Legacy IFM CANopen I/O modules with CR710S / CODESYS 3.5

mankh
2026-09-25
14 hours ago
  • mankh - 2026-09-25

    Hi,

    I am migrating an existing IFM system from CR0020 + CODESYS 2.3 to CR710S + CODESYS 3.5.

    The existing CANopen I/O modules are:

    CR9011
    CR2042
    CR2011

    My questions are:

    Can these legacy IFM CANopen modules be used as slaves with the CR710S CANopen Master?
    Can their existing EDS files be imported directly into CODESYS 3.5?
    Are there any known compatibility issues with the old IFM EDS files, PDO mapping, or startup SDO configuration?
    Has anyone successfully used these modules with a CR710S? If so, could you share the recommended configuration procedure?

    The goal is to replace the CR0020 with a CR710S while keeping the existing CANopen I/O modules

     
    πŸ‘
    1
  • TimvH

    TimvH - 2026-09-29

    Yes, you can use the .eds files also in CODESYS 3. Install them through the menu Tools - Device Repository. Then you can add the CANopen devices to your CANopen manager in your device configuration.

     
  • mankh - 2026-10-01

    Thanks,You sure there are not compatibility issues with the old IFM EDS files, PDO mapping, or startup SDO configuration in CODESYS 3.5?

     
  • TimvH

    TimvH - 2026-10-02

    I don't work for IFM, nor for CODESYS and didn't create the .eds file or developed the CAN protocol. I have no knowledge of the exact contents and SDO's or PDO's which are exchanged. So no, I am not sure. But if the .eds file confirms to the CANopen specifications, why shouldn't it?

     
  • YIN

    YIN - 14 hours ago

    Hi mankh, your follow-up is the right question to ask, because the EDS import itself is usually the easy part. CANopen is a standard and the CR710S manager just reads what the file describes, so a conforming EDS will load fine through the Device Repository. Where I have seen these migrations bite is not the file format but what the file assumes. The old EDS files sometimes carry default PDO mappings that don't match how the modules were actually configured under 2.3, so after importing I would open the PDO mapping for each module and compare it against the old CR0020 project before trusting it. Same story for the startup SDO entries, check that the values the manager writes on boot are the ones your old system used, and look at the heartbeat and node guarding settings and the baud rate. A module stuck in pre-operational can look like a wiring fault when it is really a config mismatch. One thing that helped me on a similar swap was to bench-test with a single module first, get it to Operational with the CR710S, and only then add the rest. If a module refuses to come up, a CAN trace usually shows quickly whether it is the mapping, an SDO abort, or a node ID clash. I would do all of this offline first and only download to the machine once the bench setup behaves, and keep the safety circuits out of anything you are still experimenting with.

     