating to the Slave device. But when the control system is not in Run there is no power applied to one of the Modbus Devices. Can I enable / disable the communications to that Modbus Slave in the code based on my running mode, so I don't get all the errors?
Last updated: 2024-08-29
Post by hassaank on CODESYS V3+ WAGO PFC200+ MODBUS RTU
CODESYS Forge
talk
(Post)
Hi everyone, I’m new to CODESYS and Wago devices, and I’m trying to set up Modbus RTU communication. I have a Wago PFC200 (8110) and a 750-653 RS485 module, and I want to read data from an energy meter using Modbus RTU. Thanks in advance for your help!
Last updated: 2025-03-17
Post by hinet on 22kW Wallbox mit Modbus
CODESYS Forge
talk
(Post)
Hallo an alle, ich schaue mir gerade ein paar 22kW Wallboxen an: https://shop.einfacheauto.de/collections/22-kw-wallboxen Mir wäre vor allem wichtig, dass die Kommunikation per Modbus gut funktioniert. Es werden zwar ein paar Wallboxen gelistet, die Modbus ermöglichen, trotzdem wollte ich euch nach Erfahrungen fragen, welche Modelle in der Hinsicht besonders problemfrei funktionieren.
Last updated: 2 hours ago
Post by spiritcore on Server not adding PLC
CODESYS Forge
talk
(Post)
I added new Gateway and I can see it connected. When I scan the server for PLC, it finds the PLC but when I click the Add To Server button, it shows "PLC was added." in the status. But I can't find the PLC in the list. I tried removing the gateway and re-configure everything again but it didn't solve. Any ideas?
Last updated: 2025-02-17
Post by timvh on Accessing ModbusTCP addresses from python
CODESYS Forge
talk
(Post)
https://en.wikipedia.org/wiki/Modbus
Last updated: 2023-09-20
Post by ahuckphin on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
duplicate
Last updated: 2024-07-11
Post by dohy on Modbus RTU Response CRC fail
CODESYS Forge
talk
(Post)
Did you resolve it?
Last updated: 2024-09-19
Post by dkugler on STRING size and reading STRING with Modbus
CODESYS Forge
talk
(Post)
Last updated: 2025-01-31