Post by pernockham on Pointer/reference to Codesys trend recording object?
CODESYS Forge
talk
(Post)
I have a Hmi that acts as an interface for many (mostly identical) units. This is managed by a sort of "mux" where you select which unit that should be presented on the HMI. Backbone is solved by a HMI-gvl defined as reference/pointer to "unit-data", which then can be set to the individual units. While this works for most data I still have not sorted how to solve this for the trend recordings. One solution would be to have already "mux:ed" data values as source for the/one trend. However then the trend would contain data from different units/sources which could/will cause confusion. If its possible to "clear" this can be mitigated. Possibly let the trend have its own "mux-selector" (ie, the hmi are focusing on unit#3 however trend data is locked on unit#5), that could also work.. Or, let each unit have its own trend recording, which is focused if the unit is "selected". Can I reach the trend recording objects programmatically (those defined in the device tree)? Ie, can I use a "reference/pointer to these trend recording objects"? There is a field "data source" in the trend properties dialog which seems to resemble what Im looking for? But Im not sure if I can use it in some way, I cannot change anything in this field it only says <local application="">. </local>
Last updated: 2025-09-16
Post by william-blandon on RecipeManCommands.ReloadRecipes
CODESYS Forge
talk
(Post)
Hi Dave. Thanks for your answer. I still struggling with this. I have done everything according with the Codesys help even I have looked in detail at the example. I have double checked the recipe manager configuration and the use of all the methods. There are two methods that do not work as expected. I'm using Codesys 3.5.19.20 and recipe management 4.4.0.0 .CreateRecipe just create a recipe in the recipe definition but do not create the file. This have a walk around just giving a .ReadAndSaveRecipe afterwards. .ReloadRecipes do nothing but do not generate any error as well. After calling it I call the .GetRecipeCount and the number is always 0. When I create a new recipe (using the function block methods) then the number changes. Looks like this method is looking to the wrong directory finding nothing. I don't know if there is a missing configuration in the CODESYSControl.cfg file. I'm thinking in a walk around for this but I need to create a strings array with the recipe names as retentive and making all the management when deleting and adding recipes. Have had some one the same problem?
Last updated: 2024-05-23
Post by julianramirez on ModbusFB write update
CODESYS Forge
talk
(Post)
Hello everyone, I am testing the ModbusFB library tcp server and so far I am able to create holding registers successfully, however, I am trying to identify after each write which registers got updated (i.e. function code, write value). I can even see the var udiNumWriteRequests, which increases with every write. I noticed that there is logging with the LogStatusInfo method. After I call it I am able to read in the console stuff that I want. Nevertheless, this is only available at the logs and is not easy to decode because it consists on several messages, I would like to know if there is a way for me to retrieve this information from the function itself with pointers or if there is any way to copy the logs messages (assuming that I can filter them with the LoggingOptions to only show what I need) inside the runtime code and not in the console. Thanks for your help :)
Last updated: 2024-09-16
Post by clarenced on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I am looking for an example of how to run 2 applications on 1 device that would have global variables shared between the two apps. In this case what I am trying to do is to have the main program logic run as one application and then have the visualization run as a second application. I find this https://us.store.codesys.com/media/n98_media_assets/files/000013-F/0/Multiple%20Applications_en.pdf, that talks about exactly what I want to do, but I can't find the download. The main reason I want to do this is for download speed. Right now it takes at least a minute to download our application to the PLC. A simple program downloads to the PLC in a very short time, but add visualization and the download time gets much longer. If I could download the program separately from the visualization I think that a simple program change would take very little time to download. I have tried create a GVL in the POUs view. This partly works in that both applications can see the GVL, but they each create their own instance of it and the variables are not shared between the two apps. There are ideas of using OPCUA but this raises problems with licensing and having to move any variable that needs to be shared into the Symbol Configuration. This adds a lot of management to keep this up to date. Any ideas would be appreciated thanks.
Last updated: 2025-02-20
Post by risele on dynamic modbus devices
CODESYS Forge
talk
(Post)
Have the same issue: I'm making a test setup for modbus devices testing and calibration. One is run for every possible address, and it starts with minimal request: if the device is found, it continue to work with it, otherwise it's set to Disabled temporary. Those state machines are running under FOR cycle, and disabled are just skipped. Every instance have its own timer for not running too frequently and a start delay, so the actual requests are separate in time. I also check not for a single error, but have some timer to allow one-two timeouts. The small program disables and re-enables devices temporary (manually, since i could not iterate over MB devices). VAR Reset:ARRAY[1..GVL_MB.MD_COUNT] OF R_TRIG; i:INT; END_VAR {IF hasconstantvalue(GVL_MB.MD_COUNT, 1, >= )} i:=1; MD_1.Enable:=GVL_MB.MDPortsEnable[i]; Reset[i](CLK:=GVL_MB.MDPortsEnable[i]); MD_1.xReset:=Reset[i].Q; {END_IF} {IF hasconstantvalue(GVL_MB.MD_COUNT, 2, >= )} i:=2; MD_2.Enable:=GVL_MB.MDPortsEnable[i]; Reset[i](CLK:=GVL_MB.MDPortsEnable[i]); MD_2.xReset:=Reset[i].Q; {END_IF} There is also program to re-enable devices periodically. METHOD ScanBus VAR_INPUT END_VAR VAR j:INT; (*block auto scanning if calibration is running for any device since it's data-reach process that should not be interrupted with modbus timeouts *) CalibrationBusy:BOOL:=FALSE; END_VAR CalibrationBusy:=FALSE; FOR j:=1 TO GVL_MB.MD_COUNT DO CalibrationBusy:=CalibrationBusy OR MD_Calibrate.AutoTesters[j].xBusy; END_FOR; IF CalibrationBusy THEN RETURN; END_IF tBusScanSchedule(IN:=(NOT tBusScanSchedule.Q), PT:=tBusScanPeriod); IF (NOT tBusScanDelayer.Q) AND (tBusScanSchedule.Q OR (NOT xFirstScanPerforemed)) THEN xBusScanBusy:=TRUE; MissingCounter:=0; xFirstScanPerforemed:=TRUE; FOR j:=1 TO GVL_MB.MD_COUNT DO (* MD_Calibrate is main calibration program. Identifiers - is array of State machines mentioned above Phase_Faulted is a state of Identifiers where I'm sure device is missing on the bus *) IF MD_Calibrate.Identifiers[j].state=eStateMDIdentifier.Phase_Faulted THEN MD_Calibrate.Identifiers[j].Rescan(); MissingCounter:=MissingCounter+1; END_IF END_FOR END_IF tBusScanPauser(IN:=tBusScanDelayer.Q AND (MissingCounter>0),PT:=tBusScanDelay*MissingCounter); xBusScanBusy:=tBusScanPauser.Q; xFirstScanPerforemed:=xFirstScanPerforemed OR tBusScanPauser.ET>=tBusScanPauser.PT; Also the GUI have buttons for each address possible that re-enables the device if required.
Last updated: 2026-02-13
Post by trycyclepower on Only single ehternet ip drive is communicating
CODESYS Forge
talk
(Post)
Hi all, I have two ethernet IP drives not communicating together. If I disable one, then other one starts working. ENIPScnannerIOTak cycle is setup as 20ms. Also, PLC updating variables setting is on.
Last updated: 2024-03-08
Post by comingback4u on Memory Address Overlap
CODESYS Forge
talk
(Post)
Hello, We use a controller that comes with a bunch of predefined faults. These faults are considered active and historic. They are a 32 byte array but only take up 26 bytes of data. Because of this the historic faults start at address 26 instead of 31. Active faults variable take up address location 0 to 31. Historic faults variable take up address location 26 to 57. Because of this overlap I get an error that these overlap and it wont allow me to download to my controller. This isn't an issue in 3.5.5.4 but becomes an issue in newer version. Is there a way to turn this off? If I change the address location, the historic faults then become broken without doing some manipulation in the code. The software will build just fine. Thank you for your time.
Last updated: 2024-03-07
Post by spice on WebVisu Recipe Save/Load
CODESYS Forge
talk
(Post)
I'm currently reworking the controls on a cnc press brake and wanted to load various recipes as programs to run. I'm using a 2d array of REALs to store the X and Y coordinates as well as some other program parameters in a recipe. I'd like to store all of the recipes on a computer used as the HMI that way the text files can be edited and uploaded offline. I'm using Automation Directs P2CDS-622 Can this be done through webvisu? If not would a license for Codesys HMI SL on the computer allow me to accomplish this? I've attached the Project File Thanks, Spice
Last updated: 2024-05-31
Post by mandeepahujaifm on Ethernet/IP 4.6.0 causing exceptions?
CODESYS Forge
talk
(Post)
I have experienced the same with one of our customers after updating EIP Scanner to 4.6.0.0 and really baffled by it. The core dump simply shows error with ENIPScanner I/O task and on analyzing it says no source code available for 4.6.0.0. Contemplating to go back to 4.5.1 but 4.6.0.0 has some really nice fixes. I guess it don't matter if it crashes anways. Please keep us posted if you find anything.
Last updated: 2024-07-11
Post by dogulas on Removing a symbol from the IEC Symbols Editor grid
CODESYS Forge
talk
(Post)
In the CODESYS IDE I have several symbols defined and I have IEC Symbol Publishing installed. On the IEC Symbol Publishing window and under the IEC Symbols Editor tab, I have dragged symbols from the tree on the left to the grid on the right. All this works fine. Now I want to remove one of the symbols from the grid on the right and I cannot see any way to do this. How can I remove a symbol from the grid on the right once I've added it?
Last updated: 2025-02-07
Post by timvh on I want to show the current recipe name in the visualization screen
CODESYS Forge
talk
(Post)
Maybe the easiest solution for you is to add one STRING variable to your recipe and enter the name of the recipe in variable value. This is little bit double the work (naming the recipe and entering the value of the STRING variable), but in that case you always have the current value of the variable which you can read from the application and show in the visualization.
Last updated: 2025-09-04
Post by ofey on two different OPC clients with different privileges
CODESYS Forge
talk
(Post)
Hi! I have usually only connected one OPC client (our system) to an OPC server created in the codesys environment on a PLC. This OPC client has a lot of write privileges. A customer also want OPC access, but I want to restrict his access to only read certain values. Do you know if this is possible inside the single codesys runtime running on a controller?
Last updated: 2024-02-01
Post by jinlee on Multiple WebVisu
CODESYS Forge
talk
(Post)
Hi, thank you for replying. Basically, I have a main visu with frame selection. So, under some condition the frame will switch to a specific frame. It used to be controlled by variable using "Switch frame variable". However, I realise it will change all the HMI screen at one time. So I removed the variable, and still looking for a solution to do that. Do you have any idea?
Last updated: 2024-02-06
Post by ndzied2 on Rounding error in simple addition
CODESYS Forge
talk
(Post)
This is a consequence of how computers store floating point numbers. 0.1 cannot be exactly represented in a computer. This is not a CoDeSys thing. Here is a link to a converter to show you the exact value that is represented when you use a REAL data type (which is a 32 bit float). https://baseconvert.com/ieee-754-floating-point If you really need to keep track of 0.1 increments. use INT OR DINT and then add 1 each time and assume that there is one decimal place.
Last updated: 2024-05-24
Post by jonasz on Deploy LicenseServer for Linux SL
CODESYS Forge
talk
(Post)
Hello, I'm asking for help with installing the license server for Linux SL 4.18.0.0. When I try to install it, I get a message that the WIBUCodeMeter package is missing. I checked the package manager tab to see if the package is installed, and it is - Codemeter 8.40.7120.501. I've checked the CodeMeter Runtime on the target machine, and everything seems to be working fine. One thing caught my eye: the Device Architecture tab says "None" Please help me solve this problem.
Last updated: 2025-11-14
Post by seler on Custom button with output status
CODESYS Forge
talk
(Post)
Just to clarify. Output for lamp will have two inputs: from plc IN (wall switch) and from visu button. Until now I had separate object for visu button and separate for visu lamp. Now I want it to be one object, bulb icone which will change color on lamp status and yet by touching it will change visu button state. Tried "Switch Image" object but there is no way to assign switch var.
Last updated: 2025-11-19
Post by reinier-geers on draw 1000 nails the easy way
CODESYS Forge
talk
(Post)
Because codesys dont has a draw command like Circle in Qbasic ( 20 years ago ) i want to draw 1000 nails, and then move them in the screen when they needed. I dont know if codesys can handle this. But is ther an easy way to draw 1000 nails with every single one has a pointer for movement, color and invisable. Of is there a linux command to draw a circle so i can do it with a process command
Last updated: 2026-05-06
Post by bertrand-major on Cancelling a selection from a "combobox array" in Visu
CODESYS Forge
talk
(Post)
Hi Joanm, Did you get an answer from anybody in anather section ?
Last updated: 2024-07-17
Post by pilouuu on problem OPC UA array
CODESYS Forge
talk
(Post)
Hello, why can't I read the arrays on my PLC's UA OPC server with codesys, even though they are accessible from UA Expert?
Last updated: 2025-02-26
Post by pilouuu on problem OPC UA array
CODESYS Forge
talk
(Post)
Hello, why can't I read the arrays on my PLC's UA OPC server with codesys, even though they are accessible from UA Expert?
Last updated: 2025-02-26
Post by wollvieh on Array of UDT Compare
CODESYS Forge
talk
(Post)
use sysmemcmp. https://content.helpme-codesys.com/en/libs/SysMem23/Current/POUs/SysMemCmp.html
Last updated: 2024-04-08
Post by albertovalente on How extract JSONElement containing Array data
CODESYS Forge
talk
(Post)
Hi Creator: hazarath, Have you fix the problem? because I have the same issue Thanks a lot
Last updated: 2025-11-12
Post by albertovalente on How extract JSONElement containing Array data
CODESYS Forge
talk
(Post)
Hi Creator: hazarath, Have you fix the problem? because I have the same issue Thanks a lot
Last updated: 2025-11-12
Post by gatto on warning C0195
CODESYS Forge
talk
(Post)
I answer myself: xyz : ARRAY [1..10] OF BYTE := [10(BYTE#100)] ; // no warning :-)
Last updated: 2025-11-20
Post by ofey on Codesys Soft PLC OPC UA server
CODESYS Forge
talk
(Post)
Hi! I'm sorry if this has been asked before. I have tried looking up previous topics regaring this, but even though I'm following tutorials and other posts I cant seem to get this to work consistently. I actually got the connection established on a test project after some trial and error. I only got it to work with the "Anonymous login". But after i deleted the test project and tried to get the same thing to work on another project I cant get it to work anymore. What I'm trying to do: Set up and OPC UA Server using CODESYS with the free soft PLC. I then try to connect to the OPC UA Server with the program "UaExpert". What happens: I get the error Error "'BadUserAccessDenied' was returned during ActivateSession". What I have done in CODESYS: - Added the object "Symbol configuration" and checked some test variables - Checked "Support OPC UA features - In "Communication settings -> device -> Change runtime security policy" I have checked "Allow anonymous login" What I have done in UAExpert: - Found the OPC UA server under "local". (It is showing two servers though, I do not know why. It showed the same when it worked yesterday). Se attachment - Checked "Anonymous" under "Authentication settings in the OPC UA server. I'm new to CODESYS, so it could be something elementary wrong in my settings. Maybe something in the user settings in CODESYS regarding user rights or something?
Last updated: 2023-09-14
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.