    Hello all.

    I am trying to bring a stepper drive online, and it seems to be configured correctly, BUT I have the Orange triangle near it, and the diagnostic screen says "register session at the adapter"

     
  • dhumphries - 2024-02-03

    Make sure the O->T and T->O bytes required by the remote device match the configuration in Codesys. Most of the EDS files I've imported have not worked by default. See the attached images for the connections and assemblies tabs. Note that the connections are in Bytes and the assemblies are in bits, you have to have enough bits to equal the bytes. Either mismatch will give a red/orange triangle.

    Page 343 of the manual (assuming the STF10-IP is an applied motion microstep driver) has some recommended connection settings, you should be able to confirm the input and output bits somehow, some devices have a web GUI, some require a software tool.

     

    Last edit: dhumphries 2024-02-03