Problem:
EtherCAT device might disconnect after running 2~3 hours, the red triangle appear on the left side of the EtherCAT device.
Any of experience shared from you would be appreciated.
br/listenyang
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Edwin Schwellinger hat geschrieben:
Hi,
please check the plc log for more Information
cu
Hi, Edwin
attached is the picture, i counldn't got any information in that, can you help to check a little bit???
<loggerentries xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance" xmlns:xsd="http://www.w3.org/2001/XMLSchema">
<logger name="<Default logger>">
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
... ...
... ...</logger></loggerentries>
thanks a lot...
br/listenyang
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
hi,
either there is really a disconnect Problem by Hardware (wiring) or somehow, the Driver does not manage to send and receice ethercat frames, which CODESYS Ethernet Driver are you using eepro 1000 or realtek?
cu
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Edwin Schwellinger hat geschrieben:
hi,
either there is really a disconnect Problem by Hardware (wiring) or somehow, the Driver does not manage to send and receice ethercat frames, which CODESYS Ethernet Driver are you using eepro 1000 or realtek?
cu
hi, Edwin
I dodn't remember exactly what CODESYS Ethernet Driver using.
but the original Adapter is: Intel(R) Gigabit Network
Ethernet Driver name is:net541ex.inf
after update Driver, it showing:CoDeSys EtherExpress GBit PCI Ethernet Adapter
br/listenyang
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Edwin Schwellinger hat geschrieben:
hi,
either there is really a disconnect Problem by Hardware (wiring) or somehow, the Driver does not manage to send and receice ethercat frames, which CODESYS Ethernet Driver are you using eepro 1000 or realtek?
cu
hi, Edwin
one more thing, every time when this problem happen, it need update the Driver the Adapter again, and the MAC address has changed in EtherCAT Master, and need to press brower button and select the correct Adapter again.
br/listenyang
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
this seems to be the problem,
what exactly you mean with 'it need update the Driver the Adapter again' you mean you have to reinstall the Windows driver?
- I thought this is a Control RTE System (with SoftMotion)?
Never seen that....
cu
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Edwin Schwellinger hat geschrieben:
this seems to be the problem,
what exactly you mean with 'it need update the Driver the Adapter again' you mean you have to reinstall the Windows driver?
- I thought this is a Control RTE System (with SoftMotion)?
Never seen that....
cu
hi, Edwin
'it need update the Driver the Adapter again' means:
go property of network adapter, and update Driver, select has disk, browse the file:net541ex.inf, and need to browse the adapter for EtherCAT Master.
i hadn't seen this, only the onsite people tolk me about that.
I thought this is a Control RTE System (with SoftMotion)?
I have no idea about this, but the device is: CoDeSys Control from ABB Engineering
br/listenyang
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
"EtherCAT disconnect automatically when running 2~3 hours" even couple of miutes
Dear Admin
I faced similar problem with 2 different raspberry pi_3 and beckhoff EK1100 (ethercat communication) While I power on system starts to run for a while then I get this problem If I force to PLC as a Online->Reset_cold then Dubug->start
Problems solving (this symptom shows me it is not a cabling problem)
Do you have any idea?
Image taht shows you error sequence
Image that shows you ethercat status
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Mine system equipped with Raspberry pi (licansed)
Even if you see attachment in mine previous post you will undrestand it
Δ°n mine case PLC Application is running
Problem is: Ethercat communication terminating rundomly and can able to restart with commands Please see prewious post
I accept from this sympton (Ethercat bus cupler is ok)
How we can figure out what is the problem ?
Do you know any command via Putty that we can check status of ethercat communications
Do you have any suggestion? (Please dont tell me cable ext... already changed )
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hi,
do you have applied a rt_preemt patch on your Rasbian?
Seems that distributed clocks is enabled on any slave in your network. ( If you need this - rt_preempt is needed probably)
If not a workaround might be ( depends on your application needs) to enable restart slave in the ethercat master (brings the slaves up back operational)
Anyway you need to check the jitter in the taskmonitor on the ethercatmaster Task and the plc logger if it occure.
In your case it Shows a changed Network amount slave..?!
BR
Edwin
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
hi, all
System HWοΌ
1.IPC+win7 Ultramate
2.CODESYS V3.5 SP3
3.EtherCAT Master + 1 ABB Servo Driver
4.Modbus TCP Master + 1 AC500(ABB Product)
Problem:
EtherCAT device might disconnect after running 2~3 hours, the red triangle appear on the left side of the EtherCAT device.
Any of experience shared from you would be appreciated.
br/listenyang
Hi,
please check the plc log for more Information
cu
Hi, Edwin
attached is the picture, i counldn't got any information in that, can you help to check a little bit???
<loggerentries xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance" xmlns:xsd="http://www.w3.org/2001/XMLSchema">
<logger name="<Default logger>">
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Warning: number of slaves has changed or is different to the configuration!</entry>
<entry severity="error" component="IoDrvEtherCAT" user="nobody" timestamp="8/8/2013 11:56:20">Error: communication lost ! check the cables !</entry>
... ...
... ...</logger></loggerentries>
thanks a lot...
br/listenyang
hi,
either there is really a disconnect Problem by Hardware (wiring) or somehow, the Driver does not manage to send and receice ethercat frames, which CODESYS Ethernet Driver are you using eepro 1000 or realtek?
cu
hi, Edwin
I dodn't remember exactly what CODESYS Ethernet Driver using.
but the original Adapter is: Intel(R) Gigabit Network
Ethernet Driver name is:net541ex.inf
after update Driver, it showing:CoDeSys EtherExpress GBit PCI Ethernet Adapter
br/listenyang
hi, Edwin
one more thing, every time when this problem happen, it need update the Driver the Adapter again, and the MAC address has changed in EtherCAT Master, and need to press brower button and select the correct Adapter again.
br/listenyang
this seems to be the problem,
what exactly you mean with 'it need update the Driver the Adapter again' you mean you have to reinstall the Windows driver?
- I thought this is a Control RTE System (with SoftMotion)?
Never seen that....
cu
hi, Edwin
'it need update the Driver the Adapter again' means:
go property of network adapter, and update Driver, select has disk, browse the file:net541ex.inf, and need to browse the adapter for EtherCAT Master.
i hadn't seen this, only the onsite people tolk me about that.
I have no idea about this, but the device is: CoDeSys Control from ABB Engineering
br/listenyang
"EtherCAT disconnect automatically when running 2~3 hours" even couple of miutes
Dear Admin
I faced similar problem with 2 different raspberry pi_3 and beckhoff EK1100 (ethercat communication)
While I power on system starts to run for a while then I get this problem
If I force to PLC as a Online->Reset_cold then Dubug->start
Problems solving (this symptom shows me it is not a cabling problem)
Do you have any idea?
Image taht shows you error sequence
Image that shows you ethercat status
Any one have similar problem?
I have the same problem
Hi,
which plc are you using?
Are there other fielbus involved ( for example modbus connections)?
BR
Edwn
Dear Edwin
Mine system equipped with Raspberry pi (licansed)
Even if you see attachment in mine previous post you will undrestand it
Δ°n mine case PLC Application is running
Problem is: Ethercat communication terminating rundomly and can able to restart with commands Please see prewious post
I accept from this sympton (Ethercat bus cupler is ok)
How we can figure out what is the problem ?
Do you know any command via Putty that we can check status of ethercat communications
Do you have any suggestion? (Please dont tell me cable ext... already changed )
Hi,
do you have applied a rt_preemt patch on your Rasbian?
Seems that distributed clocks is enabled on any slave in your network. ( If you need this - rt_preempt is needed probably)
If not a workaround might be ( depends on your application needs) to enable restart slave in the ethercat master (brings the slaves up back operational)
Anyway you need to check the jitter in the taskmonitor on the ethercatmaster Task and the plc logger if it occure.
In your case it Shows a changed Network amount slave..?!
BR
Edwin