Post by fajean on CODESYS control on RPi starts, shortly runs, then exits CODESYS Forge talk (Post)
I have a Raspberry Pi 4 we have been using for years to run CODESYS for development purposes. I recently have had to re-install the OS (Raspberry OS lite). The only change to the default configuration is not creating the "pi" user during install. I (apparently successfully) installed the 4.10.0.0 control on the Raspberry Pi. We have licences on a dongle. I am able to start the control. systemctl status shows it as running for a little while (exactly, precisely 30 seconds as per my tests, every time), then it becomes exited. I can restart the control, and the same thing happens again. Every time. In the brief moments it is running, I can log in to the PLC. Working fast and restarting the control many times, I have been able to configure users. I have been able to download my application. I have been able to run the application, and stop on a breakpoint. I have been able to connect with the licence manager and confirm the dongle is detected and licences are listed as OK. I see nothing wrong until the service just exits. I have found nothing in the logs. It is like the runtime just terminates with no error code or message after exactly 30 seconds. Any help would be appreciated.
Last updated: 2024-06-13

Post by kaotic2499 on Upgraded Raspberry 2b to Raspberry 5, Trends Broken? CODESYS Forge talk (Post)
Hello! Raspberry pi 2b just is getting a bit slow so decided to go for a Raspberry 5. Project is now upgraded to suit Pi 64 SL... so, now although everything runs perfectly... for some reason my trends will not save! its driving me nuts... ^Tried merging tasks with main program & trends ^tried re-prioritizing tasks (shifting 1 - 31 etc) ^Recreated the Trend Recording manager from scratch ^Tried swapping persisitant vars to GVL Retains then non-retains... (Project attached is as per before trial&error) Raspberry Pi 2b still runs "perfectly" though its very chuggy (Still saves the trends, note this is of an pretty much identical project minus the device compatibility) Does anyone have any advice to offer? project attached.... I feel it could be outside of Codesys itself causing the issues, but cant see/find anything on the internet to assist (or anyone else with the same problem as me...) Can attach project in another format (non archive) any assistance is much appreciated!
Last updated: 2025-10-19

Post by vtec35 on search runtime 4.9.0.0 for pi 3 CODESYS Forge talk (Post)
yes but impossible to upload runtime 4.9.0.0 now we have put an image on the sd card with 4.13.0.0, i have 27 error message to this type, and if i test some output not work, et some work ------ Processus de compilation entamé : application : Device.HiddenOnlineConfigModeApp ------- Affecter un type à un code... [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0032: Le type 'Type inconnu : 'ADR(GVL_Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1.Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1)'' ne peut pas être converti en type 'POINTER TO IoConfigParameter' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0077: Type inconnu : 'GVL_Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1.Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0046: Identificateur 'GVL_Io_73f6cbf3_7be8_4500_8421_47e565d899a0_HPS_1' non défini [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0032: Le type 'Type inconnu : 'ADR(GVL_Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1.Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1)'' ne peut pas être converti en type 'POINTER TO IoConfigParameter' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0077: Type inconnu : 'GVL_Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1.Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0046: Identificateur 'GVL_Io_1b6dcc3b_ae11_4288_b9a9_86f9323448d1_HPS_1' non défini [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0032: Le type 'Type inconnu : 'ADR(GVL_Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4.Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4)'' ne peut pas être converti en type 'POINTER TO IoConfigParameter' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0077: Type inconnu : 'GVL_Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4.Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4' [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj 241025: C0046: Identificateur 'GVL_Io_5ae6fa5a_c197_4038_9581_03e1650806a0_HPS_4' non défini [ERREUR] conditionneuse_camphre-ssa-05-02-24-V3 maj
Last updated: 2025-10-26

Post by gatto on Backtick identifiers CODESYS Forge talk (Post)
Hello, I’m in Codesys 3.5.20.40 and I try to declare the variable ´var1´ but I get an error. here : https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_rules.html i read : Backtick identifiers By using backticks, characters can also be used in identifiers that are not normally permitted in identifiers, such as special characters. The acute accent character is used for backticks: ´ (Unicode: U+02CA) The use of backticks is recommended in order to be able to use the same identifiers in CODESYS as in other programming languages or documents, such as circuit diagrams. Any character may be used between two backticks, except line breaks and other backticks. Keywords are also allowed as identifiers between backticks. Examples: ´Variable+9´ ´INT´ The backticks are part of each identifier and therefore var1 and ´var1´ are two different identifiers. Example PROGRAM PLC_PRG VAR var1 : INT; ´var1´: INT; END_VAR var1 := var1 + 1; ´var1´ := 12; Are there any limitations or is something missing in my development environment?
Last updated: 2025-10-28

Post by nixola on CmpCharDevice blocks gpiochip access on Raspberry Pi 5 since update from SP18 to SP21 CODESYS Forge talk (Post)
Hi, I added the following lines to /etc/codesyscontrol/CODESYSControl_User.cfg: [CmpCharDevice] PermittedPath.0=/dev/i2c* PermittedPath.1=/dev/spidev* PermittedPath.2=/sys/class/gpio/* PermittedPath.3=/dev/gpiochip* However, I'm still unable to read or control GPIO pins from any CODESYS application. Specifically, setting the pin direction (and, thus, the IoDrvGpioSysfs driver configuration) fails, with a rather non-descript error in the logs: Description Component Setting direction failed for GPIO pin 586 IEC Update configuration failed from driver IoDrvGPIOSysfs CmpIoMgr I'm running CODESYS Control for Linux ARM64 SL version 4.21.0.0; it's running in rootless mode, as the codesyscontrol user, but said user is in the gpio group and can otherwise normally interact with GPIO, both via gpioset/gpioget and via the sysfs driver in /sys/class/gpio/. The system is a custom 64-bit Raspberry OS based distro, running on a Raspberry Pi CM5 on kernel 6.18.34 with PREEMPT_RT scheduling.
Last updated: 2026-07-21

Post by mrkm-dic on CODESYS: Combining Master Redundancy with EtherCAT Ring Topology – Is it Supported? CODESYS Forge talk (Post)
Hello, I would like to ask whether it is technically supported (and practically achievable) to combine CODESYS Master Redundancy with EtherCAT ring (loop) redundancy in the same system. System setup CODESYS version: CODESYS 3.5.21.40 CODESYS Control SL for Weidmuller u-OS-4.12.2.0 Controllers (Masters): Weidmuller UC20-M4000 ×2, configured as Active / Standby using CODESYS redundancy EtherCAT Slaves: Weidmuller UR20-FBC-EC ×3, supporting EtherCAT ring / line break detection Topology: EtherCAT ring (loop) Main question Is it officially supported to use: ・CODESYS PLC/Master redundancy (Active/Standby) and ・EtherCAT ring topology (for cable redundancy) at the same time? Expected behavior Our expectation is: ・When the Active PLC fails, the Standby PLC becomes Active ・The Standby PLC then takes over the role of EtherCAT Master ・EtherCAT communication is re-established ・I/O control continues after reinitialization (a short interruption is acceptable; no strict bumpless requirement) We do not expect completely seamless / zero-cycle switchover, but we want to understand: ・Whether this combination is supported by design ・Or whether there are known limitations or restrictions when EtherCAT ring mode is used together with Master redundancy Clarification At this stage, the question is mainly about feasibility and support, not about a specific error message yet. Any official guidance, limitations, or real-world experience would be greatly appreciated. Thank you in advance.
Last updated: 2026-02-05

Post by konstantin on Lenze i950 Servo and WAGO PFC200 CODESYS Forge talk (Post)
Hello, In our workshop we have a Lenze i950 servo drive that has an EtherCAT bus and CiA402 compatibility. The WAGO is PFC200 750-8212 and as per documentation it has built-in license for SoftMotion Light functionality. It is not capable of supporting the full SoftMotion functionality like gearing and synchronizing. I added the EtherCAT esi files from Lenze and the EtherCAT master does see the drive, then I added a SoftMotion Light Axis object. The problem is that I can only energize the axis, I cannot execute any other commands. I set the positive and negative torque limits from the PDOs to 200% and when I try to move the axis by force it does not move back to its original position. I use the SML function blocks from the PLCOpen library and the error from the function blocks is that the op mode cannot be changed. Then I tried using a standard SoftMotion axis object and everything works fine, except the MC_Home function block. The axis moves back to its position when forced out of it. I follow this guide from Lenze - Lenze i950 CODESYS V3 What could cause this issue with the SoftMotion Light axis object? Best Regards Konstantin Kolev
Last updated: 2026-02-11

Post by pernockham on Gateway in China - "Gateway not connected" CODESYS Forge talk (Post)
Some new test. Now I cannot connect from Automation server to my gateway in any way also from my office setup with my unit directly connected to my router by dhcp. I can use the IDE and the tool "Connect Edge Gateway" and successfully connect to my server/link to my Automation server account. However no PLC will respond from Automation server "Network scan". I guess the traffic should be initiated by the gateway towards automation server? Any tips on how I can diagnose my problem? Ports to be opened etc? Thing is that this has been working previously but not now (base system has been updated from debian 12 to debian 13, but I dont know at which point it has stopped working). Setup as before. A "Codesys Control for Linux SL" running on a debian 13 installation. Any help/tips appreciated! Per Update. Found the error. Had a wrong gateway-setting. Which meant the PLC could not reach internet. Checked by "ping google.com" from the PLC.
Last updated: 2026-02-12

Post by konstantin on CAM Motion Recover after STO CODESYS Forge talk (Post)
Hello Mr. Seidel, both the master and the slave axis are modulo. Basically the situation is as follows: One master cycle is 100 units. Slave's modulo length is 2000 units. In the CAM table I defined 10 master cycles on X axis - 1000 units and on the Y axis is the slave - 2000 units. Then depending on the master position 0 to 1000 units the slave's position is plotted on the Y axis - 0 to 2000 units. For example, while the master is executing the 3rd cycle i.e. above 200 units, I trigger the STO function of the slave and it stops. The master executed his cycle but the slave was stopped during the execution. How can I set the slave to continue the CAM sequence from the point where it stopped i.e. third cycle of the master? When I reset the slave error and sync again, everyrhing starts from master's 0 position. Best Regards Konstantin Kolev
Last updated: 2026-02-13

Post by egr99 on Modbus TCP Server connection is ESTABLISHED but all holding registers are value 0? CODESYS Forge talk (Post)
Hi there, Read the above description and experienced the same: Reading coil/discrete input/input register/holding register doesn't fill the mapped I/O variable. Any suggestions? Defined (see attachment): - Ethernet (with parameters according to the used Ethernet adapter of my Windows 11 laptop) - -Modbus TCP Client - - -LOGO231 as Modbus TCP Server - - -WS242 as Modbus TCP Server (WaveShare Modbus TCP <-> RTU converter) - - - -WS242_01 as Modbus Server, COM port (slave-id 1 RTU) - - - -WS242_03 idem (slave-id 3 RTU) - - - -WS242_11 idem (slave-id 11 RTU) Writing coil/holding register works from a mapped I/O variable works fine. Verification of Modbus traffic with WireShark: QUERY to and the RESPONSE of all slave-ids are correct Status of all defined is CONNECTED, RESPONSE_SUCCESS, RUNNING etc. Request counters increase with expected frequency. Error counter = 0. (To have all counters works fine I had to change Modbus TCP Client's parameter OptimizationON to FALSE). LOGO231 works fine: values in mapped I/O conform expectation WS242 without Modbus Server, COM port and with defined channels (for only 1 slave-id possible) works fine. PLC Settings: Update I/O while in stop: I see xBusy changing from FALSE to TRUE and vice versa. Always update variables: Enabled 1
Last updated: 2026-04-05

Post by gseidel on Mismatch between coordinate monitor and actual motion using SMC_GroupJog2, MC_MoveLinearAbsolute (6DOF) CODESYS Forge talk (Post)
Hi darwin03, when all joints are 0°, then the 6-axis robot is in a so called singularity. This means that it is in a special position where it cannot move freely in all directions but is restricted by its own construction. For a simple example, imagine a scara robot where the arm is fully stretched. In this position it cannot move freely. You can find a lot of information about robot configurations in the www. As far as CODESYS SoftMotion Robotics is concerned, this page holds the most important links, look for the error SMC_CP_CONFIGS_DIFFER: https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_robotics_errors.html The most important rules: 1) CP movements (linear moves, circular moves, cartesian jogging) cannot change the configuration during the movement. Both start- and endpoint must be in the same configuration. This excludes also the edge case that one or both of them are in a singularity. 2) PTP movements can move through singularities and cross configurations without problems. 3) SMC_SetKinConfiguration can be used to set the configuration of the axis group. Regards, Georg
Last updated: 2026-05-04

Post by hhermsen on Codesys v3.5.22.10 - Internal error:System.AggregateException...Value cannot be null...Parameter name: expLValue CODESYS Forge talk (Post)
I pinpointed down 4 possible causes for this compiler error: Bare/empty statements (;) standing alone inside an IF/CASE branch — just removed two instances. The optimizer that tries to inline/replace expression statements may choke when a statement has no actual assignment to extract. A VAR_IN_OUT parameter used directly as a FOR loop's own control variable (FOR X := X TO Y DO) General deep-nesting complexity — every one of my decode routines has the same shape (IF busy THEN ... FOR loop containing nested CASE/IF chains ... END_IF), and the crash trace consistently shows for loop → sequence → ifst → sequence → ifst → sequence regardless of the code change. This raises the possibility that it's not one specific statement but a structural depth/complexity limit in SP22.x's compiler optimizer — which would mean no small code change fixes the issue. Only restructuring to reduce nesting depth, or downgrading the compiler will. Something entirely outside my library files — which cannot not ruled out since the exact stack trace was triggered by a Visualization object, in a totally different codebase. This means the same crash signature can come from unrelated causes. IMHO cause 3 seems the most probable one..
Last updated: 2026-07-11

Post by alexschooneveld on OPC UA PubSub SL 1.3 — UADP WriterGroup with assigned PSS.SecurityGroup still publishes plaintext CODESYS Forge talk (Post)
I am currently investigating an OPC UA PubSub connection over UDP. When I don't use encryption, the publish and subscribe are working correctly. But with encryption it does not. Environment OPC UA PubSub SL 1.3.0.0 (namespace UADP) OPC UA PubSub Security 1.3.0.0 (namespace PSS) OPC UA PubSub Base 1.3.0.0 (namespace PSB, incl. PSS.SecurityGroup / PSS.CONFIG) Programmatic PubSub in a CFC: UADP.Configuration → UADP.Connection → UADP.writerGroup → UADP.writer → writerDataSet, plus a CyclicCall gated by xEnable. Goal: publish secured UADP, SignAndEncrypt, policy PubSub-Aes256-CTR. What I do (one-shot, before xEnable := TRUE): fbSecurityGroup.SetInitialValue( 'http://opcfoundation.org/UA/SecurityPolicy#PubSub-Aes256-CTR', PSB.SECURITY.SIGNING_AND_ENCRYPTION); stSecurityCfg := fbSecurityGroup.GetConfig(eErrorID => eError); // eError=NO_ERROR, udiEncryptionKeySize=32 eError := fbSecurityGroup.SetSecurityKeys(udiTokenId, ADR(abyKey), SIZEOF(abyKey), 2436001000); // eError=NO_ERROR, SIZEOF=68 // writerGroup.itfSecurityGroup := fbSecurityGroup -- set in the WriterGroup block's Parameters (a per-scan code write got overwritten) What I verified eError = NO_ERROR after both GetConfig and SetSecurityKeys; udiEncryptionKeySize = 32. Key length = 68 bytes (signing 32 ‖ encrypt 32 ‖ nonce 4). itfSecurityGroup is set via the WriterGroup's Parameters (so it isn't clobbered each scan). Init runs before xEnable (the writer doesn't run with xEnable=FALSE). The UADP.writerGroup FB exposes only itfSecurityGroup for security — no SecurityMode/MessageSecurityMode property. Result: the published datagrams are still plaintext — ExtendedFlags1 = 0x01 (security bit 0x10 clear), no security header: b1 01 29 00 0f 16 00 … (PublisherId 41, WriterGroupId 22, RawData, no security) Questions With UADP.writerGroup, is assigning a configured + keyed PSS.SecurityGroup to itfSecurityGroup sufficient to enable message security, or is there an additional step/property/method to switch the WriterGroup to SignAndEncrypt? At what point in the WriterGroup lifecycle is itfSecurityGroup read? Must it be assigned/keyed before xActive, and does the group need a stop→start to pick it up? Is there a required call order, and does SetSecurityKeys need to be called once or repeatedly? Should security be configured on the Connection/Configuration level rather than (or in addition to) the WriterGroup? Is there a working example of secured (SignAndEncrypt) programmatic UADP publishing with this library, or a known limitation in 1.3? How can I read back at runtime whether security is actually active (via itfDiagnostics or similar)? Additional information I can confirm that the consumer side works — i.e. a standard subscriber decrypts the same keys fine — so the keys/profile aren't the issue. The Wireshark capture of the published message is: 0000 b1 01 29 00 0f 16 00 df 0d bb 25 01 00 0e 00 1b ..).......%..... 0010 0e 00 00 00 00 00 00 00 ........
Last updated: 2026-06-22

Post by alexschooneveld on OPC UA PubSub SL 1.3 — UADP WriterGroup with assigned PSS.SecurityGroup still publishes plaintext CODESYS Forge talk (Post)
I am currently investigating an OPC UA PubSub connection over UDP. When I don't use encryption, the publish and subscribe are working correctly. But with encryption it does not. Environment OPC UA PubSub SL 1.3.0.0 (namespace UADP) OPC UA PubSub Security 1.3.0.0 (namespace PSS) OPC UA PubSub Base 1.3.0.0 (namespace PSB, incl. PSS.SecurityGroup / PSS.CONFIG) Programmatic PubSub in a CFC: UADP.Configuration → UADP.Connection → UADP.writerGroup → UADP.writer → writerDataSet, plus a CyclicCall gated by xEnable. Goal: publish secured UADP, SignAndEncrypt, policy PubSub-Aes256-CTR. What I do (one-shot, before xEnable := TRUE): fbSecurityGroup.SetInitialValue( 'http://opcfoundation.org/UA/SecurityPolicy#PubSub-Aes256-CTR', PSB.SECURITY.SIGNING_AND_ENCRYPTION); stSecurityCfg := fbSecurityGroup.GetConfig(eErrorID => eError); // eError=NO_ERROR, udiEncryptionKeySize=32 eError := fbSecurityGroup.SetSecurityKeys(udiTokenId, ADR(abyKey), SIZEOF(abyKey), 2436001000); // eError=NO_ERROR, SIZEOF=68 // writerGroup.itfSecurityGroup := fbSecurityGroup -- set in the WriterGroup block's Parameters (a per-scan code write got overwritten) What I verified eError = NO_ERROR after both GetConfig and SetSecurityKeys; udiEncryptionKeySize = 32. Key length = 68 bytes (signing 32 ‖ encrypt 32 ‖ nonce 4). itfSecurityGroup is set via the WriterGroup's Parameters (so it isn't clobbered each scan). Init runs before xEnable (the writer doesn't run with xEnable=FALSE). The UADP.writerGroup FB exposes only itfSecurityGroup for security — no SecurityMode/MessageSecurityMode property. Result: the published datagrams are still plaintext — ExtendedFlags1 = 0x01 (security bit 0x10 clear), no security header: b1 01 29 00 0f 16 00 … (PublisherId 41, WriterGroupId 22, RawData, no security) Questions With UADP.writerGroup, is assigning a configured + keyed PSS.SecurityGroup to itfSecurityGroup sufficient to enable message security, or is there an additional step/property/method to switch the WriterGroup to SignAndEncrypt? At what point in the WriterGroup lifecycle is itfSecurityGroup read? Must it be assigned/keyed before xActive, and does the group need a stop→start to pick it up? Is there a required call order, and does SetSecurityKeys need to be called once or repeatedly? Should security be configured on the Connection/Configuration level rather than (or in addition to) the WriterGroup? Is there a working example of secured (SignAndEncrypt) programmatic UADP publishing with this library, or a known limitation in 1.3? How can I read back at runtime whether security is actually active (via itfDiagnostics or similar)? Additional information I can confirm that the consumer side works — i.e. a standard subscriber decrypts the same keys fine — so the keys/profile aren't the issue. The Wireshark capture of the published message is: 0000 b1 01 29 00 0f 16 00 df 0d bb 25 01 00 0e 00 1b ..).......%..... 0010 0e 00 00 00 00 00 00 00 ........
Last updated: 2026-06-22

Post by cfam on Codesys Control for PLCnext (PLC - AXL F 2152) CODESYS Forge talk (Post)
Good day All I would like to share some information on this site for the Codesys team as well for the future members using Codesys Control for PLCnext if it is allowed. I hope that i Post it in the correct spot. Subject: Codesys, Codesys Control for PLCnext Objective: Using the following Phoenix components to built a PLC Rack and run it on Codesys: Hardware and Software used 1. 2404267, AXC F 2152 - Controller 2. 1088136, AXL F BP SE6 - Module carrier 3. 1088129, AXL SE DO16/1 - Digital module 4. 1337224, AXL SE PD16 GND - Potential distributors 5. 1088127, AXL SE DI16/1 - Digital module 6. 1337223, AXL SE PD16 24V - Potential distributors 7. 1088123, AXL SE AO4 I 4-20 - Analog module 8. 1088134, AXL SE SC-A - Cover 9. Codesys v3.5 SP19 Patch 4 10. Codesys Control for PLCnext V4.10.0.0 Process: Firstly I built the Rack according to the Phoenix Project+ Software tool. Where I rebuilt it onto my test bench . I used the PLCnext Engineer IDE from Phoenix and all Communications where up and running and my PLC program executed successfully. THEN I tried the same PLC Layout with Codesys and Codesys Control for PLCnext. It was not successful and gave me the "Error: Local Bus not Running". I searched the web for answers but was unsuccessful in finding a solution. So I tried to change my configuration and found that the following Modules COULD NOT be recognized by Codesys Control. The result was that the Local Bus Failed to run. 1337224, AXL SE PD16 GND - Potential distributors 1337223, AXL SE PD16 24V - Potential distributors Example 1, Resulted in "Error: Local Bus Not Running": Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module Module carrier slot 2: 1337224, AXL SE PD16 GND - Potential distributors Module carrier slot 3: 1088127, AXL SE DI16/1 - Digital module Module carrier slot 4: 1337223, AXL SE PD16 24V - Potential distributors Module carrier slot 5: 1088123, AXL SE AO4 I 4-20 - Analog module Module carrier slot 6: 1088134, AXL SE SC-A - Cover Example 2, Result "Successful": Module carrier slot 1: 1088129, AXL SE DO16/1 - Digital module Module carrier slot 2: 1088127, AXL SE DI16/1 - Digital module Module carrier slot 3: 1088123, AXL SE AO4 I 4-20 - Analog module Module carrier slot 4: 1088134, AXL SE SC-A - Cover Module carrier slot 5: 1088134, AXL SE SC-A - Cover Module carrier slot 6: 1088134, AXL SE SC-A - Cover Result: Codesys or Codesys Control for PLCnext, has a PROBLEM to identify the following Modules. 1. AXL SE PD16 24V - Potential distributors 2. AXL SE PD16 GND - Potential distributors Hope that this information could be useful in future. Best regards Jaco Pretorius
Last updated: 2023-12-06

Post by ryandmg on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS) CODESYS Forge talk (Post)
Hey Everyone, I'm having a bit of a struggle finding settings that will reliably maintain a connection between the webvisu and a touchscreen client. Every so often the HMI disconnects and will perpetually display the red spinning arrow with the "Error Happened, Will resume automatically" text. Power cycling the HMI to force a reconnect will re-establish comms. It seems to happen during periods of inactivity if that's a clue. From what I've gathered so far this seems to have something to do with the webvisu update rate, buffer size as well as the visu task scan rate. We first tried the default settings as follows: Webvisu Update Rate: 200 ms Webvisu Buffer Size: 50,000 Visu Task Scan Rate: 100 ms Priority 31 Other Tasks for Reference: Main Task Scan Rate: 100 ms Priority 1 Alarm Manager Scan Rate: 50 ms Priority 31 Ethercat Task: 4 ms Priority 1 This would disconnect some what regularly. We then made the following changes to try and stabilize: Webvisu Update Rate: 150 ms Webvisu Buffer Size: 75,000 Visu Task Scan Rate: 75 ms Kept other tasks the same. This seems to disconnect even more frequently. Also for reference the network is very small and only consists of the PLC, a small switch and the HMI. We're also not controlling frames from outside the visu program itself. The frame changes are all done natively. Any suggestions to get this to stop disconnecting? Oh and whatever the issue is the log does not record it. Figured I would ask here before opening a ticket. Thanks in advance for your help!
Last updated: 2023-09-06

Post by fmon on Modbus : dis- / re-connect cable: modbus does not re-start CODESYS Forge talk (Post)
Hello, I am using codesys Modbus TCP client (4.4.0.0) to communicate with a python modbus server (package pyModbusTCP). I first start my python server on the distant machine. After a fresh codesys compilation, a plc connection/transfer and a PLC run, the modbus connection is OK. Every time in this context the connection is created correctly. When I shut down the server, the modbus connection falls, that is normal. When I restart the python server, impossible to recreate the modbus connexion. With the client autoreconnection, I see on my server that the client tries to connect but unsuccesfully. I have the following message : DEBUG:pyModbusTCP.server:accept new connection from ClientInfo(address='192.168.1.20', port=33476) DEBUG:pyModbusTCP.server:Exception during request handling: NetworkError('recv return null') I tried to stop the codesys client and to restart it with these commands : Modbus_TCP_Client.xStop := True; // Or False Modbus_TCP_Client.Enable := True; // Or False Modbus_TCP_Server.Enable := True; // Or False I tried to confirm the error manually to force reconnection with: Modbus_TCP_Server_Motors.xConfirmError := TRUE; I tried also this command to STOP/RESET/START client and server (codesys side) but nothing happens : status_client := Modbus_TCP_Client.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.STOP); // .RESET & .START The answer of this function when executed is "status_client = NOT_SUPPORTED" It seems that is a socket problem, but I do not understand if it is on the client or server side. I tried a modbus simulator called "ananas.exe" and the result is the same. Impossible to get a modbus reconnection. What is different at the first connection and at a reconnection attempt ? Thanks for your help
Last updated: 2025-03-14

Post by fmon on Modbus TCP client reconnection problem CODESYS Forge talk (Post)
Hello, I am using codesys Modbus TCP client (4.4.0.0) to communicate with a python modbus server (package pyModbusTCP). I first start my python server on the distant machine. After a fresh codesys compilation, a plc connection/transfer and a PLC run, the modbus connection is OK. Every time in this context the connection is created correctly. When I shut down the server, the modbus connection falls, that is normal. When I restart the python server, impossible to recreate the modbus connexion. With the client autoreconnection, I see on my server that the client tries to connect but unsuccesfully. I have the following message : DEBUG:pyModbusTCP.server:accept new connection from ClientInfo(address='192.168.1.20', port=33476) DEBUG:pyModbusTCP.server:Exception during request handling: NetworkError('recv return null') I tried to stop the codesys client and to restart it with these commands : Modbus_TCP_Client.xStop := True; // Or False Modbus_TCP_Client.Enable := True; // Or False Modbus_TCP_Server.Enable := True; // Or False I tried to confirm the error manually to force reconnection with: Modbus_TCP_Server_Motors.xConfirmError := TRUE; I tried also this command to STOP/RESET/START client and server (codesys side) but nothing happens : status_client := Modbus_TCP_Client.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.STOP); // .RESET & .START The answer of this function when executed is "status_client = NOT_SUPPORTED". Is it normal ? It seems that is a socket problem, but I do not understand if it is on the client or server side. I tried a modbus simulator called "ananas.exe" and the result is the same. Impossible to get a modbus client reconnection. What is different at the first client connection and at a reconnection attempt ? Thanks for your help
Last updated: 2025-03-17

Post by jeindhoven on Deploying to raspberry pi 5 hangs CODESYS Forge talk (Post)
Yep sure, though now that i think of it, its a pi 4. My bad. The whole ordeal was necessary to use the VGA666 adapter. That needs the old graphical system and GPIO directly on the CPU. Edit: Putty on the virtual development machine connects fine. But i did change the login/pw. The account is still a sudo'er so that should be all right. Edit2: Sorry i get a "Comment rate limit exceeded" from the forum. Then i'll add it as edit here. So i have tried the stock raspberry pi image on a different pi5 (truly 5 this time). Packages updated. Standard password. Same symptoms, no runtime deployed and long hang time. Versions of this pi: pi@raspberrypi:~ $ uname -a Linux raspberrypi 6.12.25+rpt-rpi-2712 #1 SMP PREEMPT Debian 1:6.12.25-1+rpt1 (2025-04-30) aarch64 GNU/Linux pi@raspberrypi:~ $ lsb_release -a No LSB modules are available. Distributor ID: Debian Description: Debian GNU/Linux 12 (bookworm) Release: 12 Codename: bookworm pi@raspberrypi:~ $ apt list --installed | grep openssh-server openssh-server/stable,now 1:9.2p1-2+deb12u6 arm64 [installed,automatic] Attached is the Device information and error text that Codesys comes up with. Edit 3 (Comment rate limit, otherwise it would be a new post) Now i have tried booting an older native Windows 10 machine (no virtualization), and it just works as expected. I have now a raspberry pi 4 and raspberry pi 5 with version 4.16.0.0 of the control application. Windows 10 native: build 19045 (same as virtualised Win 10), same .NET version, same CODESYS version. It seems that running CODESYS virtualized somehow messes with the deployment?
Last updated: 2025-06-23

Post by serwis on Dynamic target position tracking CODESYS Forge talk (Post)
Hello, I am trying to control a servo drive and dynamically set its position. I control the drive via EtherCAT with a cycle time of 500us. I use the MC_MoveAbsolute block for this. The problem is that when using a PID controller, I generate the positions I want the drive to move to on an ongoing basis, and I would like the position to be set immediately. The MC_MoveAbsolute block must receive a rising edge to execute, and I would like the movement to be performed without waiting for this edge. I have created a function that generates a rising edge every 1 ms, but I am unable to change this time to 500 µs because the TON function does not support times shorter than 1 ms. Below is the code to call the rising edge: IF Exe = TRUE THEN delay1(IN:=TRUE, PT:=T#1MS); IF delay1.Q = TRUE THEN Exe := FALSE; delay1(IN:=FALSE); END_IF END_IF IF Exe = FALSE THEN delay(IN:=TRUE, PT:=T#1MS); IF delay.Q = TRUE THEN Exe := TRUE; delay(IN:=FALSE); END_IF END_IF END_IF Here is the code for calling the MC_MoveAbsolute function: MoveDegree( Axis:= Tilt, Execute:= Exe, Position:= position_target - (base_angle_real * feedforward_turn), Velocity:= vel, Acceleration:= acc, Deceleration:= dec, Jerk:= jerk, Direction:= MC_DIRECTION.shortest, BufferMode:= MC_BUFFER_MODE.Aborting, Done=> , Busy=> , Active=> , CommandAborted=> , Error=> , ErrorID=> ); I realize that there are probably better methods for performing this type of task. How can I implement motion with a dynamically changing setpoint? THANKS
Last updated: 2025-09-05

Post by cer-wa on Not able to connect multiple profinet encoder in codesys Linux ARM64 CODESYS Forge talk (Post)
Hello, currently im working with a RevPi connect 5 on a codesys project. Up until now I was having a blast because things were going really smooth but for like almost a day im kind of stuck on the integration of multiple profinet sensors into my project. This is kind of a bummer because that should be an easy thing to do. What I tried so far was to create and additional ethernet adapter where I then tried to connect my devices. in the beginning I tried to connect the devices directly which was not working because I could assign the IP-adress only to the ethernet adapter and not to the devices but the device was found in the device repository (this gets important in the second part) So what I tried next was to setup a PN-Controller and connect my devices subsequently to the Controller. Sadly now the devices wont show up in the device repository anymore. To me its not clear why this is happening. And the worst thing is: I went ahead and setup a device completely like I would want to have it in the project and when I then click on scan devices I can even find the device. But it can not be added to project for whatever reason eventhough im 100% certain that the gsdml file is the correct one. Can anyone help me with this. Like I said this seems like an easy thing to do and its taking me way longer than expected already. The only thing that came to my mind why this might not work is because I have codesys license which only allows one profinet instance. Could that be the case? The error message seems then pretty unfit but ok. I will be grateful for every advice. Thanks in advance! Best regards!
Last updated: 2025-09-25

Post by tk096 on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup CODESYS Forge talk (Post)
Hi, under this circumstances the performance of a Raspberry Pi 4 should be sufficient to run a Softmotion robotics application. A closer look at the project would be required. Maybe you could contact the codesys support? Usually it is recommended to run the planning task cyclically every 2ms with task priority of 0 on a dedicated core. In the task configuration you can have a look at the average and maximum execution time of the planning task. You could use the function block SMC_TuneCPKernel (https://content.helpme-codesys.com/en/libs/SM3_Robotics/Current/SM3_Robotics/POUs/AdministrativeConfiguration/Computation/SMC_TuneCPKernel.html) to define suitable values for the parameters 'fSyncBufferDuration' and 'fPlanningInterval'. However, as previously mentioned, the performance of a Raspberry Pi 4 with realtime patch should be sufficient. The 'fPlanningInterval' parameter specifies the maximum planning step width in seconds. The cycle time of the planning task should not permanently exceed this value. A higher value reduces the computational effort, but can lead to a violation or no full utilization of the set limit values for velocity, acceleration and jerk. From a starting value of 0.016 seconds, the value should be increased gradually until the performance is acceptable. The parameter 'fSyncBufferDuration' specifies the size (in seconds) of the buffer between the planning and fieldbus task. The cycle time of the planning task must not exceed this value at peak times (this will lead to the error SMC_CP_QUEUE_UNDERRUN). A higher value can compensate for peaks in the cycle time of the planning task. At the same time, however, this also increases the latency for executing interrupts and aborting movements.
Last updated: 2024-03-22

Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins CODESYS Forge talk (Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15

Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins CODESYS Forge talk (Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15

Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins CODESYS Forge talk (Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15