I have set up a simple project using the CIFX Ethernet/IP Scanner device and soft PLC device. The project builds without issue. When I go to download I get 24 unresolved references. See attachment for snippet of Messages. What is missing? Thanks!
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I have set up a simple project using the CIFX Ethernet/IP Scanner device and soft PLC device. The project builds without issue. When I go to download I get 24 unresolved references. See attachment for snippet of Messages. What is missing? Thanks!
Hi,
which plc do you want to use?
BR
Edwin
I am using the CODESYS V3 Soft-PLC for Windows with non real-time capabilities
You need to add 1. ethernet connector then 2. EIP scanner not the Cifx based card.. this needs additional hardware in you pc.
BR
Edwin