Scanner EtherNet/IP with TM241

pach30
2020-07-01
2020-07-01
  • pach30 - 2020-07-01

    Hello,
    I try to exchange datas between CodeSys SoftPLC (x64) on my PC and an TM241 (real) using EtherNet/IP .
    Soft PLC is the scanner and TM241 has an adapter . I use the TM241_generic.EDS.
    For each PLC , connexion is OK but no datas are exchanged and i don't understand why !
    I have the last version of codesys and SoMachine V4.3 .
    Any idea ?

     
  • i-campbell

    i-campbell - 2020-07-01

    Try the drop-down "always update variables in bus cycle task" on the IO mapping page

     
    πŸ‘
    1
  • pach30 - 2020-07-01

    Thanks i_Campbell , it's working :-)

     