Hello all, I have an PiXtend V2L complete kit and installed everything like in the manual. Ive installed Codesys V3.5 S20 Codesys Control for Raspberry Pi PiXtend_V2_Professional_for_CODESYS.package But as soon as i Create a Project, i get a lot of error messages, and i cant find the PLC via Ethernet Thanks a lot
Last updated: 2024-06-19
Post by gatto on variables between two applications
CODESYS Forge
talk
(Post)
Hello, I'm experimenting with two applications. I was able to start stop applications with the CmpApp library. Currently in my test the variables declared in the first application are not visible and writable in the second. I ask if there is the possibility of having variables that are visible both in the first application and in the second.
Last updated: 2024-06-22
Post by kuegerls on SysProcessExecuteCommand2 and CANopen Device
CODESYS Forge
talk
(Post)
I have now conducted some tests. The problem occurs when the Python script establishes an OPCUA connection, even if I only establish the connection without reading or writing any data. Is there another way to exchange data between Python and CODESYS without having to put in a lot of effort?
Last updated: 2024-06-24
Post by timvh on Persistent Retain Variables Not Visible in Online View (WAGO PFC100 + CODESYS)
CODESYS Forge
talk
(Post)
It is a known issue. It only happens with CODESYS and Wago controllers and the Persistent Variables. It seems related to using 64 bit variables in the PV list (e.g. LREAL). Internally in the PLC everything works okay. It is just a monitoring issue.
Last updated: 2025-10-26
Post by scrisp on Source code changes since last download
CODESYS Forge
talk
(Post)
Why does CODESYS 3.5 show the message “Source code changes since last download” even though I did not create or modify any new variables? When I go online with the PLC, it detects changes and suggests synchronizing, but nothing was actually changed in the project. What could cause this and how can I fix it?
Last updated: 2025-11-28
Post by gseidel on SMC_ERROR SMC_CGR_INVALID_POSPERIOD
CODESYS Forge
talk
(Post)
Hi blitz, that usually means that the modulo period, when converted to increments, is larger than 2^31. (The bus bandwidth is usually 2^32.) What is your "technical unit", do you program in angular degrees? And what is the modulo period? If you want you can post the drive configuration (screen shot of the "General" and "Scaling/Mapping" page). Best regards, Georg
Last updated: 2025-12-16
Post by eschwellinger on Deploy LicenseServer for Linux SL
CODESYS Forge
talk
(Post)
for the package you net to install 32bit support(to have the native timprovider availble to deploy) sudo apt-get install libc6:i386 Then native Safeplc and native Safetimeprovider should be available to install. Raspi yes - but there is no official package available till now and you need have a rt_preemt patched kernel on the Pi, then it works like charm
Last updated: 2025-11-18
Post by blitz on SMC_ERROR SMC_CGR_INVALID_POSPERIOD
CODESYS Forge
talk
(Post)
Codesys - SMC_ERROR SMC_CGR_INVALID_POSPERIOD - Invalid modulo period less than or equal to zero or greater than half the bus bandwidth. Has anyone seen this error and actually understands what it means and how to get rid of it? I tried to work around it by reducing the number of increments on the drive but then the drive itself starts throwing errors.
Last updated: 2025-12-15
Post by mascara on CloseTargetVisu
CODESYS Forge
talk
(Post)
I need to add a button to the Visualization to close it. And create a shortcut on the Windows desktop to reopen the Visualization. This is necessary to configure, for example, a local IP address. Is this possible? What command closes the Visualization? Which program opens Visualization? System: Win10 Codesys: Control RTE V3 x64 Program: Codesys V3.5 SP20 Using only a touchscreen monitor, without keyboard and mouse.
Last updated: 2026-03-11
Post by ilarioimi on Date Picker
CODESYS Forge
talk
(Post)
Hello, I am new here and need some help. I have added the Date Picker to a visualization page. The date selection works, but the current day is not highlighted. The date and time are displayed correctly by the system, which is set by default to “VisuElems.Visu_DateTime.DisplayUTC:= FALSE;”. Is there some project setting or Visualization Manager setting that I am missing? Thank you. Ilario.
Last updated: 2026-01-14
Post by davidbo on Two licenses have to be installed forgot to enable one license
CODESYS Forge
talk
(Post)
I have to install "Basic M" and "Visualization M", but it seems that during installation of "Basic M" you have to enable "Visualization S" I assume if you here after want to install my "Visualization M". And I forgot to enable "Visualization S" How do I fix that?
Last updated: 2026-02-02
Post by timvh on CODESYS: Combining Master Redundancy with EtherCAT Ring Topology – Is it Supported?
CODESYS Forge
talk
(Post)
Yes, this works (at least we have it running with Wago PLC and Beckhoff I/O), but the concept works. You need 2 PLC's with at leat 3 network interfaces. And 2 switches (can be unmanaged). See the attached simple diagram for the solution.
Last updated: 2026-02-05
Post by pernockham on Unable to deploy "Control for Linux SL 4.18.0.0"
CODESYS Forge
talk
(Post)
Ok, I think I understand. The problem is my language-setting being "swedish". I will check if I can switch to english. Update/confirmed. Change LANG to en_GB, this enabled the architechture to be correct and the control SL again to appear and to be possible to be updated. Thanks!
Last updated: 2026-02-23
Post by poliautomacao on Absolute movement controlled by an external encoder.
CODESYS Forge
talk
(Post)
Hello, is it possible to perform an MC_MoveAbsolute movement, and have the servo move using an external encoder (freeEncoder)? In my application, I have slippage on the main shaft of the servo motor, and I would like to add an encoder to measure the actual position of the material.
Last updated: 2026-03-04
Post by buczekj on ERROR: Calling the program "AlarmStorage_Prg" is not allowed from multiple tasks
CODESYS Forge
talk
(Post)
Many issues with the alarmmanager and alarmstorage can be solved by deleting the configuration, rebooting, and redownloading. I've found that the configurator doesn't always update when you make chanegs. For linux installations it is typically located in /var/opt/codesys/PlcLogic/alarms/ look for file Application.AlarmConfiguration.xml cd /var/opt/codesys/PlcLogic sudo rm -r alarms sudo reboot
Last updated: 2026-04-09
Post by automa on Best practice to reduce CPU load
CODESYS Forge
talk
(Post)
I am experiencing quite high CPU load on My Schneider M241 PLC with WebVisu. I would like to know what is best practice and how you create your application with pages, frames, tags, dialogs and settings to make an efficient HMI with low CPU load. Thanks
Last updated: 2026-04-10
Post by garyl on Comments in arrays and assigning RST coil's to 600 outputs
CODESYS Forge
talk
(Post)
Hello all, im working on a project that requires me to convert an old automation direct DirectSoft PLC d2-250-1. One of the problems im encountering is that all of the comments are attached to members of the different addresses. When i convert the addresses (1777 "C" registers, 777 X registers, and 20,0000 V registers) im running into difficulties keeping the inputs/outputs correct since they are missing documentation. Is there a good way to retain the comments of the indexes in the array? Secondly, initially i was declaring the "C" and "V" addresses individually and this worked to retain the comments as to which register did what, however i ran into a problem when one rung reset (or set to 0) approximately 600 C Addresses. Since each tag is separately declared this proved to be nearly impossible without a literal wall of code that attempted to crash the program. So i converted all of the registers (C,X,Y,V) into separate structs, declared them as arrays and pointed all of the original call outs in the program to the newly defined structs. However i have now lost comments and the program is very hard to follow. Thanks for any help with this issue.
Last updated: 2023-08-31
Post by danwoodlock on RPI Zero w - Edge gateway cant install
CODESYS Forge
talk
(Post)
Hello all, First post. I recently acquired an RPI zero W from amazon, and have been using it with Codesys v3.5 SP19 patch 2. I first got it working yesterday, and after installing the runtime on the Pi, I was prompted to install the edge gateway. Installation of the edge gateway failed because of unsupported architecture, undeterred I was able to connect to the pi and program as I wanted. The issue I've noticed is that if I do not load anything to the pi overnight, I can then no longer connect to the pi and download, although I can still ping it from my pc. I found that if I power cycle the PI, I am then able to connect again, and it works as normal. I did some googling and found instances where people recommended downloading the newest edge gateway, which brings me here. Wondering if there are any suggestions, or if this is a known issue. I actually tried installing all 3 versions of edge gateway for science, but all fail with the same message. Thanks -Dan
Last updated: 2023-09-13
Post by sturmghost on Initialization of visualization variables and cyclic code execution
CODESYS Forge
talk
(Post)
I'm looking for a smart and short way to implement initialization of visualization variables depending on the visualization input. For an easy example consider a rectangle which rests at XPos := 0 when the input state is false and at XPos := 50 when the input state is true. My visualization variables look like this: VAR_IN_OUT State : BOOL; END_VAR VAR XPos : INT; END_VAR I put this rectangle via a visualization frame element into another visualization and link a frame reference variable with the state to it. If the variable is true, the rectangle should rest at XPos := 50 and false at XPos := 0 at visualization init but how should I assign the 50 or 0 to the internal visualization variable XPos? I would need some init-methode for the visualization but I dont want a global init-method for such tasks. I want to do it inside of the visualization element but I can't see any solution for this? It would be good to be able to define ST-code within the visualization element which runs cyclic at each VISU_TASK task-cycle then I could just check the input state and change the XPos accordingly. Does someone have a solution?
Last updated: 2023-10-01
Post by timvh on VisuElems.CurrentUserGroupId is not stable
CODESYS Forge
talk
(Post)
I'm not sure what you are trying to do, but getting the CurrentUserGroupID like this will not work, because there could be multiple Visualization Clients and each can have a different user that is logged in. Also when you go online with CODESYS and open an Visualization, this is counted as a client. Probably this is the reason you see it changing. What you can to is "iterate" over all clients and then see which user is logged in on which visualization Client. For this you need to add the Visu Utils library to the project and call the FbIterateClients. See https://content.helpme-codesys.com/en/libs/Visu%20Utils/4.4.0.0/VisuUtils/VisuActionUtilities/Function-Blocks/FbIterateClients.html fbClientIteration( xExecute := x_Execute, itfClientFilter := VU.Globals.AllClients, itfIterationCallback := fbIterator, xDone => x_Done, xBusy => x_Busy, xError => x_Error, eError => e_Error); The fbIterator, in the example above, should be an instance of an FB which you have created yourself and this must implement VU.IVisualizationClientIteration. For example: FUNCTION_BLOCK FB_ITERATOR IMPLEMENTS VU.IVisualizationClientIteration Then automatically the corresponding methods will be called. In the HandleClient Method, you will get an interface to the client(s) and then you can get the current user through this interface: itfClient.UserGroupId You can also get the UserName: itfClient.UserName
Last updated: 2023-11-14
Post by climblinne on Calling OPC UA Methods from UaExpert
CODESYS Forge
talk
(Post)
Hello, I hope someone could help me. I installed the newest Codesys 3.5 SP 20 Patch 1. When loading the demo files from @i-campbell I can upgrade them to the latest version and everthing works on the OPC-UA client side as expected (object "a" is visible, I can use the "ExampleMethod"). Now I * remove the "Information Model", * delete the "OPC_UA_Symbols Objects", * Add "Information Model" again * add "TestRootObjectType" again and "Generate IEC declarations" * and search for mapped instances (to get instance "a" again) Very good still working as expected. Now I delete the OPC_UA_Symbols and add it again referring to the "objecttest" from 16.9.2020. Also I redo the steps from above. The result is now, that I can't see the "a" object in the "Root/Objects" folder. Why ist this and how can I make it running? I think, it could may be a different version of the UA configuration file. I tried to build my own model definition files and got the same problem (but I am really not an expert). When someone has a actual model, which is also running in the actual Codesys I would be very grateful. Or even better, how to make the correct model in e.g. UA Modeler SW (I followed the description https://documentation.unified-automation.com/uamodeler/1.6.0/html/howprojnet_sec.html).
Last updated: 2024-07-01
Post by tariq on Using Hilscher CIFX Cards as EtherCAT Masters in CODESYS
CODESYS Forge
talk
(Post)
Dear Codesys Support Team, I hope this message finds you well. I am currently working on a project that involves using a Hilscher CIFX card to act as an EtherCAT master within the CODESYS environment. Despite following the available documentation and setup guides, I have encountered some challenges and require assistance to ensure proper configuration and operation. Questions: 1- Could you please confirm if the Hilscher CIFX card is supported as an EtherCAT master in CODESYS? If so, are there specific drivers or configuration files that need to be installed? 2- Are there detailed setup guides or example projects available that demonstrate the integration of Hilscher CIFX cards with CODESYS for EtherCAT communication? 3- Is there any additional software or plugins required for ensuring seamless communication between the CIFX card and the EtherCAT slaves within CODESYS? Your support and guidance on these matters would be greatly appreciated, as it is crucial for the success of our project. Thank you for your time and assistance. I look forward to your prompt response. Best regards, TB
Last updated: 2024-07-02
Post by aliazzz on Unable to deploy Virtual Control SL on ARM64 (Raspberry Pi5)
CODESYS Forge
talk
(Post)
Hi, I have successfully deployed "Virtual Control SL" on a few x86/64 machines now. However, I'd now like to deploy this to a Raspberry Pi (ARM64). To do this I prepared the Raspberry Pi5 with the following prereq's; * Minimal PREEMPT Debian * Latest Bootfirmware * full SSH access via non-root account * Podman * RedHat Cockpit with CODESYS LicensServer plugin up and running However, I can't seem to resolve copying the correct (deploy) Images as they wont show up in the CODESYS IDE I have added CODESYS Virtual Control for Linux SL and the CODESYS LicenseServer for Linux SL via the CODESYS installer on my DevBox. I open CODESYS > Tools > Deploy Control SL Next I enter the SSH targets IP and Credentials and for my RPi5 and it shows "Connected". In the next tab, Deployment, the dropdown box only shows one (1) image, which also is the incorrect CPU architecture. Only Virtual Control AMDx64 shows up (!?) while I expect to see the ARM64 based images for both Edge and Control. Has someone encountered this too? I'd like to hear other people experiences with Virtual Control deployment on ARM based architecture. attachment 1: AMD64 based deployment pulldown menu (correct images) attachment 2: ARM64 based deployment pulldown menu (incorrect images) regards,
Last updated: 2024-07-28
Post by z870623 on About CPU Loading
CODESYS Forge
talk
(Post)
I am running a runtime environment on an ARM A35 dual-core processor (1.5GHz) and have encountered some issues. The CPU load (both CPU0 and CPU1) occasionally spikes above 50% before returning to normal, and this happens around 2-3 times per minute. At the same time, I’ve noticed that the Max Cycle Time in the Codesys monitoring screen shows much worse performance compared to the A53 (1.2GHz), with nearly double the cycle time. The optimizations I have made so far are as follows: Set the CPU to performance mode. Isolated CPUs: CPU0 is dedicated to running Linux services and the runtime itself, while CPU1 runs the EtherCAT task and the MainTask. Despite CPU1 only running these two tasks, the utilization still increases above 50%, which I find unreasonable. Additionally, I performed tests using cyclictest both without and with the runtime running. The performance is shown in the following image: From the results, I believe the CPU performance should be fine, but I am unsure why the monitoring results are not as expected. The testing outcomes should ideally be as close as possible to the cyclictest results. Does anyone have related solutions to this issue?
Last updated: 2024-10-14
Post by mubeta on Profibus DP master with EL6731 and automatic restart of slaves
CODESYS Forge
talk
(Post)
WHEREAS, I have already searched various posts and forums, where mostly there are few references and mostly geared toward integration in TwinCAT. I am looking for how to properly configure the EL6731 board as a DP master, (where I have its 3S license), with CoDeSys 3.5.19.x. I have three types of slaves, all integrated with their GSD descriptors. In the tab for the various slaves, I don't see options related to node restart on 'station return'. On the card manual, I read that for each slave I should be able to configure parameter 8000:2C: “8000:2C Restart behavior after DP fault Reserve, must be 0 BIT1 RW 0x00 (0dec)” However, in the project I see no way to configure this parameter, in any of the boards; and the arrays do not always have such an extensive size; most of the time they are only two or three words in size. The problem is that, after the hot reset of CoDeSys, the master restarts by starting all slave nodes, but if one or more get lost and go offline, there is then no automatic restart upon their return. I would need to figure out any solution, even via software, how to figure out that this one is back available and restart it.
Last updated: 2025-02-02
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.