Codesys OPC UA not working?

dutchplc
2022-09-19
2022-09-20
  • dutchplc - 2022-09-19

    I'm currently using Codesys 3.5 SP 18 on an Wago PFC200 (750-8212). In the WBM I turned the Wago OPC UA server off. I make a GVL and Symbol Configuration and exported the GVL.

    When using Prosys OPC UA Client to check for the variables I only see DeviceSet -> CODESYS Control for PFC200 SL -> Resources but no underlaying GVL or variables.

    What goes wrong?

     
  • ndzied2 - 2022-09-19

    You say that you turned the OPC/UA server off. I would think that you have to have the OPC/UA server on to be able to reach it from the client....

     

    Last edit: ndzied2 2022-09-19
  • eschwellinger

    eschwellinger - 2022-09-19

    no there is an OPC UA server embedded in the CODESYS Runtime, therefore it must be turned off.

     
  • dutchplc - 2022-09-20

    The internal one on the Wago page is not the Codesys OPC UA server right?

    How is it possible I don't see any Symbols?

     
  • dutchplc - 2022-09-20

    I have deleted the Symbol Manager and added a new one and now it works.

     