Codesys ControlWinV3x64 with EtherCat Slave

russells
1 day ago
10 hours ago
  • russells - 1 day ago

    Hi there

    I am running Codesys ControlWinV3x64 (Patch 4) on my laptop for demonstration purposes but I am unable to get connection to the EtherCAT master and slave device.
    This is the process that I have followed:
    * Installed NPCap.
    * Added the xml file for the SMC slave device to the Device Repository.
    * Activated Control Win SysTray x64 and selected Start PLC.
    * Scanned the network for the local device (my laptop).
    * Added an EtherCAT master to the project and scanned the EtherCAT master for the Network and then selected the correct network.
    * Selected "Scan for devices" to identify the connected I/O.
    * Add the SMC EtherCAT slave manually because I was unable to scan it in.
    * Selected "Scan for devices".

    I have followed the steps described above but I can't scan in the EtherCAT slave or connect to it.

    I thought this situation was unique to the EtherCAT slave but I have also tried the same for an EtherNet/IP slave using the Ethernet Adaptor and EtherNet/IP scanner and I am also unable to scan in the device or activate the EtherNet/IP network.

    Any assistance will be appreciated.

     

    Last edit: russells 1 day ago
  • eschwellinger

    eschwellinger - 23 hours ago

    please check the plclog for more information. sounds like NPCap does not work.

     
    • russells - 10 hours ago

      Much thanks. I reinstalled NPCap and it is now working. Much thanks.

       