Post by tomast on Codesys and Siemens SINAMICS 20 modbus RTU "Response CRC Fail"
CODESYS Forge
talk
(Post)
Hi everyone, I'm currently working on a project involving the control of 5 VFDs via Modbus RTU, this time using the WAGO 750-8212 CPU. So far, I've managed to make progress, but I've encountered an issue. While I can successfully read and write to all the registers I need, I consistently encounter a "Response CRC Fail" error when attempting to write the value 1151 to the STW register at address 40100. I'm able to set the frequency via register 40101 and adjust all other parameters using different registers. Setting STW to 1150 results in the drive ready boolean from the ZSW-bit being received instantly. However, the moment I attempt to send 1151 to register 40100, I immediately receive the "Response CRC Fail" error for all channels. I've also attempted to use combined control, employing Modbus for frequency control and starting from a digital input. Everything seems to function properly until I send the start command to the VFD. Interestingly, I consistently encounter the same error the moment I send the start command, regardless of whether I use register 40006 (high) or 40100 (1151). Could someone please assist me in resolving this issue?
Last updated: 2024-03-21
Post by andrax on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
Hi, Communication with the ADS1115 is actually simple. 1. write config 2. write address pointer 3. read conversation register The ADS1115 works like a multiplexer. This means that you do this individually for each channel that you want to read. e.g: Channel 1: write config > write address pointer > read conversation register Channel 2: write config > write address pointer > read conversation register Channel 3: write config > write address pointer > read conversation register Channel 4: write config > write address pointer > read conversation register then you start again from the beginning You can also omit individual channels or read only one. It doesn't matter. I have written the driver so that I can also use it on the TCA9548. The driver is from Stefan Dreyer. In your case, the driver works and communication with the ADS1115 is running. As you can see, the cfgWrong:=FALSE If you could not write or read data, cfgWrong:=TRUE; This means that either something is wrong with your ADS1115 or you have connected something incorrectly. Question: what voltage do you want to measure?
Last updated: 2024-11-08
Post by mehakfatima on Need Help Configuring Energy Analyzers via Modbus TCP & RTU (RS-485) in CODESYS 3.5
CODESYS Forge
talk
(Post)
Hello everyone, I am currently working on reading data from energy analyzers using Modbus TCP and RTU (RS-485). In my previous software, I used the following method to add slave devices (i have attached the image) and configure registers: Add the Modbus slave device. Configure the communication parameters (baud rate, parity, etc.). Define the registers and their addresses for data retrieval. Now, I am trying to achieve the same in CODESYS 3.5, but I am not sure how to configure the Modbus master, add slave devices, and set up the registers properly. If anyone has experience with Modbus TCP/RTU setup in CODESYS 3.5, I would really appreciate your guidance! A step-by-step explanation or any references/tutorials would be extremely helpful.
Last updated: 2025-03-13
Post by jeffgamsby on Accessing ModbusTCP addresses from python
CODESYS Forge
talk
(Post)
Hi, I am new to modbusTCP and I am trying to access Input registers from codesys (3.5.SP13). The offset is 16#0000 and I am trying to access Channel 1[24] %IW24 to pull analog values. I am using pyModbusTCP and I need to supply a modbus address and the number of registers to read. What does 16#0000 mean in terms of the actual offset, how do I translate this number plus the channel to access this info via python? Any help would be appreciated, thank you.
Last updated: 2023-09-20
Post by eoahe on Problem Reading Registers via Modbus from non Codesys device
CODESYS Forge
talk
(Post)
Hey Guys :) I have the following Problem using Modbus via Codesys: I'm trying to implement a Modbus Device into my codesys project. The device is a Router from Teltonika (RUT956) and it can communicate via Modbus. Currently I'm trying to implement it into my codesys prject as a slave and I'm using my windows computer as master. As it is not a codesys device (the codesys application is not uploaded to device as it has its own software) I'm having problems requesting and reading registers from the router. I've set up my windows computer as Master and implemented the router as slave. When I go online on my master device it sais that it has established a connection to the slave (router)(So I'm thinking this could work as there is a connection?). The goal is to read the GPS (latitude and longitude) data and on the homepage of teltonika you can find the register address and number of registers (adress 143 for latitude and 145 for longitude; both have a number of two registers). I've found tutorials how to read specific registers via their register address with other modbus programs (like modbus-cli), but as my entire project is established in codesys I was hoping to read these specific registers via codesys so that I can show the GPS data on my dashboard. I've tried establishing slave channels but that hasn't been working. I tried read input register channels of the length 4 but it's not possible to define specific register addresses to read via codesys so that didn't work (I jsut get a slaves device failure) and I've also tried establishing 516 (total number of registers the router sends I think?) read inputregister channels but that has the samle failure... So i guess the problem I'm having is establishing slave channels to read these specific registers. Does anyone know how to tackle this problem and has maybe had the same problem? Or maybe someone knows a workaround? I'm quite new to codesys so maybe I'm also lacking expertise...
Last updated: 2025-03-01
Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia
CODESYS Forge
talk
(Post)
Using SDO, I can read the EtherCAT mappings and offsets from various registers like 0x1c12, 0x1c13, etc. When I obtain registers mapped in the PDOs and various offsets, I could technically access directly to the statusword, controlword, etc., if they are mapped. I have noticed that on IoDrvEthercatLib.ETCSlave_Diag I can find pointers to the input and output buffers. However, although the input buffer can be easily read by referring to what has been obtained from the SDOs, it is not possible to write to the output buffer, as it is overwritten in each cycle by the data from the IOMapping task. Is there a way, knowing an instance of IoDrvEthercatLib.ETCSlave_Diag, to obtain the pointer to the first data in the IOMapping? The offsets are identical to those of the PDOs, but obviously the data is a copy. For me, the cleanest thing would be to access the pointers on IOMapping, for DS402a devices to retrieve the key data and point them to internal references. I need to know this as, having developed our own motion library, I would like to simplify the initial setup by eliminating unnecessary and nonsensical mappings that can lead users to unnecessary errors. In the current version that we have been using for years, we have to map everything manually. I would like to pass only the slave reference to the FB_init constructors and eliminate the mapping.
Last updated: 2024-02-12
Post by eschwellinger on License problem gateway
CODESYS Forge
talk
(Post)
please write to 'my question' in the CODESYS store.
Last updated: 2024-04-16
Post by garyl on Comments in arrays and assigning RST coil's to 600 outputs
CODESYS Forge
talk
(Post)
Hello all, im working on a project that requires me to convert an old automation direct DirectSoft PLC d2-250-1. One of the problems im encountering is that all of the comments are attached to members of the different addresses. When i convert the addresses (1777 "C" registers, 777 X registers, and 20,0000 V registers) im running into difficulties keeping the inputs/outputs correct since they are missing documentation. Is there a good way to retain the comments of the indexes in the array? Secondly, initially i was declaring the "C" and "V" addresses individually and this worked to retain the comments as to which register did what, however i ran into a problem when one rung reset (or set to 0) approximately 600 C Addresses. Since each tag is separately declared this proved to be nearly impossible without a literal wall of code that attempted to crash the program. So i converted all of the registers (C,X,Y,V) into separate structs, declared them as arrays and pointed all of the original call outs in the program to the newly defined structs. However i have now lost comments and the program is very hard to follow. Thanks for any help with this issue.
Last updated: 2023-08-31
Post by i-campbell on MODBUS TCP REGISTERS CODESYS V3.5
CODESYS Forge
talk
(Post)
codesys is in hex and starts at 0 your other program is set to decimal and maybe starts at 0 or 1, I can't tell.
Last updated: 2024-10-12
Post by banialuk on Modbus TCP Server
CODESYS Forge
talk
(Post)
Hello, I have poroblem with define input in function block modbusFB.serverTCP 'dataModel', in my aplication I need starting Input Registers from 3000, and I must define this in 'data Model' but I dont now how exacly to do it. Anybody now somethin about this?
Last updated: 2024-10-19
Post by pazderai on CanOpen write issue
CODESYS Forge
talk
(Post)
Hi,is there any canopen library where is implemented sdo write with unspecified datalength (command byte 0x22)? I tried caa cia405 canopen library but it doesnt support this, but my slave device accept only 0x22. Thank you for any help.
Last updated: 2024-07-16
Post by pazderai on CanOpen write issue
CODESYS Forge
talk
(Post)
Hi,is there any canopen library where is implemented sdo write with unspecified datalength (command byte 0x22)? I tried caa cia405 canopen library but it doesnt support this, but my slave device accept only 0x22. Thank you for any help.
Last updated: 2024-07-16
When running as a service, CodesysControl doesn't write log files to the disk (and other CmpLog related issuess)
CODESYS Forge
talk
(Thread)
When running as a service, CodesysControl doesn't write log files to the disk (and other CmpLog related issuess)
Last updated: 2025-03-06
Post by hanoues on Holding brake release
CODESYS Forge
talk
(Post)
I've tried using the SMC3_BrakeControl function block to control the brake, but unfortunately, it's not functioning as expected. Despite setting the appropriate parameters and inputs, the brake control does not operate correctly. Any insights or suggestions on resolving this issue would be greatly appreciated. STATE_MANUAL.UNLOCK_BRAKE: IF Button_release_brake THEN GVL.drum1_Control_Brake:=TRUE; FBA.T11_ContBrake.bExecute := TRUE; GVL.manual_state := STATE_MANUAL.WAIT_FOR_BRAKE_RELEASE; END_IF STATE_MANUAL.WAIT_FOR_BRAKE_RELEASE: IF FBA.T11_ContBrake.bDone THEN FBA.T11_ContBrake.bExecute := FALSE; GVL.manual_state := STATE_MANUAL.WAIT_START_BUTTON; END_IF
Last updated: 2024-04-08
Post by rjonker on codesys mqtt publish serialization
CODESYS Forge
talk
(Post)
pbPayload is a pointer, which it expects to point at a STRING. If you point it at an address holding a different data type, it will just assume those bytes are part of a string and likely trundle along memory until it finds a null byte (0x00) that would normally signify the end of a string PublishMessage := BOOL_TO_STRING(boolVariable);
Last updated: 2024-06-05
Post by bolopg on MODBUS TCP REGISTERS CODESYS V3.5
CODESYS Forge
talk
(Post)
Hi. I have a problem with MODBUS TCP MASTER. I treid to read HR in range 3027-3037 but I cannot read them. I have modbus slave chanel with offset 0x3037. I checked what I read and it looks like I am reading HR in range 1-10. What I am doing wrong.
Last updated: 2024-10-11
Post by eschwellinger on File Creation Issue
CODESYS Forge
talk
(Post)
use the PLClogic directory to read / write files. /var/opt/codesys/PlcLogic this is due security reasons forced to use.
Last updated: 2025-03-04
Post by eschwellinger on Edge Gateway online, but PLC is not online
CODESYS Forge
talk
(Post)
need the log file - or you write/send it in the CODESYS store my question
Last updated: 2024-01-10
Post by eschwellinger on Rpi zero w lost license after 4.11 update
CODESYS Forge
talk
(Post)
Please write to 'my question' in the CODESYS Store.
Last updated: 2024-04-16
Post by dkugler on Text List Fallback Value
CODESYS Forge
talk
(Post)
why you adding this ' ' ? you don't need them in the text field :-) delete them, write only Unknown and everything will be as expected
Last updated: 2024-04-18
Post by automa on How to write variable by name
CODESYS Forge
talk
(Post)
It has been a few years since this topic. Any solutions?
Last updated: 2024-06-04
Post by adarsh on CAN Tags in Writing in PLC Error.
CODESYS Forge
talk
(Post)
Hi Folks, I have CAN Device Connected so I am able to read and write data at J1939 Manager. But unable to write the data from the PLC. Geeting the Following error while Writing from the Ladder Logic Diagram. Error:NO Valid Assignment Target How we can Rsolve this Problem
Last updated: 2024-04-02
Post by dogulas on OPC UA C# client connecting to OPC UA CODESYS server
CODESYS Forge
talk
(Post)
Ok, I have a simple test environment. From C#, using OPC UA, I can read DINTs, write DINTs, read Structs, but when I try to write a struct I get BadNotWritable. I am using Communication Manager, OPC UA Server, and IEC Symbol Publishing. I have a struct defined with one single DINT in it. The instance of the struct is in GVL. The struct is marked read/write in IEC Symbol Publishing. Any ideas? Pointers are welcome. public static async Task WriteStructA(byte[] structAData) { if (_session == null) throw new Exception("session is null"); // create a RequestHeader RequestHeader requestHeader = new RequestHeader { Timestamp = DateTime.UtcNow, TimeoutHint = 30000 // timeout in milliseconds }; // create an ExtensionObject to wrap the value to be written ExtensionObject extensionObject = new ExtensionObject( new ExpandedNodeId("GVL_StructA", 5), structAData ); // create a WriteValue object to hold the value to be written WriteValue writeValue = new WriteValue { NodeId = _structANodeId, AttributeId = Attributes.Value, Value = new DataValue(extensionObject) }; // put the WriteValue object into a WriteValueCollection object WriteValueCollection writeValueCollection = new WriteValueCollection() { writeValue }; // perform the write operation asynchronously WriteResponse writeResponse = await _session.WriteAsync( requestHeader, writeValueCollection, CancellationToken.None ); // check the result of the write operation if (writeResponse.Results[0] != StatusCodes.Good) throw new Exception("Write failed: " + writeResponse.Results[0]); }
Last updated: 2024-12-17
Post by greenwood on CODESYS Control Raspberry Pi mit Servotreiber T6 von StepperOnline
CODESYS Forge
talk
(Post)
Hallo, ich versuche, eine Modbus-RTU-Kommunikation zwischen meinem Raspberry Pi mit CODESYS Control für Raspberry Pi 64 SL und einem Servotreiber von StepperOnline, Typ T6, herzustellen. Die Verbindung ist wie folgt: RJ45-Stecker am Servotreiber -> Kabel mit RJ45 an einem Ende und USB-A-Stecker am anderen Ende -> Seriell-zu-USB-Konverter -> Raspberry Pi. Der Seriell-zu-USB-Konverter und die Kabel habe ich zusammen mit dem Motor und Treiber von StepperOnline gekauft und sie sind dafür gedacht, den Servotreiber mit einem Computer zu verbinden, auf dem deren Setup-Software läuft. dmesg | grep tty auf dem Pi sagt mir, dass der USB-zu-Seriell-Konverter auf ttyusb0 ist. Ich weiß nicht, wie man das in einen COM-Port übersetzt, ich habe COM 1 genommen. Ich habe ein Projekt in Codesys erstellt und ein Modbus_COM-Gerät hinzugefügt, einen Modbus_Master_COM_Port und einen Modbus_Slave_COM_Port angehängt. Auf der Registerkarte "Allgemein" des Modbus_COM habe ich die folgenden Werte eingestellt: Slave address 1 Baud rate 9600 Parity None Data bits 8 Stop bits 2 Ich habe den Servotreiber auf die gleichen Werte eingestellt. (Ich habe auch andere Werte getestet, aber mit dem gleichen Ergebnis). Auf der Registerkarte "Modbus Slave Channel" des Modbus_Slave_COM_Port habe ich einen Kanal hinzugefügt und die folgenden Werte eingetragen: Access type Read Holding Registers (Function Code 3) Read Register offset 0x0000 Length 1 Ich habe noch keinen Code geschrieben, weil ich noch nicht herausgefunden habe, wie man die Kommunikation programmiert. Wenn ich das Projekt zum Raspberry Pi herunterlade scheint der Modbus_Master_COM_Port zu laufen (grünes Symbol), aber der Modbus_Slave_COM_Port nicht (rotes Dreiecksymbol). Wenn ich einen anderen COM-Port eintrage, haben sowohl der Master als auch der Slave das rote Dreiecksymbol. Ich habe dies auch mit meinem Windows-PC unter Verwendung von Codesys Control Win 64 versucht und die gleichen Ergebnisse bekommen. Ich wäre dankbar für jede Hilfe oder Tipps, wie ich den Grund dafür herausfinden kann, warum der Servotreiberreiber nicht reagiert.
Last updated: 2024-05-31
Post by razebones on sdo read write codesys 3.5
CODESYS Forge
talk
(Post)
ENG For some reason, I can't bind a variable to the data parameter. Also, why does only the sdo_read4 function work for me? I also can't write through sdo_write4. I can only view the received values via sdo_read4. Please help me with this task. Moreover, I tried to write the values through sdo write 4 and for a while the data stopped being written and I overwritten it manually and sdo read4 started working again and at the same time they do not want to work in the main task. RU Я не могу почему то привязать переменную к параметру data. Так же у меня почему работает только функция sdo_read4 так же не могу записать через sdo_write4. Могу только просматривать полученные значения через sdo_read4. Помогите пожалуйста с этой задачей. Причём я попытался записать значения через sdo write 4 и у меня на какое то время перестали записываться данные и перезаписал вручную и sdo read4 начал работать снова и одновременно они не хотят работать в main task.
Last updated: 2025-04-01