Profinet not working on WAGO 750-8212 "Opening Ethernet Adapter Failed"

2023-02-10
2023-02-11
  • a-times-three - 2023-02-10

    I'm working on a project where I want to have the following:

    • WAGO 750-8212 as controller
    • WAGO 750-340 as device
    • Raspberry Pi 4 as device

    All devices are on the same local network and I've set static IP-s for the devices. However in Codesys V3.5 SP18 Patch 4, I can't seem to get the Profinet controller to activate when put into run:

    I have the following error message(s):

    WinPcap is already installed (5.1.72.1206) so this thread is to no use. https://forge.codesys.com/forge/talk/Engineering/thread/4dee464d00/

    Is there anything else I can do to make this work?

     
  • eschwellinger

    eschwellinger - 2023-02-10

    seperate the ethernet interfaces (wbm) on PFC200 use the br1 on the controller

     

    Last edit: eschwellinger 2023-02-10
  • a-times-three - 2023-02-10

    Do you mean like this?
    I'm still getting the same error..

     
  • eschwellinger

    eschwellinger - 2023-02-11

    Hi,
    for me it works that way on br1 and with separated interfaces.
    If you let CODESYS change the IP Adress you need additional:

    [SysSocket]
    Adapter.0.Name="br1"
    Adapter.0.EnableSetIpAndMask=1

    added in /etc/CODESYSControl_Usr.cfg ( then you could enable the setting 'Adjust operating system setting'

     

Log in to post a comment.