Hi all,
Can anyone tell me how to configure a Wago 750-632 module for 2 valve operation?
The manual (http://www.wago.mx/download.esm?file=%5 ... xx_0en.pdf) says that I need 12 bytes to achieve that but my valve configuration shows only 6.
I'm using the Wago 750-632 and several other cards on a PFC200.
Thanks in advance.
Hi, could you please ask this question in the CODESYS store, 'my question' an adapted device description is needed.
BR Edwin
Use Wago I/O Check to configure wether its 1 or 2 coils among other things.
Hi, and you need an slightly changed/extended device description... BR Edwin
device_632_BothTypes.xml [1.09 MiB]
Thanks for the replies.
@Edwin I've asked this in the CODESYS store and they sent me a editted XML file.
somlioy hat geschrieben: Use Wago I/O Check to configure wether its 1 or 2 coils among other things.
I think these cards are configured for two valves out of the box. (I checked this with I/O Check)
Log in to post a comment.
Hi all,
Can anyone tell me how to configure a Wago 750-632 module for 2 valve operation?
The manual (http://www.wago.mx/download.esm?file=%5 ... xx_0en.pdf) says that I need 12 bytes to achieve that but my valve configuration shows only 6.
I'm using the Wago 750-632 and several other cards on a PFC200.
Thanks in advance.
Hi,
could you please ask this question in the CODESYS store,
'my question' an adapted device description is needed.
BR
Edwin
Use Wago I/O Check to configure wether its 1 or 2 coils among other things.
Hi,
and you need an slightly changed/extended device description...
BR
Edwin
device_632_BothTypes.xml [1.09 MiB]
Thanks for the replies.
@Edwin
I've asked this in the CODESYS store and they sent me a editted XML file.
I think these cards are configured for two valves out of the box. (I checked this with I/O Check)