Codesys control -> Festo CPX-E-PN

qdeyna
2020-03-02
2020-03-04
  • qdeyna - 2020-03-02

    Hi everyone!

    I have some issues on connecting codesys control win x64 to Profinet slave (Festo CPX-E-PN).

    I had already installed Winpcap, set the firewall (I can see everyone send packet on wireshark) and set my ip correctly.

    But for now, nothing is working... When i start "scan device" on th PN_Controller it start and run indefinitely without finding anything.
    When I start FMT (festo Maintenance Tool) this one see the Profinet slave and I can manage the I/O as I want. So I think the problem is on my codesys configuration.

    The configuration :

    Codesys control win x64 -> Ethernet device -> PN_Controller -> Festo CPX-E-PN -> CPX-E-4AI-U-I

    I had see a lot of subject on the forum with this kind of problem and for a lot of them it came from winpcap & firewall config.
    But as I had already check this and it's it steel not working I'm asking your help.

    Thanks for your time !

    Quentin

     

    Last edit: qdeyna 2020-03-02
  • eschwellinger

    eschwellinger - 2020-03-02

    Hi,
    check the following:
    Is WinPcap installed?
    turn off the firewall
    check the plclogger of control win
    an finally - which version exactly are you using?

    BR
    Edwin

     
  • qdeyna - 2020-03-02

    Hi Edwin ! thanks for your fast reply !

    so I think WinPcap is good :

    The firewall is off and below the plclogger on codesys (How can i see the plclogger of control win since this one start on the menu bar now?)

    I'm using Codesys V3.5 SP15 patch 3 and control win systray - x64

    Thanks again !

     

    Last edit: qdeyna 2020-03-02
  • qdeyna - 2020-03-04

    Hi Edwin!

    First, I need to apologize... I understand what I had missed on my configuration and why it was not working and also my lack of training...

    So, the "problem" is that I didn't set the PN_Controller.CommCycle in the task manager. I had the possiblity to see the pn_controller and the profinet fieldbus module (cpx_e_pn) but when I hit the scan nothing happened.

    In the log I had the error : "CommCycle() is not executed ! Check Task Configuration !" and this helped me a lot!

    I just need to had a task with PN_Controller.CommCycle and everything is fine now !

    So thank you again and have a good day !

     
    πŸ‘
    1

Log in to post a comment.