Post by manuknecht on Persistence Manager does not save alphabetically first value
CODESYS Forge
talk
(Post)
After some more digging I realized that I get an error on the PLC Logger saying PersistenceChannel: 150 (invalid type in data: SimpleLibrary). I suppose the issue could be found in the ConfigData, which is automatically generated and which looks like this: 1 9##83 SimpleLibrary#GVL.aMoreZeros.[1]#0#64512#15#0 <[2]#0#64520#15#0 <[3]#0#64528#15#0 <[4]#0#64536#15#0 <#0#64544#15#0 <[6]#0#64552#15#0 <<lrVar#0#64560#15#0 <strVar#0#64428#16#80 <uiDummy#0#64370#11#0 Perhaps the fact that the variable is stored within a library confused the compiler? I tried changing the PersistenceChannel parameters to xCompressTags := FALSE which changed the entry in the data file from _xCompressTags BOOL:TRUE _xCompressTags BOOL:FALSE but the actual content of the data file and also the config data did not change.
Last updated: 2023-10-17
Post by andrej on Write to File on soft PLC winV3x64
CODESYS Forge
talk
(Post)
Hello all, I would like to store some data in text file. I use the soft PLC Win V3x64, on Windows 10. I use the SysFile Library 3.5.17.0. If I store the file directly in the in the directory of the PLC i.e. in '/CODESYSControlWinV3x64/E1FA7ABE/PlcLogic/LogAU.txt' the file is correctly filled with the data. However, If I use an absolute path to a different directory no data is stored in the respective file. Despite the fact that the respective file exists and the Filehandler is correctly opened (see in picture _fdSysFHandle <> -1). // sFileName : STRING := 'LogAU.txt'; // STORES FILE IN ../CODESYSControlWinV3x64/../PlcLogic/LogAU.txt' sFileName : STRING := 'C/Temp/LogAU.txt'// DOES NOT WORK --------------------- // FILE DESCRIPTOR _fdSysFHandle := SysFile.SysFileOpen( szFile:= sFileName,am:= SysFile.AM_APPEND,pResult := ADR(_Result)); Does some have an idea where the problem is, resp. how I can get store a file in an arbitrary directory. Thanks a lot and kind regards Andreas
Last updated: 2023-10-24
Post by riccardo on VisuElems.CurrentUserGroupId is not stable
CODESYS Forge
talk
(Post)
Goodmorning TimvH, Thanks for the reply. I don't know if your solution solve my trouble yet, I am going to see the link you sent me. In the mean time I try to explane better what I need to do. I have a turbine system that get in alarm under some condition (E.g low speed of turbine) and block the itself. When the system is stoped there is no speed turbine and the system cannot start. To give to the operetor the possibility to bypass the alarms, there is an acknoledgement alarm pushbutton. This bypass must not work for everyone but only for those client that perform the login by (User Management). Furthermore, if the user perform the (manual or automatic) logout in alarm conditions, the acknowlegment must be annulled and block the system again. To do this, I need to know if an operator is logged in the page and is working to fix the problem; otherwise the syste must autoturn off again. Now I go to study your solution, if I have explaned better and you have another idea tell me please.
Last updated: 2023-11-16
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
Good morning everyone. In my setup I am trying to use a couple of EL7041-0052 (the EL7041 variant without terminals for an encoder) to run stepper motors without feedback. When using the softmotion drivers for the EL7041 (Rev22 and Rev24, even selecting external feedback type doesn't work) the device log shows warnings for the corresponding hardware: "SDO write error 0x1 -> 0x8012:0x08 eError 0x1 AbortCode 0x6090011". 0x8012:0x08 is the register for the Feedback Type. My best guess was setting the the register value in the start parameters to zero, but the result is the same. What else can I try to get the hardware to work? I have screenshots attatched showing the running fieldbus and the log messages. EDIT: One clarification: the "device log" that shows the error is the PLC, not the ethercat terminal. The log of the terminal itself shows neither errors nor warnings. BR Robert
Last updated: 2023-11-29
Post by spiessli on Softmotion axis to CANopen Maxon IDX drive
CODESYS Forge
talk
(Post)
Thanks for the advise, indeed, this was somewhat, what my intention was. I tried around again with EDSes and DCFs, anyway. It appears that the DCFs end up in a subfolder in the attach device dialog. Astonishingly, when attaching the DCF version I get a device in the device tree, where I can add a SoftMotion axis, whereas when I attach the device not in the subfolder, then I cannot. Further astonishingly, when looking in the CANopen parameters in supported profiles, "402" is listed in the case of the DCF variant, whereas in the EDS variant "0" is shown. Comparing EDS and DCF files I cannot guess, where the difference is coming from. I cannot tell either why I have always attached the EDS variant and apparantly never the DCF variant. As I am not in the lab right now, I cannot test if the connection actually is working. Thanks again, spiessli
Last updated: 2024-01-07
Post by levih on DocScripting
CODESYS Forge
talk
(Post)
Hello I'm trying to use the DocScripting collection in Codesys. I've made it work on one PC(1) for the 3.5.16.4 version of the script collection. But when I try the same setup on another PC(2), I get an error message: Error loading Python DLL: D:\SCRIPTING\3.5.16.40\python27.dll (error code 14001) My setup on both PC's is thus: 1. Downloaded and installed Python 2. Copied the folder with the scripting collection to C: (because of admin rights) 3. Placed my .library file in the same folder as the scripting collection Only difference is that Python is v3.12.0 on PC1 and v3.12.1 on PC2. I thought maybe it was something with Python, but then I have tried using the scripting collection from 3.5.16.1, and that seems to work. Just not for scripting collection 3.5.16.4. I also can't seem to find any scripting collections on newer versions of Codesys? (e.g. 3.5.19.10) Thanks in advance!
Last updated: 2024-01-22
Post by kevin123 on auto-answer dialog using system.prompt_answers
CODESYS Forge
talk
(Post)
I am trying to do "update device" in a project which was saved in a different version of CODESYS using ScriptEngine, a dialog with 'Yes' and 'No' button popped up showing that "Do you want to upgrade the storage format for this project? -if you click 'Yes', storage format will be upgraded... -if you click 'No', storage format will not be changed..." I have to click the 'Yes' button automatically by scriptEngine. I know from others topics here in forum, that some dialogs can be auto-answered using system.prompt_answers. And I also get the messagekey of this dialog: Key: "<< No Key>>" Message: "Do you want to upgrade the storage format for this project? - If you click 'Yes',... i have tried using the system.prompt_answers command below, but the dialog was not auto-answered. system.prompt_answers["<<No Key>>"] = PromptResult.Yes Does someone know how to auto-answer the dialog using system.prompt_answers command with messagekey"<< No key>>"? or any suggestions to solve this issue, Thanks!
Last updated: 2024-01-26
Post by kevin123 on auto-answer dialog using system.prompt_answers
CODESYS Forge
talk
(Post)
I am trying to do "update device" in a project which was saved in a different version of CODESYS using ScriptEngine, a dialog with 'Yes' and 'No' button popped up showing that "Do you want to upgrade the storage format for this project? -if you click 'Yes', storage format will be upgraded... -if you click 'No', storage format will not be changed..." I have to click the 'Yes' button automatically by scriptEngine. I know from others topics here in forum, that some dialogs can be auto-answered using system.prompt_answers. And I also get the messagekey of this dialog: Key: "<< No Key>>" Message: "Do you want to upgrade the storage format for this project? - If you click 'Yes',... i have tried using the system.prompt_answers command below, but the dialog was not auto-answered. system.prompt_answers["<<No Key>>"] = PromptResult.Yes Does someone know how to auto-answer the dialog using system.prompt_answers command with messagekey"<< No key>>"? or any suggestions to solve this issue, Thanks!
Last updated: 2024-01-26
Post by kevin123 on (no subject)
CODESYS Forge
talk
(Post)
I am trying to do "update device" in a project which was saved in a different version of CODESYS using ScriptEngine, a dialog with 'Yes' and 'No' button popped up showing that "Do you want to upgrade the storage format for this project? -if you click 'Yes', storage format will be upgraded... -if you click 'No', storage format will not be changed..." I have to click the 'Yes' button automatically by scriptEngine. I know from others topics here in forum, that some dialogs can be auto-answered using system.prompt_answers. And I also get the messagekey of this dialog: Key: "<< No Key>>" Message: "Do you want to upgrade the storage format for this project? - If you click 'Yes',... i have tried using the system.prompt_answers command below, but the dialog was not auto-answered. system.prompt_answers["<<No Key>>"] = PromptResult.Yes Does someone know how to auto-answer the dialog using system.prompt_answers command with messagekey"<< No key>>"? or any suggestions to solve this issue, Thanks!
Last updated: 2024-01-26
Post by wbj0t on System libs and I/O Drivers
CODESYS Forge
talk
(Post)
Hi everyone. My question about: where I can learn (read or watch) an info about codesys workflow through the system IO libs? I want to know how to implement I/O drivers by my self. In the system libs I see many interfaces, methods etc... But there is no explanation about them, just names of methods and fields of the FBs. I know about this page: https://forge.codesys.com/drv/io-drivers/doc/Generic/ There is so BIG the device description file and not so clear explaining of the attributes and elements, also some elements or attributes missed at it all. Yes, there are code examples on this page, but, so shortly and, for example, code about Modbus drivers is absent. And even if I try to add the IoDrvFB with lib, I get and error, something like: "failed to load IoDrvFB driver". And what about the book of codesys that written by Gary Pratt? Is there information about system libs and drivers in this book more clearly? Thank you :)
Last updated: 2024-02-02
Post by chalk on No source code available
CODESYS Forge
talk
(Post)
Hello, This is my first time using Codesys, I am trying to add EtherNetIP communication to a Raspberry PI. I’ve added the EtherNetIP Adapter configured the network setting and added some modules to the pi but when I download the project it generates the following error: “There is no source code available for the object because it is in the compiled library ‘cip object, 4.5.1.0 (3s – smart software solution gmbh)’. Do you want to browse for the original library in order to display the source code? There are 2 errors in the log which are: SOURCEPOSITION App=[Application] area=3, offset=332760 EXCEPTION [Application] occurred: App=[Application], Task=[ENIPAdapterServiceTask] I can’t for the life of me work out how to get around this. I can’t find the source code anywhere or any information regarding this error. I’m using Codesys V3.5 SP19 Patch 3, the version of the Ethernet adapter is 4.5.1.0 and the version of the modules is 4.1.0.0. Any help on this will be greatly appreciated. Thanks
Last updated: 2024-02-02
Post by axilleas on SMC_Interpolator + SMC_controAxislbyPos
CODESYS Forge
talk
(Post)
dear all I am working on a very generic gantry system (virtual drives + win v3 control) reading gcode from external file. In order to stop the interpolator function from running when gaps are detected, SMC_controlAxisByPos FB has the bStopIpo output which according to the manual is connected to the Interpolator's bEmergencyStop. Lets assume that the axis are parked in position X1000 Y1000 and the initial G code movement is G00 X500 Y500. The normal behavior is to travel from the actual x1000 y1000 to G00 X500 Y500. The SMC_Interpolator always gets the X0 Y0 as the initial position, meaning that the bStopIpo is active until the axis are in X0 Y0 and the release the interpolator to set the new positions to X500 Y500. Is there a suggested method to solve this behavior? bonus question: I get a lot of bStopIpo during standard interpolation movements (not gaps). While working with virtual axis this is not a problem but when real axis are installed this will be an issue. What exactly triggers the bStopIpo output? Slow axis accelerations compare to Gcode defaults? Kind Regards
Last updated: 2024-02-05
Post by fredsta on Unable to load dynamic modules (Download failed: Application=Application)
CODESYS Forge
talk
(Post)
Hey there, I am currently trying to find a good solution for the communication between CODESYS Control on Raspberry Pi and "the rest of the world", i. e. the things apart from CODESYS on my linux. My first approach was to use the c-integration. So I created a lib, defined extern fbs, compiled the code on my Pi using the SDK and put the .so into my lib project. When I try to log into the Pi and load the program, I get the error message which you can see in the attached picture. "Die dynamischen Module der C-Integration konnten nicht auf das Laufzeitsystem geladen werden" is german and means roughly "the modules from the c-integration could not be loaded onto the runtime system." Is this normal? Am I doing something wrong? I will have a look at the unix domain socket thing next, as I am still in the process of finding the best solution for the communication.
Last updated: 2024-02-15
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by zoronoa on J1939.ReceiveWatchdog & J1939.ReceiveParameterGroup
CODESYS Forge
talk
(Post)
Hi, I'm trying to monitor a specific PGN which I have it sending a pulse every 500mS Problem: Using the Watchdog for the ECU does not really help me as I have multiple instances with separate PGNs, if a PGN goes ghost, the ECU watchdog won't be flagged as the others will be running. I found the J1939.ReceiveWatchdog & J1939.ReceiveParameterGroup function blocks and they seem like a good solution for my problem, I just can't get them to work from my understanding you just build the J1939.ReceiveParameterGroup once and then connect it's output to the J1939.ReceiveWatchdog, here's my CODE for the setup HEARTBEAT_TIMER(IN:= TRUE, PT:= T#1000MS); //turn-on delay because of initialization race IF HEARTBEAT_TIMER.Q= TRUE THEN Glob_Var.DisplayReceive.xExecute:= TRUE; Glob_Var.DisplayReceive.itfECU:= Valve_X; Glob_Var.DisplayReceive.dwPGN:= 65511; Glob_Var.DisplayWatchdog.xEnable:= TRUE; Glob_Var.DisplayWatchdog.itfParameterGroup:= Glob_Var.DisplayReceive.itfParameterGroup; Glob_Var.DisplayWatchdog.tTimeout:= T#1500MS; END_IF Notes: Glob_Var.DisplayReceive is of type J1939.ReceiveParameterGroup Glob_Var.DisplayWatchdog is of type J1939.ReceiveWatchdog The above code is done once and not cyclically I'm monitoring Glob_Var.DisplayWatchdog.xError cyclically
Last updated: 2024-03-13
Post by anlebr on Codesys Communication Manger - Required information model version exists in the model repository but is not found
CODESYS Forge
talk
(Post)
Hi I am trying use the Codesys Communication Manager to set up an Opc ua server with a custom information model. As a start I am using the Boiler model available on Opc foundations github page. I am testing with a Wago CC100 and using Codesys V3.5 SP19 Patch 6. I get the following error: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://opcfoundation.org/UA/Boiler/ with a minimal publication date from 15/12/2023 but the device has only a model from 15/09/2021 installed. Probably the information model from 15/09/2021 is missing in the information model repository. The error message does not make sense to me. Should it not be “Probably the information model from 15/12/2023 is missing in the information model repository”? Anyway, both versions are available in the repository. How can I solve this?
Last updated: 2024-03-13
Post by thewizard8 on Raspberry PI4 Serial Port
CODESYS Forge
talk
(Post)
Hi Dear All, I'm using my raspberry PI4 as a CoDeSyS PLC (Build from scratch with custom electronics). I was able to implement all fieldbuses with the exception of Modbus Serial. I'm using the internal Port (GPIO) and I configured it in /etc/Codesyscontrol_user.cfg the following away: [SysCom] Linux.Devicefile.1=/dev/ttyUSB0 Linux.Devicefile.2=/dev/ttyS0 I'm using COM2 on Master configuration. I'm using a interface board from TTL/RS485 (bidirectional board), and it's works perfectly with other devices but not in CoDeSyS. I'm able to send data with python script and read it on my pc using putty, but when I use a modbus slave simulator to interface with codesys I always get red icons on master and slave. (Please find image attached). I'm pretty shure that this might be a bad parameter on my CoDeSyS runtime configurstion file. Can someone help me? I'm stuck and this is for my master degree certification.
Last updated: 2024-03-18
Post by squiggleypuff on RemoteTargetVisu creates Unresolved Reference
CODESYS Forge
talk
(Post)
I have a project with a Festo CPX-E-CEC-C1-PN PLC (Run-time version 3.5.12.50) that I have been developing on just fine using Codesys V3.5 SP19 Patch 5 (64bit). I am at the stage where I wanted to use the Festo HMI screen, and have added a RemoteTargetVisu object to my application. After adding this object, I am no longer able to log in to the PLC as I get an Unresolved Reference warning for 'USERMGRUSERGETPROPERTY' towards the end of the download process. I was able to find this post (https://forge.codesys.com/forge/talk/Visualization/thread/fc686a6cb2/) where the two possible solutions are to "set the placeholder to emtpy" or update the runtime. Problem is, I don't know how to do either of these things, as I'm still very green in Codesys land. I'd be happy to update the Festo PLC runtime, as that seems like the better option, but have not had any luck in finding a tutorial for this online. If anyone could point me in the right direction I'd appreciate it.
Last updated: 2024-03-19
Post by duvanmoreno24 on Modbus writing on value change
CODESYS Forge
talk
(Post)
Yes, I tried to do what you put in the first code. However, I have a problem with that and that is that the inputs must be declared with the type. I have many data types running in my code (real, int, uint, bool) and I can't put them in the same function, another thing is that I need to instantiate that function for everything I want to write to the slave. You put a for to 200 but it means that it has to be the same data type and inside the array, but I want to get them individually. I'm struggling to do it in a good and efficient way like wago's E-cockpit does. in the first screenshot you can see, you simply type in value, change the package of things you want to write in value change and it does everything by itself automatically, without comparing any old and new values and even less having the need to activate a bool. , it is perfect.
Last updated: 2024-04-03
Post by squiggleypuff on Can't Add New Version of Modbus TCP Master
CODESYS Forge
talk
(Post)
I'm having a tough time trying to get Modbus working on a Festo CPX-E PLC; it throws these pre-compiler errors as soon as I add in my Modbus TCP Master 3.5.12.30 to my project: I'm confused about the C0046 error, as I have IODrvModbusTCP 4.3.0.0 Library installed. So I thought maybe I needed to use the newest Modbus TCP Master 4.3.0.0, which is in my device repository: However, whenever I go to add this underneath the Ethernet adapter (which is version 4.2.0.0), the only TCP Master version available is the old 3.5.12.30 one, even if I have Display all versions checked.: I even went so far as to delete the old version, but then there were no options to add a Modbus TCP Master under my Ethernet adapter. What needs to be done to use the newest Modbus TCP Master? Or are these pre-compiler errors unrelated and I'm missing something? Any help greatly appreciated.
Last updated: 2024-04-04
Post by joshskellig on Publish a JSON payload via MQTT Publish (using IIot Libraries)
CODESYS Forge
talk
(Post)
I am trying to figure out how to get a JSON payload to properly publish to my MQTT Broker. I am able to generate JSON using the examples from Codesys, but when I send that payload via MQTT there are characters that are extra or not recognized by my MQTT client. Any idea what could be causing it? PROGRAM PLC_PRG VAR hostname: STRING := 'localhost'; port: UINT := 1883; topic: WSTRING(1024) := "testing/"; payload: BYTE; factory : JSON.JSONDataFactory; eDataFactoryError : FBF.ERROR; pJsonData : POINTER TO JSON.JSONData := factory.Create(eError => eDataFactoryError); fb_JBuilder : JSON.JSONBuilder; wsValue : WSTRING := "Value1"; diRootIndex, diObject1Index : DINT; iValue : INT := 1234; jsonArrayWriter : JSON.JSONByteArrayWriter; wsJsonData : WSTRING(1000); xFirst : BOOL := TRUE; mqttClient: MQTT.MQTTClient; mqttPublish: MQTT.MQTTPublish; mqttPublishProperties: MQTT.MQTTPublishProperties := (bPayloadFormatIndicator := 1, wsContentType := "application/json"); END_VAR // Json Functionality IF xFirst THEN fb_JBuilder(pJsonData := pJsonData, diRootObj => diRootIndex); fb_JBuilder.SetKeyWithValue("Key1", wsValue, diParentIndex := diRootIndex); diObject1Index := fb_JBuilder.SetKeyWithObject("Key2", diParentIndex := diRootIndex); fb_JBuilder.SetKeyWithValue("Key3", iValue, diParentIndex := diObject1Index); xFirst := FALSE; END_IF jsonArrayWriter(pwData := ADR(wsJsonData), udiSize := SIZEOF(wsJsonData), jsonData := pJsonData^, xAsyncMode := FALSE); MSU.StrTrimW(pString:= ADR(wsJsonData)); // MQTT Functionality mqttClient( sHostname:=hostname, uiPort:=port, eMQTTVersion:=MQTT.MQTT_VERSION.V5 ); mqttPublish( mqttClient:=mqttClient, pbPayload:=ADR(wsJsonData), udiPayloadSize:=SIZEOF(wsJsonData), wsTopicName:=topic, mQTTPublishProperties:=mqttPublishProperties );
Last updated: 2024-04-10
Post by salvadegianluca on How to use TON inside an FB that is instanced within a Visu page
CODESYS Forge
talk
(Post)
Hi everyone; I'm building a project in which the drag of the mouse over some controls (or the click event) changes the background color of the control items; this change of color is made with an FB that assignes a color code to the background with MUX command based on the value of an enumerator, this part is perfectly working but, when I'm using a touchpanel instead of a web visu (controlled by a mouse) I get into some issues as it seems that the touch operations are not triggering the MouseEnter and MouseLeave properties as it's done with the mouse.... For this reason I'm trying to add a TON to my FB and, if the enum that changes color remains at the same state for more then 3s I'm automatically resetting it to it's "0" so the item gets back the not selected color. Anyhow it looks like the TON function from library is not working in these FB that are instanced in the various visualizations, as instead they do if I create some instances within the POUS. Anyone has ideas of how to make them work?
Last updated: 2024-04-15