Ethernet/IP issue

Suro
2016-08-05
2016-08-05
  • Suro - 2016-08-05

    Hi,
    I'm trying to make a connection via ethernet/ip, but there is something wrong. Ethernet/IP scanner is running in demo mode (yellow icon and status about running in demo mode), but adapter is not working at all (red triangle). In I/O mapping of the adapter I have a warning "The bus is not running. The shown values might not be up-to-date).

    Does anybody know how to fix it?

     
  • eschwellinger

    eschwellinger - 2016-08-05

    Hi,
    which plc are you using (and which manufacturer)
    BR
    Edwin

     
  • Suro - 2016-08-05

    Problem solved. I had to turn on slave device. I was mistaken by collegue, who said that to test protocol I don't need to turn on all devices (scanner only).|

    Thanks for your reply

     

Log in to post a comment.