I got a problem with the communication between the codesys 2.3.9.35 and the PLC WAGO 750-880, a screen appears:"No gateway with the given settings could be found", when I try to setup the communication parameters, I need help, I've been trying to solve this problem for several days,
Hi,
this issue occure since one of the many Windows updates on some machines,
this is solved with current CODESYS 2.3 Version
2.3.9.41 or use the standalone Gateway Setup, but the better solution is to ask
the Wago-Support if it is safe to migrate to the newest Version with the wago targets.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
are the communication settings correct like direct 9600, etc.
changeable with wago ethernet settings.
please have the computer and the plc almost same number like 192.168.2.201 and 192.168.2.202
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Thankyou very much Edwin, I didn´t understand about the standalone gateway setup, this is a software WAGO? or Codesys?
Edwin Schwellinger hat geschrieben:
Hi,
this issue occure since one of the many Windows updates on some machines,
this is solved with current CODESYS 2.3 Version
2.3.9.41 or use the standalone Gateway Setup, but the better solution is to ask
the Wago-Support if it is safe to migrate to the newest Version with the wago targets.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Dear Shooter, yes the configuration is right, I think that must be something like Edwin Schwellinger is suggesting, but I can´t find the solution yet!
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Go to Online>Communication Parameters...>Gateway>TCP/IP> Click on "New..." and reestablish your connections with whatever IP address and set up information you have.
Bypass whatever is necessary as you may have to redownload to the PLC.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I got a problem with the communication between the codesys 2.3.9.35 and the PLC WAGO 750-880, a screen appears:"No gateway with the given settings could be found", when I try to setup the communication parameters, I need help, I've been trying to solve this problem for several days,
best regards,
Carlos Eduardo Ibáñez
e carloseduardo@koeln.com.bo e
Hi,
this issue occure since one of the many Windows updates on some machines,
this is solved with current CODESYS 2.3 Version
2.3.9.41 or use the standalone Gateway Setup, but the better solution is to ask
the Wago-Support if it is safe to migrate to the newest Version with the wago targets.
Hello eschwellinger, would it be possible for you to also review my issue? you can find it under this link https://forge.codesys.com/forge/talk/CODESYS-V2/thread/c6ec7fd23a/
are the communication settings correct like direct 9600, etc.
changeable with wago ethernet settings.
please have the computer and the plc almost same number like 192.168.2.201 and 192.168.2.202
Thankyou very much Edwin, I didn´t understand about the standalone gateway setup, this is a software WAGO? or Codesys?
Dear Shooter, yes the configuration is right, I think that must be something like Edwin Schwellinger is suggesting, but I can´t find the solution yet!
I'm pretty sure that this will help on that problem.
I've send you a link to download it.
cheers
I would like more information on how to solve the problem
Go to Online>Communication Parameters...>Gateway>TCP/IP> Click on "New..." and reestablish your connections with whatever IP address and set up information you have.
Bypass whatever is necessary as you may have to redownload to the PLC.