Temperature Input to PID time base output

frankwim
2006-11-19
2008-01-10
  • frankwim - 2006-11-19

    Hello, We are using a wago 750-841 and CoDeSys for the first time and have a PID application in which we need help. We will use a 750-469 Type J T/C module and would like PID control to output an on/off pulse (750-530) based on percent output of the function block. In other words...no output at 0 percent and full on output at 100%. At 50% with a 1 second cycle time the pulse width would be .5 sec on and .5 sec off. Is the PID_Fixcycle function block the best choice? What is the output units of the function block; 0-100% or 0-32767 16 bit range? Has anyone ever done the math for converting the function block output demand to a time based pulse width? TIA

     
  • Anonymous - 2008-01-09

    Originally created by: Nicolai_Hanssing

    frankwim hat geschrieben:
    Hello, We are using a wago 750-841 and CoDeSys for the first time and have a PID application in which we need help. We will use a 750-469 Type J T/C module and would like PID control to output an on/off pulse (750-530) based on percent output of the function block. In other words...no output at 0 percent and full on output at 100%. At 50% with a 1 second cycle time the pulse width would be .5 sec on and .5 sec off. Is the PID_Fixcycle function block the best choice? What is the output units of the function block; 0-100% or 0-32767 16 bit range? Has anyone ever done the math for converting the function block output demand to a time based pulse width? TIA

    The PID-fixed cycle is just a PID-controlle wher eit has to be called with a fixed time-interval, nothing else. Its still an analog output.

    Converting a analog signal to PWM when using fixed scanrate is very simple, and only takes few lines if code.

    SAy fixed cycltime for the PLC-scan of 10ms, dutycycle of 1sec:

    AO <-- Analog output to be converted [0..100%]

    cnt <- cyclecounter

    DO <-- Digital PWM-output for heating-coil

    cnt:=cnt+1;

    if count>=100 then; cnt:=0; end_if

    DO := AO>cnt

    Can be done with more finesse (among other things using residuals).

    Regards

    Nicolai Hanssing

     
  • hugo - 2008-01-10

    you can find everything you need in source code on

    w www.oscat.de w

     