Post by petra on Gateway not configured properly when read_online_value
CODESYS Forge
talk
(Post)
Here is what I use to read online the parameter value. proj = projects.primary app = proj.active_application plc = proj.find("Device", True)[0] onlineapp = online.create_online_application(app) onlineapp.login(OnlineChangeOption.Try, True) dev1 = proj.find("DEV1", True)[0] for conn in dev1.connectors: > parms = conn.host_parameters > if len(parms) > 0: > p = parms.by_id(1074855985) > p.read_online_value(2000) ---> error: Gateway not configured properly Does anyone know about this?
Last updated: 2026-06-12
Post by kambel on IO Drive on C manual
CODESYS Forge
talk
(Post)
Hello, pls help!!! Is there a more detailed manual (for dummies) for writing your own IO drive device in C? Another question: how can I add diagnostics to the IEC IO Drive device so that a red triangle lights up in the project tree in the event of a malfunction?
Last updated: 2026-01-29
Post by fabrp on CPU + EtherCAT redundancy
CODESYS Forge
talk
(Post)
Hi TimvH, thanks for feedback. I also test the redundancy with Wago PFC 8212 but when I did it (firmware 28) it was not so much stable..Did you have some issue on master/slave switchover? are you using with EtherCAT remote I/O? I was looking for a most powerful hardware (PC based, x64) BR
Last updated: 2026-02-01
Post by yannickasselin on Lenze i950 Servo and WAGO PFC200
CODESYS Forge
talk
(Post)
I don't have time to go through the whole manual but as I said earlier, the servo drive does not support any of the modes needed for SoftMotion Light to work. If you want to use the full SoftMotion, you could use SMC_Homing function block to do the homing. This function block does not use the Homing Mode. It still uses the CSP mode and does the logic in Codesys runtime instead of in the servo drive. Read the documentation about it to see if it fits your needs. But if your controller only supports SoftMotion Light, I am afraid you will not be able to use the i950. I do a lot of motion stuff with different servo brands. Some support all the modes needed for SoftMotion Light and some don't. You really need to make sure the modes are supported before choosing a brand over another. I tend not to use brand specific controllers in order not to be limited by their supported features. I usually choose a PC (Linux or Windows) and install the Codesys runtime and licences myself. This is the most flexible way to use Codesys in my opinion. Depending on how many axes are needed in your project, a full SoftMotion license may not be more expensive than SoftMotion Light because SoftMotion is available as Application based license whereas SoftMotion Light is not. But of course, SoftMotion is harder on the CPU than SoftMotion Light.
Last updated: 2026-02-13
Post by pernockham on Unable to deploy "Control for Linux SL 4.18.0.0"
CODESYS Forge
talk
(Post)
Ok, I think I understand. The problem is my language-setting being "swedish". I will check if I can switch to english. Update/confirmed. Change LANG to en_GB, this enabled the architechture to be correct and the control SL again to appear and to be possible to be updated. Thanks!
Last updated: 2026-02-23
Post by mawaloc on Current time and date
CODESYS Forge
talk
(Post)
Hello all, I'm looking to display current time and date as first, then find a way to adjust with time zone differences. I found some tuto in internet but seems I already have issues.. cf pictures Which functions I should use? thank You for the help and time. Regards
Last updated: 2026-02-23
Post by mawaloc on Time and Date vizualization
CODESYS Forge
talk
(Post)
Hello all, I'm looking to display current time and date as first, then find a way to adjust with time zone differences. I've found some tuto in internet but seems I already have issues.. cf picture Which functions I should use? thank You for the help and time. Regards
Last updated: 2026-02-23
Post by poliautomacao on Absolute movement controlled by an external encoder.
CODESYS Forge
talk
(Post)
Hello, is it possible to perform an MC_MoveAbsolute movement, and have the servo move using an external encoder (freeEncoder)? In my application, I have slippage on the main shaft of the servo motor, and I would like to add an encoder to measure the actual position of the material.
Last updated: 2026-03-04
Post by noah on "Invalid Value" for Variables at Runtime
CODESYS Forge
talk
(Post)
Hello, I also have the problem that suddenly all variables in my project were invalid and shown as "???" during runtime. Could you manage to fix the problem in the last 4,5 years ;) ? Because I tried everythin to fix it but nothing worked. I feel like maybe this is a bug. Thank you.
Last updated: 2026-03-09
Post by noah on "Invalid Value" for Variables at Runtime
CODESYS Forge
talk
(Post)
Hello, I also have the problem that suddenly all variables in my project were invalid and shown as "???" during runtime. Could you manage to fix the problem in the last 4,5 years ;) ? Because I tried everythin to fix it but nothing worked. I feel like maybe this is a bug. Thank you.
Last updated: 2026-03-09
Post by reinier-geers on Compare applications in one project
CODESYS Forge
talk
(Post)
HI,ive got one project with 6 applications. one master and 5 slaves. All 5 slaves should be the same. Can i compare applications in one project ? sind version 20.5 ive got problems. One slave freeze compleetly after a while. Ive got an other project freezes after a while , after a online change
Last updated: 2026-03-19
Post by reinier-geers on Compare applications in one project
CODESYS Forge
talk
(Post)
Ive copied slave 3 to slave 1. Runs without a problem. Then i copied 1 to 3. It hangs/freeze immediatly. not even a screen. Only thing that is diverend is the network variable. What is the problem with version 20.5 / 21.0 ? Not even my dealer knows whats the problem
Last updated: 2026-03-19
Post by gseidel on Absolute movement controlled by an external encoder.
CODESYS Forge
talk
(Post)
Hi polyautomacao, hmm, did you tune the PD parameters as shown in the link I posted above? One thing that could cause the behavior are bad parameters. I also don't understand the screen shot: when you hold the encoder to 0, why is the actual position of the DrivePosControl -208? Best regards, Georg
Last updated: 2026-03-27
Post by reinier-geers on Network variable stops sending
CODESYS Forge
talk
(Post)
I use network variables. But when i change the programm, it wil stop sending. Then is have to add or delete a variable. Then i will be compiled again and sends again. This problem wasw already in 9.20 but seems to be still in 21.0 . Is there a way to solve this ?
Last updated: 2026-04-20
Post by timvh on Issue with library updates
CODESYS Forge
talk
(Post)
tried this with SP22 P1 and I see no issues related to this. Can install the updated library in the repository, automatically get a message in my project that a new version is loaded and when I login, get a message to do an online change and see the new behaviour of the changes in my library.
Last updated: 2026-04-25
Post by malie on Issue with library updates
CODESYS Forge
talk
(Post)
I just tried with version 3.5.22.1 and librarys updates often aren't recognized, usually not. Same behavior like 3.5.21. To describe my workflow: one IDE is used to test librarys as project and two or more IDEs to edit librarys. With only two open IDEs there is no problem, the problem began with more than two open IDEs.
Last updated: 2026-05-04
Post by nulltrace on PM556-TP-ETH — How to change IP address without overwriting the PLC program?
CODESYS Forge
talk
(Post)
Depending on the Project, the used Communication-Protocol's, the way how the System was designed, there are some Options if you can answer these Question properly The Question is: are you able to connect to the Shell / Systemprompt of this PLC with administrative Rights?
Last updated: 2026-05-20
Post by timvh on <Dereference of invalid pointer>
CODESYS Forge
talk
(Post)
Yes, this can be fixed by setting the correct reference to the structure.... But by only the given information it is impossible to say what you did wrong. Maybe you can start by first creating an instance of the structure within the program to see how this works.
Last updated: 3 hours ago
Post by egret on Issue with J1939, PGN 65267 (Vehicle Position)
CODESYS Forge
talk
(Post)
I have a J1939 network (ISOBUS) connected to my PLC. I can receive various PGNs such as 65256 (Vehicle Direction/Speed) and 65254 (Time/Date). However, I cannot receive 65267 (Vehicle Position). PGN 65267 (VP) contains SPN 584 (Latitude) and SPN 585 (Longitude). On the network both SPNs return a value of -210 (meaning the CAN message payload is zero in both cases). The conversion settings are the default values and appear to be correct (see attached screenshot). Using a CAN analyser I can see that PGN 65267 (Vehicle Position) is being transmitted over the network with valid (non-zero) data that matches the latitude and longitude coordinates I would expect. I've created a program to read the raw J1939 data and this also returns valid data. It seems that the Codesys J1939 database has a problem with reading PGN 65267 messages. Can anybody else confirm this? I'm using Codesys Version 3.5 SP16 Patch 5.
Last updated: 2023-09-13
Post by damian177 on Codesys and SMS in RPi
CODESYS Forge
talk
(Post)
I tried initialize my GSM modem by write simple application in C, and GSM modem works, below used AT commands: AtChat: T : "AT" AtChat: F : "OK" AtChat: T : "AT+CMEE=1" AtChat: F : "OK" AtChat: T : "AT+CMGF=0" AtChat: F : "OK" AtChat: T : "AT+CGMI" AtChat: F : "WH_Ltd" AtChat: F : "WH_GM35" AtChat: F : "Revision: RDA BV5" AtChat: F : "OK" AtChat: T : "AT+CGMM" AtChat: F : "WH_GM35" AtChat: F : "OK" AtChat: T : "AT+CGMR" AtChat: F : "Revision: GM35-D_B5_R05_A01_D170914" AtChat: F : "OK" AtChat: T : "AT+CGSN" AtChat: F : "868221045990218" AtChat: F : "OK" AtChat: T : "AT+CNMI=2,1,0,1,0" AtChat: F : "OK" AtChat: T : "AT+CLIP=1" AtChat: F : "OK" AtChat: T : "AT+COPS?" AtChat: F : "+COPS: 0,2,\"26002\"" AtChat: F : "OK" operator name: "26002" AtChat: T : "AT+CREG?" AtChat: F : "+CREG: 1,1" AtChat: F : "OK" at+creg Modem is initialized I do not understand why Codesys SMS library send AT+CPIN? command ?
Last updated: 2023-09-29
Post by captaincookie on increase default string length in queue
CODESYS Forge
talk
(Post)
Hello, I'm using Codesys V3.5 SP18 Patch 4. In the ElementCollectionExample Project from Codesys, I test the SimpleQueueExample in a Control Win V3 x64 environment. I try to add a string of 95 characters length to a queue. The default length of strings is defined as 80 characters. In the initialization of a string variable, it is possible to increase the length by the definition of e.g. STRING(1000). But when I write the string defined like this to the queue, only 80 characters are written to it and the rest is missing. I think the default length is still set in the queue definition, so it is necessary to change this, isn't it? Is there any option to increase the default length of strings in the queue? Attached you can find the used project. Thanks in advance. If any information are missing or my description unclear please let me know.
Last updated: 2023-10-05
Post by annd on Migration von "CODESYS Control for PFC200 SL" zu WAGO FW26 "CODESYS V3.5.19.2"
CODESYS Forge
talk
(Post)
Ich hab's hinbekommen: Nach dem Controller Update hab ich ein neues Projekt gemacht und nur den PFC200(8212) eingefügt (es erscheint dann ein leerer Kbus und eine serielle Schnittstelle COM1). Dann hab ich mich am Controller eingeloggt und den Kbus (Rechtsklick: Geräte suchen) mit allen Modulen automatisch ergänzen lassen. Bei den leeren Modulen hab ich dann das E/A-Abbild in csv exportiert. Dasselbe hab ich bei meinem alten "PFC200 SL" Projekt gemacht. Und dann in Excel alle Variablennamen in die leeren csv kopiert und danach wieder im neuen Projekt importiert. Dann hab ich noch alle Programmblöcke, Tasks, Visualisierungen und auch Modbus TCP Master u. Slave und auch Modbus COM Port Master und Slave in das neue Projekt kopiert. Weiters hab ich alle notwendigen Bibliotheken im Bibliotheksverwalter eingefügt. Dann noch ein paar kleine Fehler korrigiert (ich musst einen anderen Block zum Lesen der Uhrzeit nehmen) bis ich das neue Projekt fehlerfrei übersetzen konnte. Dann konnte ich es auf den Wago Controller übertragen und direkt starten. Es sieht so aus, dass alles läuft. Gruß annD
Last updated: 2023-11-18
Post by mikek10 on Ethernet/IP 4.6.0 causing exceptions?
CODESYS Forge
talk
(Post)
Hi, I have a project currently in development, it has a number of Ethernet/IP devices (18 adapter devices with Codesys as scanner, another scanner device with codesys as adapter). This has been stable whilst on factory floor for several months (though prior to that I did have some Ethernet/IP issues which were resolved by adjusting RPI rates). Today I tried updating to Ethernet /IP 4.6.0 from 4.5.1, subsequent to this I had 2 exceptions in a 2 hour period, I reverted to 4.5.1 and have had no further exceptions. Note I do have a device (Zebra printer) that frequently times out and reconnects, this does not seem to cause any issues in operation and does not cause any exceptions with 4.5.1. I believe the root cause of this is on the Zebra side, however there does not seem to be any adjustment I can make to prevent the time outs. Information from device log is in screenshot attached.
Last updated: 2024-06-27
Post by abinvest579 on TCP Client
CODESYS Forge
talk
(Post)
Hi All, I am using codesys based plc to read and control magna power DC supply over LXI protocol using SCPI command. To connect device required socket programming for that i am using Net base service library function block TCP_Client to establish connection over TCP/IP , TCP_Write to write SCPI commands and TCP_Read to read data from Magna power DC supply. I have attached screenshot for logic developed. I am able to connect and write commands to device but i not receiving any information from device. For writing Commands i also tried various end of line character like \n,<nl>, A, D, 10, 13, 0x0A, 0x0D but not received any status from device. For testing purpose i am using simple command '*IDN?' to read data. Also if tried to check on hercules software what data actually plc read, first it read correct data after that is read wrong data as see in screen shot. 'Hello World' was correct read and after that Codesys in replaced with 'Codesysorld' that is not correct way. Same issue also appeared for send data. Any one have face same issue how i can read data directly from device correctly and send data please suggest solution on this.</nl>
Last updated: 2024-07-01
Post by climblinne on Calling OPC UA Methods from UaExpert
CODESYS Forge
talk
(Post)
Hello, I hope someone could help me. I installed the newest Codesys 3.5 SP 20 Patch 1. When loading the demo files from @i-campbell I can upgrade them to the latest version and everthing works on the OPC-UA client side as expected (object "a" is visible, I can use the "ExampleMethod"). Now I * remove the "Information Model", * delete the "OPC_UA_Symbols Objects", * Add "Information Model" again * add "TestRootObjectType" again and "Generate IEC declarations" * and search for mapped instances (to get instance "a" again) Very good still working as expected. Now I delete the OPC_UA_Symbols and add it again referring to the "objecttest" from 16.9.2020. Also I redo the steps from above. The result is now, that I can't see the "a" object in the "Root/Objects" folder. Why ist this and how can I make it running? I think, it could may be a different version of the UA configuration file. I tried to build my own model definition files and got the same problem (but I am really not an expert). When someone has a actual model, which is also running in the actual Codesys I would be very grateful. Or even better, how to make the correct model in e.g. UA Modeler SW (I followed the description https://documentation.unified-automation.com/uamodeler/1.6.0/html/howprojnet_sec.html).
Last updated: 2024-07-01
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.