Post by sumit on Remote Ethernet/ip Adapter communication with scanner running on codesys
CODESYS Forge
talk
(Post)
Hello there, I have my ethernet/ip adapter (from Texas Instrument) running on Texas Instrument Board and I have configured the scanner on codesys. I have mapped the I/Os and I can see (on wireshark) the frames coming from adapter but I don't see my input variables in scanner get updated, they just stay at 0. I wanted to see the real data that has been sent from adapter to scanner on codesys. I am not sure if the problem is in I/O mapping or there is a step/s that I have missed. I have attached the screenshot of my project for your ref. Thank you, Sumit
Last updated: 2023-12-15
Post by atone on Change IO-Link Device Interface connected to a Profinet-Slave at Runtime
CODESYS Forge
talk
(Post)
OK, I figured out that I can simply define all the sensors as 16 bytes IN/OUT, even if they are not all used. EDIT: The negative effect is that each bit is taken into account as an I/O for the license, even if not used.
Last updated: 2025-04-28
Post by selim on LS ix7nh Servo drive with Codesys
CODESYS Forge
talk
(Post)
Hello Mr./Ms., I do not find the ES driver in codesys. The setup of the project is "Rasberry PI3B>Ls ethercat I/O aps-ec-dt32k> LS ix7nh Servo drive>apmc-fbl04amk LS servo motor". How can i slove this problem. Please provide me a proper solution.
Last updated: 2025-06-02
Post by egr99 on Modbus TCP Server connection is ESTABLISHED but all holding registers are value 0?
CODESYS Forge
talk
(Post)
Hi there, Read the above description and experienced the same: Reading coil/discrete input/input register/holding register doesn't fill the mapped I/O variable. Any suggestions? Defined (see attachment): - Ethernet (with parameters according to the used Ethernet adapter of my Windows 11 laptop) - -Modbus TCP Client - - -LOGO231 as Modbus TCP Server - - -WS242 as Modbus TCP Server (WaveShare Modbus TCP <-> RTU converter) - - - -WS242_01 as Modbus Server, COM port (slave-id 1 RTU) - - - -WS242_03 idem (slave-id 3 RTU) - - - -WS242_11 idem (slave-id 11 RTU) Writing coil/holding register works from a mapped I/O variable works fine. Verification of Modbus traffic with WireShark: QUERY to and the RESPONSE of all slave-ids are correct Status of all defined is CONNECTED, RESPONSE_SUCCESS, RUNNING etc. Request counters increase with expected frequency. Error counter = 0. (To have all counters works fine I had to change Modbus TCP Client's parameter OptimizationON to FALSE). LOGO231 works fine: values in mapped I/O conform expectation WS242 without Modbus Server, COM port and with defined channels (for only 1 slave-id possible) works fine. PLC Settings: Update I/O while in stop: I see xBusy changing from FALSE to TRUE and vice versa. Always update variables: Enabled 1
Last updated: 2026-04-05
Post by transmin01 on PCAN serial "No CAN driver found"
CODESYS Forge
talk
(Post)
Hi, I am using a PCAN mini CAN board which has the Windows drivers installed on the target PLC. PCAN board can be seen in device manager. However, I am getting "No CAN driver found" error. I have read the post https://forge.codesys.com/forge/talk/CODESYS-V2/thread/44aae19318/ and have uncommented the CmpPCANBasicDrv driver in the CodesysControl.cfg file in development PC and have copied it to the target PC. Current CodesysControl.cfg file attached. Is there anything else I am missing? Regards
Last updated: 2023-09-14
Post by mikek10 on Error IoDrvEthernetIP: Connection Failure. (16#1) How to solve
CODESYS Forge
talk
(Post)
Your connection configuration should look something like the attachment. Consuming assembly O->T will be the hex of the assembly you want to reference for output data - I want 102 (DO Data Only) shown in the Wago web page 102 = 16#66. Producing assembly (T->O) is the assembly you require for input data - again shown in the Wago web page - I want 108 (DI Data Only) or 16#6C Then set the number of bytes as per the data in the Wago web page too (both 2 in my case)
Last updated: 2024-07-22
Post by fleaplc on CPU + EtherCAT redundancy
CODESYS Forge
talk
(Post)
Hi all, for a new project I'm looking for a redundant controller with EtherCAT fieldbus I/O. Actually I'm using Beckhoff and it works great! but there's not a solid redundancy yet... Does someone get experience for industrial application (not raspberry) for a redundant Codesys system? If yes please share some info (CPU / OS type, bus, number of managed I/O,... and especially feeling feedback (stability, bugs, performance)... Every suggestion is kindly appreciated!! Fabrizio
Last updated: 2026-01-27
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by peterkcontrols on Copying 2 byte word to output
CODESYS Forge
talk
(Post)
Hello. I am using codesys 3.5. I would like to know if it is possible to set a variable to an output without declaring in. I have defined a STRUCT and within this struct I have a Struct for inputs called I and a struct for outputs called O. I have declared a variable of the type of this Struct, I would like to set or alias the value in this variable to an input/output value of an IO block that has a module on the ethernet tree. Is it possible to copy the contents of %IW0 -> STRUCT.I ? The size of both of these is 2 bytes. I understand that I can declare a variable with the input like Input01 AT %IX0.0 : BOOL; However how can I make STRUCT.I.D00 AT %IX0.0? Is this possible? Thanks
Last updated: 2025-03-03
Post by qkkk on Device Scan
CODESYS Forge
talk
(Post)
Hello all, I have developed a custom I/O driver in CODESYS that communicates via a Unix Domain Socket. In my DeviceDescription.xml, I have set up the following: <scan supported="true"> <scanfbinstance fbname="IOScanDevice"> The goal is to allow the user to scan for connected I/O modules from the CODESYS GUI ("Scan for Devices") and automatically populate the device tree with detected submodules.</scanfbinstance></scan> The function block IOScanDevice is implemented in the driver library and added to the main device's FB instances. However, when I initiate the scan from the GUI, nothing appears to happen the function is not executed. Is there an example project or driver (open source or from CODESYS Forge) that demonstrates a working custom scan implementation?
Last updated: 2025-05-26
Post by yofi on Configuring an Encoder
CODESYS Forge
talk
(Post)
I have a raspberry pi trying to add encoder to it using that free encoder node. I simply dont understand where the encoder channel A/B suppoded to be mapped when i got to I/O mapping on encoder I get nothing to where to set the channels for the encoder or is there any blocks from a library or how is it that you use an encoder with Codesys it doesn't seem clear at all
Last updated: 2024-05-25
Post by adam on Get/Set I/O Address Mapping of DeviceObjects in python Script
CODESYS Forge
talk
(Post)
I want to cancel the automatic address allocation for all IO mappings. If I directly set the automatic_iec_address in class ScriptIoMapping to False, the address becomes None. So I reset manual_iec_address with itselfs value. It only work with the Input IOMapping . For output, it reports an error: "Invalid address: The channel type 'Output' requires address type '%Q'." I checked the description file ,both accessRight are total same. Does anyone know what causes this?
Last updated: 2025-11-14
Post by chris--o on ModbusTCP RaspberryPi zu Fronius Wechselrichter
CODESYS Forge
talk
(Post)
Keiner ne Idee?
Last updated: 2025-07-03
Post by mascara on TouchScreen does not work in Webvisualization.
CODESYS Forge
talk
(Post)
I am configuring a Lenovo M900 computer with CODESYS Control RTE SL 3.5.20.30. I use an Aoc E2272pwut LED 21.5 monitor. The touchscreen works perfectly in the Windows 10 PRO environment but does not work in the WebVisualization environment (Window opened at PLC startup). Does anyone know if it is necessary to configure any drivers in Win RTE? I am at your disposal for any questions. Thank you.
Last updated: 2024-11-11
Post by gatto on Profinet Exor connection drop
CODESYS Forge
talk
(Post)
did you try setup two eth ? on ethO you set ip to communicate with pc, example 192.168.0.1 on eth1 ip to communicate with weidmuler I/O, example 192.168.100.1 note : ip need the same of ip setup under system setting of hmi.
Last updated: 2024-10-16
Post by s1ack on Undertanding Application Based Licenses
CODESYS Forge
talk
(Post)
Can anyone confirm my thinking here that this project will require Control Standard M because of the I/O channel count under the fieldbus?
Last updated: 2024-11-08
Post by goki on WAGO RS485 (753-652) on a 750-362
CODESYS Forge
talk
(Post)
Forgot to describe the pictures. Modbus1: is the actual configuration in codesys 3.5 Modbus2: is the config in WAGO I/O Modbus3: is the configuration from the old one with Beckhoff twincat (we are changing from Beckhoff to wago and codesys)
Last updated: 2024-02-08
Post by timvh on Legacy IFM CANopen I/O modules with CR710S / CODESYS 3.5
CODESYS Forge
talk
(Post)
Yes, you can use the .eds files also in CODESYS 3. Install them through the menu Tools - Device Repository. Then you can add the CANopen devices to your CANopen manager in your device configuration.
Last updated: 2026-09-29