Ethercat SDO

davolm
2010-11-30
2010-12-01
  • davolm - 2010-11-30

    Hi,

    I'm tryng to read some objects by SDO from a EK1100, I'm using the ETC_CO_SDOREAD without success every time the eError return a timeout, I have tried with different objects found in the xml file without success. The communication with the device works fine I can read and write inputs and outputs.
    The Codesys version I'm using is the 3.4 sp1 and the target is a RTE 3.4.1

    Anyone can help me?

    Thanks

    Davide

     
  • spfeif - 2010-11-30

    Although I don't know EtherCat or the FB in question (I know CANopen) I would still like to make one remark. If there is an enable input to the FB you may have to keep it enabled until you receive a response otherwise you terminate the SDO READ FB prematurely and the FB aborts. What is the SDO abort message data/code? You should have 8 data bytes from the abort message.

     
  • davolm - 2010-12-01

    Hi,

    I keep the xExecute enable till the error message is showedt. You can check the FB status in the attached image.

    Thanks.

    IMG: codesys.JPG

     
  • davolm - 2010-12-01

    Hi,

    I'm sorry if someone lost time about this topic, I discovered that the EK1100 doesn't support COE message.

     