What controller are you using? Do you need to have a memory card present but the card is not there or perhaps write protected? Those are the main things that come to mind for me.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I am using Turck BL67-PG-DP programmable gateway. The unit has built in memory for boot project storage. I was suspecting that the memory might be corrupted, but I was not sure.
Let me know if there any other way to fix this.
Thanks!
Tariq
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I know this may sound simple but have you tried a Project-Clean All then a rebuild and a download? Does Turck give you a way to "reset" the PLC like back to a bootloader or something to start from scratch?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
tariq_ghuman hat geschrieben:
Hi Norm,
I am using Turck BL67-PG-DP programmable gateway. The unit has built in memory for boot project storage. I was suspecting that the memory might be corrupted, but I was not sure.
Let me know if there any other way to fix this.
Thanks!
Tariq
Ciao.
You managed to solve the problem ? I use the BL20-PG-EN-IP. I have the same problem. The firmware update does not help. This is my third controller with a mistake in the last month . What to do?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I have run into this problem on a ABB PM564 and it turned out to be too many Web Visu files (User Disk size).
Delete some Web Visu data and see if you can create a boot project.
Last edit: meisterbond 2020-06-16
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi Guys,
I am getting this error when trying to create a boot project:
The last online service has not been executed correctly!
Service number: 47, Error number: 80
File 'DEFAULT.PRG' could not be written.
Let me know if anyone can help!
Thanks!
Tariq
Hi Tariq,
What controller are you using? Do you need to have a memory card present but the card is not there or perhaps write protected? Those are the main things that come to mind for me.
Hi Norm,
I am using Turck BL67-PG-DP programmable gateway. The unit has built in memory for boot project storage. I was suspecting that the memory might be corrupted, but I was not sure.
Let me know if there any other way to fix this.
Thanks!
Tariq
I know this may sound simple but have you tried a Project-Clean All then a rebuild and a download? Does Turck give you a way to "reset" the PLC like back to a bootloader or something to start from scratch?
empty your plc, the files that are not overwritten are kept in memory of plc, thus filling it up.
got same shit with wago, however after a reset it worked fine again.
Ciao.
You managed to solve the problem ? I use the BL20-PG-EN-IP. I have the same problem. The firmware update does not help. This is my third controller with a mistake in the last month . What to do?
I have run into this problem on a ABB PM564 and it turned out to be too many Web Visu files (User Disk size).
Delete some Web Visu data and see if you can create a boot project.
Last edit: meisterbond 2020-06-16