Problem with Controller Indide and Codesys

Schatten
2005-09-30
2024-10-17
  • Schatten - 2005-09-30

    Hi, I have a communication problem between a Controller Inside made by Telemecanique and Codesys software v.2341. The problem is that it won't communicate on the RS232. The parameters were default 38400 baudrate parity:no COM1. If I change the baudrate I get a 33% quality for the first time I try to log, then 0%.

    I will paste below the log file:

    ##INSPECTOR-LOG-FILE##

    ##SECTION:HEADER##

    Instance=TODO: Lokal_

    Driver=Serial (RS232)

    Port=COM1
    
    Baudrate=19200
    
    Parity=No
    
    Stop bits=1
    
    Motorola byteorder=No
    

    Project=JP_ProjetRSX3600.pro

    Channel=1

    Created=2005-09-30 15:32:42.576
    
    Client=Local #0
    

    ##SECTION:TRACE##

    ##SECTION:SUMMARY##

    Terminated=2005-09-30 15:32:49.201

    Quality=33%

    Total=3
    
    Failed=2
    
    Β΅s per read=Unknown
    
     
  • Schatten - 2005-10-01

    I have tried with a bluetooth device and works until the end of transfer, then it disconects with the same network error. This is very strange, no one has worked with controller inside before?

     
  • Schatten - 2005-10-06

    Problem solved, the cable was bad.

     
  • Schatten - 2005-10-10

    Ok now I have other question, altho I can see that no one worked with controller inside programmed by codesys. The controller has 4 words inside a PDO3 package that is sent on canopen as far as I know. What I do not now is the adresses of those 4 words, so I can send informations across the canopen network. Any ideas?

     