I'm using two Profinet Controller. The first one is a Siemens S7-1516f (controller 1), the second one is a CoDeSys SoftPLC (controller 2). The Profinet Device is a Wago 750-375 (device) with several modules.
TIA 15.1 is used to configure controller 1 and the device. The device is marked as Shared Device and its modules are assigned.
In Codesys (V3.5 SP17 Patch 3 +) controller 2 and the devices are configured. The device is also marked as Shared Device. And here's the tricky part, which I need the guidance. Is there a way to assign the modules of the device to the controller 2?
So far I've looked through multiple options and didn't found anything. Even googling did not lead to any result.
Many thanks in advance!
Tobi
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I've got it and there is no interface to assign the modules to a controller. The solution is to deactivate every module that is used by controller 1 (within Codesys) and let all the modules used by controller 2 active.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hey there, I need some guidance.
I'm using two Profinet Controller. The first one is a Siemens S7-1516f (controller 1), the second one is a CoDeSys SoftPLC (controller 2). The Profinet Device is a Wago 750-375 (device) with several modules.
TIA 15.1 is used to configure controller 1 and the device. The device is marked as Shared Device and its modules are assigned.
In Codesys (V3.5 SP17 Patch 3 +) controller 2 and the devices are configured. The device is also marked as Shared Device. And here's the tricky part, which I need the guidance. Is there a way to assign the modules of the device to the controller 2?
So far I've looked through multiple options and didn't found anything. Even googling did not lead to any result.
Many thanks in advance!
Tobi
I've got it and there is no interface to assign the modules to a controller. The solution is to deactivate every module that is used by controller 1 (within Codesys) and let all the modules used by controller 2 active.