Post by talhaali on Alarm status in logic CODESYS Forge talk (Post)
Hi, I am trying to access active alarms in code(As alarm count variable updates only when we go to to alarm table frame in visualization). I wrote following code but it is not working: VAR iCountActiveAlarms : INT; parritfActiveAlarms : POINTER TO ARRAY[0..0] OF IAlarm; itfAlarmManagerClientAll : IAlarmManagerClient; END_VAR AlarmManager.g_AlarmHandler.GetActiveAlarms( itfAlarmManagerClient :=itfAlarmManagerClientAll, iCountActiveAlarms => iCountActiveAlarms, parritfActiveAlarms => parritfActiveAlarms); The Value is always 0. Please help.
Last updated: 2024-06-06

Post by nano on How to access to variable value through symbolic string name CODESYS Forge talk (Post)
this is not easily. From Point of SL-Licenses Codesys didnt provide the informations how to do. We created an own CDS-Component for that Behaviour. This Informations are available for OEM, if you are an OEM you can find the Informations in the RTS-Documentation.
Last updated: 2024-06-14

Post by koppit on SysComRead Timeout Parameter CODESYS Forge talk (Post)
Im using SysCom ver. 3.5.17.0 and seem to have the same issue on a Raspberry Pi. It's not waiting for the requested number of bytes, no matter if "ulTimeout := SYS_INFINITE" or any other value. The only solution I have found is to stall the program to allow the serial port to recieve the data.
Last updated: 2024-06-26

Post by stiller on OPC UA RPI 4.8.0.0 Status Code / "out of range" CODESYS Forge talk (Post)
Hello, I have an OPC-UA server with an information model. For many values, there is a defined range (e.g., 0 to 100). If a client enters a value outside this range (e.g., 120), the StatusCode should change to Bad. How can I accomplish this? Any help is appreciated! Thank you in advance. Best regards, Christian Stiller
Last updated: 2024-07-10

Post by mmpl on Array to String CODESYS Forge talk (Post)
I would like to create one large JSON string from an array of objects, where each object contains a value. My current approach involves using a for loop and string concatenation, but with 20,000 elements in the array, this method takes almost 7 seconds and negatively affects the PLC scan time. Is there a more efficient way to accomplish this?
Last updated: 2024-07-18

Post by mmpl on Array to String CODESYS Forge talk (Post)
I would like to create one large JSON string from an array of objects, where each object contains a value. My current approach involves using a for loop and string concatenation, but with 20,000 elements in the array, this method takes almost 7 seconds and negatively affects the PLC scan time. Is there a more efficient way to accomplish this?
Last updated: 2024-07-18

Post by timvh on RAMP_REAL FB is retaining my output value when i try to re use the FB CODESYS Forge talk (Post)
I think, that if you set the timebase to T#0s, that it will be reset. But you can also make your own ramp down with a Timer (make sure the PT time is not T#0s):
Last updated: 2024-07-29

Post by danieldiaz on Problem with FB execution CODESYS Forge talk (Post)
Hello everyone, I've been working on a system which needs an error function, with this purpose I've created a FB programmed in LD, after debugging I run the simulation. It seems that the variable linked to a coil doesn't change the value when the contacts are associated to input variables. When I use internal variables the logic works properly. I don't know if the problem is related to the variables definition or with the logic program. As you can see in the image, I1 and I2 are variables declared on the FB, the rest are input variables. If I force the eStop and Reset signals to TRUE the coil value should change, but it doesn't. However in the second network if I1 is TRUE the coil change to TRUE as it has to be. To sum up, my doubt is why that coil doesn't change its value? I would like someone to shed a light on this. Thanks!
Last updated: 2024-04-02

Post by duvanmoreno24 on Modbus writing on value change CODESYS Forge talk (Post)
Yes, I tried to do what you put in the first code. However, I have a problem with that and that is that the inputs must be declared with the type. I have many data types running in my code (real, int, uint, bool) and I can't put them in the same function, another thing is that I need to instantiate that function for everything I want to write to the slave. You put a for to 200 but it means that it has to be the same data type and inside the array, but I want to get them individually. I'm struggling to do it in a good and efficient way like wago's E-cockpit does. in the first screenshot you can see, you simply type in value, change the package of things you want to write in value change and it does everything by itself automatically, without comparing any old and new values and even less having the need to activate a bool. , it is perfect.
Last updated: 2024-04-03

Post by k2saki on CNC / G01 Speed is very slow (or go-stop motion) in Continuous short segment . CODESYS Forge talk (Post)
I'm using CAD/CAM that outputs GCode with G01 many short segments from NURBS Curve, only X-Y axis. But CODESYS CNC motion seems much slower ( or stop-go motion ) in simulation mode than F-Value (I checked value from SMC_Interpolator - dVel ). In GCode G01, F value is F500, but movement is very slow, actual speed (dVel) is between 0 to 30 back and forth. I think very old CNC can move like that, but nowadays, a lot of CNC can move smoothly to process free curve ( somethimes option switch ) I tried to use G51 Dxx but I got the same result. My questions are 1) How do I improve CODESYS CNC motion in this case ? 2) How can I graph the sampling from dVel of SMC_Interpolate in CODESYS? From my GCode N2006 G01 X1.4364 Y-14.6847 F500 N2007 G01 X1.6759 Y-14.6768 N2008 G01 X1.9152 Y-14.6486 N2009 G01 X2.1547 Y-14.6400 N2010 G01 X2.3943 Y-14.6090 N2011 G01 X2.6336 Y-14.6002 N2012 G01 X2.8732 Y-14.5716 N2013 G01 X3.1127 Y-14.5634 N2014 G01 X3.3520 Y-14.5410 N2015 G01 X3.5915 Y-14.5336 N2016 G01 X3.8308 Y-14.5307 ... Thansk.
Last updated: 2024-04-29

Post by xgongx on What is the insights of IoDrvEtherCAT.DCInSyncWindow? CODESYS Forge talk (Post)
It is well known that you need to increase the value of IoDrvEtherCAT.DCInSyncWindow to solve the "Fieldbus lost synchronicity" issue. In the official document, IoDrvEtherCAT.DCInSyncWindow is explained as the toleration of a certain jitter. But the official document doesn't explain what kind of the jitter is. Is it the jitter of DC sync deviation, master timer or something else? It is very important to know the insights of IoDrvEtherCAT.DCInSyncWindow. For example, if it is the toleration of DC sync deviation, and the official recommending value is 200us for CODESYS SoftMotion. It means maximum of DC sync deviation is 200us. It is unacceptable for some high precision motion control tasks, for example high speed gear task, etc. Increasing the value of IoDrvEtherCAT.DCInSyncWindow will increase the deviation of motor rotation sync if it is the toleration of DC sync deviation. So, would anyone tell me what the insights of IoDrvEtherCAT.DCInSyncWindow is? Thanks.
Last updated: 2024-07-09

Post by imdatatas on MC_CamIn did not work properly with SMC_FreeEncoder on SoftMotion 4.17.0.0 CODESYS Forge talk (Post)
Hello, I am facing a problem with the new Softmotion 4.17.0.0 version. Has anyone encountered a similar problem, what is the solution? I would be happy if you could share it. Problem description: -- "SMC_FreeEncoder" encoder axis is the master, -- The motor of the servo driver on the EtherCAT bus is the slave axis. -- When the MC_CamIn block executed, the InSync output is activated. However, although the master encoder axis position value changes, there is no movement in the slave servo axis! Test steps: 1-) EtherCAT servo axis installed, configured and motion test was performed with MC_Jog. No problem. 2-) Softmotion general axis pool > SMC_FreeEncoder was added and pulse amount configuration was performed. No problem. 3-) Incremental encoder actual count value was transferred to the "SMC_FreeEncoder.diEncoderPosition" variable as DINT under the ethercat task in every cycle and the encoder axis position value was observed. No problem. 4-) A simple CAM table with a 1:1 ratio was created under the project tree. (For example: Simply, when the encoder rotates 1 turn, the motor will rotate 1 turn.) 5-) The SMC_FreeEncoder axis enabled with MC_Power and brought to the StandStill state. 6-) The MC_CamTableSelect block was run with default input values ​​(all absolute) and only the Cam table name was specified. The Done output was seen successfully. No problem. 7-) The MC_CamIn block was activated with default input values ​​(absolute) and only the master encoder axis name, slave servo axis name, CamTableID input pins was specified and then "Execute" input set to TRUE. 8-) The InSync output information of the MC_CamIn block observed as TRUE. However, although the encoder axis value changed, the position value of the slave axis did not change at all, it did not move. It always remained at 0.0mm. 9-) When I repeated the same steps above, only changing the master axis to SM_Drive_Virtual instead of FreeEncoder and gave movement to the virtual axis, this time the slave axis moved successfully. However, when the same steps and operations are performed with the same IDE just downgrade SoftMotion version from 4.17.0.0 to 4.10.0.0, everything works normally and without problems as expected in MC_CamIn block with FreeEncoder master. (By the way, The used IDE version is Codesys V3.5 SP20patch3.) Best Regards Imdat
Last updated: 4 days ago

Post by elektron785 on Dongle von Linux-Modul (ARM64) nicht erkannt CODESYS Forge talk (Post)
Ich hatte noch einmal Zeit das mit der Lizenz zu probieren und habe dazu über den Codesys Installer das Virtual Control SL runtergeladen und ausprobiert, aber leider ohne Erfolg. Zunächst habe ich "Docker_codesyscontrol_virtuallinuxarm64_4.13.0.0_arm64.tar.gz" aufs Board geladen und das Image mit docker load geladen. Mit dem Befehl docker run --rm -dt --name codesys --network host -v /dev:/dev -v /tmp:/tmp -v /run/udev/:/run/udev/ --device-cgroup-rule='c 13: rmw' --privileged 470a708f17a2 hab ich dies dann ausgeführt, aber das Problem, dass ich das Board im Netzwerk dann nicht finden konnte. Damit ich die Verbindung herstellen konnte, habe ich die Datei "DockerRuntimeStart.sh" so verändert, dass ich den Teil: -p 11740:11740/tcp \ -p 443:443/tcp \ -p 8080:8080/tcp \ -p 4840:4840/tcp \ gegen --net host \ ersetzt habe. Das Skript habe ich dann aufs Board geladen und bash DockerRuntimeStart.sh -i codesyscontrolvirtuallinuxarm64:4.13.0.0 -c codesys -H verdin-imx8mp- ausgeführt. Nun konnte ich in Codesys wieder eine Verbindung zu dem Board aufbauen, aber der Dongle wird leider immer noch nicht im Lizenz-Manager erkannt. Wie kann ich denn prüfen, dass auf den USB-Stick vom Container aus zugegriffen werden kann?
Last updated: 2024-09-23

Post by umdee on Error when monitoring LAD programs CODESYS Forge talk (Post)
I get the following error when monitoring my program (see attached screenshots): "Unhandled exception has occured in your application. If you click Continue, the application will ignore this error and attempt to continue. If you click Quit, the application will close immediately. Value cannot be null. Parameter name: source. And the details say: See the end of this message for details on invoking just-in-time (JIT) debugging instead of this dialog box. ** Exception Text ** System.ArgumentNullException: Value cannot be null. Parameter name: source at System.Linq.Enumerable.Any[TSource] (IEnumerable1 source, Func2 predicate) at _3S.CoDeSys.NWLEditor.NWLTextCell.OnPaintCellLayer(PaintEventArgs e) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.OnPaint(PaintEventArgs e) at System.Windows.Forms.Control.PaintWithErrorHandling(PaintEventArgs e, Int16 layer) at System.Windows.Forms.Control.WmPaint(Message& m) at System.Windows.Forms.Control.WndProc(Message& m) at System.Windows.Forms.UserControl.WndProc(Message& m) at _3S.CoDeSys.Controls.Controls.GfxEdControl.WndProc(Message& m) at System.Windows.Forms.NativeWindow.Callback(IntPtr hWnd, Int32 msg, IntPtr wparam, IntPtr lparam) ** Loaded Assemblies ** (3000 lines of assemblies) ** JIT Debugging ** To enable just-in-time (JIT) debugging, the .config file for this application or computer (machine.config) must have the jitDebugging value set in the system.windows.forms section. The application must also be compiled with debugging enabled. For example: <configuration> <system.windows.forms jitdebugging="true"> </system.windows.forms></configuration> When JIT debugging is enabled, any unhandled exception will be sent to the JIT debugger registered on the computer rather than be handled by this dialog box The windows show red X's where the networks should be. Any advice on how to fix this? Additional Information PLC used: Wago 750-8212, Firmware FW26 Startup profile: CODESYS V3.5 SP19 Patch 5 OS version: Microsoft Windows NT 10.0.22631.0 .NET version: 4.0.30319.42000 Full Version info attached as .txt
Last updated: 2024-03-17

Post by ggarcia94 on IMAGE DISPLAY ACCORDING TO INPUT VARIABLE CODESYS Forge talk (Post)
Reopening this thread as I need to make a few images visible depending on the value of a variable. However, in the properties of the image I do not have the option to make the image visible (see attached image). I´m using Codesys V3.5 SP19. However, when I use V3.5 SP17 I have the option to make the images visible. Can someone help me achieve this with V3.5 SP19? EDIT: Fixed. Just had to uncheck Support client animations in the Visualization manger settings
Last updated: 2023-09-12

Post by nathant on Can't open online view of FB instance from code editor, only from Device/POU windows CODESYS Forge talk (Post)
Hello, The title pretty much says it all. When trying to open a FB from the CFC/Ladder/SFC editors while online, the FB does not open in an online view of that specific instance. Instead, it opens an offline view with '???' shown for the value of any variable. This makes debugging extremely cumbersome, as I have to find each FB in the POU window and select the specific instance I am trying to view. Anyone know the cause/solution for this? Thanks.
Last updated: 2023-11-08

Post by alink on Visu - changing auto-logout time CODESYS Forge talk (Post)
Hello is there a chance to set with a visu input the auto-logout time? At the moment, it is a fix value set in visu-manager. But for individual configurating of passwort policies I create a visu-dialog to set policies and there for an option to set auto-logout-time. But till now, I haven't found a solution. Maybe someone has an idea? Thanks
Last updated: 2023-11-30

Post by solidlogicguy on Little endian to Float from Modbus RTU CODESYS Forge talk (Post)
Hello, I got a device from which I require to read values from I am using a WAGO PLC 750-8212 and I am communicating through Modbus Master FUNCTION BLOCK from library WagoAppPLCModbus in Codesys 3.5 to this device. I already receive data from the device that is a CVM to monitor voltage from a fuel cell. The technical support of the company that makes these devices says that the data is sent in little endian form. And I want to convert it to a float value. The tech support sent me the next instructions of how to do it but I am new using codesys, so any advice or help I will really appreciate so much. Message from tech support: The process is complicated, better to do it with already implemented library in the language/program you use. Basically the process should be next: To convert the two Modbus registers containing parts of a 32-bit float in little-endian byte order to a floating-point number using mathematical operations, you first need to combine the two 16-bit integers (assuming reg1 is the lower word and reg2 is the higher word) and then interpret the result according to the IEEE 754 standard. Given: - Register 192 (reg1) = 4096 - Register 193 (reg2) = 14884 Step 1: Combine the two registers. Since we are dealing with little-endian byte order, reg2 is the high word, and reg1 is the low word: combined = reg2 * 2^16 + reg1 combined = 14884 * 65536 + 4096 combined = 975175680 + 4096 combined = 975179776 Step 2: Convert the combined value to binary: combined_binary = '1110101101011100000000000000000' Step 3: Split the binary into IEEE 754 components: Sign bit (1 bit): 0 Exponent (8 bits): 11101011 Mantissa (23 bits): 01011100000000000000000 Step 4: Convert the binary exponent to decimal and subtract the bias (127 for 32-bit floats): exponent = int('11101011', 2) - 127 exponent = 235 - 127 exponent = 108 Step 5: Calculate the mantissa as a fraction: The mantissa in IEEE 754 format is the fractional part after the leading 1 (which is implicit). Therefore, we need to convert the binary mantissa to decimal and add the implicit leading 1: mantissa_fractional = 1 + int('01011100000000000000000', 2) / 2^23 mantissa_fractional = 1 + 18688 / 8388608 mantissa_fractional = 1 + 0.002227783203125 mantissa_fractional ≈ 1.002227783203125 Step 6: Combine the sign, exponent, and mantissa to get the float value: float_value = (-1)^0 * mantissa_fractional * 2^exponent float_value = 1 * 1.002227783203125 * 2^108 Because the exponent is quite large, the resulting float value is a very large number.
Last updated: 2023-12-15

Post by tvm on multiply gives negatives CODESYS Forge talk (Post)
It's probably because you have an INT in the input to the MUL function, which will then try to output an INT as well. INT variables can only handle values of -32768 to 32767. Your value of 523000 won't fit in an INT, so it turns into an invalid number. Use a DINT. This is usually better for working with time values anyway, because time values are all 32 bit. Or if you can't, use INT_TO_DINT(gvlp.detectie_nalooptijd_s) in the input to the MUL function.
Last updated: 2024-01-04

Post by sturmghost on Visualization using methods and cyclic ST-calls CODESYS Forge talk (Post)
I found a way to do it: You can use, for example, the text variable property of any visualization element and call a function in it. Example: Write a test POU as a function (FUN), like MyTestFun which need a boolean Variable as an input value. Now write into the text variable property: MyTestFun(bBooleanValue) Thats it. The function is called at each visu_task cycle.
Last updated: 2024-01-22

Post by matt-s on HMI Pushbutton/Move Instruction CODESYS Forge talk (Post)
I have not gotten to the bottom of this yet no. I have double check that the variables are correct linked. When online with the program I can see the button and rung going true for the move instruction, yet it does not change. Forcing the bit in the program does change the value in Groov View. I am kind of at a loss here, especially since the other POU(For the pumps) does the same thing fine.
Last updated: 2024-02-02

Post by stuartjr on Disabling forcing of specific variables CODESYS Forge talk (Post)
Is there a way that I can create a variable in a GVL that I can control with logic but a user can not put a force on this variable. I have looked at the access rights but this seems to only limit editing the GVL or POU. This variable will only be assigned a value in one POU but it will be used throughout many other POUs.
Last updated: 2024-03-15

Post by dagsupport on CAA SerialCOM - hCom Reset max value 1023 CODESYS Forge talk (Post)
Hi everybody We are currently working on a project with an RS232 serial COM interface and using the CAA SerialCOM library. We have it working fine reading and writing data, although we have found an issue we cannot resolve and any suggestions would be helpful. We have noticed that after a while the RS232 stops working. We have tracked this down to the HANDLE hCom keeps increasing and when this reaches 1023 the COM returns an unknown error "5003". Is there a way to reset this hCom reference? Thanks Richard
Last updated: 2024-03-22

Post by amy123 on Alarm Manager Project Doesn't Open Successfully CODESYS Forge talk (Post)
Hello, when I download AlarmManager.project from https://forge.codesys.com/prj/codesys-example/alarm-manager/home/Home/, it gives an error when I open it. If I ignore the warning and continue to open, the alarms are missing. ** Exception Text ** System.ArgumentNullException: Value cannot be null. Parameter name: first at _3S.CoDeSys.ControlsContrib.Utilities.WeakMulticastDelegate.Invoke(Object[] args) at _3S.CoDeSys.ControlsContrib.Controls.WizardControl.OnFinishClick(EventArgs e) at System.Windows.Forms.Control.OnClick(EventArgs e) at System.Windows.Forms.Button.OnMouseUp(MouseEventArgs mevent) at System.Windows.Forms.Control.WmMouseUp(Message& m, MouseButtons button, Int32 clicks) at System.Windows.Forms.Control.WndProc(Message& m) at System.Windows.Forms.ButtonBase.WndProc(Message& m) at System.Windows.Forms.Button.WndProc(Message& m) at System.Windows.Forms.NativeWindow.Callback(IntPtr hWnd, Int32 msg, IntPtr wparam, IntPtr lparam)
Last updated: 2024-04-04

Post by tk096 on Fieldbus has lost synchronicity CODESYS Forge talk (Post)
Hi, a few suggestions on how to tackle the problem: - it might help to increase the cycle time of the ethercat task - increase the value of the ethercat parameter DCInSyncWindow (https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/pou-IoDrvEtherCAT/DCInSyncWindow.html) (see attached image) - enable FrameAtTaskStart (https://content.helpme-codesys.com/en/libs/IODrvEtherCATDriver/Current/pou-IoDrvEtherCAT/FrameAtTaskStart.html) in the ethercat master (see attached image) - if the drives can handle the synchronization problems, checking of the synchronization can be deactivated using SMC_Set_ETC_DCSyncSupervision (https://content.helpme-codesys.com/en/libs/SM3_Drive_ETC/Current/SMC_Set_ETC_DCSyncSupervision.html).
Last updated: 2024-04-11