Hello,
I try to exchange datas between CodeSys SoftPLC (x64) on my PC and an TM241 (real) using EtherNet/IP .
Soft PLC is the scanner and TM241 has an adapter . I use the TM241_generic.EDS.
For each PLC , connexion is OK but no datas are exchanged and i don't understand why !
I have the last version of codesys and SoMachine V4.3 .
Any idea ?
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,
I try to exchange datas between CodeSys SoftPLC (x64) on my PC and an TM241 (real) using EtherNet/IP .
Soft PLC is the scanner and TM241 has an adapter . I use the TM241_generic.EDS.
For each PLC , connexion is OK but no datas are exchanged and i don't understand why !
I have the last version of codesys and SoMachine V4.3 .
Any idea ?
Try the drop-down "always update variables in bus cycle task" on the IO mapping page
Thanks i_Campbell , it's working :-)