CoDeSys and C5-PCC (KEB)

Anonymous
2005-08-25
2005-09-06
  • Anonymous - 2005-08-25

    Originally created by: V.Pupkin

    Connection KEB C5-PCC (Programmable Communication Controller) with the CoDeSys via the Ethernet interface produced with the next settings:

    Online -> Communication Parameters...
    Address: 192.168.0.95 (IP of the C5)
    Port: 1200
    Block Size: 512
    Motorola Byteorder: Yes
    

    At the attempt to make connection with C5-controller CoDeSys writes in window "Messages": . But at that time gives out the message . All adjustments are taken from Users Manual of C5-PCC, IP of the unit is also true... Please help us to solve this problem.

     
  • Anonymous - 2005-08-30

    Originally created by: DP

    If I were you first of all I check connection PC<->PLC with ping. If connection is OK then make sure that CoDeSys runtime system is executed.

     
  • Anonymous - 2005-09-06

    Originally created by: V.Pupkin

    DP hat geschrieben:
    If I were you first of all I check connection PC<->PLC with ping. If connection is OK then make sure that CoDeSys runtime system is executed.
    Thanks. Now is Ok. It was necessary to establish additional components and libraries Π‘5... I'm an idiot

     