Post by trusty-squire on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
Hi, Is there a way to read the homed status from the EtherCAT drive directly? I am currently flagging the homed status on the succesful completion of the MC_Home function block, but I have had false triggers where the drive didn't actually execute the homing procedure but the MC_Home FB is marked as complete without error. I looked at other MC/SMC function blocks but the closest I can find is the "Homing" bit from MC_ReadStatus FB, but this doesn't show if the drive is succesfully homed, only that it's homing. Any guidance is welcome. Thanks!
Last updated: 2025-01-07
Post by hboertz on CamBuilder and first boundary position not zero
CODESYS Forge
talk
(Post)
Hi @niallel, it is currently not possible to create periodic cams using SMCB.BoundImplicit(). If you want to create a periodic cam which does not start/end with all slaves values equal to zero, then you must specify the boundary conditions explicitly using SMCB.Bound(). When you finished your cam, you can check via CamBuilder.CheckContinuity(), if the cam fulfills the continuity requirements for a periodic cam (see input isPeriodic). But you are right, it should be possible to create periodic cams using implicit boundary conditions. I have added the following Jira issue, so that this feature might be included in a future SoftMotion version: SM-5537: CamBuilder: It should be possible to create periodic cams using implicit boundaries I hope this answers your question. Best regards, Hendrik
Last updated: 2025-01-08
Post by trusty-squire on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
@imdatatas, thanks for the info, I increased DSP402.uiHomingMinCycles to 10 and have a good feeling that will solve the issue of "false" homings. It's an intermittent issue so I'll report back once it's confirmed. @bruno-roth, also good info. According to my documentation, bit 14 is used to indicate the homed status. I did a test and the bit always stays true after it's been homed once (eg. even if I initiate a new homing procedure then hit the the e-stop mid homing), so I need to take that into consideration, but I can work with that. Thanks!
Last updated: 2025-01-09
Post by trusty-squire on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
How are the servo drives controlled? EtherCAT, step/dir pulses, other? Another thought is that - if it's step/dir pulse based control - the pulses from the PLC to the drive are getting missed/lost at high frequencies? If that's the case then there would be multiple troubleshooting steps/corrections that could be investigated. You could try to create a simplified program, with all the same parameters, that only has an MC_SetPosition FB you manually trigger and see if you are still getting the same results? When you manually control the motor directly from the servo drive software at the speeds you are calling for, does it move precisely to the target position?
Last updated: 2025-01-18
Post by sigurdrb on OPC server in "Communication manager"
CODESYS Forge
talk
(Post)
Hi! I was thinking of switching the OPC server config from "Symbol Configuration" to the "Communication manager" in the device tree. I Have a lot of arrays of structs that I have previously declared in the "Persistent Variable" object in the device tree. It seems as it is not supported to directly expose persistant variables to the OPC server like the "older" way of doing it in the symbol config. Is this correct? Do you recommend to just do it the old fashioned way, or should I edit the structure of the global variable list / persistant data / OPC server and set up the OPC server from the "Communication manager" object?
Last updated: 2025-01-20
Post by ton on String nach erlaubten/unerlaubten Zeichen durchsuchen
CODESYS Forge
talk
(Post)
Hi Timo, FUNCTION Sonderzeichen_Check : bool VAR_INPUT sInputString : STRING; // Zu prüfender String END_VAR VAR i: INT; iAsc: INT; END_VAR Sonderzeichen_Check:= TRUE; FOR i:= 0 TO len(sInputString) - 1 DO iAscii:= sInputString[i]; //Get ASCII value //Check value between 48('0') and 65('9') or between 65('A') and 90('Z') or between 97('a') and 122('z') or IF iAscii >= 48 AND iAscii <= 57 OR iAscii >= 65 AND iAscii <= 90 OR iAscii >= 97 AND iAscii <= 122 THEN //iAscii valit ELSE Sonderzeichen_Check:= FALSE; END_IF END_FOR Diese FUNCTION anrufen: VAR xTest1: BOOL; xTest2: BOOL; sCheck: STRING; END_VAR xTest1:= Sonderzeichen_Check(sInputString:= 'abcuharoahse89347KEWDL'); //=TRUE xTest2:= Sonderzeichen_Check(sInputString:= 'abcuharoahse89347KEWDL?'); //=FALSE IF Sonderzeichen_Check(sInputString:= 'CheckThisSting,') THEN sCheck:= 'OK'; ELSE sCheck:= 'NOT OK'; END_IF
Last updated: 2025-01-20
Post by z3r091 on EtherCATStackLibrary - CmpSysEthernet Unaufgelöste Referenz
CODESYS Forge
talk
(Post)
Guten Morgen, ich habe ein Problem mit dem Lesen von IO Link Geräten. Wir nutzen einen Festo IO-Link Master den ich mittels der Funktionen ETC_ADS_IoLinkRead und ETC_ADS_IoLinkWrite lesen und schreiben möchte. Dazu implementiere ich die Bibliothek EtherCATStackLibrary 4.6.1.0. Hier geht schon das erste Problem los. Diese Bibltiothek möchte eine weitere Bibliothek nutzen, die "CmpSysEthernet". Diese muss ich über die Platzhalter manuell auf "SysEthernet 3.5.19.0" linken. Dann sind erstmal keine Fehler mehr vorhanden und das Projekt lässt sich übersetzen. Beim oder vor dem laden in die (Eckelmann) Steuerung, bekomme ich dann aber Fehler über unaufgelöste Referenzen, über Funktionen aus der SysEthernet Bibliothek (siehe Screenshot). Hat da jemand eine Idee oder Lösung?
Last updated: 2025-01-31
Post by imdatatas on String length issue in GetRecipeNames method
CODESYS Forge
talk
(Post)
Hi, If the string length in the GetRecipeNames method is lower than the default value, there will be a problem with the resulting Recipe file names. For example; When the method in the link is called, let's say the defined string length is 19. In this case, the string content is corrupted as in the image. strArr: ARRAY[0..9] OF STRING(19); https://content.helpme-codesys.com/de/libs/Recipe%20Management/Current/pou-RecipeManCommands/GetRecipeNames.html The same problem does not occur when the string definition is made in the default size. strArr: ARRAY[0..9] OF STRING; FYI Regards, Imdat
Last updated: 2025-02-19
Post by imdatatas on String length issue in GetRecipeNames method
CODESYS Forge
talk
(Post)
Hi, If the string length in the GetRecipeNames method is lower than the default value, there will be a problem with the resulting Recipe file names. For example; When the method in the link is called, let's say the defined string length is 19. In this case, the string content is corrupted as in the image. strArr: ARRAY[0..9] OF STRING(19); https://content.helpme-codesys.com/de/libs/Recipe%20Management/Current/pou-RecipeManCommands/GetRecipeNames.html The same problem does not occur when the string definition is made in the default size. strArr: ARRAY[0..9] OF STRING; FYI Regards, Imdat
Last updated: 2025-02-19
Post by george32 on TCP Server
CODESYS Forge
talk
(Post)
Dear people, I would like to create a TCP server in my PLC program. The TCP server needs to communicate with an external device. I have been searching the internet and found that the libraries Syssocket or CAA NetBaseSrv are two possible solutions to create a TCP server. From what I have read, CAA NetBaseSrv is more user-friendly to implement than the Syssocket variant. However, I am still struggling to actually implement this library. Foremost is my little knowledge about creating a TCP server and how to read/understand each function block, especially the outputs of some blocks and the types, e.g. server has an output CAA.Handle, but I cannot find the explanation of CAA.Handle. I tried to find a good document that can help me understand how to implement a TCP server, but I could not find it. Thank you in advance, George
Last updated: 2025-02-20
Post by tmarmy1 on Redundancy for RTE x64 - stuck in standalone
CODESYS Forge
talk
(Post)
Sorry if this has been asked before, but I can't seem to locate a thread that leads me answers. I am running two RTE x64 softPLCs, one on the host machine and a second via a VM. I have managed to finally get both to a position that they see each other, but they are in standalone mode instead of an active/passive state for failover (image attached). Every attempt to sync via the button fails. There is probably some step or option that I have missed in my bumbling through this learning process, but for the life of me I can't seem to figure it out. Anyone got any suggestions what I need to look at to get this into an active/passive redundancy state?
Last updated: 2025-02-20
Post by janber0206 on Adding PLC to the List view resolves in Unknown Error
CODESYS Forge
talk
(Post)
Hello, I try to add one of my PLC from the Gateways to the List view. The Gateway is shown me as online, also i have other remote tools to verify the Internet connection is working. I do the Network Scan and the Gateway shows up, i select it and click on "Add to Server". Then I type in Username and password and click on confirm. There it shows me the "Unkown Error", see screenshot. If I use the wrong credentials it gives me the error message for this. Other Devices work fine it's just this one. Greetings Jannis
Last updated: 2025-02-21
Post by rshabsh on Using Latch Variable in Alarm as input from text list
CODESYS Forge
talk
(Post)
I am currently utilizing Alarm Manager’s Latch Variable 1 to display additional information related to alarms. However, instead of mapping this latch variable to a fixed PLC variable, I would like to dynamically update its text content based on the selected language in the system. To achieve this, I am considering using a text list that corresponds to different languages rather than directly linking Latch Variable 1 to a PLC variable. This approach would allow the displayed alarm information to be automatically translated according to the active language setting. Could you please confirm if this method is feasible within the Alarm Manager configuration? Additionally, if there are specific steps or best practices to follow when implementing this functionality, I would appreciate any guidance you can provide. Looking forward to your insights.
Last updated: 2025-02-26
Post by mkintegration on Reading Absolute Encoder Position From Yasakawa Drive
CODESYS Forge
talk
(Post)
I am looking to read in the absolute position of a yaskawa servo drive Sigma 7 that is using absolute encoder. It looks like yaskawa outputs this across there CN1 I/O connecter and during operation just outputs encoder pulses. But at boot up transmits the Multiturn data position and the Position within one rotation (pulse train) on two different wires. Once the drives are enabled it just uses incremental pulses. Does any one have experience with what IEC blocks to use to read this information in. I attached the Yaskawa Manual section that talks about the format.
Last updated: 2025-02-26
Post by mkintegration on Reading Absolute Encoder Position From Yasakawa Drive
CODESYS Forge
talk
(Post)
I am looking to read in the absolute position of a yaskawa servo drive Sigma 7 that is using absolute encoder. It looks like yaskawa outputs this across there CN1 I/O connecter and during operation just outputs encoder pulses. But at boot up transmits the Multiturn data position and the Position within one rotation (pulse train) on two different wires. Once the drives are enabled it just uses incremental pulses. Does any one have experience with what IEC blocks to use to read this information in. I attached the Yaskawa Manual section that talks about the format.
Last updated: 2025-02-26
Post by struccc on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I don't exactly recall where (I think some release notes), but I read the information that this multiple application / sub application feature is to be discontinued. Please, correct me, if I'm not right about this I am a bit sad about that - I was using that feature with more or less success. However I understand the reason behind the change: it introduces huge complexity, especially when dealing with multicore and safety support... AS I understand, it's to be replaced with the new virtual plc architecture, and standard ways for synchronizing / sharing data... So, for now the "Add application" context menu item was removed, but behind the scene it is still supported... Hint: if you still want to experiment with it, might try copy-paste things within the PLCLogic tree...
Last updated: 2025-02-28
Post by clarenced on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I got this working using OPC UA. In the logic application I just added a Symbol Configuration. In the HMI application I added a Data Sources Manager and OPC UA Data Source. The one thing I don't like is the way the tags end up being named in the HMI application. In the logic application I have a program named PLC_PRG. It has a variable named testDINT. In the logic application the name I get for this variable is DeviceSet.CODESYS_Control_Win_V3_x64.Resources.Logic.Programs.PLC_PRG.testDINT. This is very long and looks like it could change if I used this on a different device type. Any ideas how I could get this name shortened down to just PLC_PRG.testDINT like it is on the Logic application?
Last updated: 2025-03-06
Post by clarenced on Multiple applications on one device sharing variables.
CODESYS Forge
talk
(Post)
I got this working using OPC UA. In the logic application I just added a Symbol Configuration. In the HMI application I added a Data Sources Manager and OPC UA Data Source. The one thing I don't like is the way the tags end up being named in the HMI application. In the logic application I have a program named PLC_PRG. It has a variable named testDINT. In the HMI application the name I get for this variable is DeviceSet.CODESYS_Control_Win_V3_x64.Resources.Logic.Programs.PLC_PRG.testDINT. This is very long and looks like it could change if I used this on a different device type. Any ideas how I could get this name shortened down to just PLC_PRG.testDINT like it is on the Logic application?
Last updated: 2025-03-06
Post by felipemsgarcia on Axis EtherCAT address
CODESYS Forge
talk
(Post)
Hello, Thank you for your answer. I'm afraid I was not clear on what I was trying to achieve. I'm trying to change parameters and command axes from inside a function block and the first thing that came to my mind was pass both the EtherCAT slave and axis to the function block (as image attached). But, I believe it's worse than just pass directly the EtherCAT slave address to the function block (is it???). However I was wondering if there was a way to get the EtherCAT address directly from the axis, so I don't need to pass the EtherCAT slave nor the EtherCAT address to the function block. Thank you again!
Last updated: 2025-03-07
Post by pernockham on Inheritence of struct,
CODESYS Forge
talk
(Post)
Apparently my construction will not work as any of the sub-types are not be able to accept any (further) value-initiation. Ie: string_item : log_data_base := (string_value := 'test', val_type := STRING_); is not eq to (the string_value will not be assigned): string_item_2 : log_data_string := (string_value := 'test'); Because effectively for the compiler this is eq. to a "double" assignment where the compiler sees only the first assignment (my guess). string_item_2 : log_data_base := (val_type := STRING_) := (string_value := 'test'); Im not sure this should be treated as a bug, but it would surely be nice to be able to use this construction (compiler is 3.5.20.40). Anyone see any other alternative for solution (other than 4 complete STRUCTS with all fields individually defined)?
Last updated: 2025-03-07
Post by atone on CAA File Handling: "Read only" error
CODESYS Forge
talk
(Post)
In case of error while opening the file to read you assume that the file doesn't exist and try to create one. But it could be that the SD card is not ready yet or simply not there. I would try to check first if the SD card is there and accessible. Otherwise with FILE.Create you could end up creating a new directory that is not mapped to the SD card. This would explain the errors even after a reboot, though it doesn't explain the READ_ONLY_CAA error I guess? I would use FILE.DirOpen and FILE.DirList to check if the SD card is there and ready.
Last updated: 2025-03-20
Post by hemuv on Dialog Open
CODESYS Forge
talk
(Post)
I'm programming an HMI for a machine. I want to log all the parameter's changes (used text field for displaying and changing) for particular User levels. Created a Numpad and want to log oldvalue and Newvalue on 'ok' Button press. To retrieve the oldvalue, i check if the dialogue opened is my Numpad, Then I retrieve the dialogue interface via GetDialogInterface(ADR(myNumpad)) --> numpadData.stVariableValue which contain my oldvalue and save it locally. Problem is sometimes i retrieve the data and sometimes not. Also observed when Numpad Dialogue is Opened, VisuDlgUtil_IsDialogOpen returns False in some cycles.Attached you will find my Project. please let me know what went wrong or if there is a better approach to collect old and New Value of a textfield. Thank you.
Last updated: 2025-03-26
Post by anlebr on Alarm group template - Is it not possible with several instances?
CODESYS Forge
talk
(Post)
Hi In the POU section of my project I have created a Fan function block and defined an alarm group template for this FB with one alarm (Motor fault). In the PLC program I define two instances of the fan function block. When going to the alarm configuration and pressing "Create or update alarm instances", I get two alarms listed. So far so good. However, when I start my program and check the alarm table in the visualization I only see one alarm, even if both are active. Am I doing something wrong, or is it not possible to define alarms on a function block level and get one set of alarms per instance of the function block?
Last updated: 2025-04-01
Post by ameba on PersistentVars and Webvisu Element
CODESYS Forge
talk
(Post)
hello everyone I would like to try to better understand how persistent variables work. I created some boolean variables in the PersistentVars section initialized to the value TRUE. I have tied these boolean variables to toggle switches placed inside the HMI interface pages. Once the PLC program is started, the lever selectors, if operated, change their state, at least at a graphical level, but the persistent variables do not undergo any variation. Initially the above variables were declared as simple global variables, in this case the operation with the levers was correct; I then tried to transform them into persistent ones with the aim of using them as "settings saver" Thank you for support Bye
Last updated: 2025-04-03
Post by jampid on Struct Literal
CODESYS Forge
talk
(Post)
Bonjour Davidmic, Il n'est pas possible d'associer une méthode à une fonction. Cela est possible sur les Blocs fonctions. En utilisant ta DUT MyStruct, je créé une fonction avec en entrée un tableau de structure :** FUNCTION F_F3 : REAL VAR_IN_OUT // bien définir un type IN_OUT IN_ptrINT: ARRAY[*] OF MyStruct; // la taille sera définie ultérieurement/ END_VAR VAR _di: DINT; // Index de parcours du tableau pour l'écriture dans les cases ENDVAR ============== //Programme F_F3: FOR _di := LOWER_BOUND(IN_ptrINT,1) TO UPPER_BOUND(IN_ptrINT,1) DO IN_ptrINT[_di].som:=IN_ptrINT[_di].a + IN_ptrINT[_di].b; END_FOR J'utilise ensuite cette fonction dans un POU Programme : PROGRAM Test_F_Fx VAR _aiTAB9:ARRAY[0..3] OF MyStruct := [(a := 1, b := 1.2), (a := 2, b := 2.2), (a := 3, b := 3.3), (a := 4, b := 4.4)]; END_VAR ** ==========** F_F3(IN_ptrINT:=_aiTAB9 ); Voilà l'idée pour avancer. Une autre idée, est d'utiliser les pointeurs ou les références. Bon développement!
Last updated: 2025-04-07