Hi, it looks like you have enabled Codesy V2 runtime version instead of e!RUNTIME. Check this settings in wago ethernet settings or in WB Management
Wysłane z mojego PLK-L01 przy użyciu Tapatalka
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Anonymous
-
2018-11-21
Originally created by: mg
That is not possible. I used the CODESYS PFC 200 version. ... not the WAGO Ecockpit, there I have not possibility to choose V2.3. For this I need to download the PFC200 first (originally I hacve done this in the 64bit-Version, then I changed to the 32bit-version ... NEW-IDEA!!! ... maybe it has done something wit this, but I do not tested it yet.)
Other hint:
When I use an other htm-File, eg visu.htm. And I put it the correct IP-Adress normally it should automatically switch to the "WEBVISUALLISIERUNG" visu.htm -> But in my case ....
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Das hat nichts mit 64 Bit und 32 Bit CODESYS zu tun das geht mit beiden
Wenn man ein neues Projekt mit Wbevisu anlegt heißt der Aufruf: http://IP_DES_PFC200:8080/webvisu.htm
Schau bitte im VisuManager ob du das übertragen der Visu Dateien versehentlich deaktiviert hast...
Grüße
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Anonymous
-
2018-11-21
Originally created by: mg
Hallo Edwin
Wie das mit dem Visu.htm und/oder WebVisu.htm ist mir schon klar. Ich habe vielleicht bei meine Screenshots etwas ungünstige Beispiele dazugegeben.
TROTZDEM: ES WIRD DEFINITIV AUF EIN JAVA APPLET VERWIESEN!
Lt unserer Recherche geschieht das im File
root@PFC200-426DFA:/etc vi webserver_conf.xml
Dort steht ... (siehe Anhang 2)
Wir habe das auch mal testweise geändert und dann kam ... (siehe Anhang 1) (zumindestens das rote rotierende Kreislein)
Nunja das war nur ein kleiner Test: ABER ICH BIN MIR SICHER SO KANN MAN DAS NICHT MACHEN ...
WIE SOLL ICH WEITER VERFAHREN
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Originally created by: mg
Ich bringe die WEBVISU auf keinen Browser. Ich bekomme immer ein leeres BrowserFenster
Erst Mal ... WEBVISU im Engineering Programm funktioniert
Aber im Browser gehts nicht ...
Ich verwende überlicherweise: http://xxx.xxx.xxx.xxx:8080/webvisu.htm
Habs aber auch mit:
http://xxx.xxx.xxx.xxx/webvisu.htm
http://xxx.xxx.xxx.xxx/webvisu/webvisu.htm
http://xxx.xxx.xxx.xxx:8080/webvisu/webvisu.htm probiert
ausprobierte Browser: Firefox, chrome, Ie
Hinweis: Interessanterweise sagt der IE sogar, daß ich auf JAVA zugreifen würde. Im Entwicklertool sieht es so aus als wäre das die WEBVisu aus der Codesys V2.3. Muß ich da noch was im Linux auf dem PFC200 ändern, daß das geht.
Hi, it looks like you have enabled Codesy V2 runtime version instead of e!RUNTIME. Check this settings in wago ethernet settings or in WB Management
Wysłane z mojego PLK-L01 przy użyciu Tapatalka
Originally created by: mg
That is not possible. I used the CODESYS PFC 200 version. ... not the WAGO Ecockpit, there I have not possibility to choose V2.3. For this I need to download the PFC200 first (originally I hacve done this in the 64bit-Version, then I changed to the 32bit-version ... NEW-IDEA!!! ... maybe it has done something wit this, but I do not tested it yet.)
Other hint:
When I use an other htm-File, eg visu.htm. And I put it the correct IP-Adress normally it should automatically switch to the "WEBVISUALLISIERUNG" visu.htm -> But in my case ....
Hi,
wenn du den Namen wie in deinen Screenshot änderst musst du:
http://IP_DES_PFC200:8080/visu.htm
aufrufen!
Das hat nichts mit 64 Bit und 32 Bit CODESYS zu tun das geht mit beiden
Wenn man ein neues Projekt mit Wbevisu anlegt heißt der Aufruf:
http://IP_DES_PFC200:8080/webvisu.htm
Schau bitte im VisuManager ob du das übertragen der Visu Dateien versehentlich deaktiviert hast...
Grüße
Edwin
Originally created by: mg
Hallo Edwin
Wie das mit dem Visu.htm und/oder WebVisu.htm ist mir schon klar. Ich habe vielleicht bei meine Screenshots etwas ungünstige Beispiele dazugegeben.
TROTZDEM: ES WIRD DEFINITIV AUF EIN JAVA APPLET VERWIESEN!
Lt unserer Recherche geschieht das im File
root@PFC200-426DFA:/etc vi webserver_conf.xml
Dort steht ... (siehe Anhang 2)
Wir habe das auch mal testweise geändert und dann kam ... (siehe Anhang 1) (zumindestens das rote rotierende Kreislein)
Nunja das war nur ein kleiner Test: ABER ICH BIN MIR SICHER SO KANN MAN DAS NICHT MACHEN ...
WIE SOLL ICH WEITER VERFAHREN
Hi,
meld dich bitte mal über den Store -> meine Frage -> Bugreport.
Auch wenn es in diesem Fall kein Fehler ist
Grüße
Edwin
Originally created by: mg
Noch ein ABSCHLUSSBERICHT:
Danke dem Hr. Schwellinger.
Es war die FW10 (Wago) drauf. Mit der hat es nicht funktioniert. Nach einem Update auf FW11 ging es wunderbar.