Hello,we bought a package of licenses to work with Linux ARM SL System, Runtime is successfully licensed, but Profinet does not.
The [0] soft container is empty.
The [1] soft container on the screen below!
P.S This configuratin works well on IOT2040 SIMATIC, but on Linux ARM not. Setting (e.g Device name is correct, physical connection also without any problems).
Thanks.
check in the library manager if codemeter library is used and resolved.
(and additional check if you are current Profinet version - by CODESYS installer - any updates available according the wrong IO_link license message in the log))
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Helped command "reload" in "PLC Shell".
But when power is lost, it again cannot find the license. As if starting a service is missing something.
p.s waited about 10 mins
Last edit: sanya0971 2022-09-09
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello,we bought a package of licenses to work with Linux ARM SL System, Runtime is successfully licensed, but Profinet does not.
The [0] soft container is empty.
The [1] soft container on the screen below!
P.S This configuratin works well on IOT2040 SIMATIC, but on Linux ARM not. Setting (e.g Device name is correct, physical connection also without any problems).
Thanks.
check in the library manager if codemeter library is used and resolved.
(and additional check if you are current Profinet version - by CODESYS installer - any updates available according the wrong IO_link license message in the log))
Helped command "reload" in "PLC Shell".
But when power is lost, it again cannot find the license. As if starting a service is missing something.
p.s waited about 10 mins
Last edit: sanya0971 2022-09-09
Device Reader Screenshots.
Problem could be solved only with "PLC SHELL -> reload".
Codemeter lib resolved.
Any ideas how to fix this?
Last edit: sanya0971 2022-09-14
I think you need to resolve the codemeter library in the library manager here:
Unfortunatelly not helped!
This works only if CodeMeter Service starts before CodesysControl Service.
oh..this might be, then I would try to delay the runtime start a few seconds.
Problem Solved.
Gateway address of Linux PLC matched with WiFi))
So stupid.
Thanks for Help