CONFIRMED WORKING:
PLC1/PLC2 identification configured via IDE
Connection IP configured via IDE
AutoSync enabled and written via IDE
Normal Active/Standby operation working
Server 2 auto-promotes when Server 1 completely fails
PROBLEM DESCRIPTION:
When NIC1 cable is removed from Server 1 β both servers
go to standalone mode.
When NIC1 cable is reconnected β both servers remain in
standalone indefinitely. Neither server auto-recovers to
Active/Standby without manual CODESYS service restart.
AutoSync fires (!!! Autosync !!! visible in log) but
recovery does not complete.
Tested with direct cable (no NIC team) β same result.
Confirmed not a hardware or NIC teaming issue.
KEY LOG MESSAGES:
"Timeout: No sync message RMSG_StartCycle (5)
from master: Standalone"
"Socket on other side closed gracefully 0"
"Standby PLC: Open acyclic work socket failed"
"Connection broke after 11806ms. Check BootupWaitTime."
Autosync(fires but does not complete recovery)
PCAP ANALYSIS (Wireshark):
CODESYS sync stops completely at T+3s
Server 1 sends TCP FIN on ports 1206 and 1208 at T+5s
No CODESYS redundancy traffic for remaining 24 seconds
Both servers stay standalone indefinitely
WHAT WE HAVE TRIED:
StandbyWaitTime = 12100ms
SynchronousTimeout = 12100ms
WatchdogTime = 12000ms (less than StandbyWaitTime)
AutoSync enabled
NIC2 set as Standby adapter
Disabled Windows Network Discovery
Direct cable test β rules out NIC hardware
QUESTION:
Per official CODESYS documentation: "No automatic
Reconnect is included in the functional scope of the
redundancy components. You can program the triggering
of a reconnect."
Is RDCY.Synchronize() the correct function to add to
our application for automatic recovery after both PLCs
go standalone?
What is preventing auto-recovery when AutoSync is
enabled and PlcIdent is correctly set?
Thank you for your support.
Last edit: pra83 1 hour ago
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,
We are facing a critical issue with CODESYS
SoftRedundancy that we have been unable to resolve despite
extensive troubleshooting.
HARDWARE:
2Γ HP EliteDesk 800 G9 SFF
Intel Core i7-14700 (20 cores)
16GB RAM, 512GB NVMe SSD
Windows 11 IoT Enterprise LTSC 2024
NIC1: Built-in Intel GbE
NIC2: Intel I210-T1 PCIe (NIC team)
SOFTWARE:
CODESYS Control Win V3 - x64 Version 3.5.22.10
CODESYS SoftRedundancy SL
Server 1 IP: 172.10.10.101 (PLC1 β Active)
Server 2 IP: 172.10.10.102 (PLC2 β Standby)
CURRENT CODESYSControl.cfg:
[CmpRedundancy]
BootupWaitTime=120000
StandbyWaitTime=12100
SynchronousTimeout=12100
[CmpSchedule]
ProcessorLoad.Maximum=80
WatchdogTime=12000
WatchdogTimeoutAction=0
CONFIRMED WORKING:
PLC1/PLC2 identification configured via IDE
Connection IP configured via IDE
AutoSync enabled and written via IDE
Normal Active/Standby operation working
Server 2 auto-promotes when Server 1 completely fails
PROBLEM DESCRIPTION:
When NIC1 cable is removed from Server 1 β both servers
go to standalone mode.
When NIC1 cable is reconnected β both servers remain in
standalone indefinitely. Neither server auto-recovers to
Active/Standby without manual CODESYS service restart.
AutoSync fires (!!! Autosync !!! visible in log) but
recovery does not complete.
Tested with direct cable (no NIC team) β same result.
Confirmed not a hardware or NIC teaming issue.
KEY LOG MESSAGES:
"Timeout: No sync message RMSG_StartCycle (5)
from master: Standalone"
"Socket on other side closed gracefully 0"
"Standby PLC: Open acyclic work socket failed"
"Connection broke after 11806ms. Check BootupWaitTime."
Autosync(fires but does not complete recovery)
PCAP ANALYSIS (Wireshark):
CODESYS sync stops completely at T+3s
Server 1 sends TCP FIN on ports 1206 and 1208 at T+5s
No CODESYS redundancy traffic for remaining 24 seconds
Both servers stay standalone indefinitely
WHAT WE HAVE TRIED:
StandbyWaitTime = 12100ms
SynchronousTimeout = 12100ms
WatchdogTime = 12000ms (less than StandbyWaitTime)
AutoSync enabled
NIC2 set as Standby adapter
Disabled Windows Network Discovery
Direct cable test β rules out NIC hardware
QUESTION:
Per official CODESYS documentation: "No automatic
Reconnect is included in the functional scope of the
redundancy components. You can program the triggering
of a reconnect."
Is RDCY.Synchronize() the correct function to add to
our application for automatic recovery after both PLCs
go standalone?
What is preventing auto-recovery when AutoSync is
enabled and PlcIdent is correctly set?
Thank you for your support.