Post by camjam on BOOL variable in OPC UA and modbus simultaneously
CODESYS Forge
talk
(Post)
I have come across this. The only way i could get it to work would be to define a word that is also the same address as the Bools. eg %MX600.0 through to %MX600.15 would be individually defined in the variables and them have another variable word defined at %MW300. You still need to break out the word in what ever program you are using to read/write the OPCUA tags.
Last updated: 2025-08-18
Post by micky on Mail_Service_SL Lib
CODESYS Forge
talk
(Post)
Hallo zusammen, ich habe folgendes Problem. Ich möchte mit der Lib Mail_Service_SL ein Mail versenden. Manchmal funktioniert es auch aber nicht zuverlässig. Wenn ich den Funktionsblock sendmail mit den entsprechenden Daten aufrufe bekomme ich die Fehlermeldung CHECK_RESULT_FAILD. Laut Dokumentation sollte im sServerMessage der Grund stehen, dieser ist aber leer. Was kann der Grund hierfür sein? Gibt es eine ander Lib mit der ich Mails versenden kann? Viele Grüße Micky
Last updated: 2025-08-19
Post by romrot on MS SQL Compact cutting off Database name?
CODESYS Forge
talk
(Post)
I'm trying to use an fbMsSQL_compact function to read data from an SQL database. It works with some databases, but there is one database that I can't seem to get it to work on. It's set up the same as the other databases that I've tested with the only difference I see is that the name of the database is cut off in the status message. I'll get a message like "User: User logged out succesfully from database: 12345" But the whole name of the database is something like 1234567.
Last updated: 2025-08-21
Post by kurtk on Screenshot with "Sys Process Execute Command"
CODESYS Forge
talk
(Post)
I am working on this same thing... I wonder if when you execute it in a "terminal" it is a graphical terminal window running under X whereas when it is run from a SysProcess, it is "headless" and hence X-less Does DISPLAY=:0 magically attach to the X session Wouldn't it make sense that scrot or imagemagick would automatically by default reference DISPLAY=:0 I'm just trying to figure out how this works or is supposed to work
Last updated: 2025-09-12
Post by timvh on How to change keyboard layout on the virtual keyboard?
CODESYS Forge
talk
(Post)
Maybe you have the "Devices" tab open(?), but the "templates" are in the POU pool. You can open it from the menu: View - POUs, or if it is already open, select the POUs tab which is normally next to the Devices tab. All objects which are part of a library are in the POU pool, because they should be device independent (at least most of them).
Last updated: 2025-09-18
Post by reinier-geers on CAnopen stack
CODESYS Forge
talk
(Post)
Ive got a project with 6 devices . Version 3.5.9.2 Now i change one to a other device 3.5.20.40 So i update the project to V3.5.20.4 Now i have a lot off faults in the canopendevices . Somehowe the first has no problem and seems that the canopenstackts stays in V3.5.9.2 the others in V4.2.0.0 But i cant put it back to 3.5.9.2 WHY ? And how can now witch one i can update and witch one not ?
Last updated: 2025-09-22
Post by reinier-geers on CAnopen stack
CODESYS Forge
talk
(Post)
Ive got a project with 6 devices . Version 3.5.9.2 Now i change one to a other device 3.5.20.40 So i update the project to V3.5.20.4 Now i have a lot off faults in the canopendevices . Somehowe the first has no problem and seems that the canopenstackts stays in V3.5.9.2 the others in V4.2.0.0 But i cant put it back to 3.5.9.2 WHY ? And how can now witch one i can update and witch one not ?
Last updated: 2025-09-22
Post by bmatlove on AXIS_REF_SM3 Error Codes?
CODESYS Forge
talk
(Post)
I'm trying to firm up alarming of axis faults. Declutter the code and figure out what's what. Diving into it, I see the AXIS_REF_SM3 function block provides uiDriveInterfaceError and dwErrorId, but I can't find any significance of these further than Drive interface error number Parameter number: 1014 and Drive specific error identifier, parameter number: 1031, respectively. Is there some corresponding appendix I could use to decode these? Also, is there any relation to the Error ID (of type SMC_Error) of the MC POUs? MC_Jog, MC_Reset, MC_MoveRelative, etc? If so, are the above errors redundant? Thanks in advance.
Last updated: 2025-09-22
Post by jzhvymetal77 on Special Chars in Visualizationfor QR code string
CODESYS Forge
talk
(Post)
In Visualization, is there any way to make special characters in a string display properly in a Text object? I wrote a function block to create QR codes at runtime. My code uses “$DB,” which in ASCII should render as a solid block. The code works, but to display it in Visualization I had to create multiple rectangles with visibility bound to a BOOL array. That works, but since each BOOL must be exposed as a separate variable, it consumes most of the available monitoring resources. See Attached image.
Last updated: 2025-09-29
Post by jzhvymetal77 on Special Chars in Visualizationfor QR code string
CODESYS Forge
talk
(Post)
In Visualization, is there any way to make special characters in a string display properly in a Text object? I wrote a function block to create QR codes at runtime. My code uses “$DB,” which in ASCII should render as a solid block. The code works, but to display it in Visualization I had to create multiple rectangles with visibility bound to a BOOL array. That works, but since each BOOL must be exposed as a separate variable, it consumes most of the available monitoring resources. See Attached image.
Last updated: 2025-09-29
Post by nz-dave on Bool turning on in case stament in wrong state?
CODESYS Forge
talk
(Post)
I have a case statement running a process. during one of the steps it has started calling a bool var that is 2 steps further on in the case? i have even tried //commenting it out but it still turns on at the same point in the case. i have also run a trace but cant see anything that would trigger it. Any Ideas? Cheers
Last updated: 2023-12-15
Post by macros8 on Translation - How to get text as reference in Frames translated?
CODESYS Forge
talk
(Post)
Hi, one more point. I have been able to create Property of Text which is added to Global text list so it´s fine. But as soon as I use Frame configuration I lose all other properties but some very basics. I need to have still possibility to set Input configuration because my element is Button. Do you know how to make visible all standard properties + my own properties created in Frame configuration? Thanks a lot. M.
Last updated: 2024-01-03
Post by usacodesysuser on How to connect serial devices ?
CODESYS Forge
talk
(Post)
@eschwellinger do you have any examples of using a USB barcode scanner? I have read through the forums here and I am unable to find how to get the barcode data to populate in a text field without having to first click into the text field to activate it. Is there a library that allows you to access the barcode data? I am really new to this in general any help is greatly appreciated, hopefully you have a pretty clear example
Last updated: 2024-01-06
Post by apurv on Cannot pass array of constant size to a function as a reference
CODESYS Forge
talk
(Post)
I have a Array of constant size defined like this Var Constant MAX_SIZE :UINT := 10; End_var VAR array : ARRAY[0..MAX_SIZE] OF INT; END_VAR Now I want to pass this array to a function by reference, Function fun : INT VAR_IN_OUT CONSTANT MAX_SIZE : UINT; END_VAR VAR_INPUT array : REFERENCE TO ARRAY[0..MAX_SIZE] OF INT; END_VAR but when I run this it gives strange Errors Error : Cannot Convert type 'ARRAY [0..MAX_SIZE] OF INT' to type 'ARRAY[0..MAX_SIZE] OF INT'
Last updated: 2024-01-07
Post by eschwellinger on Edge Gateway online, but PLC is not online
CODESYS Forge
talk
(Post)
we need some logfiles from the edge gateway /etc/Gateway.cfg [CmpLog] CmpEdgeGateway.Filter=0xFFFFFFFF Logger.0.Name=/tmp/codesysedge.log Logger.0.Filter=0x0000000F Logger.0.Enable=1 Logger.0.MaxEntries=100000 Logger.0.MaxFileSize=5000000 Logger.0.MaxFiles=1 Logger.0.Backend.0.ClassId=0x00000104 ;writes logger messages in a file Logger.0.Type=0x314 ;Set the timestamp to RTC and does the scan via Automation Server show the plc?
Last updated: 2024-01-09
Post by felipemsgarcia on Edge Gateway online, but PLC is not online
CODESYS Forge
talk
(Post)
Hi Edwin, The PLC is already in the automation server so nothing happens when I scan the network, however the PLC show offline (not connected). Please see logs below. [CmpLog] Logger.0.Name=codesysedge.log Logger.0.Filter=0x0000000F Logger.0.Enable=1 Logger.0.MaxEntries=100000 Logger.0.MaxFileSize=1000000 Logger.0.MaxFiles=1 Logger.0.Backend.0.ClassId=0x00000104 ;writes logger messages in a file Logger.0.Type=0x314 ;Set the timestamp to RTC Thank you!
Last updated: 2024-01-09
Post by haydermsalih on OSCAT Network LIBRARY: FTP_CLIENT
CODESYS Forge
talk
(Post)
Hello I am using FTP_CLIENT to donwnload/Upload a text or CSV file from FTP server. UpLoading from PLC to FTP server is working without any problem but when I try to download from FTP server I get an error. The FTP_CLIENT Block allows me to add URL but I do not where I can specify the direcory to save the downloaded file... is there anyone has an experience with downloading from FTP server using FTP_CLIENT block. Thanks in advance Hayder
Last updated: 2024-01-24
Post by jaspergain on Access to the path *** is denied
CODESYS Forge
talk
(Post)
Hello, Recently I upgraded to 3.5.19.50 and have been having errors/issues when doing a download/online change. The message as seen in the attachment pops up. The file in the path is different every time. However when I login again afterwards all works fine. This issue does not happen on older versions. Any clue what the issue could be? I did an reinstall/repair but the issue reappeared again... Thanks in advance!
Last updated: 2024-01-25
Post by wiresplus on INT_TO_WORD function not working
CODESYS Forge
talk
(Post)
Hello, I need to take an INT input, and convert it to a WORD value. VAR DRV2Speed : WORD; //IO card takes a WORD where 16000 = full 10V output (equivalent to 50Hz) PumpFillSpeed : INT; //Users enter a value between 0 and 50 END_VAR IF <conditions> THEN DRV2Speed :=INT_TO_WORD((PumpFillSpeed/50)*16000); END_IF </conditions> According to me this should work - but it stays at 0, no matter what. What am I doing wrong?
Last updated: 2024-01-26
Post by melle17 on Steuerung einer Geschirrspülmaschine
CODESYS Forge
talk
(Post)
Hallo, ich muss im Rahmen einer Hausarbeit die Steuerung einer Geschirrspülmaschine erarbeiten. Leider bin ich mit dem Programm noch nicht so vertraut und habe Probleme bei meinem Zeitschalter und finde leider selber das Problem nicht. Deswegen zu meiner Frage ob mir jemand helfen könnte. Und zwar kommt das meine Variablen nicht deklariert sind und ich finde aber nicht wieso. Die zwei Screenshots zeigen nochmal den Zeitschalter und das Programm wo der Zeitschalter eingesetzt wird. Vielen Dank im Voraus.
Last updated: 2024-01-30
Post by josephbourgeois on Tracking out product
CODESYS Forge
talk
(Post)
Hi everyone! I synchronize the operation of the tripod and the conveyor. I have a problem with the product tracking algorithm on the conveyor (PCS_1). Sometimes I need to stop tracking a product on command without completing the operation. I do this using MC_GroupStop. But when I need to start moving in WCS again (using fb movelinearabsolute), I get a tripod kinematics error - SMC_CP_INVALID_ORIENTATION (Invalid orientation (non-orthonormal matrix or non-unit quaternion, internal error)). MC_ResetGroup does not help. What could be the problem? Has anyone encountered this?
Last updated: 2024-02-05
Post by josephbourgeois on tracking out product
CODESYS Forge
talk
(Post)
Hi everyone! I synchronize the operation of the tripod and the conveyor. I have a problem with the product tracking algorithm on the conveyor (PCS_1). Sometimes I need to stop tracking a product on command without completing the operation. I do this using MC_GroupStop. But when I need to start moving in WCS again (using fb movelinearabsolute), I get a tripod kinematics error - SMC_CP_INVALID_ORIENTATION (Invalid orientation (non-orthonormal matrix or non-unit quaternion, internal error)). MC_ResetGroup does not help. What could be the problem? Has anyone encountered this?
Last updated: 2024-02-05
Post by jinlee on How do you get the CURRENT ClientData?
CODESYS Forge
talk
(Post)
Hi there, I wonder how to use this CURRENTCLIENTID. However, what I am trying to do is to use PLC_PRG.aIndexVisu[CURRENTCLIENTID]. to switch the frame within the mainpage without affecting the other screen same as the first question of this post. However, I failed to do it. Can you tell me how to do it ? Or can you advise me on this issue
Last updated: 2024-02-07
Post by matthew on New Ladder Diagram conversion does not work due to missing features
CODESYS Forge
talk
(Post)
Hi @eschwellinger, I have been trying out v1.0 of the new ladder and have a few questions. I have warnings Expression or part of it has no effect I can't get rid of them, what do they exactly mean? Using the ST_Block, is there a way when online to open the ST_Block and view the running code? Thanks!
Last updated: 2024-02-09
Post by andrax on Prüfen ob Datei existiert wenn nicht neu erstellen
CODESYS Forge
talk
(Post)
Hi, ich ich möchte prüfen ob eine Datei existiert. Wenn diese nicht existiert, soll eine erstellt werden und dort hinein geschrieben werden. Die Datei wird im Programmlauf mehrfach geöffnet und Daten hinein geschrieben. Ich will hier die Funktion File.MODE.MAPPENDPLUS benutzen, das funktioniert aber nicht. fopen.xDone bleibt false. Hier der Code: fopen.sFileName:=sFileName; fopen.eFileMode:=File.MODE.MAPPENDPLUS; // Neu erstellen und anhängen fopen.xExclusive:=TRUE; fopen( xExecute:=TRUE); IF fopen.xDone THEN hFile:=fopen.hFile; sStringToWrite:=''; writeIndex:=0; SchrittDatenlog:=60; END_IF Wo liegt mein Fehler?