i need advice. i have an application that communicates to CoDeSys V2.3 Via opc using Soft-PLC PLCWinNT only. but i want to use Codesys Vr3. is it possible to load Vr3 program into Soft-PLC PLCWinNT? if not, is there a target package that i can install into codesys vr3 that can run PLCWinNT instead of control V3?
regards
Tressure
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
I think this should work with not that much effort -
Just Import the PLCWinNT Project to CODESYS V3 (you need for the the import the CODESYS V3 32Bit version)
Depending on which IO devices are involved ( which fieldbus) It is more or less effort then.
But anyway I would just motivate to change the communication to OPC UA then.
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi all.
i need advice. i have an application that communicates to CoDeSys V2.3 Via opc using Soft-PLC PLCWinNT only. but i want to use Codesys Vr3. is it possible to load Vr3 program into Soft-PLC PLCWinNT? if not, is there a target package that i can install into codesys vr3 that can run PLCWinNT instead of control V3?