Post by timvh on Device diagnosis ( EtherCAT IO card )
CODESYS Forge
talk
(Post)
You can get the state by just using the name of your node (same name as in device tree): VAR etcState: IoDrvEthercatDriverLib.ETC_SLAVE_STATE; END_VAR etcState := EJ1100.wState; Alternatively, you can iterate through the device tree to get the status of all (Ethercat) nodes. See here an example (no guarantee it works, just give as suggestion): PROGRAM P_IO_State VAR CONSTANT uiMAX_NR_OF_TERMINALS : UINT := 100; END_VAR VAR // general device diagnosis // can only be used when the Device - PLC Settings - Advanced settings - enable diagnosis for devices is enabled // this will add the DED library coupler: DED.INode; terminal: DED.INode; aDeviceState: ARRAY[0..uiMAX_NR_OF_TERMINALS - 1] OF DED.DEVICE_STATE; uiTerminalCount : UINT; uiIndex : UINT; // for each terminal check if it implements device diagnostics xQueryResult: BOOL; itfDevice : DED.IDevice2; xDiagAvailable: BOOL; eError: DED.ERROR; xEverythingOK: BOOL; END_VAR uiTerminalCount := 0; // start at the top of the device tree with the first EtherCAT coupler coupler := EtherCAT_Master.FirstChildNode; WHILE coupler <> 0 DO // for each coupler that is found start at the first terminal terminal := coupler.FirstChildNode; WHILE terminal <> 0 AND uiTerminalCount < uiMAX_NR_OF_TERMINALS - 1 DO // for each terminal that is found get the status through the device diagnosis interface xQueryResult := __QUERYINTERFACE(terminal, itfDevice); IF xQueryResult THEN aDeviceState[uiTerminalCount] := itfDevice.GetDeviceState(xDiagnosisInfoAvailable => xDiagAvailable, eError => eError); uiTerminalCount := uiTerminalCount + 1; END_IF terminal := terminal.NextSiblingNode; END_WHILE coupler := coupler.NextSiblingNode; END_WHILE uiIndex := 0; xEverythingOK := TRUE; WHILE uiIndex < uiTerminalCount DO IF aDeviceState[uiIndex] <> DED.DEVICE_STATE.RUNNING THEN xEverythingOK := FALSE; EXIT; END_IF uiIndex := uiIndex + 1; END_WHILE
Last updated: 2025-02-06
Post by carl25 on Confused about stepper spec & tips on pwm-step/dir
CODESYS Forge
talk
(Post)
Hello! I have asked the few I know who have knowledge of this and now turn to this one inexhaustible source of knowledge aka. the electronics forum. I was going to buy stepper motors yesterday but got so confused about the spec that I need to get an answer to this first. 2 different stepper motors, quite close in size but with very different spec. https://www.oyostepper.de/goods-40-Nema-17-Schrittmotor-Bipolar-12V-18-Grad-40Ncm-04A-12-Volt-4-Dr%C3%A4hte-Hybrid-Schrittmotor.html https://www.oyostepper.de/goods-38-Nema-17-Schrittmotor-Bipolar-18-deg-22Ncm-133A-28V-4-Dr%C3%A4hte-Hybrid-Schrittmotor.html Both Nema17 but the first 1.33A and 22Ncm and the second only 0.4A but almost double the torque. I can see that the resistance is very much higher on the latter but what's the catch? Double the torque to 1/3 the current sounds a little too good to be true so what am I missing?
Last updated: 2025-02-21
Post by fabiodasilveira on PLC Shell commands via ST Code
CODESYS Forge
talk
(Post)
Hello Everybody, I have created a project for an Eaton XC303 that sends lots of data to a router via UDP. It works fine. However, when there is more than one product connected to the router, then it is necessary to change the IP address of the Ethernet port 0, from e.g. 192.168.2.11 to 192.168.2.12 (second product). It is easily done via PLC Shell (setipaddr 0 192.168.2.12), but the people in production is struggling with the PLC Shell commands and I would like to create a Visualization page that will hide that. I used the instruction: eChangeIPResult:= SysSockSetIPAddress(strEthernetPort, strIPAddress); and it works, until the PLC resets. I already read some posts and it appears that I need to stop the Ethernet 0 port and Reconfigure it, but I am really struggling to find the right way to do it. Any help will be much appreciated.
Last updated: 2025-02-28
Post by pernockham on Inheritence of struct,
CODESYS Forge
talk
(Post)
Im looking for a way to define predefined version of the same structures through "extends"/inheritance. What I want to do is best shown with an example: TYPE log_item_val_type : ( BOOL_ := 0, INT_, REAL_, STRING_ ); END_TYPE TYPE LOG_DATA_BASE STRUCT val_type : log_item_val_type; (* value, name etc *) ENDSTRUCT ENDTYPE (* this/below is not possible as I understand from the compiler?? *) TYPE LOG_DATA_BOOL extends LOG_DATA_BASE : STRUCT val_type : log_item_val_type := log_item_val_type.BOOL_; END_STRUCT END_TYPE TYPE LOG_DATA_INT extends LOG_DATA_BASE : STRUCT val_type : log_item_val_type := log_item_val_type.INT_; END_STRUCT END_TYPE etc. for LOG_DATA_REAL and ..STRING. The system will not allow me to "re-define" "val_type" however. Instead I must do the work-around of defining four different types with all fields individually defined. The benefit if I could extend the base item would be that Im (more) sure the structures are identical. In usage I can call in a specific type rather use the base type and assign which type. Usage by pointer/ref to log_data_base would also be easier.. (* Usage: *) log_data : log_data_int := (name, value etc.) (* Instead of: *) log_data : log_data_base := (name, value, val_type).. Is this possible to achieve in some way that I have missed?
Last updated: 2025-03-05
Post by imdatatas on Auto Declare window disappears by itself in the Ladder editor
CODESYS Forge
talk
(Post)
Hello Everyone, The "Auto Declare" window disappears by itself in the Ladder editor. For example, a new function block is wanted to be added to the Ladder editor. (For example; MC_Jog block and instance name will be fbMcJog). To do this, "Empty box with EN/ENO" is added to the ladder line from the Toolbox on the right and when you type MC_Jog in the empty box and press enter, normally the "Auto Declare" window appears and you are expected to be asked to write the instance name here. However, this "Auto Declare" window closes itself immediately, it does not wait for the user to enter a value or close the window. I often encounter this situation in many IDE versions. Does this seem like a bug? If anyone has encountered a similar problem while creating a new program name, function or function block instance name regarding the "Auto Declare" window and knows a solution, I would be glad if you could share it. Best wishes Imdat
Last updated: 2025-03-06
Post by ojz0r on Assignment Efficiency - Repetitive Assignment vs IF statement
CODESYS Forge
talk
(Post)
Its important that you know the difference between the two. Example 1: Coils[0] := Coils[0] OR (Buttons[0] AND Sensors[0] > 6); In this case the statements will be evaluated every scan and result in either true or false for Coils[0]. Example 2: IF NOT Coils[0] AND Buttons[0] AND (Sensors[0] > 6) THEN Coils[0] := TRUE; END_IF In this example Coils[0] will latch the result in a true evaluation, if you want it to behave the same way as example 1 then you need to do it like example 3 below: IF NOT Coils[0] AND Buttons[0] AND (Sensors[0] > 6) THEN Coils[0] := TRUE; ELSE Coils[0] := FALSE; END_IF However back to the real question. There is no problem using either example 1 or example 3, if im not requiring a latch i usually go with example 1 as it is more compact.
Last updated: 2025-03-07
Post by pikebuster on Help for a newbie
CODESYS Forge
talk
(Post)
Can somebody help me with this? I have problem with the button! This task must be solved using Sequential Function Chart (SFC), IEC 61131-3. TASK Create an SFC program to control a traffic light at an intersection. Description: You will program a traffic light that has three phases: Green, Yellow, and Red. The traffic light must follow these rules: Green light is on for 10 seconds. Yellow light is on for 3 seconds. Red light is on for 10 seconds. If the pedestrian button is pressed, the system must keep the red light on for 20 seconds during the next cycle. After the pedestrian has “crossed,” the system should return to its normal cycle. Basic Steps: Initialization: Start by setting the traffic light to Red. Green Phase: After 10 seconds, switch to Green. Yellow Phase: After 10 seconds in the Green phase, switch to Yellow. Red Phase: After 3 seconds in the Yellow phase, switch back to Red. Loop: Repeat the cycle. Use, for example, lamp symbols in the visualization module to simulate the traffic light. You may also add a simple pedestrian light if desired.
Last updated: 2025-03-11
Post by egau on Enable and Disable Project IO programmatically
CODESYS Forge
talk
(Post)
Hi @eschwellinger, I tried this with Modbus COM slaves. I was able to disable them (slave becomes greyed out in the device tree), but the DED.Reconfigure "eError" output shows "NOT_SUPPORTED". After this, when I tried to re-enable the slave, it did not work (device stayed greyed out in the device tree), and the DED.Reconfigure "eError" output also showed "NOT_SUPPORTED". Is there something to do about this, or the device just doesn't support reconfiguration? P.S: I tried this running locally on my computer (not in simulation mode). So of course I was not physically connected to the devices. I have two similar projects, but one of them doesn't have the Modbus_COM devices. I know I can "Exclude from build" the devices for that project, but I would really prefer not to do this if possible. I would prefer to dynamically toggle a configuration variable that would enable or disable the slaves.
Last updated: 2025-03-14
Post by pernockham on Persistence Manager: Config File not found?
CODESYS Forge
talk
(Post)
Back in november I paused this, but wanted to reattempt using the persistent manager, the behavior is still the same. Most "login attempts" s are stopped with the message "One or more errors occurred" but I have no idea what that error might be. The only clue is this message is presented while the lower left status box says "Generating code...: relocation pou". For clarification. Build/Generate code is successful, no errors. Error appears when I try to download/login (physical or simulation) to a device. I did manage to login (in simulation mode) at one point, but then the error message "PersistenceChannel: Config file not found!". And no persistence files were created. I have done device-tree/reset-orgin also clean/clean all etc. Removed/re-inserted persistance manager. Behaviour is just the same. Removing Persistence Manage and everything is working OK. Is there possibly more info somewhere about the "One or more errors occured"-message?
Last updated: 2025-03-20
Post by pistola on C0357: "GetNextClient" is obsolete, use VisuUtils instead
CODESYS Forge
talk
(Post)
I'm having some troubles with this same issue and I'm wondering if someone can help me out. On a settings visual I allow the operator to enter some values however if they activate the page change button it will change the change with the Numpad dialog open. Since I'm using Visuelems.CURRENTVISU to change the pages I came across this code noted below for determining if the Numpad dialog was active. This code worked great however now in 3.5.19 it's now obsolete. I've tried following the directions in the attached program above however I can't see to get it to work in my program. Can anyone provide some help to determine if a dialog is open? FUNCTION Check_Dialog_Open : Bool VAR_INPUT sDialogName : STRING; // Input variable for the name of the dialog END_VAR VAR pstClientData : POINTER TO VisuElems.VisuStructClientData; // Pointer to the client data structure itfDialogManager : VisuElems.IDialogManager; // Interface for the dialog manager itfMyDialog : VisuElems.IVisualisationDialog; // Interface for the specific visualisation dialog END_VAR // Begin the iteration over the client manager VisuElems.g_ClientManager.BeginIteration(); // Loop through each client until no more clients are found WHILE (pstClientData := VisuElems.VisuElemBase.g_ClientManager.GetNextClient()) <> 0 DO // Get the dialog manager interface itfDialogManager := VisuElems.g_VisuManager.GetDialogManager(); // Get the specific dialog interface using the dialog name itfMyDialog := itfDialogManager.GetDialog(sDialogName); // Check if the dialog is open for the current client Check_Dialog_Open := VisuDialogs.VisuDlgUtil_IsDialogOpen(itfMyDialog, pstClientData, itfDialogManager); // If the dialog is open, exit the loop IF Check_Dialog_Open THEN EXIT; END_IF END_WHILE
Last updated: 2025-03-27
Post by nz-dave on MC_HOMING
CODESYS Forge
talk
(Post)
Hi Just new to motion and i am building my own 3axis cnc cutter using servo drives. i have every thing working quite well apart from mc_home. when executed (r_trig) it stops immediately and i get fb_wasnt_called_during_motion. if i execute the mc_home fb with a toggle it just runs and runs for a while then errors out. what im unsure of is the way mc_home works. from what i understand it changes the drive mode to 6 (homing) and should then run of the drive homing settings. once origin sensor is made then homing would stop and mc_home.done is true. and the position on the fb is where i what the new home position (zero) to be? or do i feed mc_readposition to that input? so i would think its the settings in the drive that aren't quite right. but i believe they are all correct. has any one got any info to steer me in the right direction? Cheers
Last updated: 2025-04-04
Post by r-c-r on SM3RaspiStepper 0.0.0.6 issue
CODESYS Forge
talk
(Post)
Ok, so i made some tests in the meantime and i have some conclusions. It apears that the enable bit is activated only when a motion function is executed. I implemented a very simple program with MC_Power and MC_Jog. If i enable everything on MC_Power, the enable GPIO pin stays off. However, as soon as the MC_Jog function is used the enable GPIO pin turns ON and remains ON. In version 0.0.0.4 this is not happening. The GPIO enable pin turns on or off when the MC_Power is enabled or disabled. From this behaviour i understand that in version 0.0.0.6 the GPIO enable bit is activated together with pulse and dir pins when motion starts. When motion stops, enable bit remains with the last state (on in this case) and you cannot turn it off for example. For me this bit is useful because i can turn on and off the stepper drive with MC_Power function. Now i can turn it on, but never off.
Last updated: 2025-04-04
Post by pernockham on Engineering IDE from linux?
CODESYS Forge
talk
(Post)
I have done the switch (linux mint, virtual windows through QEMU/KVM) now and is generally pleased. Have had problems in two areas initially. To bridge IP to the Virtual unit (solved), I overthought things initially. Solution. Configure manually a bridge in the mint-"network connections". Use that bridge in the Qemu settings as "Bridge device", "Device name": "name of the configured bridge" Figure out where to store the projects. I started out have the data in linux world (sort of) and linking it the windows with "virtio-fs". That had some serious impact though on git-handling. It seems that virtio-fs interpreted any file-path as lowercase only even if there were uppercase, resulting in git not able to sync files between its repository and the source code (it created a new file-path for me with only lowercase). Then I switch to samba-share instead and this works much better, though (git-actions) is a part that still has low performance with lots of waiting for file-actions. What should be the best way of handling the source/git? Edit to answer myself: Save the project "locally" in windows, then a lot of slow performance is avoided. Then a git-remote sync for backup.
Last updated: 2025-05-08
Post by mondinmr on Unexpected behavior in cyclic encoder read method during INT overflow (wrap-around)
CODESYS Forge
talk
(Post)
Hi everyone, I’m investigating a potential issue with a cyclic method we use for reading incremental encoders in our libraries. I’ve come across two implementations that, at first glance, appear to perform the same operation: motionUnit.vlPositionActualValue is UINT due strange encoder type. Version A METHOD PROTECTED cyclicReadField VAR_INST actPosFieldOld: INT; rI: INT; delta: INT; END_VAR rI := TO_INT(motionUnit.vlPositionActualValue); delta := rI - actPosFieldOld; m_actPosRaw := m_actPosRaw + TO_LREAL(delta); actPosFieldOld := rI; IF settings.velocityFeebackMapped THEN m_actVelRaw := TO_LREAL(motionUnit.velocityActualValue); END_IF Version B METHOD PROTECTED cyclicReadField VAR_INST actPosFieldOld: INT; END_VAR m_actPosRaw := m_actPosRaw + TO_LREAL(TO_INT(motionUnit.vlPositionActualValue) - actPosFieldOld); actPosFieldOld := TO_INT(motionUnit.vlPositionActualValue); IF settings.velocityFeebackMapped THEN m_actVelRaw := TO_LREAL(motionUnit.velocityActualValue); END_IF Both use INT and the same delta logic, so they seem equivalent. However, when an overflow (wrap-around) occurs, version A continues correctly as expected, while version B unexpectedly resets to -32768 without a clear reason. Has anyone experienced similar behavior or can shed light on what might be happening here? It almost seems as if the cast to LREAL is being applied before the calculation — but that would be illogical and potentially very dangerous in many situations! Thanks!
Last updated: 2025-05-13
Post by jschu on Dynamical scaling of bar graph without the bar itself
CODESYS Forge
talk
(Post)
Hi there, Task: dynamical changing the scaling of an bar graph, linear scaling whitout showing the bar only the scaling values and Lines for Main and partial steps. Define 4 Limits for Hi and LO Values with different colors Option 1 : use the bar graph whitout showing the actual bar whitout showing the bar, only the scaling values and lines for main and partial steps. Then what to do with the 4 Limits ? I could use 4 moveable Rectangles with the start and end value fo the areas but then the whoel bargraph must be transparent. Best way would be if only the scale ist possible to show as it is possible for the Meter 180° but this option does not exist for the bargraph. Option 2 : user defined HMTL5 Widgets wich may be some allreay has created or where is a dome for using this kind of html5 widget. The expanse for use html is in my eyes to big and gives more option for errors. Have some one experience in this topic or a hint how to do it the easiest way? Thanks for your help.
Last updated: 2025-05-15
Post by shaunvdm on Canbus Slave SDO Read from Object
CODESYS Forge
talk
(Post)
Busy testing a solution to use Canbus Slave to replace a physical device and convert to Ethercat device but keep the Canbus Master in place. Master needs to Read SDO object 5FA2. In the Master PLC if i send the SDO with 8 bytes in message IE: 60B 40 A2 5F 00 00 00 00 00 i get my expected 58B 43 A2 5F 00 00 68 36 02 containing data back. Problem is if we issue a 4 byte command can send 60B 40 A2 5F. Surely the canbus slave should respond with a 58B 43 A2 5F 00 00 68 36 02 but it comes back as 80 A2 5F 00 00 00 00 08 - meaning this OBJECT does not exist. Is there a setting in the canbus slave driver for Canbus to allow the 4 byte command to read the SDO OBJECTS ?
Last updated: 2025-05-27
Post by jy77812 on MC_MoveCircularAbsolute Using Help
CODESYS Forge
talk
(Post)
Dear People I’m trying to draw a circle using MC_MoveCircularAbsolute, but I keep encountering an error. The error message is SMC_CP_CIRCLE_CENTER_NOT_ON_BISECTOR. What I’m trying to do is simply draw a circle with a diameter of 20, starting from the point X=0, Y=0. I’ve set CircMode to center. It seems like a simple task, but the error keeps occurring, and it’s giving me a headache. I’d appreciate your help. I’ve also attached the program, so please provide any advice you can. I want to use the mode as the center. I've tried changing multiple coordinates and it won't run. Please help. sample stCirculAuxPoint.c.X := 20; stCirculAuxPoint.c.Y := 10; stCirculEndPoint.c.X := 20; stCirculEndPoint.c.Y := 30; fbMoveCircularAbsolute( AxisGroup := AxisGroup, Execute := xGroupCirculEx, CircMode := SMC_CIRC_MODE.CENTER, AuxPoint := stCirculAuxPoint, EndPoint := stCirculEndPoint, PathChoice := 0, Velocity := 50, Acceleration := 50, Deceleration := 50, Jerk := 50, CoordSystem := SMC_COORD_SYSTEM.MCS, BufferMode := 0, TransitionMode := 0, TransitionParameter := , OrientationMode := , VelFactor := , AccFactor := , JerkFactor := , TorqueFactor := , Name := , Done => , Busy => , Active => , CommandAborted => , CommandAccepted => , Error => , ErrorID => , MovementId => );
Last updated: 2025-06-04
Post by timvh on Current Visu name without Current Visu Variable
CODESYS Forge
talk
(Post)
To get the current visu for all your individual web clients, you could iterate over them, using the same library 1) Create a new function block which implements VU.IVisualizationClientIteration 2) Create an instance of this function block + add an instance of the "iterate" function block fbIterateCallBack : FB_IterateOverClients; // this implements VU.IVisualizationClientIteration fbVuIterate : VU.FbIterateClients; // this FB iterates over all clients 3) Call the fbVuIterate and set the reference to the call back FB. Then it will automatically call the method "HandleClient" of this function block. fbVuIterate( xExecute:= NOT fbVuIterate.xDone, xDone=> , xBusy=> , xError=> , itfClientFilter:= VU.Globals.OnlyWebVisu, eError=> , itfIterationCallback:= fbIterateCallBack); In the HandleClients method you can use the property of the interface of your webclient to which page it is currently on: sCurrentVisuOfClient := itfClient.CurrentVisuName; 4) Optionally from here you could also set the visu for the webclient, but this might be obsolete, because the other function block is now available... xQueryOK : BOOL; xChangePage : BOOL; itfVisuClientRawData : VU.IVisualizationClientRaw; xQueryOK := __QUERYINTERFACE(itfClient, itfVisuClientRawData); IF xQueryOK AND xChangePage THEN VisuElems.g_VisuManager.SetMainVisu(pClientData := itfVisuClientRawData.ClientDataPointer, stVisu := 'Visu2'); xChangePage := FALSE; END_IF
Last updated: 2025-08-13
Post by pernockham on AC Persistence - values are not read from file during start?
CODESYS Forge
talk
(Post)
Im struggling with the AC Persistence. AC persistence seems to work for any variable that is changed online and values are kept during reboot. However, if I try to edit the persistence files offline or replace the persistence files with a previously downloaded older persistence file (with modified values), the online value will not follow, as if the system did not at all read the file at boot? My testing sequence. - Edit a the value of a persistenced variable (with xSaveOnChange = True) - Save/download the associated persistence file, (and confirm the value has changed). - Edit the value online for a second time . - Stop runtime - Replace (upload) the persistence file with my previously downloaded file . - Coldstart/Warmstart/Start runtime - Whatever Im trying the value of my persistence variable will always be equal to that of my second edit as if the file is not read/considered during boot. What am I doing wrong?
Last updated: 2025-09-02
Post by e13740e on Parameterized Property syntax for array element processing
CODESYS Forge
talk
(Post)
Hello. I'm trying to create a Parameterized Property(CDS V3.5 SP21) to avoid copy-pasting code for processing array elements. I can't seem to get any result. Perhaps I am making a mistake with the syntax. None of the declaration options below are accepted by the compiler. If you know and use them (Parameterized Properties) in your work, please let me know. Thank you in advance. Option 1: PROPERTY <property_name> : <data_type> VAR_INPUT <index_name> : <index_type>; // One or more index parameters are declared here END_VAR</index_type></index_name></data_type></property_name> GET Code that uses <index_name> to return a value END_GET</index_name> SET Code that uses <index_name> and the implicit variable <property_name> to write a value END_SET</property_name></index_name> END_PROPERTY Option 2: PROPERTY <property_name> (<index_name> : <index_type>) : <data_type></data_type></index_type></index_name></property_name> GET Code that uses <index_name> to return a value END_GET</index_name> SET Code that uses <index_name> and the implicit variable <property_name> to write a value END_SET</property_name></index_name> END_PROPERTY
Last updated: 2025-10-09
Post by e13740e on Parameterized Property syntax for array element processing
CODESYS Forge
talk
(Post)
Hello. I'm trying to create a Parameterized Property(CDS V3.5 SP21) to avoid copy-pasting code for processing array elements. I can't seem to get any result. Perhaps I am making a mistake with the syntax. None of the declaration options below are accepted by the compiler. If you know and use them (Parameterized Properties) in your work, please let me know. Thank you in advance. Option 1: PROPERTY <property_name> : <data_type> VAR_INPUT // One or more index parameters are declared here <index_name> : <index_type>; END_VAR</index_type></index_name></data_type></property_name> // Accessor for reading GET // Code that uses <Index_Name> to return a value END_GET // Accessor for writing SET // Code that uses <Index_Name> and // the implicit variable <Property_Name> to write a value END_SET END_PROPERTY Option 2: PROPERTY <property_name> (<index_name> : <index_type>) : <data_type></data_type></index_type></index_name></property_name> // Accessor for reading GET // Code that uses <Index_Name> to return a value END_GET // Accessor for writing SET // Code that uses <Index_Name> and // the implicit variable <Property_Name> to write a value END_SET END_PROPERTY
Last updated: 2025-10-09
Post by cihangur on C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr
CODESYS Forge
talk
(Post)
This "FB_Init" error has become very annoying lately. It's usually related to webvisu and is resolved by deleting all objects and related libraries. Of course, you need to re-add the deleted objects. Lately, we've generally been managing by not upgrading, but this problem persists in every version since SP20 and should be resolved. I updated a project from SP 19 to SP 21 and found 116 similar errors. [ERROR] alarmmanager, 4.7.0.0 (intern): ReplaceAlarmPlaceholdersConverted: C0138: No matching 'FB_Init' method found for instantiation of CharBufferString [ERROR] visuelemsalarm, 4.7.0.0 (system): protDrawRowHeader [VisuFbElemAlarmTable]: C0138: No matching 'FB_Init' method found for instantiation of CharBufferString [ERROR] alarmmanager, 4.7.0.0 (intern): AnalyzePlaceholders2 [Alarm]: C0138: No matching 'FB_Init' method found for instantiation of CharBufferString If you have an ERROR related VisuClientObjectMgr you can try to disable "Visualization Manager - Settings - Support client animations and overlay of native elements " selection "C0138: No matching 'FB_Init' method found for instantiation of VisuClientObjectMgr" etc
Last updated: 2025-10-10
Post by ph0010421 on How to create a stopwatch?
CODESYS Forge
talk
(Post)
Do you need an 'hours-run' counter? And 1 second resolution is ok? I think you're over-thinking it. (The task time needs to be < 1second) Have a look at the LAD... Then, the time in seconds can be made into hh:mm:ss with this FUNction Declarations: FUNCTION funSecondsToStringTime: string VAR_INPUT InSeconds: UDINT; END_VAR VAR AsString: STRING; Minutes: UDINT; Hours: UDINT; Seconds: UDINT; MinutesAsString: STRING(2); HoursAsString: STRING(2); SecondsAsString: STRING(2); END_VAR and the code: Hours := InSeconds / 60 / 60; //Derive hours Minutes := (InSeconds - (Hours * 60 * 60)) / 60; //Derive minutes Seconds := InSeconds - ((Hours * 60 * 60) + (Minutes * 60));//Derive seconds HoursAsString := UDINT_TO_STRING(Hours); MinutesAsString := UDINT_TO_STRING(Minutes); SecondsAsString := UDINT_TO_STRING(Seconds); IF LEN(HoursAsString) = 1 THEN HoursAsString := CONCAT('0',HoursAsString); END_IF; IF LEN(MinutesAsString) = 1 THEN MinutesAsString := CONCAT('0',MinutesAsString); END_IF; IF LEN(SecondsAsString) = 1 THEN SecondsAsString := CONCAT('0',SecondsAsString); END_IF; AsString := CONCAT(HoursAsString, ':'); //assemble string AsString := CONCAT(AsString,MinutesAsString); AsString := CONCAT(AsString,':'); AsString := CONCAT(AsString, SecondsAsString); funSecondsToStringTime := AsString;
Last updated: 2023-12-08
Post by nz-dave on Bool turning on in case stament in wrong state?
CODESYS Forge
talk
(Post)
I had the FB called via a for loop to call a few instances of my FB I have removed it the for loop and just called them 1 by 1. Seems to have sorted the problem. tho, i have other FB's and for loops doing the same thing but they are all fine. below is basically what was happening. var: mVibrator : ARRAY[1..GVL_Settings.Number_Of_Products] OF Main_Vibrator; end_var Controller(PRG) call: FOR v := 1 TO GVL_Settings.Number_Of_Products BY 1 DO; mVibrator[v] (); END_FOR So at state 30: the mVibrator[1].start was turning on 30: Main_Mixer.Start := TRUE; Process_State := 2; IF Main_mixer.Done THEN Main_Mixer.Start := FALSE; Control_State := 40; END_IF but its not till state 50: that it is actual in the code. 50: Main_Suction_valve.Open_Input := TRUE; mVibrator[1].Start := TRUE; Process_State := 4; IF GVL_Weigh_hopper.LoadCell_Weight = 0 THEN Main_Suction_valve.Open_Input := FALSE; mVibrator1.Start := FALSE; Control_State := 60; END_IF Thanks for your input.
Last updated: 2023-12-16
Post by andrax on Meine Gerätesammlung basierend auf TCA9548
CODESYS Forge
talk
(Post)
Hallo zusammen, ich programmiere öfters mal kleinere Messgeräte und Datenlogger. Je nach Einsatzzweck musste ich mir ein paar Gerätetreiber selber schreiben. Da es eine recht große Sammlung ist, stelle ich die hier einfach mal ein. Die Sammlung basiert auf den Gerätetreiber TCA9548 Multiplexer von Steffen Dreyer. Codesysversion: V3.5 SP18 Patch 4 Inhalt: -4channel Dimmer (Stefan Dreyer) -BMA456 (Andre Klien) -BME280 (Stefan Dreyer) -BMP280 (Stefan Dreyer) -EEPROM_24C512 (Stefan Dreyer) -ADS1115 (Andre Klien) -ICP10125 (Andre Klien) -PCA9555 (Stefan Dreyer) -PCA9685 (Stefan Dreyer) -PCF8575 (Stefan Dreyer) -SDP810 (Andre klien) -SSD1306 (Stefan Dreyer) -TCA9548 (Stefan Dreyer) -TSL2561 (Stefan Dreyer) Alle Gerätetreiber laufen über den Multiplexer, können aber auch ohne betrieben werden. Einschränkung: BMA456: Die Konfigurationsdaten werden erfolgreich in den Chip geschrieben, dieser meldet aber config wrong. Warum auch immer, der Sensor funktioniert und bringt hochempfindlich Beschleunigungsdaten. ADS1115: Hie habe ich nur die wichtigsten funktionen implementiert. 1-4 Kanäle, PGA, kontinuierlicher Modus, Datenrate. Alle anderen Funktionen (single-shot, komparator,alm) sind nicht implementiert. Das macht auch keinen Sinn, da diese Funktionen besser über die Steuerung realisiert werden können. Achtung beim ADS1115 ist zwingend ein Levelshifter notwendig, wenn ihr diesen mit 5V betreiben wollt. Ihr grillt sonst euren Raspi (SDA, SCL sind dann 5V) Gruß Andre
Last updated: 2023-12-18